Like most At 34s I have a reverse polarity light on the shore power 1 AC panel. It was a red light so off was good.

With the boat out of water, I plugged into a standard outlet with a #16 extension cord, turn on AC power, and the light stayed off. I then turned on the salon strip heater, pulling about 10 amps and the light came on. Used a multimeter and apparently the shipyard outlet is wired correctly. Other times I plugged into a standard marine outlet with a 30 amp power cord and the light stayed off. Why is the light coming on now?
ghost0070 is offline   Reply With Quote
Old 11-21-2018, 03:57 PM   #2
Moderator Emeritus
 
Comodave's Avatar
 
City: Au Gres, MI
Vessel Name: Black Dog
Vessel Model: Formula 41PC
Join Date: Jul 2015
Posts: 21,186
I bought a 15 amp to 30 amp adapter (Marinco) and it was wired incorrectly and had neutral and ground switched inside the molded adapter. Sent it back and got a new one and it was ok. Check your adapter and extension cord and make sure they are wired correctly.
Comodave is online now   Reply With Quote
Old 11-21-2018, 04:01 PM   #3
Guru
 
City: Seaford Va on Poquoson River, VA
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 2,264
Maybe the salon strip heater has a ground fault. If it does and you use a GFCI extension cord, turning on the heater it will trip.
But if it is only coming on when using that plug, maybe that plug has a problem.

For that light to come on, power has to be flowing on the ground wire, and returning by way of the neutral, hence a ground fault exists causing the light to some on. The reverse polarity light is typically a tiny red neon bulb set between ground and neutral wires.
sdowney717 is offline   Reply With Quote
Old 11-21-2018, 08:37 PM   #4
Senior Member
 
Duvie's Avatar
 
Join Date: Nov 2011
Posts: 340
Just thinking out load.

Possibly if there were a poor connection or very long/under sized feed within the supplying neutral. This would cause a potential difference between ground and the neutral. The potential difference would rise as the current draw increases. That is why the light comes on as the current is increased by the strip heater.

Check voltage at the strip heater with it turned on. Check line to neutral and line to ground with the heater on. Guessing you may see a significant difference.
Duvie is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 12:57 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012