Outlet troubles

I have a 48 Californian and over the weekend I lost power to 4 A/C outlets, 2 in the dinette and 2 in the galley? The breaker did not kick and I have no idea what could have caused it. They are all on the same breaker labeled Galley outlets. Thursday they worked fine and yesterday evening they were not. Everything else in the galley and dinette area works fine both A/C and D/C. Any help with trouble shooting would be appreciated.
__________________
Advertisement

knotheadcharters is offline   Reply With Quote
Old 07-05-2014, 08:15 PM   #2
TF Site Team
 
Larry M's Avatar
 
City: JAX, FL
Country: USA
Vessel Name: Hobo
Vessel Model: Krogen 42-120
Join Date: Nov 2008
Posts: 5,720
They maybe gfis. Check each outlet and see if one needs to be reset.
__________________

Larry M is offline   Reply With Quote
Old 07-05-2014, 08:26 PM   #3
TF Site Team
 
dwhatty's Avatar
 
City: Home Port: Buck's Harbor, Maine
Country: USA
Vessel Name: "Emily Anne"
Vessel Model: 2001 Island Gypsy 32 Europa (Hull #146)
Join Date: Sep 2008
Posts: 2,730
Quote:
Originally Posted by Larry M View Post
They maybe gfis. Check each outlet and see if one needs to be reset.
X2. Happened to me. After starting to try to track down the problem with a multimeter, a little voice said "check the gfis" in the circuit. Bingo.
__________________
David Hawkins
Deer Isle, Maine
dwhatty is offline   Reply With Quote
Old 07-05-2014, 08:41 PM   #4
TF Site Team
 
FlyWright's Avatar
 
City: California Delta and SF Bay
Country: Sacramento, CA, USA (boat in Vallejo)
Vessel Name: FlyWright
Vessel Model: Marshall Californian 34 LRC
Join Date: Apr 2008
Posts: 10,162
GFI was my first thought, too. My Californian has daisy-chained outlets on a GFI circuit.
__________________
Al

Custom Google Trawler Forum Search
FlyWright is online now   Reply With Quote
Old 07-05-2014, 08:49 PM   #5
Senior Member
 
knotheadcharters's Avatar
 
City: Jacksonville, FL
Vessel Name: Amar la Vida
Vessel Model: 1989 Carver Californian 48' MY
Join Date: Jan 2011
Posts: 327
Yes, I have checked the GFCI, yes they are daisy-chained. If I replace the GFCI outlet that could possibly solve the problem.
knotheadcharters is offline   Reply With Quote
Old 07-05-2014, 09:41 PM   #6
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,422
Quote:
Originally Posted by knotheadcharters View Post
Yes, I have checked the GFCI, yes they are daisy-chained. If I replace the GFCI outlet that could possibly solve the problem.
Meter the first outlet inline and make sure it's really getting 120v to it before you start randomly replacing things.
Capt.Bill11 is offline   Reply With Quote
Old 07-05-2014, 09:46 PM   #7
Guru
 
City: Tuckerton, NJ
Country: USA
Vessel Name: WIRELESS ONE
Vessel Model: 36 Gulstar MarkII
Join Date: Mar 2011
Posts: 937
I agree the 1st oulet in-line should be the GFCI. Try re-setting it, some don't like inverters I believe Xantrex/ Freedom lists the GFCI's that will work with their faux non-sine wave units.
Bill
Billylll is offline   Reply With Quote
Old 07-06-2014, 10:21 AM   #8
Guru
 
High Wire's Avatar
 
City: Cape May, NJ and Englewood, FL
Country: USA
Vessel Name: Irish Lady
Join Date: Dec 2007
Posts: 1,596
Quote:
Originally Posted by Capt.Bill11 View Post
Meter the first outlet inline and make sure it's really getting 120v to it before you start randomly replacing things.
X2
If its not the GFCI than it has to be a poor connection or the breaker. Basically where the voltage stops is the problem.
__________________
Archie
1984 Monk 36 Hull #46
Englewood, FL and Cape May, NJ
High Wire is offline   Reply With Quote
Old 07-06-2014, 10:31 AM   #9
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,858
I have a few outlets that are my next project...

Anyone ever come across where you only have 1/2 voltage (60V or so) in a string of outlets?

I post this because the outlets act like they aren't working till you meter the voltage. May help the OP too.

Nothing wrong at the breakers...and of course getting to the boxes and wiring is more trouble than it's worth...I'll probably just redo the string as I'm redoing all the wiring anyhow...more curiosity than need of info...but a quick fix would be nice depending when I get to the rewiring.
psneeld is online now   Reply With Quote
Old 07-06-2014, 02:27 PM   #10
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,390
Quote:
Originally Posted by psneeld View Post
............. Anyone ever come across where you only have 1/2 voltage (60V or so) in a string of outlets?

I post this because the outlets act like they aren't working till you meter the voltage. ..........
Voltage readings without a load on the circuit are pretty meaningless. Plug in a lamp and I'll bet the voltage goes to zero.

Other than a tripped or defective GFCI receptacle, it can only be a loose or corroded connection somewhere.

If you can figure out in what order the receptacles are wired, check in the middle. That will tell you if the problem is in the first part of the circuit or the last.
rwidman is offline   Reply With Quote
Old 07-06-2014, 05:30 PM   #11
Senior Member
 
knotheadcharters's Avatar
 
City: Jacksonville, FL
Vessel Name: Amar la Vida
Vessel Model: 1989 Carver Californian 48' MY
Join Date: Jan 2011
Posts: 327
Ok checked the receptacles. All give a open neutral reading. I am a assuming a bad GFCI? I will get one tomorrow.
knotheadcharters is offline   Reply With Quote
Old 07-06-2014, 05:37 PM   #12
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,390
Quote:
Originally Posted by knotheadcharters View Post
Ok checked the receptacles. All give a open neutral reading. I am a assuming a bad GFCI? I will get one tomorrow.
I doubt it. Take the GFCI receptacle out of the circuit. Connect the incoming wires to the outgoing wires and see if you have power.

Or measure the voltage at the incoming (probably labelled "line") terminals of the GFCI receptacle. You should have 120 volts between the hot and neutral. If you measure this on the line side but not the side feeding the other outlets, the GFCI receptacle is defective (or just tripped).
rwidman is offline   Reply With Quote
Old 07-06-2014, 05:39 PM   #13
Senior Member
 
knotheadcharters's Avatar
 
City: Jacksonville, FL
Vessel Name: Amar la Vida
Vessel Model: 1989 Carver Californian 48' MY
Join Date: Jan 2011
Posts: 327
Thanks Ron, I'll try that tomorrow
knotheadcharters is offline   Reply With Quote
Old 07-06-2014, 07:47 PM   #14
Guru
 
City: Tuckerton, NJ
Country: USA
Vessel Name: WIRELESS ONE
Vessel Model: 36 Gulstar MarkII
Join Date: Mar 2011
Posts: 937
Quote:
Originally Posted by rwidman View Post
Voltage readings without a load on the circuit are pretty meaningless. Plug in a lamp and I'll bet the voltage goes to zero.

Other than a tripped or defective GFCI receptacle, it can only be a loose or corroded connection somewhere.

If you can figure out in what order the receptacles are wired, check in the middle. That will tell you if the problem is in the first part of the circuit or the last.
I agree Ron, AC voltage readings are pretty much meaningless unless you have no voltage otherwise a load is needed.
Bill
Billylll is offline   Reply With Quote
Old 07-08-2014, 02:03 PM   #15
Senior Member
 
knotheadcharters's Avatar
 
City: Jacksonville, FL
Vessel Name: Amar la Vida
Vessel Model: 1989 Carver Californian 48' MY
Join Date: Jan 2011
Posts: 327
Replaced the GFCI. All outlets back on line.
knotheadcharters is offline   Reply With Quote
Old 07-08-2014, 02:24 PM   #16
Moderator Emeritus
 
jwnall's Avatar
 
City: St. Marks, Florida
Country: US
Vessel Name: Morgan
Vessel Model: Gulfstar 36
Join Date: Sep 2012
Posts: 3,621
Quote:
Originally Posted by knotheadcharters View Post
Replaced the GFCI. All outlets back on line.
Great! "Occam's razor (also written as Ockham's razor and in Latin lex parsimoniae) is a principle of parsimony, economy, or succinctness used in problem-solving devised by William of Ockham (c. 1287–1347). It states that among competing hypotheses, the one with the fewest assumptions should be selected. Other, more complicated solutions may ultimately prove correct, but—in the absence of certainty—the fewer assumptions that are made, the better."
__________________

__________________
John
jwnall is offline   Reply With Quote
Reply

Tags
a/c power, galley, outlets

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 12:22 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012