Not sure what happened!
Wednesday I stepped on the boat and no power. My ELCI breaker had tripped and my inverter had a fault code. Reset the inverter and all seemed to work fine. Reset the ELCI and 5 seconds later it tripped. Turned every circuit breaker off and then reset the ELCI, 5 seconds and it tripped. I have a switch that bypasses the inverter, bypassed the inverter and reset the ELCI. ELCI held, until I threw the first breaker and then it tripped. Reset, tried different breakers same result, ELCI tripped. Desperation, disconnected every neutral on the neutral bus, reset the ELCI. I then jumped each neutral, one at a time. Got to the refrigerator and the ELIC tripped. Unplugged the refrigerator, reset the ELCI, turned on all the breakers and all was well. Examined the fridge, the compressor had a catastrophic neutral/ground failure which is why the ELIC was upset. Then i turned off the inverter bypass switch, this tripped the ELIC.
Today I tested every ac wire for continuity. There is no continuity between the neutral and ground wires. I did find some continuity between positive and ground (extremely high resistance). I traced this down to some corrosion on an outdoor outlet. Now I have no continuity between positive/ground or neutral/ground. A new refrigerator has been installed and the ELCI is happy until I try to add the inverter. The inverter is working fine except it trips the ECLI. The inverter and ELCI have worked together for 3 years until now.
So, did the inverter kill the fridge, did the fridge kill the inverter, did something else kill them both? Do I buy a new inverter or is there a test i’ve Missed. The inverter is showing some resistance between ground and neutral but since I can only test it disconnect from shore power I don’t know if that’s normal.
|
|
|
08-18-2019, 04:30 AM
|
#2
|
Guru
City: Solomons, MD
Vessel Name: Branwen
Vessel Model: Hatteras 48 LRC
Join Date: Feb 2015
Posts: 645
|
Thanks for the topic and your thorough description of what you've done to troubleshoot. I regret that I can't help but thankful that I'm likely to learn something.
|
|
|
08-18-2019, 05:31 AM
|
#3
|
Guru
City: Vermont
Join Date: Jan 2013
Posts: 10,076
|
What resistance are you measuring between neutral and ground on the inverter? It may be enough to trip the ELCI.
__________________
MVTanglewood.com
|
|
|
08-18-2019, 06:35 AM
|
#4
|
Guru
City: Fort Myers, FL... Summers in the Great Lakes
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 12,818
|
Check the grounding of the inverter and whether it's tied to the hull bonding system.
Ted
__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
|
|
|
08-18-2019, 08:20 AM
|
#5
|
Guru
City: East Coast, Australia
Join Date: Jun 2012
Posts: 935
|
Quote:
Originally Posted by tiltrider1
Wednesday I stepped on the boat and no power. My ELCI breaker had tripped and my inverter had a fault code. Reset the inverter and all seemed to work fine. Reset the ELCI and 5 seconds later it tripped. Turned every circuit breaker off and then reset the ELCI, 5 seconds and it tripped. I have a switch that bypasses the inverter, bypassed the inverter and reset the ELCI. ELCI held, until I threw the first breaker and then it tripped. Reset, tried different breakers same result, ELCI tripped. Desperation, disconnected every neutral on the neutral bus, reset the ELCI. I then jumped each neutral, one at a time. Got to the refrigerator and the ELIC tripped. Unplugged the refrigerator, reset the ELCI, turned on all the breakers and all was well. Examined the fridge, the compressor had a catastrophic neutral/ground failure which is why the ELIC was upset. Then i turned off the inverter bypass switch, this tripped the ELIC.
Today I tested every ac wire for continuity. There is no continuity between the neutral and ground wires. I did find some continuity between positive and ground (extremely high resistance). I traced this down to some corrosion on an outdoor outlet. Now I have no continuity between positive/ground or neutral/ground. A new refrigerator has been installed and the ELCI is happy until I try to add the inverter. The inverter is working fine except it trips the ECLI. The inverter and ELCI have worked together for 3 years until now.
So, did the inverter kill the fridge, did the fridge kill the inverter, did something else kill them both? Do I buy a new inverter or is there a test i’ve Missed. The inverter is showing some resistance between ground and neutral but since I can only test it disconnect from shore power I don’t know if that’s normal.
|
The ELCI itself could now be faulty, tripping too easily.
|
|
|
08-18-2019, 08:46 AM
|
#6
|
Guru
City: East Coast
Vessel Name: M/V Maerin (Sold)
Vessel Model: Solo 4303
Join Date: Jun 2013
Posts: 886
|
You might also confirm that all the neutral connections for circuits powered by the inverter are connected to a buss that connects to the inverter's output neutral. If any are commingled, it can easily cause an ELCI trip. No issues whatever on a non-ELCI connection. Don't overlook pilot lamp neutrals, they count, too. A pilot LED for a 120V circuit powered by the inverter will function regardless of which neutral it's connected to. They only draw a couple of mils, but it's cumulative. A handful of LED's with crossed neutrals can be enough to hit the ELCI threshold. Some inverters are slow on the draw when they transfer the neutral-ground bond, my Magnum sometimes trips an ELCI when applying shore power and that relay is energized. Not always, it seems to depend on the ELCI, but it's a potential contributor. I turn off the inverter via the remote panel before connecting, that seems to help.
Not sure if it's relevant since it appears your ELCI is on board, but I've found that when connecting to an ELCI it helps to start with all breakers "OFF" and bring them online incrementally.
|
|
|
08-18-2019, 09:09 AM
|
#7
|
Guru
City: Seaford Va on Poquoson River, VA
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 2,264
|
I would suspect the inverter is starting to leak current somewhere inside its circuits. The mosfets in those things run on the ragged edge. Or might be a soldering fault, some component is leaking current to ground, since its ac is turning off the ELCI, must be leaking on the AC side of the inverter, even into the DC side of things.
Maybe you can test your inverter on a GFCI circuit isolated from the rest of the boat wiring.
Ground and neutral are joined in a FSW marine inverter usually, but not in a MSW inverter. When off I would think the neutral ground bond should read zero ohms, and you say you have resistance..some use an internal relay, these things are done differently by different companies. So maybe something going on with the switch over, whatever you have, I dont know how its done in your setup..how you have it wired into your boat.
Inverter is like any other AC power source, both neutral and hot must be disconnected together, when not in use.
|
|
|
08-18-2019, 09:24 AM
|
#8
|
Guru
City: Seaford Va on Poquoson River, VA
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 2,264
|
Another thing, the cheaper MSW inverters, you can not ground the neutral or the inverter gets damaged.
They put power out on both neutral and hot wires at half the voltage so about 60 vac on neutral and 60vac on hot, you had a serious neutral to ground short, so maybe it fried it, if thats the type you got.
Quote:
Examined the fridge, the compressor had a catastrophic neutral/ground failure which is why the ELIC was upset. Then i turned off the inverter bypass switch, this tripped the ELIC.
|
I have a msw 3000 watt inverter wired into my boats AC system and so far its been ok, but I do worry about the neutral ground short issue.
AFAIK, these type inverters measure overloads between hot and neutral and shutdown safely, but the neutral-ground short seems to be a problem at least in the manuals they talk about it.
|
|
|
08-18-2019, 09:39 AM
|
#9
|
Guru
City: Sea of Cortez, Mexico
Vessel Name: Irene
Vessel Model: Nordhavn 40II
Join Date: Jan 2016
Posts: 1,234
|
I will be watching and (hopefully) absorbing closely.
We tripped the ELCI at the newly-installed Friday Harbor G dock.
My electrician found continuity between neutral and ground in two circuits; a Webasto DBW 2010 furnace, and the main exhaust shroud blower. Coincidentally, both of those things have 12VDC and 110VAC parts. The Webasto is 12 VDC but the blowers are 110VAC, and the shroud blower is controlled via relay to the main engine ignition (hope I got that right). Unfortunately, he didn’t want to continue the diagnosis and finish the job. Furthermore, the wires on my multimeter know more about AC electricity than I do.
I have received a recommendation for a suitable electrician by Sunchaser, but have not had an opportunity to align that electrician and the location of the boat, yet.
__________________
Jeff
MV IRENE
|
|
|
08-18-2019, 10:50 AM
|
#10
|
Guru
City: Gulf Islands, BC Canada
Vessel Name: Sea Sanctuary
Vessel Model: Bayliner 4588
Join Date: Jul 2019
Posts: 4,993
|
The inverter bonds neutral & ground once the shore power is removed and disconnects when shore power is applied.
I am going to suggest that the inverter is not disconnecting the neutral/ground bond and thus your ELCI trips.
Test out by disconnecting the inverter ground feed to the bus bar.
|
|
|
08-19-2019, 06:21 PM
|
#11
|
Guru
City: Seattle
Vessel Name: AZZURRA
Vessel Model: Ocean Alexander 54
Join Date: Aug 2017
Posts: 4,281
|
More information. There is no continuity between neutral/ground or positive/ground in any of the boats wiring, including the wires to the inverter. This is supported by a properly functioning ECLI breaker and multimeter testing.
The inverter which is disconnected from both the DC source and the AC source, shows no continuity between neutral and ground but shows near short level of continuity between positive and ground. This I suspect is my issue but I don’t know if this is a valid test as I don’t know what would be expected from an inverter that has neither DC nor AC connected to it. I could buy a new $2,000 inverter and try it but i’ll Feel real dumb if that doesn’t solve the problem.
|
|
|
08-19-2019, 06:27 PM
|
#12
|
Moderator Emeritus
City: Au Gres, MI
Vessel Name: Black Dog
Vessel Model: Formula 41PC
Join Date: Jul 2015
Posts: 21,131
|
When you say positive and ground do you mean between hot a/c and ground. In a/c there isn’t a positive. There is a positive in dc. It could be confusing.
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you aren’t one, there is no explanation possible.
|
|
|
08-19-2019, 06:34 PM
|
#13
|
Guru
City: Seattle
Vessel Name: AZZURRA
Vessel Model: Ocean Alexander 54
Join Date: Aug 2017
Posts: 4,281
|
Quote:
Originally Posted by Comodave
When you say positive and ground do you mean between hot a/c and ground. In a/c there isn’t a positive. There is a positive in dc. It could be confusing.
|
You are correct, I mean hot a/c.
|
|
|
08-19-2019, 06:34 PM
|
#14
|
Guru
City: Gulf Islands, BC Canada
Vessel Name: Sea Sanctuary
Vessel Model: Bayliner 4588
Join Date: Jul 2019
Posts: 4,993
|
Quote:
Originally Posted by tiltrider1
More information. There is no continuity between neutral/ground or positive/ground in any of the boats wiring, including the wires to the inverter. This is supported by a properly functioning ECLI breaker and multimeter testing.
The inverter which is disconnected from both the DC source and the AC source, shows no continuity between neutral and ground but shows near short level of continuity between positive and ground. This I suspect is my issue but I don’t know if this is a valid test as I don’t know what would be expected from an inverter that has neither DC nor AC connected to it. I could buy a new $2,000 inverter and try it but i’ll Feel real dumb if that doesn’t solve the problem.
|
you need to check inverter in inverter mode trying to supply power. That is when ground and neutral are supposed to be bonded.
When AC shore power is applied to inverter it is supposed to release that bond. It will be the AC from inverter to load that should be bonded when in inverter mode only.
With the GFI doing its job it makes it difficult to run tests. Can't remember if you tried all load off and turn on Shore AC to inverter putting it into charging mode and does it still trip GFI.
|
|
|
08-19-2019, 06:39 PM
|
#15
|
Moderator Emeritus
City: Au Gres, MI
Vessel Name: Black Dog
Vessel Model: Formula 41PC
Join Date: Jul 2015
Posts: 21,131
|
I recall some people having a timing issue with some inverters that didn’t break the neutral and ground connection in time to stop the ELCI from tripping.
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you aren’t one, there is no explanation possible.
|
|
|
08-19-2019, 06:51 PM
|
#16
|
Guru
City: Gulf Islands, BC Canada
Vessel Name: Sea Sanctuary
Vessel Model: Bayliner 4588
Join Date: Jul 2019
Posts: 4,993
|
Quote:
Originally Posted by Comodave
I recall some people having a timing issue with some inverters that didn’t break the neutral and ground connection in time to stop the ELCI from tripping.
|
agree, but if working right should reset by the time the breaker is turned back on?
Also some boats had negative and AC ground bonded. He says there is a leak from hot to ground could be enough to trip GFI / ELCI.
|
|
|
08-19-2019, 06:55 PM
|
#17
|
Moderator Emeritus
City: Au Gres, MI
Vessel Name: Black Dog
Vessel Model: Formula 41PC
Join Date: Jul 2015
Posts: 21,131
|
Yes a leak from hot to ground can easily trip it. If they are individual breakers for each slip they are 30 mAmps. If they do a whole dock they are 100 mAmp but you are sharing that 100 mAmps with everyone on the dock.
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you aren’t one, there is no explanation possible.
|
|
|
08-19-2019, 06:57 PM
|
#18
|
Moderator Emeritus
City: Au Gres, MI
Vessel Name: Black Dog
Vessel Model: Formula 41PC
Join Date: Jul 2015
Posts: 21,131
|
Also, since you have a couple of issues going on, you may have had a power hit that damaged the inverter and the refer. Maybe it damaged the inverters timing circuit so it isn’t switching in time.
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you aren’t one, there is no explanation possible.
|
|
|
08-19-2019, 07:34 PM
|
#19
|
Guru
City: Seattle
Vessel Name: AZZURRA
Vessel Model: Ocean Alexander 54
Join Date: Aug 2017
Posts: 4,281
|
The ELCI breaker is on the boat so not a dock issue. I have no idea how you would do a continuity test on a powered up inverter. I am hopping the inverter is damaged as that would answer all the questions as to why it used to work and now it doesn’t. My amp clamp is one digit short of giving me a useful answer on current loss.
Since no one else on the dock has issues and since the pedestal breaker was not tripped i’m Thinking either the fridge or the inverter pulled a murder suicide on me.
|
|
|
08-19-2019, 07:37 PM
|
#20
|
Moderator Emeritus
City: Au Gres, MI
Vessel Name: Black Dog
Vessel Model: Formula 41PC
Join Date: Jul 2015
Posts: 21,131
|
Ok, that sounds like what happened.
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you aren’t one, there is no explanation possible.
|
|
|
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Trawler Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|