Isolation Transformer shorted out?

Help!
Yesterday the circuit breaker on the dock popped. Through a process of elimination, it appears the Charles Industries isolation transformer is the cause.
This has been in the system, working fine for over ten years. There are no moving parts. Has anyone heard of these shorting out?
Still waiting for Charles Ind. to respond...
Thx.
Duncan
__________________
Advertisement

Turning Point is offline   Reply With Quote
Old 10-30-2019, 01:14 PM   #2
Guru
 
City: Fairport
Country: United States
Join Date: Jan 2017
Posts: 1,693
Ground fault or actual overcurrent?
__________________

diver dave is online now   Reply With Quote
Old 10-30-2019, 01:20 PM   #3
Veteran Member
 
Turning Point's Avatar
 
City: Anacortes
Country: USA
Vessel Name: Turning Point
Vessel Model: 67’ Ed Monk Pilothouse Trawler
Join Date: Aug 2019
Posts: 25
Ground fault, not inrush. I disconnected the output leads and it still pops immediately. When I initially disconnected the input leads, everything was fine, so it’s not the cord, plug or faulty circuit breaker.
(Old school shorepower, no GFI)
Turning Point is offline   Reply With Quote
Old 10-30-2019, 01:44 PM   #4
Guru
 
Xsbank's Avatar
 
City: Pender Harbour, BC
Country: Canada
Vessel Name: Gwaii Haanas
Vessel Model: Custom Aluminum 52
Join Date: Sep 2013
Posts: 3,246
I had a Westinghouse or a GE isolation transformer (forgotten) and it gave up the ghost after about 15 years. I think its partly because we tend to spec the smallest we can get away with (cheaper) instead of a larger unit and then heat becomes the issue.
__________________
Don't believe everything that you think.
Xsbank is offline   Reply With Quote
Old 10-30-2019, 01:56 PM   #5
Guru
 
City: Fairport
Country: United States
Join Date: Jan 2017
Posts: 1,693
Yes, likely an insulation failure. The best diagnostic instrument is the Fluke 1503, which I have 6 feet away. But, with no output connected, and it trips out a 30 or 50 Amp breaker, I think that is all the real test you need. It's bad....
Most of the intrinsic value is copper, not iron, so rewinding is likely not a consideration.
diver dave is online now   Reply With Quote
Old 10-30-2019, 01:56 PM   #6
Veteran Member
 
Turning Point's Avatar
 
City: Anacortes
Country: USA
Vessel Name: Turning Point
Vessel Model: 67’ Ed Monk Pilothouse Trawler
Join Date: Aug 2019
Posts: 25
Thanks Xsbank,
I don’t think it was overloaded. It’s a robust (235 lb.) unit rated for 50Amps. I remember it getting lukewarm at most. I’m curious how yours failed....did it short out or ?
Turning Point is offline   Reply With Quote
Old 10-30-2019, 02:03 PM   #7
Senior Member
 
gsholz's Avatar
 
City: PDX
Country: Northwest
Vessel Name: Lady Anne
Vessel Model: GB 52 Europa
Join Date: Nov 2016
Posts: 265
I'd check the incoming ground wire and connections. It should be connected to the internal shield of the isolation transformer (not the output ground of the transformer). Measure resistance of the incoming ground to the incoming power wires (with shore power disconnected of course). If the short is truly internal to the transformer, it would need to be replaced.
gsholz is online now   Reply With Quote
Old 10-30-2019, 02:12 PM   #8
Veteran Member
 
Turning Point's Avatar
 
City: Anacortes
Country: USA
Vessel Name: Turning Point
Vessel Model: 67’ Ed Monk Pilothouse Trawler
Join Date: Aug 2019
Posts: 25
Quote:
Originally Posted by diver dave View Post
Yes, likely an insulation failure. The best diagnostic instrument is the Fluke 1503, which I have 6 feet away. But, with no output connected, and it trips out a 30 or 50 Amp breaker, I think that is all the real test you need. It's bad....
Most of the intrinsic value is copper, not iron, so rewinding is likely not a consideration.
Thanks Diver Dave,
Iím still in the grieving process here. I just started shopping for a replacement 😳
Iíve had drug habits cheaper than this!
Turning Point is offline   Reply With Quote
Old 10-30-2019, 03:30 PM   #9
Guru
 
angus99's Avatar
 
City: Signal Mtn., TN
Country: US
Vessel Name: Stella Maris
Vessel Model: Defever 44
Join Date: Feb 2012
Posts: 2,153
Quote:
Originally Posted by Turning Point View Post
Thanks Diver Dave,
Iím still in the grieving process here. I just started shopping for a replacement 😳
Iíve had drug habits cheaper than this!
Try calling Charles, if you havenít already, to see if they can suggest a cause. I was told by an ABYC electrician who installed many of these units that they donít often fail but a replaceable circuit board is often the cause when they do. Please post what you learn.
angus99 is offline   Reply With Quote
Old 10-30-2019, 05:26 PM   #10
Veteran Member
 
Turning Point's Avatar
 
City: Anacortes
Country: USA
Vessel Name: Turning Point
Vessel Model: 67’ Ed Monk Pilothouse Trawler
Join Date: Aug 2019
Posts: 25
Angus99,
I just got off the phone with a great guy in customer support. After my description, it sounds dead to him. He said a bench test with a “variac “ (sp)
could confirm it but doesn’t look good.
BTW: this is an older unit with no circuit board, basically just a big copper coil.
Turning Point is offline   Reply With Quote
Old 10-30-2019, 08:50 PM   #11
Guru
 
syjos's Avatar
 
City: Gig Harbor
Country: USA
Vessel Name: Sandpiper
Vessel Model: Bluewater 40 Pilothouse Trawler
Join Date: Nov 2012
Posts: 830
I sold Charles isolation transformers for over 10 years. I stopped selling it a few years ago because of too many warranty issues and news that Charles is discontinuing production soon.

The transformer is held in the case with a rubber like potting material, no fasteners. The potting material does not go all the way down to the bottom. There is a 2 or 3 inch space at the bottom. Heat causes the potting material to come loose from the case and the transformer drops sometimes breaking wires.

Also had issues with the transformer quitting shortly after installation and received a few with low output voltage.

I now sell the Victron Energy isolation transformers. They don't have a 50 amp unit yet but the 30 amp manual transformer is less than $700
syjos is online now   Reply With Quote
Old 10-30-2019, 09:06 PM   #12
Veteran Member
 
Turning Point's Avatar
 
City: Anacortes
Country: USA
Vessel Name: Turning Point
Vessel Model: 67’ Ed Monk Pilothouse Trawler
Join Date: Aug 2019
Posts: 25
Quote:
Originally Posted by syjos View Post
I sold Charles isolation transformers for over 10 years. I stopped selling it a few years ago because of too many warranty issues and news that Charles is discontinuing production soon.

The transformer is held in the case with a rubber like potting material, no fasteners. The potting material does not go all the way down to the bottom. There is a 2 or 3 inch space at the bottom. Heat causes the potting material to come loose from the case and the transformer drops sometimes breaking wires.

Also had issues with the transformer quitting shortly after installation and received a few with low output voltage.

I now sell the Victron Energy isolation transformers. They don't have a 50 amp unit yet but the 30 amp manual transformer is less than $700
Thanks syjos,
Iím not sure what is going on. Charles support told me there is usually scorched electrical smell. I have none of that and this afternoon I bypassed the unit and shorepower is driving my inverter crazy. My shorepower is 240v but the wiring is suspect. Tomorrow I research that 🤞 That would be the cheapest cure.
Turning Point is offline   Reply With Quote
Old 10-30-2019, 10:15 PM   #13
Guru
 
Xsbank's Avatar
 
City: Pender Harbour, BC
Country: Canada
Vessel Name: Gwaii Haanas
Vessel Model: Custom Aluminum 52
Join Date: Sep 2013
Posts: 3,246
50 amps isn’t really very much - a heater or two, a/c, hot water tank, lighting, battery charger? It adds up pretty fast. If you add too much load the voltage drops and it starts to heat up, then the resistance rises...

When you are on your boat, all snug in the warmth, tied up at the dock, stick your volt meter in any 120 volt outlet and read the voltage. Anything below the voltage at the dock pedestal and you are overloaded. Unplug something.
__________________
Don't believe everything that you think.
Xsbank is offline   Reply With Quote
Old 10-30-2019, 10:50 PM   #14
Veteran Member
 
EngNate's Avatar
 
City: Vancouver Isl
Country: Canada
Vessel Name: Tenacious
Vessel Model: Uniflite 31 FB Sedan
Join Date: Feb 2019
Posts: 52
Acme Transformer General Purpose Encapsulated 15KVa, multi voltage in, 120/240 out, price about $1000 US. As good as any you'll get. Sorry the model# isn't handy, find it easy enough...
__________________
Experience develops good judgement, bad judgement develops experience
EngNate is offline   Reply With Quote
Old 10-31-2019, 08:31 AM   #15
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 4,949
Quote:
Originally Posted by EngNate View Post
Acme Transformer General Purpose Encapsulated 15KVa, multi voltage in, 120/240 out, price about $1000 US. As good as any you'll get. Sorry the model# isn't handy, find it easy enough...

And they now have models with the proper dual/isolated grounding for marine use. And don't be scared by the "Acme" name. It's quality stuff, not roadrunner junk, and now part of Hubbell.
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 10-31-2019, 11:17 AM   #16
Guru
 
syjos's Avatar
 
City: Gig Harbor
Country: USA
Vessel Name: Sandpiper
Vessel Model: Bluewater 40 Pilothouse Trawler
Join Date: Nov 2012
Posts: 830
Quote:
Originally Posted by twistedtree View Post
And they now have models with the proper dual/isolated grounding for marine use. And don't be scared by the "Acme" name. It's quality stuff, not roadrunner junk, and now part of Hubbell.
I had an Acme isolation transformer on the previous boat and it worked without issue for 14 years.

They need to be mounted on top of a rubber pad to isolate hum.
syjos is online now   Reply With Quote
Old 10-31-2019, 12:05 PM   #17
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 8,085
Quote:
Originally Posted by Turning Point View Post
Thanks syjos,
Iím not sure what is going on. Charles support told me there is usually scorched electrical smell. I have none of that and this afternoon I bypassed the unit and shorepower is driving my inverter crazy. My shorepower is 240v but the wiring is suspect. Tomorrow I research that �� That would be the cheapest cure.
I'd recommend you sort out why you're having dock power and inverter issues with IT bypassed. On most vessels, an onboard IT should ideally be in place to deal with dock wiring issues not boat wiring. Are the docks you're plugged into the new marina code GFIC setups?
sunchaser is offline   Reply With Quote
Old 10-31-2019, 01:02 PM   #18
Veteran Member
 
EngNate's Avatar
 
City: Vancouver Isl
Country: Canada
Vessel Name: Tenacious
Vessel Model: Uniflite 31 FB Sedan
Join Date: Feb 2019
Posts: 52
A failed transformer may not have smell or visual indications. In bypassing your transformer you have likely left the Neutral floating - the incoming N is not used with the transformer and would have to be wired.

These encapsulated models from Acme have been shielded (a ground wire comes out from the windings, isolated from the case) for as long as I've put them in- some 25 years.

Here is a connection diagram, from Canada's Ships' Electrical Standards for Inspected Vessels:
Attached Files
File Type: pdf Transformer wiring.pdf (61.4 KB, 41 views)
__________________
Experience develops good judgement, bad judgement develops experience
EngNate is offline   Reply With Quote
Old 10-31-2019, 01:57 PM   #19
Guru
 
City: Fairport
Country: United States
Join Date: Jan 2017
Posts: 1,693
Quote:
Originally Posted by EngNate View Post
...

Here is a connection diagram, from Canada's Ships' Electrical Standards for Inspected Vessels:
Hopefully, those transformers never have a primary to shell short!
diver dave is online now   Reply With Quote
Old 10-31-2019, 03:58 PM   #20
Veteran Member
 
City: St. Petersburg
Country: USA
Join Date: Oct 2007
Posts: 95
The Canadian Standard referenced in #18 is not in accordance with ABYC E-11.
__________________

__________________
Charlie Johnson
CharlieJ is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 10:24 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012
×