Isolation transformer location

2004 Mainship 400 Trawler, single engine. Getting only 90 volts in and out on shore power feed switch. Problem may be in the isolation transformer but cannot find it. It's not behind fridge or anywhere else I can find. Anyone know where the isolation transformer is ? Anyone else have this reduced voltage issue? Local dealer no help.
__________________
Advertisement

intdln is offline   Reply With Quote
Old 06-26-2016, 03:45 PM   #2
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,422
What's the incoming voltage from the dock?

Does it drop as you put a load on it?

Are you sure you have a transformer?

If you are, is it automatic? Or do you have to tell it whether to buck or boost?
__________________

Capt.Bill11 is offline   Reply With Quote
Old 06-26-2016, 04:34 PM   #3
Member
 
City: Baltimore MD
Country: United States
Join Date: Jun 2016
Posts: 7
Isolation transformer

All voltage into boat is normal and does not drop.. Its one line from main line that feeds outlets that drops. All other lines and switches are where they should be. I have shore power inlets both stern and bow with different cords. Same results. However when gen is running voltage is normal. Mainship specs states that transformer installed but wondering if true. Driving me nuts. Thanks for your response.
intdln is offline   Reply With Quote
Old 06-26-2016, 08:13 PM   #4
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,422
Then it sounds like the problem is just on the one line.

If so, look for bad, corroded or loose connections.

See if it's a bad GFI issue as well. If one GFI protect multible outlets.
Capt.Bill11 is offline   Reply With Quote
Old 06-26-2016, 08:24 PM   #5
Member
 
City: Baltimore MD
Country: United States
Join Date: Jun 2016
Posts: 7
Isolation transformer

Thank you. All connections secure. Makes no sense.
intdln is offline   Reply With Quote
Old 06-26-2016, 08:38 PM   #6
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,422
You're going to have to trace the drop set by step segment by segment it sounds like.

Bad breaker?
Capt.Bill11 is offline   Reply With Quote
Old 06-26-2016, 09:08 PM   #7
Guru
 
boatpoker's Avatar
 
City: Port Credit
Country: Ontario
Vessel Name: DIRT FREE
Vessel Model: Benford Fantail 38
Join Date: Sep 2012
Posts: 2,011
Isolation transformers are large (think bread box) and if one is fitted (not typical on Mainship) it would be within a foot or so of the shore power inlet.
__________________
If you can live with the consequences, go for it - wg
Y'am what I y'am an' thats' all that y'am - Popeye
As God is my witness, I thought turkey's could fly. Mr.C
boatpoker is offline   Reply With Quote
Old 06-26-2016, 09:45 PM   #8
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 6,360
Intrinsic

Assuming you have the standard rotating switch between generator, input 1, input 2 and off - that switch may be suspect. With all power unplugged open that switch up and have a look. If not there you then have to go the next breaker and start checking for a bad wire - ground most likely.

Time for a pro in any event, is there a good marine electrician nearby? Many boat fires centered on incoming power connectors so be careful.
sunchaser is offline   Reply With Quote
Old 06-26-2016, 10:01 PM   #9
Member
 
City: Baltimore MD
Country: United States
Join Date: Jun 2016
Posts: 7
Thank you
intdln is offline   Reply With Quote
Old 06-26-2016, 10:35 PM   #10
Dauntless Award
 
Wxx3's Avatar
 
City: New York, NY
Country: USA
Vessel Name: Dauntless
Vessel Model: Kadey Krogen 42 - 148
Join Date: Jan 2013
Posts: 2,312
I had the same problem just a few days ago.

90 volts at the plug, when it should have been 230.

After doing all sorts of things, I finally checked the connection again and discovered the plug was only halfway into the socket. Both UK type plug and socket.

Turned
__________________
M/Y Dauntless, New York
a Kadey Krogen 42 Currently https://share.delorme.com/dauntless
Blog: https://dauntlessatsea.com
Find us: https://share.delorme.com/dauntless
Wxx3 is offline   Reply With Quote
Old 06-27-2016, 06:51 AM   #11
TF Site Team
 
Bay Pelican's Avatar
 
City: Chicago, IL
Country: USA
Vessel Name: Bay Pelican
Vessel Model: Krogen 42
Join Date: Oct 2007
Posts: 2,781
Size matters. Bay Pelican has an isolation transformer (50 amp). It is very large and it couldn't be overlooked on a 40 ft boat. It is double or more of the size of one of the inverter chargers. It has cables running directly from the shore power inlet, and another set of cables running to the breaker panel.

If you can't find it, it is likely you don't have one.

Given their cost ($3,000 to $7.000 plus), I question why an isolation transformer would be put on a boat without a specific need, certainly not a production run item. Is the literature confusing isolation transformer with galvanic isolator?
__________________
Marty
Bay Pelican is offline   Reply With Quote
Old 06-27-2016, 06:56 AM   #12
Member
 
City: Baltimore MD
Country: United States
Join Date: Jun 2016
Posts: 7
Thank you.
intdln is offline   Reply With Quote
Old 06-27-2016, 07:50 AM   #13
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,422
"Its one line from main line that feeds outlets that drops. All other lines and switches are where they should be."

If this post is correct and the only line branch that has low voltage is one line that feeds some outlets while every other line has good voltage, it can't be a loose plug, transformer issue or a main switch issue.

Or you would have an overall voltage drop.
Capt.Bill11 is offline   Reply With Quote
Old 06-27-2016, 08:58 AM   #14
Senior Member
 
mike66's Avatar
 
City: Warwick, RI
Country: USA
Vessel Name: Susan Helena
Vessel Model: Albin40
Join Date: Oct 2014
Posts: 179
My next step would be to disconnect the circuit from the breaker and then measure voltage coming out of the breaker. Also measure voltage going into the breaker. Also measure the resistance on the disconnected circuit and make sure it is open between hot, neutral and ground.
mike66 is offline   Reply With Quote
Old 06-27-2016, 03:30 PM   #15
Member
 
City: Baltimore MD
Country: United States
Join Date: Jun 2016
Posts: 7
Isolation transformer found on Mainship 400 Trawler

Located in clothes closet port stateroom behind upper panel. Problem was with it. Fixed.
intdln is offline   Reply With Quote
Old 06-27-2016, 03:46 PM   #16
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,422
Quote:
Originally Posted by intdln View Post
Located in clothes closet port stateroom behind upper panel. Problem was with it. Fixed.
OK, great.

So what was the problem?

How was it fixed?

And how was it that the voltage drop was only on one circuit?
Capt.Bill11 is offline   Reply With Quote
Old 06-27-2016, 04:11 PM   #17
Member
 
City: Baltimore MD
Country: United States
Join Date: Jun 2016
Posts: 7
One of the wires was bad. Hired a pro so did not completely understand. Tks for your responses.
__________________

intdln is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 08:05 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012