Quote:
Originally Posted by JDCAVE View Post
Peter. WRT this comment. Do you follow James Hamilton's blog?
Yes, I follow the blog and have talked to him about his modification. Our objectives are similar, and really two-fold:

1) be able to run moderate 240V loads while underway with out the generator. Our alternators can support about 7kw, so that's our max sustained load while not draining the batteries. We don't want to run that way all the time, and I'd actually like to stay more around 5kw just to keep the current levels down. But that will support cloths washing and an AC unit or two, though probably not at the same time. But I figure if we are in heavy need of AC, I'll just run the generator.

2) More seamless operation with 50hz shore power. This isn't an issue until we leave north america, but that time is coming. But the idea is to be able to run 240V appliances that require 60hz off the inverter, and take shore power in via charger(s) that are frequency and voltage insensitive. Some of our 240V appliances can run on 50 or 60hz, like our how water heater and AC. But others are locked into 60hz like the washer and dryer and the oven. Bringing power in at 50hz and converting it to DC via a charger, then inverting to 60 hz 240V allows those appliances to run seamlessly. You just need to be sure your shore chargers keep up with the load, on average.

A third possible feature, but one I don't think we can take advantage of, is regulating/limiting your shore power draw. Lots of places only have 16A@230V, so about 3.6kw. If you limit the shore power draw to 16A on the charger, then you can avoid nuisance trips of breakers while still consuming more than 3.6kw on board. Your average load of course needs to be well under 3.6kw, but the inverter and batteries can handle short term loads in excess of the shore power limit, providing much more flexibility on board. We will be able to do some of this, but not all of our 240V loads will run through the inverter, the AC in particular, so we don't have a single device that can regulate the full load.

Anyway, this is getting pretty far off topic, so maybe we can pick it up in another thread if there is interest...
__________________
Advertisement

__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 02-21-2016, 04:36 PM   #22
Guru
 
koliver's Avatar
 
City: Saltspring Island
Country: BC, canada
Vessel Name: Retreat
Vessel Model: C&L 44
Join Date: Nov 2007
Posts: 2,174
Henry:

Others have covered the inverter that you need. My thoughts are directed to your batteries. If you plan to run a household refrigerator, and other loads, you will need at least double the number of batteries that you would have without the fridge.

My own experience is the reverse of this. I took out a Norcold AC/DC unit and replaced it with a fridge run on a Danfoss DC compressor. I then reduced my battery supply to 1/2 of what had been inadequate to keep the fridge running. Now I have more than I need, and also run a 2nd Danfoss, in a small stand alone freezer.
__________________

koliver is online now   Reply With Quote
Old 02-21-2016, 10:47 PM   #23
Guru
 
City: Venice Louisiana
Country: United States
Join Date: Dec 2013
Posts: 1,097
There is no way a DC compressor can be as efficient as a 120 volt ac compressor of the same type doing the same job. Thats my opinion, I need convincing. Would convert all my fridge loads to DC if I could be sold on it.
kulas44 is offline   Reply With Quote
Old 02-22-2016, 12:46 AM   #24
Guru
 
koliver's Avatar
 
City: Saltspring Island
Country: BC, canada
Vessel Name: Retreat
Vessel Model: C&L 44
Join Date: Nov 2007
Posts: 2,174
Guess it depends on what your refrigeration loads are.
I have what used to be a Norcold 8 cu ft box, powered by their AC/DC compressor. Changing to a Danfoss DC compressor resulted in much improved efficiency, so much that I was able to reduce my battery bank to 1/2 of what couldn't keep up with the demands of the old fridge. I have been happy with the Danfoss for almost 20 years now.
koliver is online now   Reply With Quote
Old 02-22-2016, 04:07 AM   #25
TF Site Team
 
Bay Pelican's Avatar
 
City: Chicago, IL
Country: USA
Vessel Name: Bay Pelican
Vessel Model: Krogen 42
Join Date: Oct 2007
Posts: 2,793
Quote:
Originally Posted by kulas44 View Post
My Slendide will not run on my ME2012 mod sign wave inverters. Also, have never burnt up a small cordless tool charger but have talked to plenty of folks that have. Sine wave or not doesnt make any difference on load carrying ability, most mod wave units have higher start capacity than tru sine units. My experience has been that bigger loads are easier to run that very small. I would approach the inverter issue as a complete unified installation, not as an add on. And no, a stand alone charger cant even get close to a 2000 watt inverter/charger in power, efficiency or cost.
This is a known issue with the Splendide washer/dryers and the Magnum ME2012 inverter. The startup requirements of the Splendide are beyond the peak capacity of the inverter.

Magnum was very helpful with this issue and my solution was to upgrade inverters to the ME2812.
__________________
Marty
Bay Pelican is online now   Reply With Quote
Old 02-22-2016, 04:22 AM   #26
TF Site Team
 
Bay Pelican's Avatar
 
City: Chicago, IL
Country: USA
Vessel Name: Bay Pelican
Vessel Model: Krogen 42
Join Date: Oct 2007
Posts: 2,793
Quote:
Originally Posted by twistedtree View Post
My Splendide wouldn't run properly if my MasterVolt inverter/charger was even turned on. I could be on generator or shore power, and as long as the inverter/charger was turned on, the Splendide wouldn't run correctly. Of course both companies pointed the finger at the other. I think it's pretty ironic that the Splendide, which is targeted at RV and Marine applications here in the US, doesn't work in many situations with Inverters.
Missed this post when I posted on the Splendide Magnum issue. What is the capacity / output of your MasterVolt inverter, and what is the peak output.

The Splendide units have a high start up demand which has been known for years (and which I understand is true of other washers). Back in 2002 I was warned that only the Xantrex 2000 pro among the smaller units had the peak capacity for starting a washer dryer. Both the Magnum 2800 and the Victron 2800 can power the Splendide at start up.
__________________
Marty
Bay Pelican is online now   Reply With Quote
Old 02-22-2016, 07:09 AM   #27
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,531
" I have been happy with the Danfoss for almost 20 years now."

Although in the 2 decades Danfoss has gotten even better!
FF is online now   Reply With Quote
Old 02-22-2016, 08:48 PM   #28
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 3,197
Quote:
Originally Posted by Bay Pelican View Post
Missed this post when I posted on the Splendide Magnum issue. What is the capacity / output of your MasterVolt inverter, and what is the peak output.

The Splendide units have a high start up demand which has been known for years (and which I understand is true of other washers). Back in 2002 I was warned that only the Xantrex 2000 pro among the smaller units had the peak capacity for starting a washer dryer. Both the Magnum 2800 and the Victron 2800 can power the Splendide at start up.
The Mastervolt was 2500W I think. But the interesting part of the puzzle is that when the problems occurred, the inverter was not powering the washer. It was in bypass mode and passing shore power or gen power straight through. It also didn't matter if the Mastervolt was charging or not. It was clearly some sort of interference, but I was never able to sort it out, even whether it was conducted or radiated interference. I finally gave up and would just shut down the Mastervolt and throw the external bypass switch.
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 02-22-2016, 08:58 PM   #29
Master and Commander
 
markpierce's Avatar
 
City: Vallejo CA
Country: USA
Vessel Name: Carquinez Coot
Vessel Model: 2011 Seahorse Marine Coot hull #6
Join Date: Sep 2010
Posts: 10,265
Have a 24-volt DC refrigerator and a 120-volt AC air compressor for the air horn and wall plugs. The disadvantage of AC is that the air compressor won't work when the inverter is on the blink.

__________________
Kar-KEEN-ez Koot
markpierce is offline   Reply With Quote
Old 02-23-2016, 03:41 AM   #30
TF Site Team
 
Bay Pelican's Avatar
 
City: Chicago, IL
Country: USA
Vessel Name: Bay Pelican
Vessel Model: Krogen 42
Join Date: Oct 2007
Posts: 2,793
Quote:
Originally Posted by twistedtree View Post
The Mastervolt was 2500W I think. But the interesting part of the puzzle is that when the problems occurred, the inverter was not powering the washer. It was in bypass mode and passing shore power or gen power straight through. It also didn't matter if the Mastervolt was charging or not. It was clearly some sort of interference, but I was never able to sort it out, even whether it was conducted or radiated interference. I finally gave up and would just shut down the Mastervolt and throw the external bypass switch.
That is the first I have heard of that problem. Questions: Did you try and run the washer just on the inverter? Does your inverter have a maximum 110v draw setting (maximum power it will take from shore or the genset)? If so at what level is it set? Unintentionally we set our maximum draw too low one time and the bypass was unable to power the tea pot.
__________________
Marty
Bay Pelican is online now   Reply With Quote
Old 02-23-2016, 07:27 AM   #31
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,531
"There is no way a DC compressor can be as efficient."

DC is far more efficient ,the AC unit just switches on, runs at a different load , (warm box , cold box ) till the thermostat is satisfied.No attempt to match the running RPM to the coolant load can be made.

The DC units computer will match the cooling requirements , compressor RPM , to the actual box loads.

The very slow operation of the unit most of the time , just maintaining box temperature is Very efficient.

PBB had a great article a year or two back that goes into depth on the many advantages.

And they did not even bother with the 10% inverter loss from an AC unit on DC.
FF is online now   Reply With Quote
Old 02-23-2016, 08:35 AM   #32
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 3,197
Quote:
Originally Posted by Bay Pelican View Post
That is the first I have heard of that problem. Questions: Did you try and run the washer just on the inverter? Does your inverter have a maximum 110v draw setting (maximum power it will take from shore or the genset)? If so at what level is it set? Unintentionally we set our maximum draw too low one time and the bypass was unable to power the tea pot.
Yes, it was a real head scratcher. It's been several years now, so I'm going off memory which is dangerous but.... I think the kicker was that the washer wasn't even wired to the inverter. The inverter powered a select set of circuits, and the washer was not one of them. So washer load and inverter capacity never interacted with one another. They were just side by side loads on the same shore or gen power source. So it could only be electrical noise (radiated or conducted) that was tricking the washer. And the washer failure mode was very odd too. When you first start it, it goes through a short cycle to be sure the drum is pumped dry. It would remain stuck in that cycle until it errorred out. The error code said the drum was both empty and full at the same time, so some sort of sensor malfunction. Turn off the inverter (remember, it's just a side by side load, like running the TV at the same time), and the washer would work fine. I replaced all the relevant parts as my expense and to no avail. I also experimented with ferrites on the power cord, but no joy.

My final conclusion was that without a scope I would never figure it out, and I had long ago thrown away my 100 lb, tube-powered Tektronics scope.

I have encountered two other similar problems, but these are sensitivities to running on a generator. One was the electronic igniter (the spark spark spark lighter) on a gas stove. It would not go click click click when the house was running on the generator. Definitely not a load problem since the clicker draws only a tiny amount of power. It cause quite the surprise on Thanksgiving when we discovered the oven had not relit in the past 3 hours and the turkey was still raw....

I've got another such issue currently with a modern gas boiler. It's a Buderus modulated super efficient burner that heats my barn/shop. When my generator is running, it errors out. It lights, but the flame detect circuit doesn't agree and it shuts down. After a few attempts it locks out and requires a manual reset - something that does not go well with unattended operation. I ended up building a lockout circuit to keep the boiler from firing when the generator is running. The shop building is super insulated with lots of thermal mass, so the temp only drops a degree or two over an 8hr generator run, so it works OK.

One irony here is that I've had much better success running devices off inverters than off generators. I don't think I've found anything that doesn't work off a sine wave inverter, where I have a handful that don't work off of generators.
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 02-24-2016, 08:30 AM   #33
Veteran Member
 
City: Ft Myers
Country: USA
Vessel Name: Linda Lee
Vessel Model: 45' Aquarius motoryacht
Join Date: Oct 2015
Posts: 30
It appears I opened a hornet nest on this one. Thanks everyone for your input. I will continue my research with all your information as I move forward.
Coming from a sailboat for over 40 years, to our motor yacht / trawler will be a new adventure and education for us
Thank you
Henry & Linda
M/V Linda Lee
Ft Myers Fl
hfmckevitt is offline   Reply With Quote
Old 02-24-2016, 08:43 AM   #34
Guru
 
City: Seaford Va on Poquoson River, VA
Country: United States
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 1,304
If a device does not function on a typical generator when it should, then I suspect the speed of the gen is too high or low since the frequency of AC power is determined by rotating gen rpm. So maybe the gen is not close to 60 cycles.
sdowney717 is online now   Reply With Quote
Old 02-24-2016, 09:22 AM   #35
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 3,197
Quote:
Originally Posted by sdowney717 View Post
If a device does not function on a typical generator when it should, then I suspect the speed of the gen is too high or low since the frequency of AC power is determined by rotating gen rpm. So maybe the gen is not close to 60 cycles.
True, but as accurately as I can measure it, it's dead nuts on. Now that might not be exact enough for the burner control, but I can't make it any closer....
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 02-24-2016, 12:55 PM   #36
Veteran Member
 
City: Victoria, BC
Country: Canada
Join Date: Mar 2010
Posts: 49
For those having problems with the Magnum charger not playing with the Splendide washer, this may be a solution. No personal experience.
mv.VikingStar: Summary and Conclusion: Compatibility Issue Between MS2000 inverter and Splendide 2100XC Washer/Dryer
alesnloggers is offline   Reply With Quote
Old 02-24-2016, 06:09 PM   #37
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,422
Quote:
Originally Posted by hfmckevitt View Post
It appears I opened a hornet nest on this one. Thanks everyone for your input. I will continue my research with all your information as I move forward.
Coming from a sailboat for over 40 years, to our motor yacht / trawler will be a new adventure and education for us
Thank you
Henry & Linda
M/V Linda Lee
Ft Myers Fl
If all you want to do is power your fridge there is no need to get an expensive inverter/charger. Just find out the starting load for your fridge and get a simple, basic inverter that covers that load.
Capt.Bill11 is offline   Reply With Quote
Old 02-25-2016, 07:42 AM   #38
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,531
"If all you want to do is power your fridge there is no need to get an expensive inverter/charger. Just find out the starting load for your fridge and get a simple, basic inverter that covers that load."

Just so, $100 should do it.
FF is online now   Reply With Quote
Old 02-25-2016, 09:07 AM   #39
Senior Member
 
City: Mississippi
Country: USA
Join Date: Jul 2014
Posts: 202
(For those having problems with the Magnum charger not playing with the Splendide washer, this may be a solution. No personal experience.
mv.VikingStar: Summary and Conclusion: Compatibility Issue Between MS2000 inverter and Splendide 2100XC Washer/Dryer)

That should work to take care of the washer problem on a Magnum - like it says, be sure to get a Run Cap vs Starter Cap (capacitor). I have installed Start Caps on older land based A/C condensers, in my rental units, that have a hard time getting going - gives them a bit longer life. Wow, wonder if something like that will work for us old TF's?
__________________

FoxtrotCharlie is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 02:00 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012