You just need something like this.
Doesn't it matter whether you use 100 percent or 80 percent load CBe?
Then the question is does the boat really use 100 percent continuous load?
The power cord is rated to 60 amps, so if the boats panel CBs are 80 percent, not much chance of anything dangerous but nusuance trips
to specify a 40A DPCB as the first shore power CB aboard (ELCI or panelboard).For example, when I have the opportunity to design a system,
If the 50A receptacle is 120/240V, then you have up to 50A on each of the two hot legs, and the neutral carries the difference in current between the two hot legs. So if you adapt that 50A receptacle using one of these https://www.westmarine.com/buy/mari...0a-female-to-1-50a-male--12998423?recordNum=4 , you get up to 50A on each of the two 30A cords to your boat, in which case you're relying on the onboard overcurrent protection to limit the current as a backup to the design load diversity and distribution across both inlets.I thought a 30 amp shore power cord has up 30amps flowing through it. My boat has inputs for 2 30 amp cords. How am I able to use a 50 amp outlet and splitter to power both cords? Thanks.
If the 50A receptacle is 120/240V, then you have up to 50A on each of the two hot legs, and the neutral carries the difference in current between the two hot legs. So if you adapt that 50A receptacle using one of these https://www.westmarine.com/buy/marin...23?recordNum=4 , you get up to 50A on each of the two 30A cords to your boat, in which case you're relying on the onboard overcurrent protection to limit the current as a backup to the design load diversity and distribution across both inlets.
Post #13
30A/125V shore power cords are typically constructed of AWG 10 conductors which have an ampacity of 60A @ 30C and 51A @ 50C. The ABYC considers shore power cables as operating in a 30C environment. A normal shore power cable has the ampacity to handle up to 60A.
The weak link for passing 50A from a 50A/250V split phase into a wye would be the shore power inlet and the cable ends of the 30A/125V cable.
The ampacity charts I have seen show 105 degree rated insulation amoacity at 60 A.
Below and others...for ampacity, not the recommended for normal loading.
https://www.westmarine.com/WestAdvi...MIs6708qzT3AIVmoTICh06OweOEAAYASAAEgJwxPD_BwE
The ampacity charts I have seen show 105 degree rated insulation amoacity at 60 A.
Below and others...for ampacity, not the recommended for normal loading.
https://www.westmarine.com/WestAdvi...MIs6708qzT3AIVmoTICh06OweOEAAYASAAEgJwxPD_BwE
Shore power cable is heavily sheathed!
So will not be dissipating as much heat.
And it is not made from Anchor wire rated to 105*c, the insulation on anchor wire allows for the higher ampacity.
We are talking about yellow shore power cables right?
Not really and certainly not germane to the discussion of shore power cable ampacity.Total wattage must mean something here
Just to be clear: amps is the unit of measure for current flow; watts is the unit of measure for power.The NEC wont let you get away with it, using a 10 gauge wire to carry 60 amps of power.
By definition, a short circuit is "an electrical circuit of lower resistance than that of a normal circuit, typically resulting from the unintended contact of components and consequent accidental diversion of the current.not all shorts have low resistance enough to pass sufficient current to trip a breaker.
To that point, something to keep in mind is that shore power cordsets are UL and CSA (Marinco, at least) listed assemblies, not individual or bundled insulated conductors in free air (like a cable tray). That includes sheathing, plugs, receptacles, and the conductors inside, which may or may not have 105C insulation, and the plugs/receptacles at either end are 30A or 50A rated (and listed) anyway.
I don't know how the ABYC addresses this, but the NEC at least will only allow conductor ampacity higher than the 60C value if the terminations also are rated 75 or 90C (most only go to 75C), and even then, small conductors are limited to the familiar 15/20/30A values regardless of the Table 310.16 values for most common circuits (other than motor, hermetic A/C, welder, and some other 'special' circuits).
But I would use caution in selecting conductors for continuous loads in a boat, in large part because I'm not familiar enough with the codes and standards for marine wiring. Which means I shouldn't be selecting conductors or doing wiring on a boat in the first place, I suppose.
Post #13
30A/125V shore power cords are typically constructed of AWG 10 conductors which have an ampacity of 60A @ 30C and 51A @ 50C. The ABYC considers shore power cables as operating in a 30C environment. A normal shore power cable has the ampacity to handle up to 60A.
The weak link for passing 50A from a 50A/250V split phase into a wye would be the shore power inlet and the cable ends of the 30A/125V cable.
Again, I totally disagree with this, your saying a 30 amp shore cord can handle 60 amps. That is irresponsible thing to say, IMO.
Do you have evidence to say they can be used for 60 amps?
STW wire, 10 gauge is rated for 30 amps.
https://www.centurywire.com/home/portable-power-cords/stw-portable-power-cords-600v/
https://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet307
I've never read the CG regs on ampacity as referenced in the CFRs, and quite surprised to see them as high as they are.
Give or take, NEC and ABYC say 30A for #10 wire, where the CFR says 60A.
Charlie is correct. The CABLE is rated at 105 deg, therefore the high current rating. Of course, the SYSTEM is only good for 30A, due in large part to the connectors at each end.
FEP insulated 10AWG is rated at 75Amps, btw.