I’ve discovered that I have two SPST switches on my flybridge console that become real hot to the touch when energized. One services running lights, the second an engine room ventilation blower.

The running lights are standard incandescents in “new” fixtures added about 2 years ago. The lights seem to be at normal intensity and typical heat output. The blower is basic 12v dc that is probably original equipment. The blower is not overheating and functions normally.

My thought is that the switches (likely original equipment) are internally cruddy, creating a high resistance at the contact point, dictating replacement. Does this sound reasonable or am I possibly missing a downstream problem in the circuit?

The second question is: The pricing of replacement SPST switches is all over the place. As are the constituent components. Plastic, stamped brass, with full boots or half boots, screw connections or potted with leads, etc., etc.

Third: The price differential between, say, a 15 amp and a 50 amp switch is slight ($7-8). Any advantage (or disadvantage) to replacement with a higher rated switch?

Appreciate the help.
__________________
Advertisement

sbu22 is offline  
Old 10-02-2016, 09:54 AM   #2
Guru
 
City: Seaford Va on Poquoson River, VA
Country: United States
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 2,185
Could be bad switches. Most digital meters, you can measure amp flow inline. See if it is reasonable currents.
Under the load, measure the volts at the powered devices, if it is low could also point to high resistance in the switches. Jumper over the switches and see if the voltage rises.

Up on my flybridge, I have those push-pull round chrome knob switches. I have cleaned them before by using PB Blaster. Take them off and saturate the inside, then work them. It dissolves corrosion off the brass contacts. I have also taken those apart and repaired them, but I like to do things like that.

Lower helm, I have Carling breaker switches. Get a breaker and a switch in one. They are not too expensive on Ebay. Just bought a 20 amp one for $8.95. It was NOS (new old stock).

Breakers are sized to protect the wire, but a switch going with higher amps is ok, if you want to spend more money than needed.
__________________

sdowney717 is offline  
Old 10-02-2016, 10:50 AM   #3
Guru
 
sbu22's Avatar
 
City: New Orleans
Country: US
Vessel Name: Panache
Vessel Model: Viking 43 Double Cabin '76
Join Date: Mar 2011
Posts: 1,113
Good idea sdowney - I'll check that this afternoon. Due to space/layout, I think I'm stuck with the toggle arrangement.

I see I didn't complete question 2 - The second question is: The pricing of replacement SPST switches is all over the place. As are the constituent components. Plastic, stamped brass, with full boots or half boots, screw connections or potted with leads, etc., etc. Any preferred configuration for this use?
sbu22 is offline  
Old 10-02-2016, 10:53 AM   #4
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 5,532
The size of the wireing may also be marginal causing low voltage which will increase the current draw. Look at the total length of the circuit run and see if the wireing is adequate for the blower. The running light are a small draw even with incandescent bulbs.
Comodave is online now  
Old 10-02-2016, 10:57 AM   #5
Guru
 
City: Seaford Va on Poquoson River, VA
Country: United States
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 2,185
I don't have any booted switches on the boat except at the windless.
I prefer screw connections, wire leads can break off. At least it makes for easier repairs having a screw.

I prefer screws over spade lugs too, I think they offer more secure connections, especially if more exposed to the weather.

Any metal handled switches I prefer outside in the weather, I just think they hold up better to the sunlight. Never seen one rust on me.
sdowney717 is offline  
Old 10-02-2016, 11:29 AM   #6
Guru
 
kchace's Avatar
 
City: Brookline, NH
Country: USA
Vessel Name: Blue Heaven
Vessel Model: Albin 43 classic double cabin, twin 135 Lehmans
Join Date: Sep 2013
Posts: 1,589
A failing switch can indeed have too much internal resistance and get hot even if everything else is good. Another possibity are the connections AT the switch. A poor connection can also get very hot and be felt in the switch.

Ken
kchace is offline  
Old 10-02-2016, 11:31 AM   #7
TF Site Team
 
FlyWright's Avatar
 
City: California Delta and SF Bay
Country: Sacramento, CA, USA (boat in Vallejo)
Vessel Name: FlyWright
Vessel Model: Marshall Californian 34 LRC
Join Date: Apr 2008
Posts: 12,301
Stupid question, but do these switches have indicator lights incorporated into them that illuminate when the switch is selected ON?
__________________
My boat is my ark. It's my mobile treehouse and my floating fishing cabin. It's my retreat and my respite. Everyday I thank God I have a boat! -Al

@DeltaBridges - 25 Delta Bridges in 25 Days
FlyWright is offline  
Old 10-02-2016, 12:14 PM   #8
Guru
 
DHeckrotte's Avatar
 
City: Philadelphia, PA
Country: USA
Vessel Name: Revel
Vessel Model: 1984 Fu Hwa 39
Join Date: Nov 2015
Posts: 999
Replace 'em with waterproof toggle switches. I got mine from McMaster-Carr, an over-the-internet supply company. You may find that the waterproof ones are slightly larger behind the mounting, and might have a larger diameter penetration through the mounting. A moment's work with your Dremel.
DHeckrotte is offline  
Old 10-02-2016, 12:35 PM   #9
Guru
 
City: Seaford Va on Poquoson River, VA
Country: United States
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 2,185
HEXSEAL® Sealing Boots - APM Hexseal | Digi-Key
I have a couple boots which I have not used yet.
These screw on to seal the toggle.
sdowney717 is offline  
Old 10-02-2016, 12:36 PM   #10
Guru
 
High Wire's Avatar
 
City: Cape May, NJ and Englewood, FL
Country: USA
Vessel Name: Irish Lady
Join Date: Dec 2007
Posts: 2,796
Hot to the touch is a warning sign of high resistance. Nav lights draw about one amp each so thats only 4 amps. Blower fans will need a little homework. To make it easy, buy switches with like kind connections and at least 10 amp DC ratings from a reputable manufacturer. A rubber boot keeps the water out.
High Wire is offline  
Old 10-02-2016, 04:16 PM   #11
Senior Member
 
Toolbuddie's Avatar
 
City: Huntsville, AL
Country: USA
Vessel Name: Sea Note
Vessel Model: Mainship 40
Join Date: May 2014
Posts: 185
Agreed with above statements. Mostly.
Simplest way to evaluate a switch is either:
1. With the switch made, ON that is, use your volt meter to measure the voltage DROP from one terminal of the switch to the other. Should be .02 VDC or less. If you have a volt or more replace the switch. Higher ampacity at rated voltage for a switch never hurts if it fits. Use ring lugs on screw terminals.
2. Turn off the circuit, Remove the wires measure the resistance of the switch with it ON. If more than one Ohm. Replace as above. 0.2 Ohms would be acceptable but high for my criteria.

Are the wires getting hot also? Away from the switch. Hot wires suggest circuit problems as others have noted.
Good luck, Dave
Toolbuddie is offline  
Old 10-03-2016, 05:27 AM   #12
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 19,657
One problem with DC switches is they are liable to fail in the ON position.

This can be hard on the batt if you don't notice.
FF is offline  
Old 10-03-2016, 06:20 AM   #13
Guru
 
Shoalwaters's Avatar
 
City: Rodney Bay Lagoon
Country: St. Lucia, West Indies
Vessel Name: "Dragon Lady"
Vessel Model: DeFever 41
Join Date: Feb 2008
Posts: 681
Quote:
Originally Posted by Toolbuddie View Post
Simplest way to evaluate a switch is either:

1. With the switch made, ON that is, use your volt meter to measure the voltage DROP from one terminal of the switch to the other. Should be .02 VDC or less. If you have a volt or more replace the switch. Higher ampacity at rated voltage for a switch never hurts if it fits. Use ring lugs on screw terminals.

2. Turn off the circuit, Remove the wires measure the resistance of the switch with it ON. If more than one Ohm. Replace as above. 0.2 Ohms would be acceptable but high for my criteria.
Straightforward diagnostics with a multi-meter. Excellent!
__________________
Mike
If all else fails, read the instructions
If it ain't broke, don't fix it
Shoalwaters is offline  
Old 10-03-2016, 07:02 AM   #14
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,385
Quote:
Originally Posted by Comodave View Post
The size of the wireing may also be marginal causing low voltage which will increase the current draw. ............
That is incorrect and bad advice. Any resistance in the wiring will reduce the voltage and reduce the current draw. Honestly, I don't know how this crap keeps getting posted on the internet.

If the switches are getting hot in use, they should be replaced, It a simple and inexpensive job. Make sure the replacement switches are rated for the current draw of whatever they are switching on and off. Or, match the switch capacity to the fuse or circuit breaker that protects the circuit.


kchace is correct that resistance at the connections can cause a switch to overheat so check for this condition.


As for different construction and price, we are talking three or four dollars for a cheap switch and perhaps twenty dollars for a good one. Go to a marine store and buy the good one.
rwidman is offline  
Old 10-03-2016, 10:02 AM   #15
Senior Member
 
Join Date: Dec 2007
Posts: 380
Wes K is correct, just replace the switches. Two points- If you are using the same connection points on the wires(i.e. stakons),make sure you clean, or replace with new. Second,most VOM's are only rated for a ten ampere feed thru, at which point you will either blow an internal fuse, or damage the VOM. The correct instrument to use is an amprobe.
tinped is offline  
Old 10-03-2016, 02:51 PM   #16
TF Site Team
 
Bacchus's Avatar
 
City: Seneca Lake NY
Country: US
Vessel Name: Bacchus
Vessel Model: MS 34 HT Trawler
Join Date: Nov 2014
Posts: 2,849
Quote:
Originally Posted by WesK View Post
That is incorrect and bad advice. Any resistance in the wiring will reduce the voltage and reduce the current draw. Honestly, I don't know how this crap keeps getting posted on the internet.
.
Ohm's Law E (voltage) = I * R
__________________
Don
2008 MS 34 HT Trawler
"Bacchus"
Bacchus is offline  
Old 10-03-2016, 06:12 PM   #17
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 5,532
What Wes is forgetting is Watts Law. P=IxE. Power is equal to I (current) times E (voltage). Every device requires power to operate, in this case a blower. If the voltage is low then the current must go up in order to get the power (watts) that the device needs to operate. Yes Ohms Law does not include watts, but you must include it in the overall picture. You still need so much power to operate the device and in order to get it if there is resistance in the wiring due to undersize wire, the current flow will go up and that is when it gets hot. The device will draw the power it needs, it can get it from higher voltage or higher current. If the voltage is low, the current draw will go up, unless it exceeds the breaker rating. That is why we have breakers and fuses to protect the wiring. The switch can also get hot due to higher current flow.
Comodave is online now  
Old 10-03-2016, 08:11 PM   #18
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,385
I'm not forgetting anything. I did this stuff for a living.


Forget Ohm's law, forget the math, consider this: When the batteries get weak in your flashlight, does the bulb shine brighter or dimmer?


When the voltage goes down, the power goes down.
rwidman is offline  
Old 10-03-2016, 08:41 PM   #19
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 5,532
Ok, this is my last post on this subject since I do not want to get into a contest. Unfortunately you can not ignore Ohms Law, Watts Law, physics and the math because they do tell you what you need to know when you are calculating voltage drop, current draw and power consumption. I guess what you are telling me from my original post is that wire size does not matter in voltage drop and current draw. Ok, I am glad that I never had you do wiring on my boat. I will continue to use adequate size wiring. Comparing a flashlight with a dead battery is apples and oranges to a 12 volt system that can supply plenty of current to undersize wiring.
Comodave is online now  
Old 10-04-2016, 12:55 AM   #20
FOG
Guru
 
FOG's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: DreamQuest
Vessel Model: Prairie 36
Join Date: Jan 2016
Posts: 549
Using Ohm's law (E=I*R) is correct and easy to prove in this case.
Go to your boat and turn on lights one at a time and watch the amp meter go up while the volt meter stays the same provide you have a good charge on your batteries. E = the battery voltage measured by the volt meter, I = the current measured by the amp meter, and R = the lights (resistance).
If you leave the lights on long enough your battery voltage will begin to drop (assuming your battery charger is off) the current will also go down and the lights will begin to dim. This is also the case of the flashlight getting dimmer because the batteries get weaker.
So as the resistance goes up, the current goes up..... to a certain point at which time the circuit breaker trips. If the resistance goes up and the current was to go down, which it doesn't, the circuit breaker would never pop.

Using Watt's law P=I*E does not apply in this case. If the voltage is low then the current must go up in order to get the power (watts) that the device needs to operate is not true.
If the voltage is low (or the current is low) then the device will not operate properly or possibly not operate at all. The blower may not work at all, or may blow less air, or may become hot and get highly resistive and pop a circuit breaker (another discussion). A light will just get dimmer.
__________________

FOG is offline  
Closed Thread

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 09:45 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012
×