ground question

At the risk of starting a controversy.....
a simple question that should have a simple answer...

if a boat has an isolation type transformer (i.e. 120 to 240 VAC transformer that "separates" the shore power from the boat.) will it cause the boat to seem as if it has an open ground on the AC outlets?
__________________
Advertisement

tmiller1116 is offline   Reply With Quote
Old 08-05-2014, 03:16 PM   #2
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,390
Quote:
Originally Posted by tmiller1116 View Post
At the risk of starting a controversy.....
a simple question that should have a simple answer...

if a boat has an isolation type transformer (i.e. 120 to 240 VAC transformer that "separates" the shore power from the boat.) will it cause the boat to seem as if it has an open ground on the AC outlets?
I would think the neutral and ground wire on the boat would be connected together at the transformer (point of origin) so it shouldn't seem like it has an open ground.

It would help if you posted or quoted the installation instructions for the transformer.

Understand though that if the boat's wiring is isolated from shorepower with a transformer, the boat's wiring will have no relationship to shorepower.
__________________

rwidman is offline   Reply With Quote
Old 08-05-2014, 03:23 PM   #3
Guru
 
djmarchand's Avatar
 
City: East Greenwich, RI
Country: USA
Vessel Name: Bella
Vessel Model: Mainship Pilot 34
Join Date: Aug 2012
Posts: 2,883
No. The electrical code requires the neutral and the ground to be tied at the power source- main panel in most cases but also at any isolation transformer. So the neutral and the ground are tied inside the case of the isolation transformer.

FWIW, Charles Industries does not do this automatically at the factory. They expect the installer to do it. And on my new Mainship 34 the ground and the neutral were not tied. I contacted Charles and got their installation instructions which said to tie them. I did and the open ground indication went away.

And of course the foregoing is only applicable to US 120/240V wiring. European will be different, which is probably why Charles doesn't do it at the factory.

David
djmarchand is online now   Reply With Quote
Old 08-05-2014, 06:29 PM   #4
Guru
 
N4712's Avatar
 
City: South FL
Country: U.S.A
Vessel Name: Oliver
Vessel Model: Nordhavn 47 Hull# 12
Join Date: Apr 2013
Posts: 3,613
We have a Isolation transformer, the ground and neutral are tied at the panel.
__________________
Thanks, Oliver
M/V Oliver
Nordhavn 47 Hull #12
N4712 is offline   Reply With Quote
Old 08-05-2014, 07:14 PM   #5
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,920
here's one of many diagrams available...
Attached Thumbnails
Click image for larger version

Name:	diagram7.jpg
Views:	118
Size:	177.3 KB
ID:	31838  
psneeld is online now   Reply With Quote
Old 08-05-2014, 08:25 PM   #6
Master and Commander
 
markpierce's Avatar
 
City: Vallejo CA
Country: USA
Vessel Name: Carquinez Coot
Vessel Model: 2011 Seahorse Marine Coot hull #6
Join Date: Sep 2010
Posts: 10,265
Electrical is beyond my comprehension. I leave it to the experts.
__________________
Kar-KEEN-ez Koot
markpierce is offline   Reply With Quote
Old 08-05-2014, 08:34 PM   #7
Guru
 
boatpoker's Avatar
 
City: Port Credit
Country: Ontario
Vessel Name: DIRT FREE
Vessel Model: Benford Fantail 38
Join Date: Sep 2012
Posts: 2,012
Quote:
Originally Posted by djmarchand View Post
No. The electrical code requires the neutral and the ground to be tied at the power source- main panel in most cases but also at any isolation transformer. So the neutral and the ground are tied inside the case of the isolation transformer.

FWIW, Charles Industries does not do this automatically at the factory. They expect the installer to do it. And on my new Mainship 34 the ground and the neutral were not tied. I contacted Charles and got their installation instructions which said to tie them. I did and the open ground indication went away.

And of course the foregoing is only applicable to US 120/240V wiring. European will be different, which is probably why Charles doesn't do it at the factory.

David
The panel is not a power source and the neutral/ground should never be joined there or anywhere else on the boat except at the isolation transformer, inverter (automatically switched) or generator also automatically switched.

If you join them at the panel you run the risk of feeding AC into your DC system if that is properly bonded as required.
__________________
If you can live with the consequences, go for it - wg
Y'am what I y'am an' thats' all that y'am - Popeye
As God is my witness, I thought turkey's could fly. Mr.C
boatpoker is offline   Reply With Quote
Old 08-06-2014, 12:27 PM   #8
Veteran Member
 
City: Oregon
Country: USA
Vessel Model: 1979 42' Californian
Join Date: Oct 2013
Posts: 53
so any electrical experts here live in Portland, OR and be available some day to help trace wires... I can probably afford a couple of Coronas
tmiller1116 is offline   Reply With Quote
Old 08-07-2014, 09:42 AM   #9
Veteran Member
 
thomasonw's Avatar
 
City: San Juans, WA
Country: USA
Vessel Name: Viking Star
Vessel Model: 45' Monk / McQueen
Join Date: Apr 2014
Posts: 34
In general ABYC calls for safety ground and neutral to be bonded "At the Source", and with regards to isolation transformers 11.5.5.2.2 calls specifically for this.

However, there is an exception as follows: "For systems using an isolation transformer or polarization transformer, both the generator or inverter neutral and the transformer secondary neutrals may be grounded at the AC main grounding bus instead of at the generator, inverter, or transformer secondaries."
ref: Diagram #5 - E-11.17.3


So, it is fully acceptable to provide the bonding point inside the AC panel, but one needs to make sure to read all rest of the spec to make sure all is done consistently and correctly. Example: Depending on how an inverter is wired into the boat, it may be necessary to defeat the auto bonding capability inside inverters.



Back to the OPs question: With an on-board isolation transformer there should be somewhere a bonding between the safety ground and the neutral wire. (North America standard here). If you are not able to measure that, something is wrong.



-al-
thomasonw is offline   Reply With Quote
Old 08-15-2014, 11:02 AM   #10
Veteran Member
 
City: Oregon
Country: USA
Vessel Model: 1979 42' Californian
Join Date: Oct 2013
Posts: 53
OH, if it helps any.. this is the diagram sent to me by the manufacturer... am I wrong in thinking this is an isolation transformer?

http://i143.photobucket.com/albums/r...16/winding.jpg
tmiller1116 is offline   Reply With Quote
Old 08-15-2014, 03:24 PM   #11
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,390
Quote:
Originally Posted by tmiller1116 View Post
OH, if it helps any.. this is the diagram sent to me by the manufacturer... am I wrong in thinking this is an isolation transformer?

http://i143.photobucket.com/albums/r...16/winding.jpg
It's a transformer. It can be used to double or halve the voltage and would isolate one side from the other. We don't know from the diagram if yours is installed correctly and actually isolating the boat from shore power.
rwidman is offline   Reply With Quote
Old 08-15-2014, 04:20 PM   #12
Veteran Member
 
thomasonw's Avatar
 
City: San Juans, WA
Country: USA
Vessel Name: Viking Star
Vessel Model: 45' Monk / McQueen
Join Date: Apr 2014
Posts: 34
Quote:
Originally Posted by tmiller1116 View Post
OH, if it helps any.. this is the diagram sent to me by the manufacturer... am I wrong in thinking this is an isolation transformer?

http://i143.photobucket.com/albums/r...16/winding.jpg
As rwidman pointed out, it is a transformer - and it is indeed an isolation transformer. Key here are the separate windings which are not connected. Another type of transformer, not as often seen but out there, is an "Auto-transformer" which can also change voltages, but shares part of the one winding between both the 'input' and 'output' sides. Though an Auto transformer will allow voltage changes, it provides no isolation.

The photo you posted is a proper isolation transformer, but again as Rwidman pointed out much depends on how it is wired into your boat.

Should also note: ABYC has some specific requirements for a 'marine' isolation transformer. Specifically with regards to the construction of the internal isolation shield and labeling requirements around same. Industrial transformers often (never?) will meet this unique spec.

Not to get into a ABYC vs. rest of the world discussion, but just to point out a knowledgeable surveyor may flag any transformer that meets industrial / ship specifications but not 'marine' when used in recreational boats.

-al-
__________________

thomasonw is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 09:06 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012