GFI outlets
When I had my boat surveyed after the accepted offer, the surveyor indicated that all AC outlets on a boat should be GFI regardless of whether they were in spaces other than kitchen or head, or whether the breakers were GFCI.
Are there GFI outlets specific for marine use in a boat interior or will standard ones from Home Depot be suitable.
Jim
|
|
|
03-18-2014, 03:47 PM
|
#2
|
Guru
City: South FL
Vessel Name: Oliver
Vessel Model: Nordhavn 47 Hull# 12
Join Date: Apr 2013
Posts: 3,607
|
Quote:
Originally Posted by JDCAVE
When I had my boat surveyed after the accepted offer, the surveyor indicated that all AC outlets on a boat should be GFI regardless of whether they were in spaces other than kitchen or head, or whether the breakers were GFCI. Are there GFI outlets specific for marine use in a boat interior or will standard ones from Home Depot be suitable. Jim
|
Home Depot.
__________________
Thanks, Oliver
M/V Oliver
Nordhavn 47 Hull #12
|
|
|
03-18-2014, 04:13 PM
|
#3
|
Guru
City: Ft Pierce
Vessel Name: Sold
Vessel Model: Was an Albin/PSN 40
Join Date: Oct 2011
Posts: 28,148
|
I don't think GFIs are required for every outlet....just ones in "weather" or "wet" environs.
If one protects an breakered circuit....or if you have a GFI circuit breaker I think you are OK.
I have heard but don't have the info at my fingertips that while "home style" GFIs will work on a boat, marine GFIs are a better in the sense they don't trip as easily.
|
|
|
03-18-2014, 04:31 PM
|
#4
|
Technical Guru
City: Wilmington, NC
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 6,194
|
When I wired my boat, I put in two gfci outlets, and daisy chained other outlets to them. I used Home Depot outlets, and have had no problems with spurious trips.
I don't see the need to have dry areas like cabins gfci protected, but I am not a student of the rules. I went ahead and protected those areas with the daisy chain, but only because when running new wire it is easy.
|
|
|
03-18-2014, 04:59 PM
|
#5
|
Guru
City: Bayview
Vessel Name: Puffin
Vessel Model: Willard Vega 30
Join Date: Aug 2013
Posts: 1,444
|
Trip settings for GFCI outlets are mandated by UL at a specific level regardless of application. Marine grade may be more robust in materials or construction. I prefer hospital grade for both standard and GFCI.
If your circuit is protected by a GFCI breaker and it's wired properly it meets the requirements.
Multiple GFCI's on a single circuit will only operate if wired correctly, ie...pigtails to each device (not good practice in a marine environment).
Best method is to install the GFCI as the first outlet in the circuit and connect the remaining outlets to the load side of it. Wire into and out of each outlet and do not pigtail with wirenuts.
__________________
What kind of boat is that?
|
|
|
03-18-2014, 06:18 PM
|
#7
|
TF Site Team
City: Brisbane
Vessel Name: Insequent
Vessel Model: Ocean Alexander 50 Mk I
Join Date: Mar 2012
Posts: 4,262
|
Quote:
Originally Posted by Bob Cofer
Trip settings for GFCI outlets are mandated by UL at a specific level regardless of application. Marine grade may be more robust in materials or construction. I prefer hospital grade for both standard and GFCI.
If your circuit is protected by a GFCI breaker and it's wired properly it meets the requirements.
Multiple GFCI's on a single circuit will only operate if wired correctly, ie...pigtails to each device (not good practice in a marine environment).
Best method is to install the GFCI as the first outlet in the circuit and connect the remaining outlets to the load side of it. Wire into and out of each outlet and do not pigtail with wirenuts.
|
Provided of course that such series connections dont result in potential current overloading of the wiring itself - be careful!
__________________
Brian
|
|
|
03-18-2014, 06:24 PM
|
#8
|
Guru
City: Bayview
Vessel Name: Puffin
Vessel Model: Willard Vega 30
Join Date: Aug 2013
Posts: 1,444
|
Best advice is:
Electricity will kill you if you make a mistake.
Hire a professional.
How much is your or your families life worth?
__________________
What kind of boat is that?
|
|
|
03-18-2014, 06:49 PM
|
#9
|
Guru
City: Ft Pierce
Vessel Name: Sold
Vessel Model: Was an Albin/PSN 40
Join Date: Oct 2011
Posts: 28,148
|
No need for forums if all we had to do is hire professionals every time our boats burped....
Drowning will kill you too...but we all go out on the water...many without professional captains to keep us safe.
|
|
|
03-18-2014, 06:56 PM
|
#10
|
TF Site Team
City: Brisbane
Vessel Name: Insequent
Vessel Model: Ocean Alexander 50 Mk I
Join Date: Mar 2012
Posts: 4,262
|
+1 to both Bob and Scott above
Finally found some something I wanted to post earlier. It gives the specs for GFI in Australia. I had my electrical system refitted in Port Townsend, but needed it compliant with Australia. Key difference is we have 230VAC, same as Europe. I bought the AS/NZS standard for Recreational Marine Boats, it is 73 pages, and the sparky who did my work followed it to the letter and did a great job.
I cant even copy and past one word out of the document as its a protected pdf, but here is re-typed some relevant parts:
6.2.1 (in part)
On boats with relatively small single-phase a.c. electrical installations powered intermittently from a shore-supply, a single RCD protecting the whole of the boats a.c system is commonly fitted.
6.2.2
Not every marina or boat yard has RCD protected shore power outlets as standard. The RCD needs to have a rated residual operating current not exceeding 30 mA and an operating time not exceeding 40 ms at a residual current of 150 mA.
I ended up with 2 to cover the needs, and they weren't too difficult to source.
__________________
Brian
|
|
|
03-18-2014, 07:29 PM
|
#11
|
Member
City: New York
Vessel Name: BoomerangII
Vessel Model: Doral SC270
Join Date: Jan 2014
Posts: 22
|
Quote:
Originally Posted by Insequent
Provided of course that such series connections dont result in potential current overloading of the wiring itself - be careful!
|
The reason behind properly sized wire (ampacity rating) and CB.
|
|
|
03-18-2014, 07:29 PM
|
#12
|
Guru
City: Here
Join Date: Sep 2012
Posts: 2,940
|
Quote:
Originally Posted by Insequent
+1 to both Bob and Scott above
Finally found some something I wanted to post earlier. It gives the specs for GFI in Australia. I had my electrical system refitted in Port Townsend, but needed it compliant with Australia. Key difference is we have 230VAC, same as Europe. I bought the AS/NZS standard for Recreational Marine Boats, it is 73 pages, and the sparky who did my work followed it to the letter and did a great job.
I cant even copy and past one word out of the document as its a protected pdf, but here is re-typed some relevant parts:
6.2.1 (in part)
On boats with relatively small single-phase a.c. electrical installations powered intermittently from a shore-supply, a single RCD protecting the whole of the boats a.c system is commonly fitted.
6.2.2
Not every marina or boat yard has RCD protected shore power outlets as standard. The RCD needs to have a rated residual operating current not exceeding 30 mA and an operating time not exceeding 40 ms at a residual current of 150 mA.
I ended up with 2 to cover the needs, and they weren't too difficult to source.
|
An RCD is not the same thing as a G.F.C.I.
|
|
|
03-18-2014, 07:53 PM
|
#14
|
Guru
City: Here
Join Date: Sep 2012
Posts: 2,940
|
Quote:
Originally Posted by Insequent
|
ABYC definitions .....
A residual current device protects equipment ground fault leakage current and disconnects all ungrounded (110V & 240V) and grounded (110V neutral) current carrying conductors from the supply source at a preset trip threshold.
G.F.C.I. – A device intended for the protection of personnel that functions to de-energize a circuit, or portion thereof, within an established time when a current to ground exceeds some pre-determined value that is less than that required to operate the overcurrent protective device of the supply circuit.
I have not read the Wikipedia definitions on this topic but I was reading some of their stuff on electrolytic corrosion the other day and a great deal of it is simply incorrect. I would not use a crowd source like that for any critical information.
|
|
|
03-18-2014, 08:02 PM
|
#15
|
TF Site Team
City: Brisbane
Vessel Name: Insequent
Vessel Model: Ocean Alexander 50 Mk I
Join Date: Mar 2012
Posts: 4,262
|
Fair enough re: Wikipedia.
But to me both the ABYC definitions are saying the same thing. There is nothing in those definitions to say there are two different devices.
__________________
Brian
|
|
|
03-18-2014, 08:06 PM
|
#16
|
Guru
City: Here
Join Date: Sep 2012
Posts: 2,940
|
Quote:
Originally Posted by Insequent
Fair enough re: Wikipedia.
But to me both the ABYC definitions are saying the same thing. There is nothing in those definitions to say there are two different devices.
|
One disconnects all power from the source (shore power or generator) and the other disconnects a specific circuit from the panel while leaving all other circuits alone.
|
|
|
03-18-2014, 08:13 PM
|
#17
|
TF Site Team
City: Brisbane
Vessel Name: Insequent
Vessel Model: Ocean Alexander 50 Mk I
Join Date: Mar 2012
Posts: 4,262
|
So, same device and function but different point of installation.
__________________
Brian
|
|
|
03-18-2014, 08:15 PM
|
#18
|
Guru
City: Here
Join Date: Sep 2012
Posts: 2,940
|
Quote:
Originally Posted by Insequent
So, same device and function but different point of installation.
|
Pretty much ... but the RCD is a heavier piece of equipment with a higher threshold, primarily designed to protect equipment while the GFCI is specifically designed to protect crew.
|
|
|
03-18-2014, 08:21 PM
|
#19
|
Member
City: New York
Vessel Name: BoomerangII
Vessel Model: Doral SC270
Join Date: Jan 2014
Posts: 22
|
Quote:
Originally Posted by boatpoker
Pretty much ... but the RCD is a heavier piece of equipment with a higher threshold, primarily designed to protect equipment while the GFCI is specifically designed to protect crew.
|
In the US we're not too familiar with the RCD. My understanding is that it does not provide overload protection though..correct? They must be wired downstream of CB (Unless, it's an RCBO).
|
|
|
03-18-2014, 08:36 PM
|
#20
|
Guru
City: Here
Join Date: Sep 2012
Posts: 2,940
|
Quote:
Originally Posted by BoomerangIII
In the US we're not too familiar with the RCD. My understanding is that it does not provide overload protection though..correct? They must be wired downstream of CB.
|
In the US they are referred to as
"ELCI" ... "Electrical Leakage Circuit Interrupter"
An ELCI (RCD) shall be installed with or in addition to the main shore power disconnect circuit breaker(s) or at the additional overcurrent protection whichever is closer to the shore power connection.
|
|
|
|
|