Extending a cable

I’m installing an AC subpanel to create two separate feeds—one (15 amps) for a cooktop and the other (20 amps) for a convection/microwave oven. The cable that feeds the subpanel from the main panel is 8 mm three-wire. It’s in excellent condition, but very stiff, which makes it difficult to wire the panel inside the polycarbonate box I’m using to house the subpanel. I’d like to extend it a couple of feet with more flexible number 8 boat cable—which will be much easier to make connections inside the box.

What’s the preferred way of doing this: install a terminal block to make the transition or use heat-shrink butt connectors? (I don’t want to replace the 8 mm cable unless both of the above are patently unsafe.)
angus99 is online now   Reply With Quote
Old 06-01-2019, 08:51 AM   #2
Valued Technical Contributor
 
DavidM's Avatar
 
City: Litchfield, Ct
Join Date: Aug 2012
Posts: 6,786
All AC splices or terminal blocks need to be inside NEMA enclosures. Plus it is generally bad practice but within code to make such extensions.

I would replace that cable sized consistent with whatever breaker is protecting the wire or bigger and at least 8 gauge.

David
DavidM is offline   Reply With Quote
Old 06-01-2019, 09:22 AM   #3
Senior Member
 
Pcpete's Avatar
 
City: Mukilteo, WA
Vessel Name: Glauben
Vessel Model: 1988 3818 Bayliner
Join Date: Mar 2019
Posts: 128
I think you may run afoul of the ABYC wiring standards. For instance, if you extended it in your home you could run the ends into a 2x4” electrical box and use wire nuts to connect the wires. However, all boat connections must be mechanical and sealed, so that seems to say you could use a marine butt connection with a shrink plastic cover then the connector and an inch or so of wire covered with marine shrink tube. Here’s where I have a problem with that, even if it meets the standard. You note that the existing cable is stiff which to me suggests some hardening of the insulation caused by heat generated by resistance in the wires. Then there’s the state of the art of the wire. I’m betting that it’s stranded plain copper which we all know tends to corrode. I know it’s a PITA, but if it were me, I’d replace the cables with new marine tinned cable.
That’s a great looking boat by the way. Btw, those amperages seem backwards. Are you sure the cooktop is only 15 amp?
Pcpete is offline   Reply With Quote
Old 06-01-2019, 09:28 AM   #4
Guru
 
foggysail's Avatar
 
City: Ashland, MA
Vessel Model: 1990 Silverton 40 aftcabin
Join Date: Jul 2016
Posts: 1,208
I would just replace the entire cable if the one there is accessible Pcpete suggested above.
foggysail is offline   Reply With Quote
Old 06-01-2019, 01:15 PM   #5
Guru
 
angus99's Avatar
 
City: Signal Mtn., TN
Vessel Name: Stella Maris
Vessel Model: Defever 44
Join Date: Feb 2012
Posts: 2,742
Thanks, all. The cable is stiff because the individual wire strands are thicker than the strands used in the finer flexible marine cable you find today. It’s very bright copper and there’s no evidence of corrosion or of it ever overheating.

The cooktop is a two-burner induction unit and indeed only requires a 15-amp breaker.

Not sure why ABYC would prohibit the use of a properly rated terminal block with cover. Every AC circuit on the boat—positive, neutral and safety ground—currently goes through terminal blocks before being routed to various loads.
angus99 is online now   Reply With Quote
Old 06-01-2019, 01:20 PM   #6
Moderator Emeritus
 
Comodave's Avatar
 
City: Au Gres, MI
Vessel Name: Black Dog
Vessel Model: Formula 41PC
Join Date: Jul 2015
Posts: 21,191
You could do either a butt connector or a junction strip. I would probably go with the junction.
Comodave is offline   Reply With Quote
Old 06-01-2019, 01:43 PM   #7
Guru
 
High Wire's Avatar
 
City: Cape May, NJ
Vessel Name: Irish Lady
Vessel Model: Monk 36
Join Date: Dec 2007
Posts: 4,966
I would split this into two circuits of 20a each with 12/3 boat wire. The original wire is not boat wire. Not illegal but hard to work with.
__________________
Archie
Irish Lady
1984 Monk 36 Hull #46
Currently in Cape May, NJ
High Wire is offline   Reply With Quote
Old 06-01-2019, 01:56 PM   #8
Guru
 
tiltrider1's Avatar
 
City: Seattle
Vessel Name: AZZURRA
Vessel Model: Ocean Alexander 54
Join Date: Aug 2017
Posts: 4,309
Like Comodave said, a marine approved junction box is an acceptable practice. None of us know if the existing wire is to current standards. If it was installed by the builder then it is to the standard your insurance company has accepted.
tiltrider1 is offline   Reply With Quote
Old 06-01-2019, 08:51 PM   #9
Guru
 
angus99's Avatar
 
City: Signal Mtn., TN
Vessel Name: Stella Maris
Vessel Model: Defever 44
Join Date: Feb 2012
Posts: 2,742
I was able to reach an ABYC electrician I know and he explained the standards; so I will be using a terminal strip inside a covered junction box to extend the existing cable. That wire is definitely boat cable that was commonly used in late 80s Defevers and many other trawler-types. The entire boat is wired with it. I always replace any of it that looks corroded, but this one is bright and shiny.

Thanks again for the advice.
.
angus99 is online now   Reply With Quote
Old 06-02-2019, 04:18 PM   #10
Guru
 
foggysail's Avatar
 
City: Ashland, MA
Vessel Model: 1990 Silverton 40 aftcabin
Join Date: Jul 2016
Posts: 1,208
Quote:
Originally Posted by tiltrider1 View Post
Like Comodave said, a marine approved junction box is an acceptable practice. None of us know if the existing wire is to current standards. If it was installed by the builder then it is to the standard your insurance company has accepted.
While that might be good practice, ABYC recommends using insulated butt crimp connectors for splicing. Insulated crimp connectors are common for #8 wire and readily available for splicing. Personally I would not hesitate using a wire size rated insulated splice terminal block inside a panelboard. And remember, ABYC suggestions are not LAW!
foggysail is offline   Reply With Quote
Old 06-02-2019, 04:57 PM   #11
Guru
 
psneeld's Avatar
 
City: Ft Pierce
Vessel Name: Sold
Vessel Model: Was an Albin/PSN 40
Join Date: Oct 2011
Posts: 28,153
I vote the terminal strip in a box too...I bet it is acceptable under ABYC tandards if the connectors, etc inside the box meet the applicable ABYC standard.


Here's but a few AC system snipits from ABYC....there may be additional pertinent items...did"t see any but I scanned quick.



11.14.5.3 Each splice joining conductor to conductor, conductor to connectors, and conductor to
terminals must be able to withstand a tensile force equal to at least the value shown in Table XV for the
smallest conductor size used in the splice for a one minute duration, and not break.



11.14.6 INSTALLATION - GENERAL
11.14.6.1 Junction boxes, cabinets, and other enclosures in which electrical connections are made shall
be weatherproof, or installed in a protected location, to minimize the entrance or accumulation of moisture or
water within the boxes, cabinets, or enclosures.
11.14.6.1.1 In wet locations, metallic boxes, cabinets, or enclosures shall be mounted to minimize the
entrapment of moisture between the box, cabinet, or enclosure, and the adjacent structure. If air spacing is
used to accomplish this, the minimum shall be 1/4 inch (7.0 mm).
11.14.6.1.2 Unused openings in boxes, cabinets, and weatherproof enclosures shall be closed.
11.14.6.2 All conductors shall be supported and/or clamped to relieve strain on connections.
psneeld is online now   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 06:55 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012