We have a vessel that was built to European standards. We are wanting to use US (4 wire) 240v shore power on the vessel that is European (3 wire).
There is nothing on board that is voltage or frequency sensitive.

The other item that we are trying to accomplish is a step up transformer to increase the 120v shore power (it powers a battery charger, then the batteries run a 240v inverter) to 240v.
__________________
Advertisement

zeta is offline   Reply With Quote
Old 04-26-2012, 02:51 AM   #2
Senior Member
 
Larry H's Avatar
 
City: Pacific Northwest
Country: USA
Vessel Name: Jacari Maru
Vessel Model: 2014 Ranger Tug R-27
Join Date: Nov 2010
Posts: 359
Here is a link to step up-step down transformers. Step Up Voltage Transformer Converter - Step Up/Down Voltage Transformer, Step Down Transformer, Step up Transformer, Step up Voltage Transformer, Step UP/Down voltage converter/Regulator, step up and down voltage converters

USA 240v 4 wire power has two hot wires with 240volts between them, a neutral, and a ground. Using the two hot wires you get 240 volts, using either of the hots and the neutral gets 120volts. The ground is a safety ground.

You can try google search on the terms 'step up transformer 120volt to 240 volt'
Another google search would be 'convert usa marine electricity to european marine electricity'

Hope this gets you started in the right direction.
__________________

__________________
Larry H
Cruising the Pacific Northwest
Larry H is offline   Reply With Quote
Old 04-26-2012, 06:27 AM   #3
Guru
 
swampu's Avatar


 
City: Biloxi, MS
Country: USA
Vessel Name: Cajun Rose
Vessel Model: Biloxi Lugger
Join Date: Jul 2011
Posts: 1,328
Quote:
Originally Posted by zeta View Post
We have a vessel that was built to European standards. We are wanting to use US (4 wire) 240v shore power on the vessel that is European (3 wire).
There is nothing on board that is voltage or frequency sensitive.

The other item that we are trying to accomplish is a step up transformer to increase the 120v shore power (it powers a battery charger, then the batteries run a 240v inverter) to 240v.
The circuit breakers are frequency sensitive. and maybe the plugs look different?
swampu is offline   Reply With Quote
Old 04-26-2012, 08:20 AM   #4
Member
 
zeta's Avatar
 
City: Cruising
Country: US
Vessel Name: Zeta
Vessel Model: Diesel Duck 41-Plus
Join Date: Apr 2012
Posts: 11
I understand the differences between the two methods of supplying shore power (US vrs European). At this time there are no CB's until the system gets to a component (this was one of the "dings" that showed up in the purchase servey, no CB for either the 120v or 230/240v shore power connections within 10 feet).

There is already a 120v shore power connection that supplies power to a battery charger (that is all it does). The battery charger then supplies 24v DC to the batteries and an inverter that supplies 230V, 50hz to the vessel.

As stated, there is nothing on the vessel that is not able to operate on a 230-240v, 50-60hz range.

Ideally, the step up transformer would be able to supply 30 Amps (this is what the vessel is set up for) when going from 120v to 240v.
zeta is offline   Reply With Quote
Old 04-26-2012, 09:03 AM   #5
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,385
A circuit breaker should not be sensitive to frequency. It's not even sensitive to the difference between AC and DC. It measures current flow, that's all.

Two thoughts:
1) This is probably a job for a qualified marine electrician. Electricity and water do not play well together so everything needs to be "by the book"

2) If you're going to keep and use the boat in the USA, I suggest converting everything to use the power that's commonly available in the USA. Running everything from batteries and an inverter is pretty inefficient and a battery or inverter failure leaves you without power.
rwidman is offline   Reply With Quote
Old 04-26-2012, 10:50 AM   #6
Guru
 
Phil Fill's Avatar
 
City: Everett Wa
Country: US
Vessel Name: Eagle
Vessel Model: Roughwater 58 pilot house
Join Date: Oct 2007
Posts: 2,919
Quote:
Originally Posted by zeta View Post
We have a vessel that was built to European standards. We are wanting to use US (4 wire) 240v shore power on the vessel that is European (3 wire).
There is nothing on board that is voltage or frequency sensitive.

The other item that we are trying to accomplish is a step up transformer to increase the 120v shore power (it powers a battery charger, then the batteries run a 240v inverter) to 240v.
The concern is the sizing of the wire. If the wire was truly sized for 24 volt DC it maybe to small to handle 12 volt DC. Watts= Amps X volts, so if the volts go down that amps go up. So make sure the wire is sized for 12 volts DC.

Also, I donít think you can combine the two lets of 120 volts AC to make One leg of 240 volts AC. In all application I have done/see the two legs are kept separate. However, again the wire sized for 240 volts may not be able to handle 120 volts AC. watts=amps X volts.

Before you start changing things contact a Marine Electrician. When buying a boat out side of the US make sure it the elecrrical can hand the US electrical. We sell machinery world wide so the electrical is has to be clarified so we buy the correct motors and controlls.
Phil Fill is offline   Reply With Quote
Old 04-26-2012, 11:05 AM   #7
Member
 
zeta's Avatar
 
City: Cruising
Country: US
Vessel Name: Zeta
Vessel Model: Diesel Duck 41-Plus
Join Date: Apr 2012
Posts: 11
Volts and amps

We are getting a bit lost here. We are not trying to change any voltage in the vessel.. It will stay 24v dc and 230/240v AC.

We are trying to step up the 120v AC when that shore power is used to the vessels 230/240v AC needs.

Then with a separate shore power source supply directly 240v AC.
zeta is offline   Reply With Quote
Old 04-26-2012, 03:33 PM   #8
Guru
 
Phil Fill's Avatar
 
City: Everett Wa
Country: US
Vessel Name: Eagle
Vessel Model: Roughwater 58 pilot house
Join Date: Oct 2007
Posts: 2,919
Quote:
Originally Posted by zeta View Post
We are getting a bit lost here. We are not trying to change any voltage in the vessel.. It will stay 24v dc and 230/240v AC.

We are trying to step up the 120v AC when that shore power is used to the vessels 230/240v AC needs.

Then with a separate shore power source supply directly 240v AC.

You can buy a converter or a transformer that will step up 120 volts to 240. http://www.220-electronics.com/Transformers/trans/prod.html Keep in mind the converted amps/volts ,the wire size and fuse size required.

It would best to know if the wire is sized for 12 volt DC and/or 120 volt AC?
Phil Fill is offline   Reply With Quote
Old 04-26-2012, 06:25 PM   #9
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,385
Let me see if I can make this clear;

All the AC appliances on your boat run on 240 volt AC. All the DC appliances on your boat run on 24 volts DC.

The boat is wired for 140 volts AC and 24 volts DC.

That's fine if you're at a marina that offeres 240 volts AC after you have an electrician change your shorepower inlet and possibly the wiring to the main panel.

You want to install a transformer so you can use your 240 volt appliances at marinas that only offer 120 volts AC shorepower connections.

Am I close?

You need a transformer that will input 60 amps AC at 120 volts and output 30 amps AC at 240 volts. I've never seen a marina with 60 amps at 120 volts, the most I'm aware of is 50 amps so you're only going to get 25 amps at 240 volts.

If you're satisfied with pluggung things in, you can find the transformer and cables. If you want something automatic or switched, you better call in an electrician. I would be looking for something industrial or marine, something that will stand up to the salt air and vibration in a marine environment.

I don't think it will be lightweight or inexpensive.
rwidman is offline   Reply With Quote
Old 04-26-2012, 10:37 PM   #10
Member
 
zeta's Avatar
 
City: Cruising
Country: US
Vessel Name: Zeta
Vessel Model: Diesel Duck 41-Plus
Join Date: Apr 2012
Posts: 11
Just about right...

The vessel is wired for 24V dc and 230V ac. There are two shore power connections.. one 120V ac (3 wire) and one 230V ac (European 3 wire).

The 120V shore power supplies power to a 24v dc battery charger, and that is all it does.

The batteries supply power to an inverter that produces 230V ac, 50hz power to the vessel.

The 230v shore power was used in Europe to supply power directly to the vessel.
zeta is offline   Reply With Quote
Old 04-27-2012, 05:11 AM   #11
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 19,145
You might consider simply purchasing a modern batt charger.]

Some will accept most any input 120v US or 230V euro and still work fine.
Matervolt , and Charles should be looked at.

FF
FF is online now   Reply With Quote
Old 04-27-2012, 05:59 AM   #12
Guru
 
swampu's Avatar


 
City: Biloxi, MS
Country: USA
Vessel Name: Cajun Rose
Vessel Model: Biloxi Lugger
Join Date: Jul 2011
Posts: 1,328
Quote:
Originally Posted by rwidman View Post
A circuit breaker should not be sensitive to frequency. It's not even sensitive to the difference between AC and DC. It measures current flow, that's all.
rwidman, what is the difference between the 50 and 60 hz circuit breaker panels? The only reason I ask is that I found one for sale that was cheep but it was 50hz euro design. They said it wouldn't work.
swampu is offline   Reply With Quote
Old 04-27-2012, 07:07 AM   #13
Guru
 
Anode's Avatar
 
City: Missourah
Country: USA
Vessel Name: M/V Scout
Vessel Model: Sundowner Tug 30'
Join Date: Jul 2010
Posts: 645
There are breakers that are specific to 50 Hz or to 60 Hz and cannot be interchanged safely. There are breakers that can be interchanged. The new BlueSea breakers that I just purchased can be interchanged.
There are breakers that are specific to DC or AC and breakers that can be interchanged. DC breakers need beefier contacts and larger air gaps for the same current and voltage. Especially true at the higher ratings and should not be interchanged unless clearly marked.
Carefully reading the ratings labeled on the breakers and using the appropriate ones is your only safe option.
__________________
Chip

Deliveries & Yacht Services
www.captainchip.com
Anode is offline   Reply With Quote
Old 04-27-2012, 07:29 AM   #14
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,385
There are speciality circuit breakers of course, but when you go to the marine store to but a circuit breaker for your boat, it will be fine for AC or DC, and aany normal frequency.

rwidman is offline   Reply With Quote
Old 04-27-2012, 07:52 AM   #15
Member
 
zeta's Avatar
 
City: Cruising
Country: US
Vessel Name: Zeta
Vessel Model: Diesel Duck 41-Plus
Join Date: Apr 2012
Posts: 11
It is not the battery charger that we are concerned with. There are two battery chargers on the vessel. One for the 120v and another that is a charger/inverter that is 240v (accepts the 200+V range).

What we need is a method of connecting the US 240v four wire system to the European three wire system.

Blue Sea Systems carry's CB panels that are specified as European for 50hz. These can be seen on their web site: bluesea.com
zeta is offline   Reply With Quote
Old 04-27-2012, 07:54 AM   #16
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 7,825
Zeta, you have received enough conflicting advice, that if followed, will insure your boat will burn. Dependent upon where the vessel is located there should be a good marine electrician who works for a reputable firm and is experienced at how your problem best be solved. It cannot be done over the internet unless you have drawn up an accurate line diagram, and even then you have no idea whether the advice you are receiving is accurate.

This is not a new question or a unique set of circumstances. Boats travel from NA to Europe, Latin and South America and the South Seas every day. As R Widman suggested, get a good marine electrican/firm engaged. Where is the vessel located?
sunchaser is offline   Reply With Quote
Old 04-27-2012, 08:09 AM   #17
Member
 
zeta's Avatar
 
City: Cruising
Country: US
Vessel Name: Zeta
Vessel Model: Diesel Duck 41-Plus
Join Date: Apr 2012
Posts: 11
I do not "follow" any advise without verification. In part, that is what we are doing. The situation has already been looked at by a firm in Ft. Lauderdale. They provided a wiring diagram. But even "experts" can be wrong, thus the verification.

Some good, some bad advise is found on the internet. It is always a place to start when doing research.

The vessel is working it's way to San Diego.
zeta is offline   Reply With Quote
Old 04-27-2012, 08:18 AM   #18
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 7,825
You will have no problem finding reliable and experienced dual voltage marine electrical people in San Diego and vicinity. Nice to see you using your boat, that is what DDs are intended.
sunchaser is offline   Reply With Quote
Old 04-27-2012, 09:15 AM   #19
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,385
Quote:
Originally Posted by zeta View Post
It is not the battery charger that we are concerned with. There are two battery chargers on the vessel. One for the 120v and another that is a charger/inverter that is 240v (accepts the 200+V range).

What we need is a method of connecting the US 240v four wire system to the European three wire system.

Blue Sea Systems carry's CB panels that are specified as European for 50hz. These can be seen on their web site: bluesea.com
The first response (by Larry H) explains the USA standard electrical system pretty well.

Once your electrician has converted the boats input connections to the USA standard, you will have 120 volts AC available for your charger and 240 volts AC for your other appliances..
rwidman is offline   Reply With Quote
Old 04-27-2012, 10:30 PM   #20
Guru
 
swampu's Avatar


 
City: Biloxi, MS
Country: USA
Vessel Name: Cajun Rose
Vessel Model: Biloxi Lugger
Join Date: Jul 2011
Posts: 1,328
Quote:
Originally Posted by sunchaser View Post
Zeta, you have received enough conflicting advice, that if followed, will insure your boat will burn.
__________________

swampu is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 08:48 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012