C Lectric, Yes, the cumulative amp draw is shown but that is for all appliances together as they come on and off. I collected the instantaneous amperages and estimated the daily requirements based on what I thought would be realistic for the usage this summer.

Jim, Sent from my iPad using Trawler
__________________
Advertisement

JDCAVE is offline   Reply With Quote
Old 02-19-2014, 11:40 PM   #22
Guru
 
C lectric's Avatar
 
City: Somewhere
Country: , Canada
Vessel Name: Island Pride
Vessel Model: Palmer sedan 32'
Join Date: Oct 2007
Posts: 1,868
Ok, yes, I understand what you have done. I thought the cumulative function was either missing or not functional.

Keep track and it will tell you as the seasons change and the equipment useage changes how good your estimates were.

Sounds like you are on your way.
__________________

C lectric is offline   Reply With Quote
Old 02-20-2014, 03:12 AM   #23
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,518
Of what value ia a SOC meter if a battery in a bank is partially or totally dead?

The SOC meter is a system , not used for just a one time snap shot.

IT observes the batts being charged (any source) and discharged and then gives a current state of charge .

If a batt fails usually its best to replace the entire set , not just one.
FF is offline   Reply With Quote
Old 02-20-2014, 09:50 PM   #24
Dauntless Award
 
Wxx3's Avatar
 
City: New York, NY
Country: USA
Vessel Name: Dauntless
Vessel Model: Kadey Krogen 42 - 148
Join Date: Jan 2013
Posts: 2,312
Jim,

nice summary, but as Larry mentioned, you really just need a full 24 hours not connected and see what your consumption really is.

Also,I think your Novacool is actually pretty close and the muffin fan will only make a small change, if measurable at all.

I replaced my halogen spreader lights with LEd's and they are just as bright. Halogens are a terrible power hog and heat producer. You can find LEDs that will replace with the same color.

lastly, one of the first things I did was to separate my start and house bank by buying ONE Group 31 as the new engine start and it works great.
__________________
M/Y Dauntless, New York
a Kadey Krogen 42 Currently https://share.delorme.com/dauntless
Blog: https://dauntlessatsea.com
Find us: https://share.delorme.com/dauntless
Wxx3 is offline   Reply With Quote
Old 02-21-2014, 11:45 AM   #25
Guru
 
JDCAVE's Avatar
 
City: Lions Bay, BC
Country: Canada
Vessel Name: Phoenix Hunter
Vessel Model: Kadey Krogen 42 (1985)
Join Date: Apr 2011
Posts: 1,605
Richard: I agree that monitoring a full 24 hour day is a good approach to the problem, however I'm trying to estimate the summertime consumption and it's currently winter. The fridge and freezer will be working the hardest when it's hot inside the boat. The method I used is referenced in Nigel Calder's book and the algebra is pretty straight forward. I was trying to obtain a ballpark estimate of consumption to see if I could replace the current bank with a smaller one and the answer is no. Also, note that the meter on the boat only measures the cumulative amp hours for the total vessel systems. I think it was important for me to understand which systems have the most draw. The large draw from "circumvent" was a surprise and I will consider that during the summer when I am off-grid.

Note that the Novacool draw includes the muffin fans, which go on and off as the fridge and freezer cycle on and off. I'm just trying to make the system more efficient by more effectively cooling down the space where the units are located. I intend to redirect the muffin fans' efforts to remove hot air from that space.

Jim
JDCAVE is offline   Reply With Quote
Old 02-22-2014, 06:56 AM   #26
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,518
Looking at the huge power requirements of this boat , my first thought would not be how to make and store that much power , but how could I live with 1/4 or 1/2 the daily power load.
FF is offline   Reply With Quote
Old 02-22-2014, 07:36 AM   #27
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 6,361
As an attempt to shed some load as FF suggests some thoughts are :

Is your Novakool a fridge freezer combination?
If yes, why do you need a separate freezer?
The purpose of the circumvent, as you noted, needs another look.
What does the bubbler do?

But when cruising, between the on engine alternator and genset it would appear you have no problems but merely curiosities.
sunchaser is offline   Reply With Quote
Old 02-22-2014, 08:35 AM   #28
Guru
 
O C Diver's Avatar
 
City: Fort Myers, FL... Summers in Crisfield, MD
Country: USA
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 4,813
For anyone looking for a 0 to 60 volts DC and up to 130 amps version of a Kill A Watt meter, here is a DC Watt Meter.

Click image for larger version

Name:	WattMeter-PP_xlrg.jpg
Views:	85
Size:	76.5 KB
ID:	27601

Measures current draw and cumulative total over an extended period. Wiring it inline with your fridge for a week would give you a real good idea of average consumption. Unfortunately they aren't as plug and play as the Kill A Watt meter. Have been very happy with mine for non boating related uses.

DC Watt Meter

Ted
__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
O C Diver is offline   Reply With Quote
Old 02-22-2014, 11:21 AM   #29
Guru
 
JDCAVE's Avatar
 
City: Lions Bay, BC
Country: Canada
Vessel Name: Phoenix Hunter
Vessel Model: Kadey Krogen 42 (1985)
Join Date: Apr 2011
Posts: 1,605
The fridge and freezer are separate and large units. As mentioned I intend to make them more efficient by adding insulation to the doors and providing better ventilation of the space where the units are housed. We are going to be away from reliable food stores for several months at a time so prefer these fridge and freezer units.

I like that kill a watt meter! Must get one.

Jim, Sent from my iPad using Trawler
JDCAVE is offline   Reply With Quote
Old 05-13-2014, 10:16 AM   #30
Guru
 
JDCAVE's Avatar
 
City: Lions Bay, BC
Country: Canada
Vessel Name: Phoenix Hunter
Vessel Model: Kadey Krogen 42 (1985)
Join Date: Apr 2011
Posts: 1,605
As mentioned elsewhere, I finally went through the approach of insulating the freeze and fridge doors and reversing the muffin heater fans so they vent air out of the pilothouse watch berth.

I talked to one of the managers at Novakool at the manufacturing plant when I weren't by to pick up a new gasket for the fridge. He mentioned that the duty cycle on these is typically 50%, meaning that they run 50% of the time. That will go up to 80% of the time on hot days.

So planning electrical loads on my system, that would work out to 4.9 amps for the fridge and 6.6 for the freezer, 11.5 amps or 138 amp hours for the day. Probably conservative.

Jim
JDCAVE is offline   Reply With Quote
Old 05-13-2014, 12:15 PM   #31
Dauntless Award
 
Wxx3's Avatar
 
City: New York, NY
Country: USA
Vessel Name: Dauntless
Vessel Model: Kadey Krogen 42 - 148
Join Date: Jan 2013
Posts: 2,312
my draw for the Vitrifrigo Fridge and Freezer seems to average about 5 amps an hour or 120 amps, 1440 watts per 24 hours.

In the coming days, i will post a more detailed analysis. The addition for the solar panels has also made a huge difference.
__________________
M/Y Dauntless, New York
a Kadey Krogen 42 Currently https://share.delorme.com/dauntless
Blog: https://dauntlessatsea.com
Find us: https://share.delorme.com/dauntless
Wxx3 is offline   Reply With Quote
Old 05-13-2014, 12:43 PM   #32
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 6,361
Quote:
Originally Posted by JDCAVE View Post
We are going to be away from reliable food stores for several months at a time so prefer these fridge and freezer units.

Nowhere in the PNW are you away from reliable food stores months at a time. Days maybe, weeks at the most if you're a hermit. The whole area is set up to supply workers and fun seekers on the water.

Years ago we overstocked badly when traveling in the PNW and agonized over how to keep stuff frozen, it turned out to be not a concern and freezer size and needs dropped a lot.

We have some friends on a KK42 who justified a huge freezer for dog food storage different strokes.
sunchaser is offline   Reply With Quote
Old 05-14-2014, 07:10 AM   #33
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,518
If I stay with the current size of bank, it would be prudent to fire up the generator after 36 hour or so.

The fastest charge from the noisemaker will come from a large alternator belted on to it with a smart V regulator .

IF your set is over 10KW , a large 150 A or more big buck battery charger Might be able to match the charge of a 135A alt.

The question then becomes TIME.

Will you pay 2x for batts that can accept a higher RATE of charge to lower noisemaker operating hours?

NOT requiring the energy is always cheaper than creating/storing it.

Extra insulation on the reefer?
FF is offline   Reply With Quote
Old 05-14-2014, 11:27 AM   #34
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 3,952
In my opinion... This whole power system thing that folks get into tends to miss the point completely from an engineering prospective.

The key to success is to size your battery bank, your charger, and your generator to compliment each other. Daily loads don't much matter from an engineering standpoint unless you have a pre-conceived "cycle time" target in mind, (as long as you can meet your peak load requirements)

Then, and only then is it prudent to look at your actual daily loads in an effort to lengthen your cycle time.

I'm going to use our boat as an example of a properly engineered power system.

We have...

840 amp hours of house bank
150 amp inverter/charger
9 KW generator

Everything is sized to work together.

Our battery bank can accept our chargers full output current, and recharge our battery bank in practice in a reasonable amount of time.

Our generator can supply the full current requirement of the charger, plus all the other loads we have on the boat.

Our actual DC loads are not relevant to this system design for the most part. All they do is determine how often we need to go in to a charge cycle.
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
www.mvlisasway.com
ksanders is offline   Reply With Quote
Old 05-14-2014, 12:23 PM   #35
Guru
 
JDCAVE's Avatar
 
City: Lions Bay, BC
Country: Canada
Vessel Name: Phoenix Hunter
Vessel Model: Kadey Krogen 42 (1985)
Join Date: Apr 2011
Posts: 1,605
FF. Yes, I have insulated the refer units as best as I can. Also added 1inch high density foam on the doors.

House bank is 1125 (10 T-105's). Genset is a near new Entec West 4.1 kW, so it's small and it seems to be able to handle the charger. Inverter charger is an older Freedom 20, 100 amp. I'm expecting to cycle the batteries 50-80% SOC. 1-2 hours on the genset at 0.5 GPH. Will heat the water at the same time.
JDCAVE is offline   Reply With Quote
Old 05-14-2014, 02:12 PM   #36
Guru
 
timjet's Avatar
 
Join Date: Apr 2009
Posts: 1,905
[QUOTE=ksanders;233843

Our actual DC loads are not relevant to this system design for the most part. All they do is determine how often we need to go in to a charge cycle.[/QUOTE]

Another example:
I have only 420 ah house bank.
100 amp charger.
Daily DC load is about 250 amps per day.

250 amp load will require a genny run time of 2.5 hrs but with inefficiencies probably 3 hrs or more.

So I run the genny 1.5 hrs in am and again in pm.

If I plan on running the boat then the genny gets a rest as the 2 100 amp alternators will replenish the dc amps used in 1.5 hrs.
__________________
Tim
Tampa Bay
Carver 355 ACMY Twin Cummins Diesels Sold
timjet is offline   Reply With Quote
Old 05-14-2014, 03:59 PM   #37
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 3,952
Quote:
Originally Posted by timjet View Post
Another example:
I have only 420 ah house bank.
100 amp charger.
Daily DC load is about 250 amps per day.

250 amp load will require a genny run time of 2.5 hrs but with inefficiencies probably 3 hrs or more.

So I run the genny 1.5 hrs in am and again in pm.

If I plan on running the boat then the genny gets a rest as the 2 100 amp alternators will replenish the dc amps used in 1.5 hrs.
Exactly!

Your system appears to be well designed, IE everything works together well

If you increased the size of your house bank you would probably want to increase your charger as well for example.
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
www.mvlisasway.com
ksanders is offline   Reply With Quote
Old 05-14-2014, 04:11 PM   #38
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 3,952
Quote:
Originally Posted by JDCAVE View Post
FF. Yes, I have insulated the refer units as best as I can. Also added 1inch high density foam on the doors.

House bank is 1125 (10 T-105's). Genset is a near new Entec West 4.1 kW, so it's small and it seems to be able to handle the charger. Inverter charger is an older Freedom 20, 100 amp. I'm expecting to cycle the batteries 50-80% SOC. 1-2 hours on the genset at 0.5 GPH. Will heat the water at the same time.

If I'm reading your post correctly...

You intend to cycle between 50% and 80% on your 1125 amp hour battery bank?

So you'll start recharging at 50% or 562 amp hours remaining.
You'll stop charging at 80% or 900 amp hours remaining.
So, during your charge cycle you're planning on replacing 338 amp hours.

Your charger is 100 amps max, but it really wont put out exactly 100 the whole recharge time, but we'll use that number for calculation sake.

You're looking at a generator run time of 3 hours 20 minutes, minimum. You're really looking at probably more like 4 or 41/2 hours.

If you're expecting 1-2 hours (as in your post) of generator run time, that is not possible.
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
www.mvlisasway.com
ksanders is offline   Reply With Quote
Old 05-15-2014, 06:53 AM   #39
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,518
Your charger is 100 amps max, but it really wont put out exactly 100 the whole recharge time,

Agreed , most old small chargers are not capable of creating their rating for many minuets , never mind holding 100A for hours!

My guesstimate is at least 4 hours , probably 5 hours to go from 50% to 80% or 85%.

A SOC meter will tell everything required as this is attempted.

After a couple of weeks of cruising I hope the actual results are posted.

Armchair guesstimates relying on company advertising seldom come true.

Will be interesting to learn the percent of charge that is done by the main engine as the boat travels.
FF is offline   Reply With Quote
Old 05-16-2014, 11:23 AM   #40
Guru
 
JDCAVE's Avatar
 
City: Lions Bay, BC
Country: Canada
Vessel Name: Phoenix Hunter
Vessel Model: Kadey Krogen 42 (1985)
Join Date: Apr 2011
Posts: 1,605
Thanks everyone. I've got a better idea of things now, than I had last summer that for sure. I've gone through the power draw calculations again with a cycle time on the fridge and freezer of 12 hours per day. That works out to 120 amp hours per day. Other systems another 60 for a total of 185 amp hours.

The reality is I have a 4.1 kW genny and a 100 amp charger. It seems to run at about 75 plus amps, so that would indicate a genny runtime of 3-4 hours.

Jim
__________________

JDCAVE is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 04:33 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012