Can you "clean" a power cord?

So we finally had a dry day yesterday and I stopped by the boat to check the power cord connections. I usually do this every couple of weeks but this is a new to us boat and it had been raining for a long time and hadn't had a chance to check it before. I found fairly substantial corrosion on the boat side power input plug. So I pulled it apart... I spent the rest of the day replacing wiring. I am now replacing all connections in the boat as well.

A few pics... I know, not really that bad huh? I mean, shouldn't you use wire nuts on boat wiring? Note the solid "Romex"!!!

My question is, I hate to trash the power cord. In the AF, we used a burnishing tool to clean contacts. Has anyone tried to clean the contacts of a power cord or is it a replacement of the connector. The cord is fine other than corrosion on where it plugged into this mess!

~ Jeff
Attached Thumbnails
Click image for larger version

Name:	image.jpg
Views:	85
Size:	92.3 KB
ID:	27696  
__________________
Advertisement

Jbear is offline   Reply With Quote
Old 02-26-2014, 08:52 AM   #2
Senior Member
 
Jbear's Avatar
 
City: Anacortes
Country: US
Vessel Name: Adelante
Vessel Model: Shin Shing, Eagle 35'
Join Date: Oct 2013
Posts: 127
And associated wiring...
Attached Thumbnails
Click image for larger version

Name:	image.jpg
Views:	73
Size:	125.5 KB
ID:	27697  
__________________

Jbear is offline   Reply With Quote
Old 02-26-2014, 09:27 AM   #3
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,390
You can try to clean the contacts with electrical contact cleaner (from the home center or electrical supply house) and you can try using a very fine abrasive or tool made for the purpose. Depending on how corroded the contacts are, you may be able to make a satisfactory repair.

Remember though, if either the plug or socket is damaged and not making good contact, they will soon both be damaged and in need of replacement.

BTW: It's close to impossible to clean the contact surfaces of the female connector other than with the contact cleaner and repeated inserting and twisting the male part.
rwidman is offline   Reply With Quote
Old 02-26-2014, 11:36 AM   #4
Guru
 
Phil Fill's Avatar
 
City: Everett Wa
Country: US
Vessel Name: Eagle
Vessel Model: Roughwater 58 pilot house
Join Date: Oct 2007
Posts: 2,919
Our power cord is 15+ years old and check/clean it every year. I just use light grit sand paper.

It is recommend on older boats to install a double throw circuit breaker between the boats shore power plug and the main power selector switch. Most older boats do not have. So if there is a problem there is a circuit breaker at both ends.
Phil Fill is offline   Reply With Quote
Old 02-26-2014, 03:59 PM   #5
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,390
Quote:
Originally Posted by Phil Fill View Post
Our power cord is 15+ years old and check/clean it every year. I just use light grit sand paper.

It is recommend on older boats to install a double throw circuit breaker between the boats shore power plug and the main power selector switch. Most older boats do not have. So if there is a problem there is a circuit breaker at both ends.
A double pole circuit breaker is supposed to be the "main" breaker on the AC electrical panel. It controls all the others and disconnects the hot and neutral conductors.

If the distance (measured along the conductors) from the shore power inlet to the AC electrical panel exceeds ten feet, a double pole circuit breaker is to be installed within ten feet of the shore power inlet.

It doesn't matter how old the boat is.
rwidman is offline   Reply With Quote
Old 02-26-2014, 04:09 PM   #6
Senior Member
 
City: Dayton, OH
Country: USA
Join Date: Apr 2013
Posts: 195
To get into tight spots to clean, ask the admiral for her fingernail emory board thing. Don't forget to buy her a new one, or just say, "what you talking about, hon?" when she wants it back..
Bluto is offline   Reply With Quote
Old 02-26-2014, 04:55 PM   #7
Guru
 
Xsbank's Avatar
 
City: Pender Harbour, BC
Country: Canada
Vessel Name: Gwaii Haanas
Vessel Model: Vancouver Shipyards Custom Aluminum 52
Join Date: Sep 2013
Posts: 2,447
Can you use dielectric grease on the contacts to protect from corrosion?
__________________
Don't believe everything that you think.
Xsbank is offline   Reply With Quote
Old 02-26-2014, 05:42 PM   #8
TF Site Team
 
FlyWright's Avatar
 
City: California Delta and SF Bay
Country: Sacramento, CA, USA (boat in Vallejo)
Vessel Name: FlyWright
Vessel Model: Marshall Californian 34 LRC
Join Date: Apr 2008
Posts: 10,184
Why not just replace the corroded outlet? When I questioned mine, I replaced the boat plug and the cord end. Now I know the precise condition of the components. No worries and no regrets.
__________________
Al

Custom Google Trawler Forum Search
FlyWright is online now   Reply With Quote
Old 02-27-2014, 08:17 AM   #9
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,390
Quote:
Originally Posted by Xsbank View Post
Can you use dielectric grease on the contacts to protect from corrosion?
Yes and that's good practice.
rwidman is offline   Reply With Quote
Old 02-27-2014, 08:21 AM   #10
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,390
Quote:
Originally Posted by FlyWright View Post
Why not just replace the corroded outlet? When I questioned mine, I replaced the boat plug and the cord end. Now I know the precise condition of the components. No worries and no regrets.
Any shorepower cord that's in daily use outdoors in the sun and with the boat and possibly the dock moving with the waves and wind is going to deteriorate. It's a good idea to check it now and then and consider replacing it after several years.

When I replaced my cord and shorepower inlet (on the boat), I found that the original installer had not followed the directions and had tinned the wires before putting them in the clamps.

I cut that part off and redid it the correct way.
rwidman is offline   Reply With Quote
Old 02-27-2014, 10:31 AM   #11
Senior Member
 
Jbear's Avatar
 
City: Anacortes
Country: US
Vessel Name: Adelante
Vessel Model: Shin Shing, Eagle 35'
Join Date: Oct 2013
Posts: 127
Yes, already replaced the outlet on the boat, re-terminated all 120VAC wiring, cleaned up all cabling, replaced entrance cable from outlet to dbl throw main breaker, replaced all outlets with GFI, replaced cable to batt charger, etc. it's been a fun couple of days. One of the great times to have a single engine as there is much more space below.

I just hate to toss a 100' power cable for a corroded end. I may try to replace the end and keep it as a spare.

Jeff
Jbear is offline   Reply With Quote
Old 02-27-2014, 10:47 AM   #12
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,390
Quote:
Originally Posted by Jbear View Post
Yes, already replaced the outlet on the boat, re-terminated all 120VAC wiring, cleaned up all cabling, replaced entrance cable from outlet to dbl throw main breaker, replaced all outlets with GFI, replaced cable to batt charger, etc. it's been a fun couple of days. One of the great times to have a single engine as there is much more space below.

I just hate to toss a 100' power cable for a corroded end. I may try to replace the end and keep it as a spare.

Jeff
If you can get the correct end (cord cap) and can install it correctly, you should be fine. Usually it's best to cut the cord back a few inches or even a couple feet because there has been a lot of flexing near the ends over the years. At the very least, cut the cord back to where you have clean (not black) wire.
rwidman is offline   Reply With Quote
Old 02-27-2014, 11:00 AM   #13
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,919
If you have a cord with molded plugs and it was a goor shore power cord to start...it's pretty rare that there is corrosion in the cord itself...usually the plug ends take all the beating.

Check for damage and buy replacement ends...do it right and take care of the replacement ends and it should last till the next time you plug into a crappy dock receptacle and the whole process starts over again....buying a whole new cord every time would be a huge waste.
psneeld is online now   Reply With Quote
Old 02-27-2014, 12:46 PM   #14
Guru
 
City: Fort Myers
Country: USA
Join Date: Jul 2013
Posts: 956
I think the original question from the OP was can you clean it. I've witnessed many attempts at this on my dock, generally if done later in the afternoon will gather a crowd with all kinds of opinions, in the end the cord maybe a little cleaner, but now the protective plastic layer removed it didnt take long to discolor again.
Marlinmike is offline   Reply With Quote
Old 02-27-2014, 02:00 PM   #15
Senior Member
 
Jbear's Avatar
 
City: Anacortes
Country: US
Vessel Name: Adelante
Vessel Model: Shin Shing, Eagle 35'
Join Date: Oct 2013
Posts: 127
Sorry, should have been more clear. I meant can you clean the contacts in the plug. Specifically the female portion that connects to the boat outlet. I think I am just going to replace the plug end.

Thanks,
Jeff
Jbear is offline   Reply With Quote
Old 02-28-2014, 06:09 AM   #16
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,531
>I think I am just going to replace the plug end.<

There are many quality levels , sadly the bargain plugs may not be ideal.

Hubbel costs more initially , but,,,,,,
__________________

FF is online now   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 01:56 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012