Old 06-21-2016, 01:10 PM   #1
Guru
 
angus99's Avatar
 
City: Signal Mtn., TN
Country: US
Vessel Name: Stella Maris
Vessel Model: Defever 44
Join Date: Feb 2012
Posts: 1,382
Breaker ratings

I have an older but unused Airpax breaker labeled "F.L. Amps-40" and "Trip amps-50."

Which of these ratings should I be paying attention to for correct sizing? This is for a davit that seems to have done well with a 50-amp breaker for many years. I'm replacing it because it was damaged.

Thanks in advance.
__________________
Advertisement

angus99 is offline   Reply With Quote
Old 06-21-2016, 01:45 PM   #2
Guru
 
City: Seaford Va on Poquoson River, VA
Country: United States
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 1,301
The breaker protects only the wiring, not the powered device.
What gauge is the wire?
http://forums.mikeholt.com/showthread.php?t=125173
Difference may be motor current versus resistive current . FLA is full load amps.

Your breaker is likely a 40 amp breaker.
The 50 amp is instantaneous trip.
A breaker can run at it's rating, when amps go over that, it will eventually trip off.
__________________

sdowney717 is offline   Reply With Quote
Old 06-21-2016, 03:25 PM   #3
Guru
 
angus99's Avatar
 
City: Signal Mtn., TN
Country: US
Vessel Name: Stella Maris
Vessel Model: Defever 44
Join Date: Feb 2012
Posts: 1,382
Thanks, I understand that it protects the wire (which I believe is #6). I just need to know whether I have a 40 or 50-amp breaker.
angus99 is offline   Reply With Quote
Old 06-21-2016, 06:35 PM   #4
Guru
 
City: Seaford Va on Poquoson River, VA
Country: United States
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 1,301
Wire Sizes and Fuses
6 gauge wire good up to 80 amps.
So a 50 amp breaker is ok. I would probably go to 50 amp breaker. The motor may occasionally draw more than its rated power. And the motor might also has an internal thermal breaker.

Does the motor have a plate telling you any info?
sdowney717 is offline   Reply With Quote
Old 06-21-2016, 08:12 PM   #5
Guru
 
kchace's Avatar
 
City: Brookline, NH
Country: USA
Vessel Name: Blue Heaven
Vessel Model: Albin 43 classic double cabin, twin 135 Lehmans
Join Date: Sep 2013
Posts: 757
Quote:
Originally Posted by angus99 View Post
Thanks, I understand that it protects the wire (which I believe is #6). I just need to know whether I have a 40 or 50-amp breaker.
You have a 40 amp breaker. It's normal for a breaker to hold until about 20% over its rating (common for fuses too). Manufacturers even publish "trip charts" which document how long it will take a fuse or breaker to trip depending on level of overload. All common fuses and breakers I've ever researched are roughly in that 20% above range, after that, time to blow all depends on the extent of the
Overload.

Ken
kchace is offline   Reply With Quote
Old 06-21-2016, 09:19 PM   #6
Guru
 
angus99's Avatar
 
City: Signal Mtn., TN
Country: US
Vessel Name: Stella Maris
Vessel Model: Defever 44
Join Date: Feb 2012
Posts: 1,382
Appreciate the info. I'll be at the boat tomorrow and will verify the wire size and amp draw of the motor.
angus99 is offline   Reply With Quote
Old 06-22-2016, 11:44 AM   #7
Guru
 
Join Date: Oct 2007
Posts: 734
Be aware that the "amp draw" of your motor as stated on the motor plate is most likely the draw while the motor is running. The initial start-up current draw can be significantly higher. For example, I had a problem with my garage door opener 15 amp breaker going off occasionally. The "draw" was stated as only 3.5 amps. Turned out start-up draw could be as high as 18 amps. Solved the problem with a slow-blow hiogh magnetic 15 amp breaker. Now multiple doors operate simultaneously just fine.
In your situation I would definitely replace with another 50amp breaker (not the 40amp) or even higher, no matter what the motor plate indicates.
Chrisjs is offline   Reply With Quote
Old 06-22-2016, 12:11 PM   #8
Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 3,882
All breakers have trip characteristics that can be expressed on a curve. Likely your breaker can run continuously at 40a, trip in xxx seconds at 45a, and trips quickly ?? at 50a. Without the curve, can't really tell.

But you should be ok to install it and try it. If it does not trip, you should be good to go.
Ski in NC is offline   Reply With Quote
Old 06-23-2016, 01:46 PM   #9
Guru
 
angus99's Avatar
 
City: Signal Mtn., TN
Country: US
Vessel Name: Stella Maris
Vessel Model: Defever 44
Join Date: Feb 2012
Posts: 1,382
Sounds like a plan. Thanks, Ski and all.
__________________

angus99 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 01:45 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012