Boat Battery problem Help!

Boat Battery problem Help!

OK - This is what I need help with:

There are two (2) banks of batteries on the boat - 1 House - 1 Engine start.
They each go to a 4 position Battery switch: Position 1 - Both - 2 - Off. The switch has been disconnected & tested for the propper continuity & working when cycled. There is no continuity between positions 1 & 2 and it’s off when in that position.

Here is the problem, it doesn’t matter which position the switch is in, both banks are connected to all loads. The house circuits can be used when in the “start” (position1) & the engine can be started from the “house” (Position 2). It’s as if the switch is always in the “Both” position.

Again the switch itself works and positions 1 - 2 - Both are isolated in the switch.

On the battery banks the Neutral terminals (“Minus” - ) are joined & then go to ground. I can’t see any other joining of the positive terminals.

Where do I start looking?
__________________
Advertisement

1Sailor is offline   Reply With Quote
Old 09-30-2016, 04:15 PM   #2
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 6,146
Sounds like you have a parallel switch in the on position.
__________________

sunchaser is offline   Reply With Quote
Old 09-30-2016, 04:35 PM   #3
Guru
 
O C Diver's Avatar
 
City: Fort Myers, FL... Summers in Crisfield, MD
Country: USA
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 4,671
It sounds to me (and I could be wrong) like the switch is wired wrong. Normally, the load is switched between the batteries. If one of the batteries is connected where the load should be and the load is where the battery should be, you might get that result. Trace the cables and make sure they're on the correct terminals on the battery switch.

Ted
__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
O C Diver is online now   Reply With Quote
Old 09-30-2016, 04:58 PM   #4
Senior Member
 
Ka_sea_ta's Avatar
 
City: Puget Sound
Country: USA
Vessel Name: Ka_sea_ta
Vessel Model: 48 Defever
Join Date: Jun 2016
Posts: 258
It may be that the switch instead of switching load is switching the charge output from the engine meaning that the battery lead from the starter is the common pole of the switch and just switches the bank that gets charged. In this case with the description from the OP the house bank would be wired direct to the load....
Ka_sea_ta is offline   Reply With Quote
Old 09-30-2016, 05:57 PM   #5
Guru
 
High Wire's Avatar
 
City: Cape May, NJ and Englewood, FL
Country: USA
Vessel Name: Irish Lady
Join Date: Dec 2007
Posts: 1,419
Quote:
Originally Posted by 1Sailor View Post


There are two (2) banks of batteries on the boat - 1 House - 1 Engine start.
They each go to a 4 position Battery switch: Position 1 - Both - 2 - Off. The switch has been disconnected & tested for the propper continuity & working when cycled. There is no continuity between positions 1 & 2 and it’s off when in that position. NORMAL

Here is the problem, it doesn’t matter which position the switch is in, both banks are connected to all loads. ABNORMAL If the battery switch is truly working correctly, then there has to be an external connection such as a Combiner, Voltage Sensing Relay, or Emergency Parallel solenoid connecting the 2 banks which have failed closed. My question is how do you know there is a problem?

The house circuits can be used when in the “start” (position1) & the engine can be started from the “house” (Position 2). It’s as if the switch is always in the “Both” position. NORMAL

Again the switch itself works and positions 1 - 2 - Both are isolated in the switch. NORMAL

On the battery banks the Neutral terminals (“Minus” - ) are joined & then go to ground. I can’t see any other joining of the positive terminals. NORMAL

Where do I start looking?
Go to Blue Sea Systems catalog and download it.
Normally, 2 batteries and one switch are setup like this diagram. The switch selects which battery feeds ALL loads.
Attached Thumbnails
Click image for larger version

Name:	BatterySwitch.PNG
Views:	35
Size:	97.9 KB
ID:	56877  
__________________
Archie
1984 Monk 36 Hull #46
Englewood, FL and Cape May, NJ
High Wire is offline   Reply With Quote
Old 09-30-2016, 08:20 PM   #6
Veteran Member
 
1Sailor's Avatar
 
City: Peconic
Country: USA
Vessel Name: Moondance
Vessel Model: Atlantic Prarie 30 LRC
Join Date: Sep 2012
Posts: 30
Quote:
Originally Posted by Ka_sea_ta View Post
It may be that the switch instead of switching load is switching the charge output from the engine meaning that the battery lead from the starter is the common pole of the switch and just switches the bank that gets charged. In this case with the description from the OP the house bank would be wired direct to the load....
This is the only reply that may be the case. I know that on the battery switch terminal 1 goes to the starter battery & 2 goes to the house bank. If this is true, how do I isolate the batteries so, when away from shore power at anchor, I can have the house bank run the load while preserving the power in the starter bank?
1Sailor is offline   Reply With Quote
Old 09-30-2016, 11:28 PM   #7
Senior Member
 
Ka_sea_ta's Avatar
 
City: Puget Sound
Country: USA
Vessel Name: Ka_sea_ta
Vessel Model: 48 Defever
Join Date: Jun 2016
Posts: 258
Quote:
Originally Posted by 1Sailor View Post
This is the only reply that may be the case. I know that on the battery switch terminal 1 goes to the starter battery & 2 goes to the house bank. If this is true, how do I isolate the batteries so, when away from shore power at anchor, I can have the house bank run the load while preserving the power in the starter bank?
The best way is to use an ACR between the starting Bat and the house bank... leave the battery switch wired as is... Just leave the switch to the start batt... The ACR will isolate the house bank once the charging source is removed..
Ka_sea_ta is offline   Reply With Quote
Old 10-01-2016, 09:02 AM   #8
Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 3,679
Could be the house loads are directly connected to house bank, and engine connected directly to start bank. Batt sw then connect the two when in all.

Does house loads and engine work when batt sw is off?

If so, start engine and turn charger off. Measure batt volts at batt terminals, if getting charged volts will be around 14. If not getting charged it will be under 13.

Nothing replaces drawing an accurate schematic in these situation.
Ski in NC is offline   Reply With Quote
Old 10-01-2016, 10:42 AM   #9
TF Site Team
 
Baker's Avatar
 
City: League City, Tx
Country: Texas
Vessel Model: Carver 356
Join Date: Oct 2007
Posts: 5,566
Quote:
Originally Posted by 1Sailor View Post
This is the only reply that may be the case. I know that on the battery switch terminal 1 goes to the starter battery & 2 goes to the house bank. If this is true, how do I isolate the batteries so, when away from shore power at anchor, I can have the house bank run the load while preserving the power in the starter bank?
And this is how my Prairie was wired. I left it that way. As long as you have your generator start battery isolated you will have redundancy. I also carried jumper cables in case generator start battery died. Never had to use them.

When I put my inverter in I ended up doing this all over again. I did not see that it was necessary to run the inverter off of 2 Group 31s....seeing as I only had 4 total. So the entire house bank is also the start bank...with the generator battery isolated. I am not saying this is ideal. But it is simple and it was a solution when installing an inverter without a huge amount of batteries.

PS....the generator is the 5th battery and it was the same high quality Odyssey Group 31 as the rest. I have since added it to the battery bank and bought a smaller Group 24 for the generator.
__________________
Prairie 29...Perkins 4236...Sold
Mainship Pilot 30...Yanmar 4LHA-STP...Sold
Carver 356...T-Cummins 330B
Baker is offline   Reply With Quote
Old 10-01-2016, 01:19 PM   #10
TF Site Team
 
FlyWright's Avatar
 
City: California Delta and SF Bay
Country: Sacramento, CA, USA (boat in Vallejo)
Vessel Name: FlyWright
Vessel Model: Marshall Californian 34 LRC
Join Date: Apr 2008
Posts: 9,888
Be careful of running the engines with the switch OFF in case it isolates the alternator charge and blows a diode.
__________________
Al

Custom Google Trawler Forum Search
FlyWright is offline   Reply With Quote
Old 10-02-2016, 06:23 AM   #11
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,170
"Be careful of running the engines with the switch OFF in case it isolates the alternator charge and blows a diode. "

YES!, but a properly chosen and wired rotary switch will have a field cut off built in, so fried diodes should not become a problem
FF is online now   Reply With Quote
Old 10-02-2016, 06:45 AM   #12
Guru
 
High Wire's Avatar
 
City: Cape May, NJ and Englewood, FL
Country: USA
Vessel Name: Irish Lady
Join Date: Dec 2007
Posts: 1,419
Quote:
Originally Posted by FF View Post
"Be careful of running the engines with the switch OFF in case it isolates the alternator charge and blows a diode. "

YES!, but a properly chosen and wired rotary switch will have a field cut off built in, so fried diodes should not become a problem
One in ten wired this way at best.
High Wire is offline   Reply With Quote
Old 10-02-2016, 08:35 AM   #13
Guru
 
City: Seaford Va on Poquoson River, VA
Country: United States
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 1,231
Quote:
Originally Posted by High Wire View Post
One in ten wired this way at best.
I wired my alternator output to #1 post on the 4 way switches, this way rotating switches never will disconnect the alternators from a battery. I also have an 80 amp Blue Sea fuse inline to the alternator close to the 4 way battery switch. You can fit a 100 amp fuse in that holder.
sdowney717 is offline   Reply With Quote
Old 10-02-2016, 10:47 AM   #14
Guru
 
BobH's Avatar
 
City: Montgomery, TX
Country: USA
Vessel Model: None, but looking
Join Date: Feb 2012
Posts: 778
Had a similar problem on our last sailboat. No matter the switch position, the house load was always energized. Checked the wiring, starter battery went to direct to starter and one input of the switch. House bank to the other input on the switch. Why was the house load always hot? Then I noticed there were two cables on the starter solenoid, one to the starter battery but where did the other one go? Turns out it was connected to the output terminal of the selector switch, hence the starter battery was always connected to the house load.
Why did someone do that? It's one of those things that you know is wrong, doesn't make sense, yet somebody did that. You try to think of what you are missing here but can't come up with an answer. Disconnected that cable and all was well.
On our current boat there was supposed to be an isolated start battery for the genset, start battery for the engines and house battery. Turns out all three were connected together somewhere. Don't ask how we found out.
The point is, on an older boat trace and document all battery cables. There is no telling what a PO might have done.
BobH is offline   Reply With Quote
Old 10-02-2016, 05:15 PM   #15
Veteran Member
 
TowLou's Avatar
 
City: Flanders, NJ
Country: USA
Vessel Name: Bassey
Vessel Model: 17' Bass
Join Date: Aug 2016
Posts: 63
I would be wondering if both banks are tied together at the alternator.
TowLou is online now   Reply With Quote
Old 10-02-2016, 05:32 PM   #16
Guru
 
CaptTom's Avatar
 
City: Southern Maine
Country: USA
Vessel Name: Cygnus
Vessel Model: Prairie 36 Coastal Cruiser
Join Date: Dec 2012
Posts: 1,287
Quote:
Originally Posted by BobH View Post
On our current boat there was supposed to be an isolated start battery for the genset, start battery for the engines and house battery. Turns out all three were connected together somewhere.
Wonder if you bought yours from the same guy as I did. Mine had the same arrangement. An earlier PO installed a battery combiner that allows you to (optionally) charge all banks from one source. My PO had jumpered them all together at the combiner terminals so they were always all connected.

Genius. Pure Genius. No more worrying about which bank to select
CaptTom is offline   Reply With Quote
Old 10-02-2016, 05:38 PM   #17
Guru
 
Northern Spy's Avatar
 
City: Powell River, BC
Country: Canada
Vessel Name: Northern Spy
Vessel Model: Nordic Tug 26
Join Date: Feb 2012
Posts: 2,600
Quote:
Originally Posted by FF View Post
"Be careful of running the engines with the switch OFF in case it isolates the alternator charge and blows a diode. "

YES!, but a properly chosen and wired rotary switch will have a field cut off built in, so fried diodes should not become a problem
Or a make before break selector switch, like my big old Guest.
Northern Spy is offline   Reply With Quote
Old 10-02-2016, 07:06 PM   #18
TF Site Team
 
FlyWright's Avatar
 
City: California Delta and SF Bay
Country: Sacramento, CA, USA (boat in Vallejo)
Vessel Name: FlyWright
Vessel Model: Marshall Californian 34 LRC
Join Date: Apr 2008
Posts: 9,888
Quote:
Originally Posted by Northern Spy View Post
Or a make before break selector switch, like my big old Guest.
The problem with that one is if it gets switched to OFF, you just fried your diode.

To avoid this, I hard-wired my alternators to my batteries with 4AWG (IIRC) and use my switches to control load only. It's a much simpler system for me to manage and is similar to an airplane where the charge and load sides are split and controlled separately. My boat manufacturer saved money, as many do, by using undersized wires on the alternator charge output which is connected to the starter hot cable which carried the charge through the switches to the batteries. (insert head scratch here)

I recabled with my load side with oversize aviation-grade APU cable that was being discarded due to a 1-inch length of broken cable insulation from a cable clamp. This wire is as fine as a redhead's hair and is capable of carrying over 3500A/28V. It should be fine for my lil' boat.
__________________
Al

Custom Google Trawler Forum Search
FlyWright is offline   Reply With Quote
Old 10-02-2016, 07:16 PM   #19
Guru
 
Northern Spy's Avatar
 
City: Powell River, BC
Country: Canada
Vessel Name: Northern Spy
Vessel Model: Nordic Tug 26
Join Date: Feb 2012
Posts: 2,600
Quote:
Originally Posted by FlyWright View Post

The problem with that one is if it gets switched to OFF, you just fried your diode.

To avoid this, I hard-wired my alternators to my batteries with 4AWG (IIRC) and use my switches to control load only.
Come to think of it... I did the same thing when I repowered. Duh.

Also went from a 2 start/2 house batteries to a 1start/3 house battery setup.
Northern Spy is offline   Reply With Quote
Old 10-02-2016, 08:17 PM   #20
Guru
 
City: Seaford Va on Poquoson River, VA
Country: United States
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 1,231
I suppose It just makes too much sense to wire the alternator output to the battery, which is why more people don't do that.

I recognized this issue years ago and made the switch. It is one of those KISS principles.
__________________

sdowney717 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 05:56 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012