BAD GROUND reading when running generator

HI All,

I was checking the 110v outlet circuits when I was running my genset and I was getting a BAD GROUND reading with one of the plugin type circuit checkers. Switch to Shore power and all is good, switch back to the generator and get the BAD GROUND reading again. I looked at my transfer switch, looked inside the power box on the generator and did not see anything obvious, but I am going to keep trouble shooting.

Any thoughts on this?
__________________
Advertisement

__________________
Chris
Morning Star
ChrisL is offline   Reply With Quote
Old 09-22-2016, 12:19 AM   #2
Senior Member
 
City: Gig Harbor
Country: USA
Vessel Name: Selah
Vessel Model: Ocean Alexander 40
Join Date: Dec 2011
Posts: 183
The generator ground is not connected to the neutral. If this is the case you can measure 120 vac between hot and neutral and aprox. 67 vac between either hot and ground and between neutral and ground.
__________________

av8r is offline   Reply With Quote
Old 09-22-2016, 02:17 PM   #3
Guru
 
kchace's Avatar
 
City: Brookline, NH
Country: USA
Vessel Name: Blue Heaven
Vessel Model: Albin 43 classic double cabin, twin 135 Lehmans
Join Date: Sep 2013
Posts: 649
To expand a bit further, 120VAC ground and neutral should be connected together *At the source*. So they must not be connected inside the boat when the boat is running off shore power. When on shore power, the connection between neutral and ground is made inside a shoreside breaker panel. When running on the boat's internal generator, ground and neutral need to be connected together usually in or near the generator distribution panel. This can be done a few different ways but usually resides in or near the switch that changes over from internal power to shorepower. Its possible a wire or switch is broken, or somebody did some rewiring and inadvertently disconnected it. Whetever the reason, it must be fixed. Not having this connection when running on the generator is extremely hazardous, because right now there is probably no AC safety ground anywhere on the boat when running on the generator.

Ken
kchace is offline   Reply With Quote
Old 09-22-2016, 03:03 PM   #4
Guru
 
City: East Coast
Country: USA
Join Date: Dec 2013
Posts: 2,832
kchance has it right. I would hope the ground connection would be made and broken automatically with the transfer switch.
WesK is offline   Reply With Quote
Old 09-22-2016, 03:38 PM   #5
Guru
 
City: Seaford Va on Poquoson River, VA
Country: United States
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 1,165
Actually the generator transfer switch disconnects both white neutral and black hot.
So physically bond (connect) the gen ground to neutral in the gen control box, is good and should be done.

When the transfer switch opens, the gen neutral is disconnected, so the ground to neutral bond is broken to the ship's electrical wiring.

End of story.
sdowney717 is offline   Reply With Quote
Old 09-22-2016, 10:38 PM   #6
Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 3,502
Who ever installed the gennie should have connected the neutral and frame ground together. When gennies are shipped, this connection is normally not made at the factory. Sounds like you need to add a jumper. Common issue.
__________________

Ski in NC is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 01:56 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012