Amp rating on AC unit

All,

A question for you electrical genius.....

On my 16K BTU Airrrr AC unit the specs show the fuse rating as 20 max 14 min. Why the difference?

If it can run on 14a, why put a larger fuse in?

As I understand AC units, they usually put out a high power or serge when starting then operate at a lower power.

I'm looking at power requirements for a shore power plug in, on another thread. Thanks
__________________
Advertisement

__________________
Seevee
Seevee is offline   Reply With Quote
Old 03-13-2019, 09:29 AM   #2
Guru
 
O C Diver's Avatar
 
City: Fort Myers, FL... Summers in Crisfield, MD
Country: USA
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 6,820
I would imagine that has to do with breaker style (slow blow or instantaneous). There is a peak surge every time the compressor starts and the ranging of fusing is likely to compensate for that. As is often mentioned on TF, you are fusing to protect the circuit (wire size and plug rating). I would focus on that more than the unit. If you're wire size will handle 20 amps, go that route with your 30 amp shore power plug.

Ted
__________________

__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
O C Diver is offline   Reply With Quote
Old 03-13-2019, 09:32 AM   #3
Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 4,997
Fuses and breakers (most) have a current vs time trip curve, which effectively allows a brief current surge above the trip point. So a 20A breaker can handle 30A for say a few seconds, but will trip at 25A in say 20sec. Hit it with 50A and it will probably trip instantly. This varies between designs and mfr's.

There are breakers that are fast acting, basically anything over setpoint causes a trip.

If your pump will be fed by the same circuit, I'd go with a 20A breaker. My 12.5kBtu unit with pump can draw about 12A, and I run it through a 15A breaker. A 16 with pump might trip a 15A breaker.
Ski in NC is online now   Reply With Quote
Old 03-13-2019, 09:42 AM   #4
Guru
 
djmarchand's Avatar
 
City: Litchfield, Ct/Punta Gorda, Fl
Country: USA
Vessel Model: Atlas Pompano 23- outboard
Join Date: Aug 2012
Posts: 4,409
To Ski's point above, the amperage specs for A/C units generally exclude the raw water circulation pump which typically adds a couple of amps to the total.


David
djmarchand is online now   Reply With Quote
Old 03-14-2019, 06:51 AM   #5
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 18,928
All large induction motors have a measured LRS (locked rotor start) number that usually is 2x to 3x the amperage to operate the unit.

Air cond can install special devices to lower the LRS if dock or noisemaker power is minimal.
FF is offline   Reply With Quote
Old 03-14-2019, 07:24 AM   #6
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 4,601
My interpretation of that spec would be that you need a minimum of a 14A breaker to run the unit, and anything less will trip in normal operation. And the units wiring is can only handle 20A of fault current, so your breaker can't be any larger than that without creating a fire hazard in the unit itself. So using common breaker sizes, you could use a 15A or 20A breaker.


Good point made by others about possible piggy back loads like the circulation pump. You would have to dig deeper to see if that's included in the 14A min, or in addition to the 14A min. Or just assume it's in addition to, and use a 20A breaker.
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 03-14-2019, 10:00 AM   #7
Guru
 
Seevee's Avatar
 
City: st pete
Country: usa
Vessel Model: 400 Mainship
Join Date: Sep 2016
Posts: 2,006
Good points and thx

I wonder if the install manual goes into more detail with the proper breaker with mention of slow or fast blow factors. Need to pull the panel to see what size I have. (wish they'd put that number on the switch).

As for other items like the water pump (only 1.2a), I'll figure them in separately as to the needs of a shore power supply.
__________________
Seevee
Seevee is offline   Reply With Quote
Old 03-14-2019, 10:11 AM   #8
Guru
 
Aquabelle's Avatar
 
City: sydney
Country: australia
Vessel Name: Aquabelle
Vessel Model: Ocean Alexander Flushdeck
Join Date: Jun 2012
Posts: 811
Quote:
Originally Posted by Seevee View Post
All,

A question for you electrical genius.....

On my 16K BTU Airrrr AC unit the specs show the fuse rating as 20 max 14 min. Why the difference?

If it can run on 14a, why put a larger fuse in?

As I understand AC units, they usually put out a high power or serge when starting then operate at a lower power.

I'm looking at power requirements for a shore power plug in, on another thread. Thanks
What's the hertz rating of your ac? Is it a range 50~60hz or a fixed 60hz?
__________________

Aquabelle is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 10:21 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012