AC Generator Ground Question

I am connecting the AC wiring for a newly installed generator (new installation, not a replacement) and would appreciate some feedback regarding the ground.

Currently the boat has two 125V 30 amp shore power connections, one feeds the power supply for the air conditioner (nothing else) the other feeds the 125V panel for the boat. I am using a blue seas system switch 6337 that will allow these two circuits to run through the same switch (isolated from each other but controlled by the same lever) or connect to separate legs of the generator 250V so each has 125V. The switch controls the hot and neutral lines for each source and load but does not support grounds. My intention is to tie the grounds from boat loads together with the grounds from the two shore power connection together on one side of a heavy one/off, two post switch (4 wires on a single post) and have the other post connect to a grounding wire leading to the generator), the switch would remain open when on shore power and closed when on generator power to protect from galvanic corrosion and prevent ground fault troubles. An alternate approach would be a galvanic isolator but this seems like an unnecessary item if the AC ground is not bonded to the boat unless away from the dock.
Attached Thumbnails
Click image for larger version

Name:	6337.jpg
Views:	61
Size:	63.5 KB
ID:	52946  
__________________
Advertisement

Gdavid is online now   Reply With Quote
Old 06-10-2016, 11:07 PM   #2
Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 3,884
Since all loads on boat are 125v, reconnect gen so both windings are paralleled. No need for them to be in series at 250v and windings then subject to imbalanced load. Wire them in parallel and ground N inside the control box. Reconnect output breaker for windings in parallel at 125v.

Instructions for this are in the gennie operator's manual.
__________________

Ski in NC is offline   Reply With Quote
Old 06-11-2016, 07:00 AM   #3
Senior Member
 
mike66's Avatar
 
City: Warwick, RI
Country: USA
Vessel Name: Susan Helena
Vessel Model: Albin40
Join Date: Oct 2014
Posts: 179
Forgetting to close the ground circuit would be dangerous. I wouldn't do it.
mike66 is offline   Reply With Quote
Old 06-11-2016, 07:13 AM   #4
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,518
ALL electric is grounded AT its source.

At the dock side power pole its done somewhere for you.

In an inverter its IN the inverter

With a noisemaker its done AT the noisemaker,

The hard part is switching between the Sources and keeping the ground requirement.

I prefer a plug that is ALL the boat loads and a socket for each source.

This is house sourced stuff , $30 gets everything and there is NO confusion

.And no big buck transfer switch and system.
FF is offline   Reply With Quote
Old 06-11-2016, 07:45 AM   #5
Senior Member
 
tadhana's Avatar
 
City: New England to Florida
Country: USA EAST
Vessel Name: Tadhana
Vessel Model: Helmsman 38 Pilothouse
Join Date: Jul 2011
Posts: 481
According to ABYC the green grounding conductors for the shore power and the generator must be connected to the engine negative terminal or its bus. There can be no switch in the green grounding wire. The generator output neutral must be grounded at the generator. The generator switch must break both hot and neutral conductors but NOT the green grounding conductor .
tadhana is offline   Reply With Quote
Old 06-11-2016, 09:39 AM   #6
TG
Senior Member
 
TG's Avatar
 
City: Oceanside, CA
Country: USA
Vessel Name: Tera Grace
Vessel Model: Californian 42 LRC
Join Date: Oct 2012
Posts: 153
Quote:
Originally Posted by tadhana View Post
According to ABYC the green grounding conductors for the shore power and the generator must be connected to the engine negative terminal or its bus. There can be no switch in the green grounding wire. The generator output neutral must be grounded at the generator. The generator switch must break both hot and neutral conductors but NOT the green grounding conductor .
I agree with the above. All AC grounds should be bonded directly to the ground buss and as a side note; don't use the neutral buss for grounds or vise versa as is common in residential panels.
TG is offline   Reply With Quote
Old 06-11-2016, 10:55 AM   #7
Senior Member
 
tadhana's Avatar
 
City: New England to Florida
Country: USA EAST
Vessel Name: Tadhana
Vessel Model: Helmsman 38 Pilothouse
Join Date: Jul 2011
Posts: 481
Right. ABYC is quite clear that shore power neutrals must only be grounded at the shore distribution panel. They must not be connected to the on board ground bus. The generator neutrals must be connected to the on board ground bus. I was ABYC tech VP for 11 years before going back into boat building.
tadhana is offline   Reply With Quote
Old 06-11-2016, 08:29 PM   #8
Guru
 
City: Seaford Va on Poquoson River, VA
Country: United States
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 1,301
No switches for grounds, all grounds are always positively tied together all the time.

With the gen your breaking hots and neutrals together, so when gen is out of the circuit, the gen's neutral to ground bonding is open circuited by the transfer switch opening the neutral to ground bond, so that is playing nice.

And good idea to switch the gen to 120 VAC only, just jumper the 2 hots and neutrals on the gen side, this way the entire system can share the gen's poles balanced together

I did the same on my own boat, same basic setup. Instead of manual switch I used 2 4PDT power relays to switch the circuits by means of small toggle switches.

I have it set, so that when I plug in shore power, the relay is automatically energized and switch to shore power.

With no incoming power, it is defaulted to gen,
When inverter turns on, it energizes the other relay to switch to inverter power.

these here, but I got the off ebay cheap.
they are rated 35 amps.
https://www.zoro.com/struthers-dunn-...B&gclsrc=aw.ds


I have a safety disconnect relay that if the gen is powered on, breaks the coil power driving the inverter's 4PDT relay, just in case something weird happens. Inverters are delicate devices

I control them though with DC volts about 15 to 16 vdc will activate them.
DC stopped the buzzing, since our marina power is so crappy, big loads on the dock would cause the relays to vibrate and make annoying noise. Alternatively, is get these with 12VDC coils.

the basic schema is this, you can rearrange power in any way you wish.


inverter, grid, gen are power in sources, ship is power destination.
Using these 4PDT relays, never can any power source interconnect with any other, and all poles are switched.

IF you wanted a fourth AC power source, simply add another power relay, maybe if you had a backup gen? Otherwise can't imagine needing 4 input sources configured.
sdowney717 is offline   Reply With Quote
Old 06-11-2016, 08:53 PM   #9
Guru
 
City: Seaford Va on Poquoson River, VA
Country: United States
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 1,301
Not the best picture, but here it is, I even welded this box together from an old distribution panel I cut it and welded and made a cover.
Of course this is before all the power wires were hooked into it.



Been working great for years now. I wanted to go with the 4 pole manual switch, but they wanted $600 and I said no way.
sdowney717 is offline   Reply With Quote
Old 06-11-2016, 08:58 PM   #10
Senior Member
 
City: Owings, Md
Country: US
Join Date: Jan 2016
Posts: 224
Thanks to all for the feedback. I did not find any consensus on generator grounding (in my initial research).

Quote:
Originally Posted by Ski in NC View Post
Since all loads on boat are 125v, reconnect gen so both windings are paralleled. No need for them to be in series at 250v and windings then subject to imbalanced load. Wire them in parallel and ground N inside the control box. Reconnect output breaker for windings in parallel at 125v.

Instructions for this are in the gennie operator's manual.


Makes sense. I was thinking that long range a 240 stove may be considered but there is no existing requirement. I did not realize the gen is imbalanced by the series configuration. Easy fix, I will put the jumpers at the generator back to how they were. I used the instructions to set it up for 250v.

I am still not understanding the matter of the generator ground. Specifically, posts 5 and 7 seem to conflict (to me). I understand that the grounding for shore power should only be in the distribution panel on onshore and that is what I am trying to accomplish, but when I am away from the dock I want the ground buss connected to the generator's block but don't see how both can be accomplished without a switch. I would like to clarify that the shore power recepticals are always connected to the ground buss, the switch is just controlling whether the ground buss connects to the generator.
Gdavid is online now   Reply With Quote
Old 06-11-2016, 09:07 PM   #11
Senior Member
 
City: Owings, Md
Country: US
Join Date: Jan 2016
Posts: 224
Quote:
Originally Posted by FF View Post
I prefer a plug that is ALL the boat loads and a socket for each source.

This is house sourced stuff , $30 gets everything and there is NO confusion

.And no big buck transfer switch and system.
This was considered, but dismissed as a bit cumbersome, but it certainly would have simplified the grounding issue. The big buck switch is easy and right next to the generator's remote panel. The gen manufacturer made a grave warning (posible to break crank shaft) about starting or shutting down with a load on a circuit. Having a convenient transfer switch makes this easy.

As of yesterday, everything is connected and functioning well.
Gdavid is online now   Reply With Quote
Old 06-11-2016, 09:28 PM   #12
Senior Member
 
City: Owings, Md
Country: US
Join Date: Jan 2016
Posts: 224
sdowney717

I wrote my two last posts before noticing yours. I will read it over again but it is starting to sink in.

Thank you to all and I appreciate no one telling me the stock answer to "hire a professional". In my experience it doesn't always guarantee it being right unless I understand it enough to check the work.
Gdavid is online now   Reply With Quote
Old 06-11-2016, 10:29 PM   #13
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,877
Quote:
Originally Posted by Gdavid View Post
sdowney717

I wrote my two last posts before noticing yours. I will read it over again but it is starting to sink in.g

Thank you to all and I appreciate no one telling me the stock answer to "hire a professional". In my experience it doesn't always guarantee it being right unless I understand it enough to check the work.
Oh so true.....

And all but a few "hire a pro" posters have moved along thru the years.
psneeld is offline   Reply With Quote
Old 06-12-2016, 07:03 AM   #14
Senior Member
 
tadhana's Avatar
 
City: New England to Florida
Country: USA EAST
Vessel Name: Tadhana
Vessel Model: Helmsman 38 Pilothouse
Join Date: Jul 2011
Posts: 481
There are three AC conductors. Black (hot) White (grounded neutral) and the Green grounding conductor. The green grounding conductors from any on board AC power source must all be connected at the engine negative terminal or bus. From there the shore power green is run to shore at the shore distribution panel. The shore power white grounded neutral conductor must never be grounded on the boat. It must be grounded at the shore distribution panel. The shore power switch must break both the hot and neutral leads. The grounded neutral of the generator must be grounded and tied to the green grounding conductor on the frame of the generator.The Generator switch must break both the hot and neutral leads. The AC grounded neutral of the inverter must be grounded and connected to the green grounding wire at the frame of the inverter. The inverter switch must break both the hot and neutral leads. According to the National Electrical code and ABYC standards, there can be NO SWITCH in the green grounding conductor! The NEC has only one exception to this and it does permit a galvanic isolator in the green aboard boats.
tadhana is offline   Reply With Quote
Old 06-12-2016, 07:14 AM   #15
Senior Member
 
mike66's Avatar
 
City: Warwick, RI
Country: USA
Vessel Name: Susan Helena
Vessel Model: Albin40
Join Date: Oct 2014
Posts: 179
Very clear explanation. I don't understand the op's reluctance to have the gen green ground wire permanently wired to ship's ground as the standards call for.
mike66 is offline   Reply With Quote
Old 06-12-2016, 07:32 AM   #16
Senior Member
 
City: Owings, Md
Country: US
Join Date: Jan 2016
Posts: 224
Quote:
Originally Posted by tadhana View Post
There are three AC conductors. Black (hot) White (grounded neutral) and the Green grounding conductor. The green grounding conductors from any on board AC power source must all be connected at the engine negative terminal or bus. From there the shore power green is run to shore at the shore distribution panel. The shore power white grounded neutral conductor must never be grounded on the boat. It must be grounded at the shore distribution panel. The shore power switch must break both the hot and neutral leads. The grounded neutral of the generator must be grounded and tied to the green grounding conductor on the frame of the generator.The Generator switch must break both the hot and neutral leads. The AC grounded neutral of the inverter must be grounded and connected to the green grounding wire at the frame of the inverter. The inverter switch must break both the hot and neutral leads. According to the National Electrical code and ABYC standards, there can be NO SWITCH in the green grounding conductor! The NEC has only one exception to this and it does permit a galvanic isolator in the green aboard boats.
So the switched connection I ran between the ground buss and the generator is unnecessary ( my greens between the ground buss and each shore power connection never ran through any switch). I do have the generator's neutral grounded at the generator and since it runs does run through the blue sea system switch which makes and breaks both hot and neutral, that is preventing the neutral from being grounded at the boat when on shore power.
Gdavid is online now   Reply With Quote
Old 06-12-2016, 07:36 AM   #17
Senior Member
 
tadhana's Avatar
 
City: New England to Florida
Country: USA EAST
Vessel Name: Tadhana
Vessel Model: Helmsman 38 Pilothouse
Join Date: Jul 2011
Posts: 481
Correct, a switch in the green grounding conductor is not only unnecessary, it is unsafe. There can be no switch in the green wire per code and standards.
tadhana is offline   Reply With Quote
Old 06-12-2016, 07:44 AM   #18
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,518
"Very clear explanation. I don't understand the op's reluctance to have the gen green ground wire permanently wired to ship's ground as the standards call for."

Ground wires , are connected to neutral wires .

Neutral wired carry some current esp in a 120v setup split from a 240v source (USA) .

The reluctance to induce even minor ac current is to keep down the chance of electrocuting a swimmer , and not add a corrosive load to any underwater metal.
FF is offline   Reply With Quote
Old 06-12-2016, 08:08 AM   #19
Senior Member
 
mike66's Avatar
 
City: Warwick, RI
Country: USA
Vessel Name: Susan Helena
Vessel Model: Albin40
Join Date: Oct 2014
Posts: 179
I don't see where the inducement of ac current comes in. If the ground lead from the boat to the dock is compromised, then ac faults to ground have no place to go but through the water back to the source. But on the boat, assuming a good shore connection, or away from the dock on generator, the green grounding wire gives a path for faults, rather than have a hot appliance be touched and grounded through a person.
mike66 is offline   Reply With Quote
Old 06-12-2016, 08:59 AM   #20
Senior Member
 
tadhana's Avatar
 
City: New England to Florida
Country: USA EAST
Vessel Name: Tadhana
Vessel Model: Helmsman 38 Pilothouse
Join Date: Jul 2011
Posts: 481
In an ideal world, the shore power green grounding conductor would be connected only to shore and would not be connected aboard. But it is far from an ideal world, and in addition to the two ends of the power cord which might have a spot of corrosion and hence resistance, and then the multiple connections and junctions in the dock wiring and resistance in the connection to the ground stake ashore it is very likely that the green wire will have resistance. If there is an on board fault the current it will get to ground through any available path. Therefore we ground the system on the boat too. This protects people aboard from being in the ground path between an on board fault and the engine block and from the engine back to the shore. But it does add increased risk to swimmers around the boat especially in fresh water. This is the subject of the ESD problem we are familiar with. This is a difficult trade off for standards writers to balance. But no one should ever, ever, swim near boats that are plugged into shore power. Especially in fresh water!

It is relatively easy to test to see if you have a ground leak with a clamp on ammeter. Clamp the ammeter around your shore cord with a heavy load on the AC system. The ammeter should read 0 amps. IF it does not read 0, then some current is going to ground through the water. You then de energize all loads and turn them on one at a time to find the problem circuit.
__________________

tadhana is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 10:49 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012