Old 12-23-2015, 07:15 PM   #1
Veteran Member
 
jstauffer's Avatar
 
City: Poulsbo, WA
Country: USA
Vessel Name: Serenus
Vessel Model: Tollycraft 44
Join Date: Mar 2011
Posts: 74
Water Heater Pressure Relief Valve

Every time I turn the power on to the water heater (water in tank is cold) and after it heats up I get about a cup of water in the bilge from the pressure relief valve. If I leave a hot water faucet drip it does not happen. I have replaced the pressure relief valve three times (thinking maybe the second one was bad off the shelf) and still have the same problem.). They have all been 150 psi valves. Is this normal? I know water expands when heated but other boating friends say their's do not do this. If I leave the water heater circuit breaker on all the time I do not have a problem, but when we are on it when it is cold I need to turn it if so I can run electric heaters and other electrical devices without tripping the main breaker. Any thoughts?

Thanks,
Jerry
__________________
Advertisement

__________________
Jerry & Mona Stauffer
Serenus
Liberty Bay Marina
Poulsbo, WA
jstauffer is offline   Reply With Quote
Old 12-23-2015, 07:25 PM   #2
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,390
Quote:
Originally Posted by jstauffer View Post
Every time I turn the power on to the water heater (water in tank is cold) and after it heats up I get about a cup of water in the bilge from the pressure relief valve. If I leave a hot water faucet drip it does not happen. I have replaced the pressure relief valve three times (thinking maybe the second one was bad off the shelf) and still have the same problem.). They have all been 150 psi valves. Is this normal? I know water expands when heated but other boating friends say their's do not do this. If I leave the water heater circuit breaker on all the time I do not have a problem, but when we are on it when it is cold I need to turn it if so I can run electric heaters and other electrical devices without tripping the main breaker. Any thoughts?

Thanks,
Jerry
I suggest contacting the manufacturer of the water heater and/or the valve.

Let me ask you this: Have you had this problem ever since you got the boat or is it something new? Were any changes made to the plumbing system just before you noticed this problem? And of course, is 150 PSI the correct rating for the valve?


And is the thermostat adjustable and set to too high a temperature or is it possibly sticking and overheating the water?
__________________

rwidman is offline   Reply With Quote
Old 12-23-2015, 07:44 PM   #3
Guru
 
O C Diver's Avatar
 
City: Fort Myers, FL... Summers in Crisfield, MD
Country: USA
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 4,817
Do you have a water storage / pressure tank in your water system?

Ted
__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
O C Diver is offline   Reply With Quote
Old 12-23-2015, 07:45 PM   #4
Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 3,887
Put an air charged pressure tank in the system somewhere to absorb the volume from expansion. Or just let a faucet drip.
Ski in NC is offline   Reply With Quote
Old 12-23-2015, 08:05 PM   #5
Guru
 
ulysses's Avatar
 
City: Gulf Shores, Ala.
Country: USA
Vessel Name: Ulysses
Vessel Model: Romsdal 1963
Join Date: May 2013
Posts: 876
It would appear that your Pressure Relief Valve is serving as both a PRV and a Thermal expansion relief. There should not be a problem with that except that over time the valve may start dripping from numerous opening and closings. You may wish to install a true thermal expansion tank. It looks somewhat like a small pressure tank attached to the water heater.
ulysses is offline   Reply With Quote
Old 12-23-2015, 09:03 PM   #6
Veteran Member
 
jstauffer's Avatar
 
City: Poulsbo, WA
Country: USA
Vessel Name: Serenus
Vessel Model: Tollycraft 44
Join Date: Mar 2011
Posts: 74
This problem has been with this boat the 5 years I have owned it. I have the temperature set as low as it can go (120) degrees, but think I need to test the temperature of the water to verify, but it does not really feel all that hot. The system does have an expansion tank in it but there is a one way (check valve?) valve between the expansion tank and water heater. Maybe there should not be but suspect that is to prevent water in the tank from draining back in the system when system pressure drops.
__________________
Jerry & Mona Stauffer
Serenus
Liberty Bay Marina
Poulsbo, WA
jstauffer is offline   Reply With Quote
Old 12-23-2015, 09:30 PM   #7
Guru
 
O C Diver's Avatar
 
City: Fort Myers, FL... Summers in Crisfield, MD
Country: USA
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 4,817
Remove the check valve. When the water heats, it expands. Has to be some place for it to go. Water won't back flow as it's not compressible and there shouldn't be any air space after the water heater.

Ted
__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
O C Diver is offline   Reply With Quote
Old 12-23-2015, 10:48 PM   #8
Senior Member
 
Jeff F's Avatar
 
City: London, ON
Country: Canada
Vessel Model: Mainship 34 Original
Join Date: Nov 2015
Posts: 333
Expansion tank may be waterlogged. I've had this happen in homes, just bleed some air in.
Jeff F is offline   Reply With Quote
Old 12-23-2015, 11:02 PM   #9
Veteran Member
 
jstauffer's Avatar
 
City: Poulsbo, WA
Country: USA
Vessel Name: Serenus
Vessel Model: Tollycraft 44
Join Date: Mar 2011
Posts: 74
Jeff...if there is a check valve between the water heater and the pressure tank the problem would not be the pressure tank would it? Researching the internet I found a couple articles on installing water heaters on boats and two of them recommend the check valve just before the cold water input to the tank to prevent hot water migration back to the pump but not sure that is a problem.
__________________
Jerry & Mona Stauffer
Serenus
Liberty Bay Marina
Poulsbo, WA
jstauffer is offline   Reply With Quote
Old 12-23-2015, 11:34 PM   #10
Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 3,887
I don't see a good reason for a check valve on the inlet to the water heater. And you must have the only check valve on the planet that actually seals!! Try your system with it removed.
Ski in NC is offline   Reply With Quote
Old 12-23-2015, 11:52 PM   #11
TF Site Team
 
FlyWright's Avatar
 
City: California Delta and SF Bay
Country: Sacramento, CA, USA (boat in Vallejo)
Vessel Name: FlyWright
Vessel Model: Marshall Californian 34 LRC
Join Date: Apr 2008
Posts: 10,179
Are there any signs of visible rust on the outside of the water heater?

I had similar symptoms in my new-to-me tank in 2008. Changed the relief valve and the problem continued. Two months later, the whole tank started to leak. When I started paying closer attention, I saw rust strips in two corners. It was toast. When I pulled it, it had a stamped date of 1976. My boat was built in 1977...OEM tank! I think it did pretty well for 30+ years!
__________________
Al

Custom Google Trawler Forum Search
FlyWright is offline   Reply With Quote
Old 12-24-2015, 07:10 AM   #12
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,525
Move the pickup location for the expansion tank to the HW line.

Pressure test the tank to be sure there is some air in it.

The best is the largest (12 20? Gal) expansion that can be fit below , and monitor its pressure at least once a year.
FF is offline   Reply With Quote
Old 12-24-2015, 08:26 AM   #13
Guru
 
Phil Fill's Avatar
 
City: Everett Wa
Country: US
Vessel Name: Eagle
Vessel Model: Roughwater 58 pilot house
Join Date: Oct 2007
Posts: 2,919
As mentioned remove the one way valve or have the water drain into a plastic container and over time it will evaporate. Many older boats use to have bilge drain sumps where the sink shower water was drain into and the bilge pump pump the water over board, but there was always some water in the sump. Your boat probably has a sump? Besides its fresh water? The easiest is open a faucet a tad, scoshe.

We have the hot water heater turned of most of the time and on a timer as AC power is limited on the boat than heating hot water.
Phil Fill is offline   Reply With Quote
Old 12-24-2015, 09:47 AM   #14
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 6,369
Quote:
Originally Posted by Ski in NC View Post
I don't see a good reason for a check valve on the inlet to the water heater. And you must have the only check valve on the planet that actually seals!! Try your system with it removed.
Ski and OC Diver are absolutely correct IMHO. Had a new tank installed in 2013 to replace the POS aluminum tank. The new install TP valve kept popping off. Removed the newly installed check valve (innards) and no more popping off as pressure then regulated by expansion tank.
sunchaser is offline   Reply With Quote
Old 12-24-2015, 10:28 AM   #15
Guru
 
ulysses's Avatar
 
City: Gulf Shores, Ala.
Country: USA
Vessel Name: Ulysses
Vessel Model: Romsdal 1963
Join Date: May 2013
Posts: 876
The only reason for the check valve on the inlet side of the water heater is to allow the water heater to be replaced/serviced without having to shut down and or drain out the cold water side of the system. I agree that by removing the check valve any expansion taking place within the water heater would then be relieved through the systems existing pressure tank.
ulysses is offline   Reply With Quote
Old 12-24-2015, 10:39 AM   #16
Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 3,887
Quote:
Originally Posted by FF View Post
Move the pickup location for the expansion tank to the HW line.

Pressure test the tank to be sure there is some air in it.

The best is the largest (12 20? Gal) expansion that can be fit below , and monitor its pressure at least once a year.
This will not work very well. With expansion tank on hot leg downstream of check valve, if you use just cold water, the check valve will be shut and the expansion tank effectively isolated from the cold leg. Pump will then short cycle.
Ski in NC is offline   Reply With Quote
Old 12-24-2015, 11:09 AM   #17
Veteran Member
 
jstauffer's Avatar
 
City: Poulsbo, WA
Country: USA
Vessel Name: Serenus
Vessel Model: Tollycraft 44
Join Date: Mar 2011
Posts: 74
Will remove the check valve today and see what happens.

Thanks guys.
__________________
Jerry & Mona Stauffer
Serenus
Liberty Bay Marina
Poulsbo, WA
jstauffer is offline   Reply With Quote
Old 12-24-2015, 11:15 AM   #18
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,390
Quote:
Originally Posted by Ski in NC View Post
I don't see a good reason for a check valve on the inlet to the water heater. And you must have the only check valve on the planet that actually seals!! Try your system with it removed.
Many water heaters have a check valve built into the intake fitting. Other manufacturers suggest an external one. There is a reason for the check valve. Removing it will allow hot water to mix with the cold.

jstauffer, My boat has a short hose on the TP valve outlet that leads to an empty one gallon container. If any water escapes, it goes into the container and eventually evaporates. I've never had to empty it and don't even know if the valve has ever opened. My water is heated by electricity and/or excess engine heat and gets dangerously hot.

Adding a hose and container (mine is an empty antifreeze jug) may solve your problem with no additional modifications.
rwidman is offline   Reply With Quote
Old 12-24-2015, 12:17 PM   #19
Guru
 
O C Diver's Avatar
 
City: Fort Myers, FL... Summers in Crisfield, MD
Country: USA
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 4,817
Quote:
Originally Posted by ulysses View Post
The only reason for the check valve on the inlet side of the water heater is to allow the water heater to be replaced/serviced without having to shut down and or drain out the cold water side of the system.
Doesn't work that way. Water would still flow from the cold water side through the check valve. That is the normal flow direction. The check valve keeps it from flowing the other way.

Ted
__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
O C Diver is offline   Reply With Quote
Old 12-24-2015, 01:40 PM   #20
Senior Member
 
Jeff F's Avatar
 
City: London, ON
Country: Canada
Vessel Model: Mainship 34 Original
Join Date: Nov 2015
Posts: 333
Quote:
Originally Posted by jstauffer View Post
Jeff...if there is a check valve between the water heater and the pressure tank the problem would not be the pressure tank would it? Researching the internet I found a couple articles on installing water heaters on boats and two of them recommend the check valve just before the cold water input to the tank to prevent hot water migration back to the pump but not sure that is a problem.
Yeah, I take back my comment. Was thinking that the expansion tank was on the HW side, and that's not the case. And if there was an issue with the expansion tank the pump would be cycling too much as someone else pointed out. Sounds like your check valve is working a bit too perfectly :-)
__________________

Jeff F is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 03:35 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012