Well, I'm at a crossroads with my Marine Air spilt system (Heat and cool). I have the 3 knob manual controls (2) and two air handlers. One air handler in the forward V birth area and another in the salon. Had the system recharged with R22 and ran it for 24 hrs. Clean both coils but only keeps the boat at around 78 degrees at night. Air coming out of salon duct measures 68 degrees (with a lazer gun) and 72 degrees in birth area. Temp of air going into the evaporators is 78 degrees. Compressor never shuts down. AC tech says the pressure was a little high when he was charging the system. Thought it might be dirt in the system blocking freon exchange.??? Don't know how old the system is. Anyway, how do I identify the BTU rating on the condenser. Label gone or painted over. Thinking I would change out the condensing unit first before tackling the evaporators. Or should I just scrap the whole thing and replace everything. Kind of at a quandary right now. I'm going down to the boat this weekend and run some cleaner through the water cooling system. Maybe it is scaled up and not transferring heat the way it should. Sea water strainer is clean and I have a good stream of water exiting the boat. Maybe, I'm overlooking something. Any ideas?
__________________
Advertisement

ddalme is offline   Reply With Quote
Old 06-01-2015, 04:54 PM   #2
Senior Member
 
obthomas's Avatar
 
City: Seabrook Texas
Country: USA
Vessel Name: TheVenture
Vessel Model: 1985 Bestway Labelle Sundeck 40ft
Join Date: May 2013
Posts: 462
Should have more temperature drop across the evaporators. Need some pressure readings to diagnose the problem. Most likely compressor is not providing enough suction. With split system you are at the mercy of HVAC guy with special tools. I would replace the system with two self contained units. re-route some power and water and be free of the special tool requirement. Freon/compresser problem, remove the unit and send it to shop for repair. comes back tested and ready to reinstall.
__________________

obthomas is offline   Reply With Quote
Old 06-01-2015, 07:25 PM   #3
Guru
 
Steve's Avatar
 
City: Thibodaux, Louisiana
Country: USA
Vessel Name: Gumbo
Vessel Model: 2003 Monk 36
Join Date: Oct 2007
Posts: 3,605
I have never dealt with Marine Air so don't know how their tech support is, some companies have good folks who will really try to help, it might be worth giving them a call. Strange, I had AC problems last week too but simple, a relay was bad easy and cheap to fix.
Good luck!
__________________
Steve W.
http://mvgumbo.blogspot.com/
Steve is offline   Reply With Quote
Old 06-02-2015, 06:42 AM   #4
Guru
 
cappy208's Avatar
 
City: Cape Cod
Country: USA
Vessel Name: Slip Aweigh
Vessel Model: Prairie 29
Join Date: Oct 2013
Posts: 1,131
What's the difference in intake and outlet water temp? I would eliminate the easy (cheap) stuff first before calling in a tech. Vinegar in the raw water side would be a start.

Do you have frost on the condenser when operating?
cappy208 is offline   Reply With Quote
Old 06-02-2015, 03:13 PM   #5
Senior Member
 
ddalme's Avatar
 
City: LAFAYETTE,LA
Country: USA
Vessel Name: Relenti
Vessel Model: Atlantic 30, 1983
Join Date: Mar 2015
Posts: 406
no frost-I did measure the temp on the raw water inlet and outlet but for the life of me I can remember what it was. I think it was 5 degrees difference. I'll clean the raw water system and see what happens.
ddalme is offline   Reply With Quote
Old 06-02-2015, 04:38 PM   #6
Guru
 
cappy208's Avatar
 
City: Cape Cod
Country: USA
Vessel Name: Slip Aweigh
Vessel Model: Prairie 29
Join Date: Oct 2013
Posts: 1,131
You could call marineairr. I called them last fall and discussed my cooling issues. They helped me out to narrow it down. There is a small valve on your saltwater pump. It is supposed to be throttled to provide a certain amount of GPH to cool.

Strange thing about fluid dynamics, there is actually a 'too fast' rate that slows heat transfer down in heat exchangers. Find out what the "gallon per minute" rate is, either by your manual, or calling marinairr. then use a gallon jug over the side and time how long it takes to fill a gallon of water. Make sure the flow rate is correct.
cappy208 is offline   Reply With Quote
Old 06-02-2015, 05:18 PM   #7
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,422
Don't waste time with vinegar. Use a stronger acid.

You should be seeing outlet air temps in the mid 50s to low 60s.

How hot are the compressors running? Can you put your hand on them for a short time? Is the Freon return line cold/cool right up to where it goes into the compressor?

I doubt it has anything to do with the flow rate of the pump if the system worked well in the past and the pumps the same.

Flush the raw water system properly first and then check the pressures. High pressure is indicative of poor water flow/heat exchange. If your tech did not catch this find a new one.

Are the units getting their return air directly from the rooms they are trying to cool? Or a more indirect path that could allow them to pull warm/hot air from some where else?
Capt.Bill11 is offline   Reply With Quote
Old 06-02-2015, 06:20 PM   #8
Guru
 
City: kemah
Country: USA
Join Date: May 2015
Posts: 997
Capt. Bill, what would be a good acid to use?
what_barnacles is offline   Reply With Quote
Old 06-02-2015, 07:12 PM   #9
Senior Member
 
City: Marathon
Country: Usa
Vessel Name: silver gift
Vessel Model: 45 jefferson
Join Date: Nov 2013
Posts: 202
Take a five gallon bucket put a 3/4 ,5/8 thru hull fitting in the side near bottom . Put intake hose on pump to nipple and discharge hose in the bucket and let pump circulate cleaner thru for an hour or so . You can get a rescaled from a marine store or engine supp layer. Put gauges on before and check head pressure before and after. No gauges then temp of coil or water. Was the system out of freon or just needed a shot? Did he do a evacuation of the system? Could be air in system if he added gas. If out then you need to find the leak,start at the flare nuts or any area that might look oily or rusty causing a leak. You can use soapy water to locate a leak. Temp coming out of the vent should be about 15 to 18 degree different from air temp going in. If all else fails call your guy back and say its not working right.
Deckape is offline   Reply With Quote
Old 06-02-2015, 07:57 PM   #10
Senior Member
 
ddalme's Avatar
 
City: LAFAYETTE,LA
Country: USA
Vessel Name: Relenti
Vessel Model: Atlantic 30, 1983
Join Date: Mar 2015
Posts: 406
The tech added 2 lbs of R22-didn't evacuate. Checked for leaks and found none. Did find, whenever he attached his gauges, that whoever charged it last (I think in Sept) they hadn't shut off the high pressure valve and it was leaking slightly around the cap for inlet port. I can keep my hand on the compressor for a while-warm not hot-pressure line is cool not cold-return line is warm not hot. The return air comes from the room being cooled.
ddalme is offline   Reply With Quote
Old 06-15-2015, 09:08 AM   #11
Senior Member
 
ddalme's Avatar
 
City: LAFAYETTE,LA
Country: USA
Vessel Name: Relenti
Vessel Model: Atlantic 30, 1983
Join Date: Mar 2015
Posts: 406
Got back to the boat and chemically cleaned the water cooling tubes on the condenser. Water flow did increase a little. Water outgoing was 5 degrees warmer leaving the unit. Unit still not cooling enough. Incoming air was 75 degrees and outcoming was 67 degrees, High pressure line was cold and suction line was cool. Compressor was 65 degrees. I did find a label under the electric cover. It is a 16000 BTU unit. Guess I'll call the technician and set up another appointment. Only thing I can think of is the unit my be airlocked somewhere.
ddalme is offline   Reply With Quote
Old 06-15-2015, 09:24 AM   #12
Guru
 
SCOTTEDAVIS's Avatar
 
City: Vero Beach, FL.
Country: US
Vessel Name: FIREFLY
Vessel Model: Pilgrim 40
Join Date: Nov 2012
Posts: 913
High pressure line should be hot, low pressure should be cold and sweating. How old is the unit?
SCOTTEDAVIS is offline   Reply With Quote
Old 06-15-2015, 09:54 AM   #13
Senior Member
 
City: Marathon
Country: Usa
Vessel Name: silver gift
Vessel Model: 45 jefferson
Join Date: Nov 2013
Posts: 202
You are low on gas again.. Find that leak,look for oil around any joint,connection . Use a soapy mixture a round the subjected area. Check top of access valves at unit. Have tech evacuate system ,see if vacuum is loss. Find that leak.
Deckape is offline   Reply With Quote
Old 06-16-2015, 09:42 AM   #14
Senior Member
 
ddalme's Avatar
 
City: LAFAYETTE,LA
Country: USA
Vessel Name: Relenti
Vessel Model: Atlantic 30, 1983
Join Date: Mar 2015
Posts: 406
Tech coming out this week after jury duty. Hope he makes it before Friday.
ddalme is offline   Reply With Quote
Old 06-16-2015, 10:11 AM   #15
Senior Member
 
wyoboater's Avatar
 
City: Clear Lake Shores,Tx
Country: USA
Vessel Name: In Disguise
Vessel Model: 1985 Mainship 40 DC
Join Date: Aug 2014
Posts: 448
Lafayette, La is the wrong place to be with semi functional AC....good luck!
wyoboater is offline   Reply With Quote
Old 06-16-2015, 10:28 AM   #16
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,859
that is why I got rid of split systems and bought smaller self contained units.


a couple screws to loosen, a few hose clamps, umplug a couple wires and off to the nearest inexpensive but AVAILABLE AC&R guy...even if a couple hour drive.


saves time and money.


then again I just found out my genius son is also doing all his own AC&R work so maybe I was premature....
psneeld is online now   Reply With Quote
Old 06-16-2015, 10:33 AM   #17
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,422
Quote:
Originally Posted by what_barnacles View Post
Capt. Bill, what would be a good acid to use?
TRAC Barnacle Buster, Rydlime, phosphoric or diluted muratic acid. You could even use CLR Clear.
Capt.Bill11 is offline   Reply With Quote
Old 06-16-2015, 12:51 PM   #18
Senior Member
 
ddalme's Avatar
 
City: LAFAYETTE,LA
Country: USA
Vessel Name: Relenti
Vessel Model: Atlantic 30, 1983
Join Date: Mar 2015
Posts: 406
Quote:
Originally Posted by wyoboater View Post
Lafayette, La is the wrong place to be with semi functional AC....good luck!
Ain't that the truth!!!
ddalme is offline   Reply With Quote
Old 06-16-2015, 02:33 PM   #19
TF Site Team
 
dimer2's Avatar
 
City: Houston
Country: USA
Vessel Name: Baobab
Vessel Model: Bayliner 4788
Join Date: Aug 2013
Posts: 2,192
I just happen to have a drop in replacement unit sitting in my locker (minus the oil capacitor). If you need it you know where I am LOL
__________________
No one who achieves success does so without acknowledging the help of others.
dimer2 is offline   Reply With Quote
Old 06-16-2015, 05:07 PM   #20
Senior Member
 
ddalme's Avatar
 
City: LAFAYETTE,LA
Country: USA
Vessel Name: Relenti
Vessel Model: Atlantic 30, 1983
Join Date: Mar 2015
Posts: 406
Dimer2
I might take you up on that. I'll see what the tech says. I need to visit you anyway, so I'll have an excuse to trawler west. Plus, I owe you for a battery and a set of jumpers.LOL My crew is anxious to take another trip. Hey, I might find some more gems in your locker.hehe
Did you decide to keep the new boat??
__________________

ddalme is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 03:38 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012