I have three Marineair units onboard. I believe 2 12,000btu's, salon and stateroom, and a 9,000 btu in the v-berth. To the best of my knowledge all three are original to the 1987 boat. I had them looked at a few months ago and was told:

1) The 9,000 up forward, putting out 1/2 cooled air, is "losing pressure between sides". Nothing they could do but they refilled coolant and it was better for a while.

2) The 12K in the salon had a slow leak out the valve. "The valve is located in the back and we can't service or replace it, have to pull the unit and you might as well get a new one as it is so old." refilled coolant, worked better.

3. The stateroom unit still works well on AC. Was told that pressure was fine and it was cooling normally. Issue with it is that when I do anything funky with the controls or electrical onboard while it is running it flips its main breaker. Not good.

All 3 have no working heat function. I believed it to be due to lack of use and the valves were stuck. I tried exercising them, tapping them, on/off, etc. and got to where I could hear the valve flipping but no real heat.

Sorry for the long details, my question is whether or not these old units can be pulled and rebuilt with any success or are they simply old and need replacement. Do they rebuild AC units or am I just wasting money trying it?

Thanks for comments.
__________________
Advertisement

__________________
Hal
BLACK EYED SUSAN
Grand Banks 42 Classic
firstbase is offline   Reply With Quote
Old 10-31-2019, 11:42 AM   #2
Guru
 
Aquabelle's Avatar
 
City: sydney
Country: australia
Vessel Name: Aquabelle
Vessel Model: Ocean Alexander Flushdeck
Join Date: Jun 2012
Posts: 907
I am in almost exactly your situation, with 2 x 16k, 1 x 12k and 1 x 10k units which when I bought my boat were all 1986 installed. A 16k failed first a few years back and was judged not worth repair due to extensive rust. The 10k cool only failed next and I replaced that with a used but newer reverse cycle model to have heat in the master stateroom it serves. The 12k in the VIP stateroom has just failed and needs a new compressor. These are readily available and not huge $, but gas and labor costs and the overall state of the unit means I've decided to replace with new. These units are very easy for an owner to uninstall and reinstall without specialist help and if you can wait for Defender or whoever to have one of their regular sales, at under $1700 (16k) it's not so painful. But once you involve specialist aircon techs repair costs quickly become prohibitive. If you want to explore a repair option, pull the unit yourself (it has to come out either way) and take it to a regular home ac place for evaluation. Remember to take the control panel with you too...they just unplug via a standard RJ cable.
__________________

Aquabelle is offline   Reply With Quote
Old 10-31-2019, 11:55 AM   #3
Guru
 
djmarchand's Avatar
 
City: Litchfield, Ct/Punta Gorda, Fl
Country: USA
Vessel Model: Atlas Pompano 23
Join Date: Aug 2012
Posts: 4,856
Well, a few points:


To the OP: If you believe the advice you are getting, then replace them all. And maybe even if the advice is flawed, I would probably replace them as well as they are old, the reverse cycle doesn't work, etc. But replacing is not likely to solve your electrical problem.


For Aquebelle: I don't think you will save anything by taking the unit out and taking it to a home A/C place. I don't think that the average HVAC tech understands how to set the freon properly in a marine A/C unit. You usually have to empty it completely and then weigh the new freon to get the right amount.


But I agree that DIY replacement is very doable. It usually consists of just unbolting the main unit and ducts and putting another in its place and hooking up the wiring. Also replace the temp control unit with the one that comes with the new one, but as he notes it is usually a simple cable plug in.


David
djmarchand is online now   Reply With Quote
Old 10-31-2019, 01:03 PM   #4
Guru
 
ranger42c's Avatar
 
City: Maryland
Country: USA
Vessel Model: 42' Sportfish
Join Date: Aug 2013
Posts: 4,664
Quote:
Originally Posted by firstbase View Post
I have three Marineair units onboard. I believe 2 12,000btu's, salon and stateroom, and a 9,000 btu in the v-berth. To the best of my knowledge all three are original to the 1987 boat. I had them looked at a few months ago and was told:


Sorry for the long details, my question is whether or not these old units can be pulled and rebuilt with any success or are they simply old and need replacement. Do they rebuild AC units or am I just wasting money trying it?

Marineaire... or Marine Airrrrrr (latter is now a Dometic thing)?

Might not matter, but we had two 16k BTU Marine Airrrrrr Vector Compact models, originally from 2002... and I just replaced both with the Dometic Turbo (which was named the Vector Turbo before Dometic acquired Marine Airrrr).

So far, so good; quieter, better airflow, improved drain pan, etc.

The original units were still working, but sometimes a little balky and getting really loud... and I reckoned I was close to having gotten my money's worth.

-Chris
__________________
South River, Chesapeake Bay
ranger42c is offline   Reply With Quote
Old 10-31-2019, 02:05 PM   #5
Senior Member
 
obthomas's Avatar
 
City: Seabrook Texas
Country: USA
Vessel Name: TheVenture
Vessel Model: 1985 Bestway Labelle Sundeck 40ft
Join Date: May 2013
Posts: 476
New units use modern Freon replacement and are so much more efficient. Amperage from 1985 to today is cut in half. Re-building the old ones is like putting lipstick on a pig. I have Flagship marine units. They have heat coils. All the controls are common AC parts none over $25. No expensive circuit Boards. Use same thermostat as a house.
obthomas is offline   Reply With Quote
Old 10-31-2019, 02:22 PM   #6
Guru
 
djmarchand's Avatar
 
City: Litchfield, Ct/Punta Gorda, Fl
Country: USA
Vessel Model: Atlas Pompano 23
Join Date: Aug 2012
Posts: 4,856
Quote:
Originally Posted by obthomas View Post
New units use modern Freon replacement and are so much more efficient. Amperage from 1985 to today is cut in half. Re-building the old ones is like putting lipstick on a pig. I have Flagship marine units. They have heat coils. All the controls are common AC parts none over $25. No expensive circuit Boards. Use same thermostat as a house.

Really!! I thought that the new replacements for Freon 12 and 22 are inherently less efficient. That is why F12 and 22 existed for so long. I have only seen maybe a 20% improvement in power draw per BTU of cooling over the years more due to more efficient motors, compressors and heat exchangers, not the refrigerant.


The first marine A/C unit I had was a 1990 Cruisair. It drew 15 amps to make 16,000 BTUs. Modern Dometic Cruisairs draw about 10 amps but you have to add another 2-3 for the raw water pump so that makes them overall about 20% more efficient.



David
djmarchand is online now   Reply With Quote
Old 10-31-2019, 02:25 PM   #7
Senior Member
 
City: Rochester, NY
Country: USA
Vessel Name: Hour Glass
Vessel Model: Chris Craft Catalina 381
Join Date: Aug 2019
Posts: 489
The new refrigerants are less efficient when retrofitted into an older unit, as they often require different condenser or evaporator sizing to work at their best. In a system designed around the newer refrigerant those issues are mitigated.
rslifkin is online now   Reply With Quote
Old 10-31-2019, 03:41 PM   #8
Guru
 
djmarchand's Avatar
 
City: Litchfield, Ct/Punta Gorda, Fl
Country: USA
Vessel Model: Atlas Pompano 23
Join Date: Aug 2012
Posts: 4,856
Quote:
Originally Posted by rslifkin View Post
The new refrigerants are less efficient when retrofitted into an older unit, as they often require different condenser or evaporator sizing to work at their best. In a system designed around the newer refrigerant those issues are mitigated.

David
djmarchand is online now   Reply With Quote
Old 10-31-2019, 03:48 PM   #9
Guru
 
Aquabelle's Avatar
 
City: sydney
Country: australia
Vessel Name: Aquabelle
Vessel Model: Ocean Alexander Flushdeck
Join Date: Jun 2012
Posts: 907
Quote:
Originally Posted by rslifkin View Post
The new refrigerants are less efficient when retrofitted into an older unit, as they often require different condenser or evaporator sizing to work at their best. In a system designed around the newer refrigerant those issues are mitigated.

I think this is exactly correct! And the power efficiencies new vs old are very, very minor: physics is physics. Start-up power demands can be mitigated by the use of products such as Dometic's 'Smart Start', but that's about it.
Aquabelle is offline   Reply With Quote
Old 10-31-2019, 04:20 PM   #10
Guru
 
Airstream345's Avatar
 
City: Seattle, WA USA
Country: United States
Vessel Name: FORTITUDE
Vessel Model: Kadey Krogen 54-8
Join Date: Jul 2017
Posts: 626
Any strong recommendations for replacement units? We'll be pulling and replacing two CruiseAir 16K units with heat pumps soon. Self contained and DIY-friendly would be preferred.
__________________
FORTITUDE
Blog: mvfortitude.com
Instagram: @mvfortitude
Airstream345 is online now   Reply With Quote
Old 10-31-2019, 04:26 PM   #11
Guru
 
Aquabelle's Avatar
 
City: sydney
Country: australia
Vessel Name: Aquabelle
Vessel Model: Ocean Alexander Flushdeck
Join Date: Jun 2012
Posts: 907
Quote:
Originally Posted by Airstream345 View Post
Any strong recommendations for replacement units? We'll be pulling and replacing two CruiseAir 16K units with heat pumps soon. Self contained and DIY-friendly would be preferred.

Lots of opinions on that topic here on TF! Many like smaller outfits like Mermaid, etc that use off-the-shelf parts that can be locally sourced. Depends what is most important to you. For me, I care a lot about noise levels...I want the quietest possible (self contained) units. So I'm going for the Dometic Turbo models with sound shield.
Aquabelle is offline   Reply With Quote
Old 10-31-2019, 04:30 PM   #12
Guru
 
rgano's Avatar
 
City: Southport, Florida
Country: USA
Vessel Name: FROLIC
Vessel Model: Mainship 30 Pilot II since 2015. GB-42 1986-2015. Former Unlimited Tonnage Master
Join Date: Oct 2007
Posts: 806
Send a message via Skype™ to rgano
I replaced a 7 KBTU Dometic unit with a 10 KBTU Dometic Turbo Unit and find it quite quiet and effective. You can (and should in my opinion) buy one with their proprietary soft start device installed. I don't think they had that option when I bought my DTU so I installed a Micro-Air Easy Start. No more ka-thud when the compressor cycles form either it on the generator.
__________________
Rich Gano
FROLIC (2005 MainShip 30 Pilot II)
Panama City area
rgano is offline   Reply With Quote
Old 10-31-2019, 05:18 PM   #13
Guru
 
City: Clearwater, FL
Country: United States
Vessel Name: Seas the Bay
Vessel Model: 1981 42' Hardin Europa
Join Date: Aug 2016
Posts: 633
I just skimmed this thread, so I might well have missed some things, but a couple of notes:

1) The schrader (service) valves are a common cause of leaks in any AC system. This is especially true with age. There are removable caps with o-rings/gaskets inside that can seal them. They can be bought online, from Amazon, etc. If ever recharging a system -- install or replace the cap with a good one with a gasket/o-ring. Some systems have caps without o-rings/gaskets, in other cases the o-rings/gaskets have dried out/shrunk/dry-rotted/over-tightened-and-damaged and/or the cap is plastic and has stretched or shrunk and isn't keeping the cap tight on the valve. In any case, if recharging, it is worth replacing the cap with a good brass one with a seal. These valves aren't the only cause of leaks by any imagination and may not be the cause of a majority of problems -- but they are a very common cause of leaks.

2) Someone in thread said that one needs to empty an R-22 HVAC system and weigh the refrigerant to recharge it. This is most certainly not true (.) And, empty the unit to weight it requires vacuuming it down before recharging. Depending upon the unit it can be charged in place, without emptying, by one or more of a variety of techniques. For example, using a manufacturer's charging table calibrated to ambient temperature or temperature differences, or according to pressures and temps on suction and liquid lines (super heat or super cool methods). Or, one of my friends, an old timer HVAC-tech and plumber, by listening to the operation and feeling the lines (I didn't believe it, either, and still don't know how he does it -- but it has always squared with the gauges when I've checked him).

The upshot is that, if there is a leak in an older system that, I'd try (a) injecting a leak sealer, (b) recharging, and (c) capping the valves before doing anything major. If it works, you could get years more use from either the valve caps and/or the leak sealer. If not, you may still get days to months more use. And, even if it gets you nothing -- it was still a low cost nothing.

I've had remarkable luck getting old systems to keep working. They all die eventually. But, eventually can often (again, not always, and again, not necessarily mostly) be a season or several later.

I saw something in the thread about a bad reversing valve. First check the electrical, because it could just not be energized. After that, try tapping on it. If stuck after periods of non-use (not opening and closing), they can often be coerced into working again. Lastly, remember that a bad valve can mess with pressures and look like a compressor failure.
gkesden is offline   Reply With Quote
Old 10-31-2019, 06:29 PM   #14
Guru
 
fryedaze's Avatar
 
City: Solomons Island Md
Country: USA
Vessel Name: Fryedaze
Vessel Model: MC 42 (Overseas Co) Monk 42
Join Date: Sep 2011
Posts: 1,304
Just removed two 16K split units with compressors in ER. Installed a 16K, 12K and 6K Marineaire self contained units. The install required a bigger pump and running water to the three units. The big plus was eliminating the two large compressors and many feet of insulated Freon lines. Easy DIY job if your comfortable running the electrical for the units and the pump relay control box. About 5 boat bucks for the job.
__________________
Dave Frye
Fryedaze, MC 42 (Monk 42') 1989 Overseas Co
http://mvfryedaze.blogspot.com/
fryedaze is offline   Reply With Quote
Old 10-31-2019, 06:32 PM   #15
Senior Member
 
Pete Meisinger's Avatar
 
City: Marinette, WI
Country: USA
Vessel Name: Best Alternative
Vessel Model: 36 Albin Aft Cabin
Join Date: Oct 2012
Posts: 216
My Marine Airrrr makes a racket. Clunks on and off and growls when running. Still heats and cools just fine. I don't use it a lot so will just wait until it dies. Thanks for the related info on it being a pretty easy "boat owner" swap. That's what I'll do when the time comes.

pete
Pete Meisinger is offline   Reply With Quote
Old 10-31-2019, 06:38 PM   #16
TF Site Team
 
Larry M's Avatar
 
City: JAX, FL
Country: USA
Vessel Name: Hobo
Vessel Model: Krogen 42-120
Join Date: Nov 2008
Posts: 7,925
We installed 2-16K Dometic Vector Turbo units. Full on cool they draw ~10.5 amps. Other than the wallet flush they’re great and would replace them with the same unit. They come with a plastic/fiberglass pan so no rust to deal with from the condensate. Another plus is the air duct pivots so you have more install options. The install was in 2008.
Larry M is offline   Reply With Quote
Old 10-31-2019, 08:23 PM   #17
Guru
 
firstbase's Avatar
 
City: Jupiter, Florida
Country: United States
Vessel Name: Black Eyed Susan
Vessel Model: Grand Banks 42' Classic
Join Date: Nov 2016
Posts: 1,378
Quote:
Originally Posted by djmarchand View Post
Well, a few points:


To the OP: If you believe the advice you are getting, then replace them all. And maybe even if the advice is flawed, I would probably replace them as well as they are old, the reverse cycle doesn't work, etc. But replacing is not likely to solve your electrical problem.


For Aquebelle: I don't think you will save anything by taking the unit out and taking it to a home A/C place. I don't think that the average HVAC tech understands how to set the freon properly in a marine A/C unit. You usually have to empty it completely and then weigh the new freon to get the right amount.


But I agree that DIY replacement is very doable. It usually consists of just unbolting the main unit and ducts and putting another in its place and hooking up the wiring. Also replace the temp control unit with the one that comes with the new one, but as he notes it is usually a simple cable plug in.


David
I believe the advice was good but along the lines of most things these days. Nobody fixes anything any more, just replaces. Wasn't sure if they were rebuildable like a transmission or similar. My mind and wallet were set for replacement so I will most likely go that route. They are Marineair not Marinearrrrr. On the electrical issue, that has to be checked by an electrician and probably best to get that done prior to replacement. The question is whether I replace myself or pay for install. I keep reading comments about how easy they are to replace as long as electrical is good to go on wire size, breakers. I have old manual controls so will have to use a plate of somesort to cover the old openings in the teak woodwork. Luckily the ducting is very short and seems straight forward. "Seems" being the big word.
__________________
Hal
BLACK EYED SUSAN
Grand Banks 42 Classic
firstbase is offline   Reply With Quote
Old 10-31-2019, 08:23 PM   #18
Guru
 
O C Diver's Avatar
 
City: Fort Myers, FL... Summers in Crisfield, MD
Country: USA
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 7,629
While it sounds like the decision has been made, here's more reason for upgrading. Part of the change from older units to newer one involves rotary compressors which are much more efficient and generally quieter. If you pay for metered electricity and use the unit a fair amount, this added efficiency starts to pay for itself in saved electric dollars. Secondly, if you run the units off your generator, in addition to saving fuel dollars, the generator runs under a reduced load, which is better for its life expectancy.

Ted
__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
O C Diver is online now   Reply With Quote
Old 10-31-2019, 09:01 PM   #19
Guru
 
firstbase's Avatar
 
City: Jupiter, Florida
Country: United States
Vessel Name: Black Eyed Susan
Vessel Model: Grand Banks 42' Classic
Join Date: Nov 2016
Posts: 1,378
Quote:
Originally Posted by O C Diver View Post
While it sounds like the decision has been made, here's more reason for upgrading. Part of the change from older units to newer one involves rotary compressors which are much more efficient and generally quieter. If you pay for metered electricity and use the unit a fair amount, this added efficiency starts to pay for itself in saved electric dollars. Secondly, if you run the units off your generator, in addition to saving fuel dollars, the generator runs under a reduced load, which is better for its life expectancy.

Ted
Thanks Ted. Sitting here thinking about it and while I have been leaning towards replacing all three it might not be a bad idea for me to pull the salon unit, the one I was told had the leaky valve, and take it in for review. The stateroom unit works well and, assuming the circuit breaker flipping is no big deal, can stay until it gives up the ghost. The one up front I honestly don't care too much about as we never have anyone staying up there. It does cool somewhat but I wouldn't want guests using it for cooling in a Florida summer. Also, summer is almost gone so I have the winter to see what is what. If I am missing AC for a while it doesn't put a hurt on anything. Pulling one at an opportune time lets me educate myself on what is what without the stress of having it out during 92 degree heat. Right now I have one RW pump handling all three units. Hopefully I wouldn't have to change that as well if I replace them all at some point. Not sure what GPM it is.
__________________
Hal
BLACK EYED SUSAN
Grand Banks 42 Classic
firstbase is offline   Reply With Quote
Old 11-01-2019, 06:56 AM   #20
Veteran Member
 
Flatswing's Avatar
 
City: Windmill Harbour, Hilton Head Island, SC
Country: United States
Vessel Name: River Girl
Vessel Model: 2004 DeFever 49 RPH
Join Date: Sep 2016
Posts: 96
Assuming yours are not split units, I would replace them with new. Quieter, more efficient, no pan rust. Since u already have power, ducts, raw water & condensate, should be a straight forward DIY job depending on new control wiring. (Measure everything before u buy the new unit).
__________________

__________________
Jeremy
Flatswing is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 10:19 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012
×