Marine air Question

Had the reverse cycle heat on last night. 3 units running. This morning one unit had tripped its breaker and shutdown. Turned it back on and it tripped the breaker again. I let it sit for an hour and tried again. This time it displayed an error code that is defined as "high current." It attempted to restart and then ran just fine.

Does anyone know the meaning of "high current?" Should I be concerned or keep running it?

Thanks all.
__________________
Advertisement

__________________
Howard
Magic, 1996 Grand Banks Europa
Westport, CT and Stuart, FL
hmason is online now   Reply With Quote
Old 05-10-2016, 08:02 PM   #2
Guru
 
menzies's Avatar
 
City: Jacksonville
Country: USA
Vessel Name: SONAS
Vessel Model: Grand Alaskan 53
Join Date: May 2014
Posts: 2,204
Did it actually report "High current" or a code that you believe reflects high current?

Similar to Hi PS?
__________________

menzies is offline   Reply With Quote
Old 05-10-2016, 08:03 PM   #3
Guru
 
hmason's Avatar
 
City: Westport, CT
Country: USA
Vessel Name: Magic
Vessel Model: Grand Banks 46 Europa
Join Date: Aug 2013
Posts: 1,904
No, high pressure is different. The actual code was H-C. Checked the manual and it is defined as high current.
__________________
Howard
Magic, 1996 Grand Banks Europa
Westport, CT and Stuart, FL
hmason is online now   Reply With Quote
Old 05-10-2016, 08:07 PM   #4
Guru
 
hmason's Avatar
 
City: Westport, CT
Country: USA
Vessel Name: Magic
Vessel Model: Grand Banks 46 Europa
Join Date: Aug 2013
Posts: 1,904
BTW, the incoming voltage measures 120V
__________________
Howard
Magic, 1996 Grand Banks Europa
Westport, CT and Stuart, FL
hmason is online now   Reply With Quote
Old 05-10-2016, 09:41 PM   #5
Enigma
 
RT Firefly's Avatar
 
City: Slicker?
Country: Bumpkin?
Join Date: Oct 2007
Posts: 9,996
Greetings,
Mr. hm. Are you anchored in a river with a large tidal flow?
__________________
RTF
RT Firefly is online now   Reply With Quote
Old 05-10-2016, 09:51 PM   #6
Guru
 
hmason's Avatar
 
City: Westport, CT
Country: USA
Vessel Name: Magic
Vessel Model: Grand Banks 46 Europa
Join Date: Aug 2013
Posts: 1,904
RT, I never thought of that!
__________________
Howard
Magic, 1996 Grand Banks Europa
Westport, CT and Stuart, FL
hmason is online now   Reply With Quote
Old 05-10-2016, 09:54 PM   #7
Senior Member
 
City: Marathon
Country: Usa
Vessel Name: silver gift
Vessel Model: 45 jefferson
Join Date: Nov 2013
Posts: 202
If the unit was running and the pressure was building as water flow decreased, amps (current) will increase as the compressor works harder and gets hotter . I would check for a restricted water flow as well as a loose connection or wire. Clear fault, and check water flow after cleaning. If the boat was dry docked ,and now in the water ,might have air lock at that units water supply.
Deckape is offline   Reply With Quote
Old 05-10-2016, 10:00 PM   #8
Enigma
 
RT Firefly's Avatar
 
City: Slicker?
Country: Bumpkin?
Join Date: Oct 2007
Posts: 9,996
Greetings,
Mr. hm. THAT'S why I get the BIG bucks...
__________________
RTF
RT Firefly is online now   Reply With Quote
Old 05-10-2016, 10:00 PM   #9
Guru
 
hmason's Avatar
 
City: Westport, CT
Country: USA
Vessel Name: Magic
Vessel Model: Grand Banks 46 Europa
Join Date: Aug 2013
Posts: 1,904
Boat is at our YC slip. Water flow is fine, strainers are clean. All units run off the same raw water pump and the others run fine as well.
__________________
Howard
Magic, 1996 Grand Banks Europa
Westport, CT and Stuart, FL
hmason is online now   Reply With Quote
Old 05-10-2016, 10:01 PM   #10
Guru
 
hmason's Avatar
 
City: Westport, CT
Country: USA
Vessel Name: Magic
Vessel Model: Grand Banks 46 Europa
Join Date: Aug 2013
Posts: 1,904
RT, you are worth every $$.
__________________
Howard
Magic, 1996 Grand Banks Europa
Westport, CT and Stuart, FL
hmason is online now   Reply With Quote
Old 05-11-2016, 12:21 AM   #11
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,422
Have you contacted Marine Air/Dometic?
Capt.Bill11 is offline   Reply With Quote
Old 05-11-2016, 12:23 AM   #12
Guru
 
hmason's Avatar
 
City: Westport, CT
Country: USA
Vessel Name: Magic
Vessel Model: Grand Banks 46 Europa
Join Date: Aug 2013
Posts: 1,904
No. It's running fine now. I guess I should though.
__________________
Howard
Magic, 1996 Grand Banks Europa
Westport, CT and Stuart, FL
hmason is online now   Reply With Quote
Old 05-11-2016, 06:58 AM   #13
Guru
 
fryedaze's Avatar
 
City: Solomons Island Md
Country: USA
Vessel Name: Fryedaze
Vessel Model: MC 42 (Overseas Ltd) Monk 42
Join Date: Sep 2011
Posts: 1,052
Maybe the reversing valve is hung up. I have had that happen and the breaker trips. To free it up I jumpered power to the solenoid and cycled it a bunch with the unit off. I have had this happen twice in the last four years. The method freed it up each time. My units are 1988 models.
__________________
Dave Frye
Fryedaze, MC 42 (Monk 42') 1989 Overseas Co
http://mvfryedaze.blogspot.com/
fryedaze is offline   Reply With Quote
Old 05-11-2016, 09:24 AM   #14
Senior Member
 
City: Marathon
Country: Usa
Vessel Name: silver gift
Vessel Model: 45 jefferson
Join Date: Nov 2013
Posts: 202
A reversing value will hang up if not cycled . Some unit cycle the valve for cooling ,others only on heat. Good idea to cycle the system every couple of months or so.. With three units on one pump ,I would take a amp reading of each unit, and see if that one is working harder . Water will flow to the least resistance so maybe that unit has less water because of the distance of the run. I installed a pump for our two forward units and one pump for the aft cabin. Had a water flow problem with one pump for all three units. No problems since. Just because water is going overboard don't mean the units are getting the water flow they need . If you have a temp gun you might see a higher discharge temp.
Deckape is offline   Reply With Quote
Old 05-11-2016, 11:00 AM   #15
Guru
 
hmason's Avatar
 
City: Westport, CT
Country: USA
Vessel Name: Magic
Vessel Model: Grand Banks 46 Europa
Join Date: Aug 2013
Posts: 1,904
Thanks all. The reversing valve must have been the issue as I have now run the unit in both cooling and heat mode with no further issues. I will exercise the valve every now and again in the future.

I'm also now considering adding another raw water pump for the furthermost unit as it does have significantly less water flow. (This was not the troublesome unit.)
__________________
Howard
Magic, 1996 Grand Banks Europa
Westport, CT and Stuart, FL
hmason is online now   Reply With Quote
Old 05-11-2016, 11:10 AM   #16
Guru
 
Nomad Willy's Avatar
 
City: Concrete Washington State
Country: USA
Vessel Name: Willy
Vessel Model: Willard Nomad 30'
Join Date: Oct 2007
Posts: 13,717
"Marine air" ....
Sounds like a weather question to me.
__________________
Eric

North Western Washington State USA
Nomad Willy is online now   Reply With Quote
Old 05-11-2016, 02:16 PM   #17
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,390
Quote:
Originally Posted by fryedaze View Post
Maybe the reversing valve is hung up. I have had that happen and the breaker trips. To free it up I jumpered power to the solenoid and cycled it a bunch with the unit off. I have had this happen twice in the last four years. The method freed it up each time. My units are 1988 models.
A stuck reversing valve can usually be freed up by tapping on it with a tool handle or hammer. "Tapping" is the key word here, not pounding.
rwidman is offline   Reply With Quote
Old 05-11-2016, 06:14 PM   #18
Guru
 
hmason's Avatar
 
City: Westport, CT
Country: USA
Vessel Name: Magic
Vessel Model: Grand Banks 46 Europa
Join Date: Aug 2013
Posts: 1,904
I haven't had the opportunity to look at the unit yet as it is working again. However, for the uninitiated, could you describe what the reversing valve looks like? Thanks
__________________
Howard
Magic, 1996 Grand Banks Europa
Westport, CT and Stuart, FL
hmason is online now   Reply With Quote
Old 05-11-2016, 06:32 PM   #19
Guru
 
fryedaze's Avatar
 
City: Solomons Island Md
Country: USA
Vessel Name: Fryedaze
Vessel Model: MC 42 (Overseas Ltd) Monk 42
Join Date: Sep 2011
Posts: 1,052
Quote:
Originally Posted by WesK View Post

A stuck reversing valve can usually be freed up by tapping on it with a tool handle or hammer. "Tapping" is the key word here, not pounding.
Agree, but that didn't work for me so I went the next step.
__________________
Dave Frye
Fryedaze, MC 42 (Monk 42') 1989 Overseas Co
http://mvfryedaze.blogspot.com/
fryedaze is offline   Reply With Quote
Old 05-11-2016, 06:41 PM   #20
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,422
Quote:
Originally Posted by hmason View Post
I haven't had the opportunity to look at the unit yet as it is working again. However, for the uninitiated, could you describe what the reversing valve looks like? Thanks
See the valve in the center of the coils?
Attached Thumbnails
Click image for larger version

Name:	image.jpg
Views:	80
Size:	166.9 KB
ID:	51862  
__________________

Capt.Bill11 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 05:40 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012