Old 03-13-2012, 01:19 AM   #1
Sam
Senior Member
 
Sam's Avatar
 
City: Kalama, WA
Country: USA
Vessel Name: "Restitution"
Vessel Model: 38' Californian
Join Date: Mar 2012
Posts: 130
Low hour generator/new owner with no experience

Just bought the Californian.* No instructions, no lessons.* The generator has low hours (500) EW 4200B generator.* It is clean and relatively new looking.* It turns over but doesn't start.* A manual would be wonderful, but I don't have one.* I am mechanical and do understand mechanical/electrical principles.* Is there a simple missing procedure for start up that I am missing or any suggestions?
__________________
Advertisement

Sam is offline   Reply With Quote
Old 03-13-2012, 03:41 AM   #2
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 15,601
RE: Low hour generator/new owner with no experience

http://www.managemylife.com/

Look in the section that puts manuals in line , you might get lucky.

Or google the mfg and unit ID and see if a manual can be downloaded.
__________________

FF is online now   Reply With Quote
Old 03-13-2012, 05:18 AM   #3
Senior Member
 
Fighterpilot's Avatar
 
Join Date: Apr 2011
Posts: 373
RE: Low hour generator/new owner with no experience

I learned that my Westerbeke took more cranking to get the oil pressure up before it would stay on line. Symptoms were it would start but as soon as I released the start switch it would quit. Had to hold it there a little longer. It sounds as if yours doesn't fire off at all, but just in case it acts like mine I offer my 2cents.
Fighterpilot is offline   Reply With Quote
Old 03-13-2012, 05:39 AM   #4
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 14,253
Low hour generator/new owner with no experience

the 2 quick things that come to mind ...

Are you preheating?* If not...it's important to get operators manual and fnid out if any cautions about duration of preheat..

Low oil pressure shutdown...you arent holding the start switch long enough for the pressure to build to over 10-20 psi (or close...not sure when they kick in).


-- Edited by psneeld on Tuesday 13th of March 2012 06:40:34 AM
psneeld is offline   Reply With Quote
Old 03-13-2012, 09:19 AM   #5
Sam
Senior Member
 
Sam's Avatar
 
City: Kalama, WA
Country: USA
Vessel Name: "Restitution"
Vessel Model: 38' Californian
Join Date: Mar 2012
Posts: 130
RE: Low hour generator/new owner with no experience

On my start switch at the helm, there is no "pre heat" button/switch. I assume that the generator's engine should have one? I turn the engine over 15 seconds at a time or so and it doesn't sound like it wants to pop at all. Also, I have googled on line and have NOT found a manual. I will keep searching and working on this. Thank you.
Sam is offline   Reply With Quote
Old 03-13-2012, 09:35 AM   #6
Guru
 
City: Full Time Cruising East Coast
Country: USA
Vessel Name: Meridian
Vessel Model: Krogen-42
Join Date: Aug 2011
Posts: 670
RE: Low hour generator/new owner with no experience

http://www.entecwest.com/operators.htm
meridian is offline   Reply With Quote
Old 03-13-2012, 12:59 PM   #7
Guru
 
Phil Fill's Avatar
 
City: Everett Wa
Country: US
Vessel Name: Eagle
Vessel Model: Roughwater 58 pilot house
Join Date: Oct 2007
Posts: 2,894
Low hour generator/new owner with no experience

Is it a gsas or diesel gen set?* If you can tell*in more detail of how you go about starting the gen and what it does it will help.* **

It sounds like there is no pre heat, many older gen. sets do not.***It is turning/cranking over so*it has power.*When you flip/push the start do you hear/see the fuel solenoid move/click.* Its the fuel solenoid that shuts down the engine, and or allows fuel to the engine.* If you see/hear the fuel solenoid open and still does not start then the engine might need bleeding to get air out of the lines.***

Also make sure there is no AC electric load on the gen set so turn the AC off, usually at the main panel as the gen set has to turn fast enough to start and pump fuel.**

If you have to bleed or prime the engine let us know.*

PS.* I installed a start swtich on the gen set so usually start the enigne in the engine room so I can hear/feel and see what is happening.

*


-- Edited by Phil Fill on Tuesday 13th of March 2012 04:01:53 PM
Phil Fill is offline   Reply With Quote
Old 03-13-2012, 01:04 PM   #8
dvd
Senior Member
 
dvd's Avatar
 
City: California Bay Area
Country: US
Vessel Name: RUNTIME
Vessel Model: Nordic Tug 32
Join Date: Feb 2011
Posts: 317
RE: Low hour generator/new owner with no experience

My generator has an emergency on-off switch on the engine. If that ever gets shut off inadvertently the start switch on the panel will not work.

dvd
dvd is offline   Reply With Quote
Old 03-13-2012, 03:00 PM   #9
Sam
Senior Member
 
Sam's Avatar
 
City: Kalama, WA
Country: USA
Vessel Name: "Restitution"
Vessel Model: 38' Californian
Join Date: Mar 2012
Posts: 130
RE: Low hour generator/new owner with no experience

Thanks all. I will research more tonight. It is a diesel pot. I do NOT see any pre heat buttons anywhere. There are three different leavers on the front of the motor. Interestingly, the motor is white and someone, perhaps the PO, painted these bright red?
Sam is offline   Reply With Quote
Old 03-13-2012, 03:10 PM   #10
Guru
 
bobofthenorth's Avatar
 
City: Cowichan Bay, BC
Country: Canada
Vessel Name: Gray Hawk
Vessel Model: Defever 43 Offshore Cruiser
Join Date: Oct 2009
Posts: 570
RE: Low hour generator/new owner with no experience

Google says EW 4200B is an Entech West genset.* Their online manuals indicate no preheat and that there is a NO oil pressure switch in the run circuit.* The starter needs to crank long enough*to build sufficient oil pressure to close that switch before fuel will flow.* Figure out where the run solenoid is - if its not activating while you are cranking the engine then your problem is somewhere in that circuit.

Diesels are fundamentally simple machines - they need to turn over and have fuel - if those conditions are met they will run.* Unfortunately engineers get in the way of that simplicity.

*
bobofthenorth is offline   Reply With Quote
Old 03-14-2012, 02:11 AM   #11
Sam
Senior Member
 
Sam's Avatar
 
City: Kalama, WA
Country: USA
Vessel Name: "Restitution"
Vessel Model: 38' Californian
Join Date: Mar 2012
Posts: 130
RE: Low hour generator/new owner with no experience

Perfect. Just found the manual and copied it over. I see that I can hand crank it too. I found the hand crank and wondered what the heck it was for. It's starting to come together now. Thanks all. I'm leaving got Mississippi tomorrow but will work on starting generator upon my return.
Sam is offline   Reply With Quote
Old 03-14-2012, 03:27 AM   #12
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 15,601
RE: Low hour generator/new owner with no experience

One simple cheat , even in FL is to use a magnetic block heater that will lower the cranking time .

These are usually only 800w so will take 3 -4 hours to heat up a small block. Stick on cylinder if you can.

IF you can see the injection pipes a proper wrench (not a box wrench) can be used to loosen the nut on the injector.

A single 1/2 or full turn is usually enough to see if fuel is being delivered to the injector.
FF is online now   Reply With Quote
Old 03-14-2012, 05:46 AM   #13
TF Site Team
 
Larry M's Avatar
 
City: JAX, FL
Country: USA
Vessel Name: Hobo
Vessel Model: Krogen 42-120
Join Date: Nov 2008
Posts: 5,107
RE: Low hour generator/new owner with no experience

Have you closed the thru-hull for the raw water sytem on the generater as you are trying to start it?* This from the owners manual:
CAUTION
Whenever the engine is cranked, the Raw Water Pump continues to pump water through the raw water system. With continued cranking, it is possible to fill the Exhaust Percolating Muffler, the Exhaust Hose, the Exhaust Elbow, and if the Exhaust Valve is open, the engine combustion chamber, with raw water. If the raw water is sea water, the damage to the engine can be severe. If this ever happens, corrective action must be taken at once. If the engine will not start within 7 to 10 seconds, stop cranking!

*
Larry M is offline   Reply With Quote
Old 07-28-2016, 08:06 PM   #14
Sam
Senior Member
 
Sam's Avatar
 
City: Kalama, WA
Country: USA
Vessel Name: "Restitution"
Vessel Model: 38' Californian
Join Date: Mar 2012
Posts: 130
Ha, four years later.... Got Gen set running well four years ago. Took an old school diesel mechanic to tell me remedy. Had carbon buildup on valves. Told to either remove them and clean or....use Pam oven spray. Pam worked great. Started right up. Then years later (last night) wouldn't start. So I cranked it for 30 seconds. Unfortunately I didn't remember warning about over cranking and filled crankcase with water. I am in the hopes that I didn't bend the rod. Ebgine does turn by hand without noise? We will soon see.
Sam is offline   Reply With Quote
Old 07-28-2016, 09:50 PM   #15
Guru
 
C lectric's Avatar
 
City: Gibsons, B.C.
Country: Canada
Join Date: Oct 2007
Posts: 1,605
Get the water out fast or damage may be beyond a quick repair.

Pull injectors, SEAWATer Off and crank engine to blow any water out, SPRAY wd40 or similar into cylinders and crank to spread around. Change engine oil and filter as water may have gotten down. Reinstall injectors, bleed and get started soonest. Once running ensure water gets turned on again immediately. Let run with a good load to fully heat it up for several hours to dry out any remaining water.
Change oil/filter again and run again.

Hopefully you save it. But quick action is essential as rusting of the cylinders and rings won't wait.
C lectric is offline   Reply With Quote
Old 07-28-2016, 11:05 PM   #16
Sam
Senior Member
 
Sam's Avatar
 
City: Kalama, WA
Country: USA
Vessel Name: "Restitution"
Vessel Model: 38' Californian
Join Date: Mar 2012
Posts: 130
Ok. Drained oil and refilled tonight (twice) after cranking a bit. . Bled lines, good fuel flow. Cranked with sea water off. Blew out water. Going on 4 hr voyage tomorrow. Will wait until engine room and generator is good and warm. Will begin the starting process. I had tried tonight, but no love. Cranks well, no noise, but wondering if rod did bend and thus low compression? Will know more tomorrow. Thank you for the advice. I will reply with results tomorrow. She was always a hard starter.
Sam is offline   Reply With Quote
Old 07-28-2016, 11:07 PM   #17
Sam
Senior Member
 
Sam's Avatar
 
City: Kalama, WA
Country: USA
Vessel Name: "Restitution"
Vessel Model: 38' Californian
Join Date: Mar 2012
Posts: 130
Water was blowing out of intake which was the first notice of a problem (water all around generator). May be too late?
__________________

Sam is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
How low can I go? Tony B Voyagers and other Boaters on the Go! 2 08-24-2011 08:15 AM
Newbie generator owner stupid question dwhatty Electrical and Electronics & Navigation 4 05-10-2009 06:19 PM
Portable watt hour meter Keith Electrical and Electronics & Navigation 9 03-03-2009 03:05 PM
3 hour tour!!! Baker Voyagers and other Boaters on the Go! 9 12-21-2007 05:47 AM
Low Sulfur Diesel, Ultra Low Sulfur Diesel, and Bio Diesel Phil Fill General Discussion 5 11-14-2007 07:07 PM




All times are GMT -5. The time now is 05:30 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012