Unless you are a commercial vessel you are not required to have anything. So you can add or not add what ever you like to your system.
__________________
Advertisement

Capt.Bill11 is offline   Reply With Quote
Old 08-15-2014, 12:21 PM   #22
Senior Member
 
obthomas's Avatar
 
City: Seabrook Texas
Country: USA
Vessel Name: TheVenture
Vessel Model: 1985 Bestway Labelle Sundeck 40ft
Join Date: May 2013
Posts: 462
If you choose to install a fire system it must be installed per the rules. You may not leave bits and pieces out and choose to do it any old way.

Yes to a manual release outside the engine room.
Yes to a status indicator at a monitored location.
Ventilation and engines must be shut down or the fire extinguishing will not work. This shut-down is to be automatic. A manual shut down would not be necessary.

O.B. Thomas
__________________

obthomas is offline   Reply With Quote
Old 08-15-2014, 12:25 PM   #23
Senior Member
 
obthomas's Avatar
 
City: Seabrook Texas
Country: USA
Vessel Name: TheVenture
Vessel Model: 1985 Bestway Labelle Sundeck 40ft
Join Date: May 2013
Posts: 462
Oh, I am a fire protection engineer . O.B. Thomas, P.E. TEXAS 59630
obthomas is offline   Reply With Quote
Old 08-15-2014, 12:26 PM   #24
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 16,887
check to see what your insurance is looking forthen go from there...

as Capt. Bill said...not a requirement except for your insurance...a friend of mine just sold his boat to another friend. New owner's insurance mandated...old owner's did not.

I like a manual/auto set up.

Auto when off the boat...manual with just smoke/heat sensors when running it. I'm the captain...not a thermal sensor...

I decide decide when the engine goes off...not 35 cents worth of electronics.
psneeld is online now   Reply With Quote
Old 08-15-2014, 12:39 PM   #25
Senior Member
 
obthomas's Avatar
 
City: Seabrook Texas
Country: USA
Vessel Name: TheVenture
Vessel Model: 1985 Bestway Labelle Sundeck 40ft
Join Date: May 2013
Posts: 462
I do not have an automatic fire extinguishing system. It's not because I do not want one, I t's just because I have not added one to my boat yet. I do have engine room fire detection. I have two heat detectors that sound a very large bell. When I do get a fire extinguishing system it will be a pre engineered system like the ones sold by fireboy. You must follow manufacturers recommendations and they will tell you what must be done to comply with their UL listing. One of the things that must be done is to install their automatic engine and ventilation shutdown. Now if you want to be Captain and do it your way so be it. You may never get caught. You may never need the fire extinguisher. On the other hand I want mine to work like it should.

O.B.
obthomas is offline   Reply With Quote
Old 08-15-2014, 12:47 PM   #26
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 16,887
Yep...I want it to auto shutdown because of a malfunction (no...I forgot they never happen) when I'm in a breaking inlet, picking up a MOB, navigating a narrow fairway in a marina full of mega yachts is just a bad idea.

No ...I'm not perfect but I've been on the boating end of things long enough (also aircraft safety end of things)...that I know auto shutdown of an engine without an override or manual intervention is absolutely a bad idea.

There are just some things that still need humans to decide....there's ALWAYS the possibility of a bigger picture. A fire can be manually fought in those cases or even ignored for a calculated bit.

I'd rather fight a fire after clearing a breaking inlet than roll over and say to the crew treading water..."good news...either the fire suppression worked perfectly or that big wave did the trick".....

Fortunately there are systems that allow override....

from Fireboy manual...

The Fireboy engine shutdown system provides this function by means of a pressure switch at the extinguisher (Fireboy CG, MA and GA models only), a relay-terminal box installed at the helm station, and an instrument display unit. The display unit provides
system status (charged/discharged both visual and audible) and an override to allow restarting of the engine after a discharge or to prevent engine shutdown in a crowded water-way
psneeld is online now   Reply With Quote
Old 08-15-2014, 01:09 PM   #27
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,437
Quote:
Originally Posted by obthomas View Post
If you choose to install a fire system it must be installed per the rules. You may not leave bits and pieces out and choose to do it any old way.
What rules? It's a private vessel. There are no rules it HAS to follow. Sure there is common sense that should be used. Like following the manufacturers RECOMMENDATIONS. But you don't have to have a manual pull. You don't have to have an engine shut down system. You don't have to make and install an automatic ER vent block off system. Etc.

Sure they are all good ideas. But there are no rules for a pleasure craft that say you have to have them. You can just install a fire bottle with only a heat sensor on it to activate it and be done with it if that is what you close to do. And in fact they sell a basic systems like that.

Heck you could buy an automatic system that has a manual pull with it and leave off the manual pull if you felt like it. No one is going to come and fine you.
Capt.Bill11 is offline   Reply With Quote
Old 08-15-2014, 03:35 PM   #28
Senior Member
 
Dswizzler's Avatar
 
City: LaPaz ,Mexico and the Sea of Cortez
Vessel Name: Delta Swizzler
Vessel Model: 1988 58' Vantare
Join Date: Feb 2010
Posts: 229
Capt Bill and everyone else THANKS, as I suspected on a private vessel it is not required. Nice, but not required. I do plan to install the auto detect and activate system with a manual activation cord outside the engine room. As for the ventilation panels, I suspect I'll pass. I do have the ability to shut down the engines from the helm ( a key and stop switch) and the blowers from the helm (0n/Off and the ckt breaker panel) which seems enough for me. My insurance who i talked to this morning is worldwide and does not require it, by I do get a $12 discount for having it, so they don't really care.

Again my thanks
Dswizzler is offline   Reply With Quote
Old 08-15-2014, 03:52 PM   #29
Guru
 
ben2go's Avatar
 
City: Upstate,SC
Country: USA
Join Date: May 2012
Posts: 1,161
I prefer halon systems.I've seen them save lives in auto racing and restaurant kitchens.They should work really well in a boats engine room where the halon could be easily contain by having a system that automatically shuts down everything in the engine room,including any vents,blowers,fans,fuel pumps,all electrical equipment,and disconnects the batteries from the boats systems.

Fire Suppression Systems | | PassageMaker


And these systems may help save on insurance costs.
__________________


ben2go is offline   Reply With Quote
Old 08-15-2014, 04:43 PM   #30
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,437
Quote:
Originally Posted by ben2go View Post
I prefer halon systems.I've seen them save lives in auto racing and restaurant kitchens.They should work really well in a boats engine room where the halon could be easily contain by having a system that automatically shuts down everything in the engine room,including any vents,blowers,fans,fuel pumps,all electrical equipment,and disconnects the batteries from the boats systems.

Fire Suppression Systems | | PassageMaker


And these systems may help save on insurance costs.
While I agree systems like that are great. A complete system like you describe is not that easy to put together nor cheap to assemble and install. And as Scott mentioned, you better be able to override them in a hurry if need be.

Also since they are not required on a private vessel, other than one built to class, I doubt you would save much on your insurance premium. But it would be comforting to have on board.

And of course you can't buy a true Halon system anymore. But you probably know that.
Capt.Bill11 is offline   Reply With Quote
Old 08-15-2014, 05:58 PM   #31
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 16,887
for those interested....general info...not specific to your boat.

USCG: Fixed Fire Extinguishing Systems for T-Boats
psneeld is online now   Reply With Quote
Old 08-15-2014, 06:39 PM   #32
Guru
 
High Wire's Avatar
 
City: Cape May, NJ and Englewood, FL
Country: USA
Vessel Name: Irish Lady
Join Date: Dec 2007
Posts: 1,925
$12 discount? YAHOO!

Smoke detectors are great for alarms alerting you of a potential fire but you want the system to dump on an actual fire. For an auto discharge system, use thermal detectors. Where I used to work, we had a computer room protected by smoke detector activated Halon 1301 system. A small instrument power supply overheated one night and dumped $140K worth of Halon based on a little smoke. A 50 cent fuse down powered the power supply before getting anywhere near a fire.
__________________
Archie
1984 Monk 36 Hull #46
Englewood, FL and Cape May, NJ
High Wire is offline   Reply With Quote
Old 08-15-2014, 09:43 PM   #33
Senior Member
 
eagle419's Avatar
 
City: Sydney
Country: Australia
Join Date: Apr 2012
Posts: 223
Quote:
Originally Posted by FF View Post
The old system , where a cable is pulled , the exhaust blower is de-powered and the ER vents are closed ,
then massive CO2 is released seems reliable.
This is what I've got courtesy of previous commercial survey requirements.

All manual, simple to operate, and totally over the top.

Unless my ER is on fire of course.
Attached Thumbnails
Click image for larger version

Name:	DSC05546.jpg
Views:	92
Size:	93.9 KB
ID:	32091   Click image for larger version

Name:	DSC04484.jpg
Views:	85
Size:	78.1 KB
ID:	32092  
__________________
John
eagle419 is online now   Reply With Quote
Old 08-15-2014, 09:53 PM   #34
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,437
Nice!
Capt.Bill11 is offline   Reply With Quote
Old 08-15-2014, 11:33 PM   #35
Guru
 
HopCar's Avatar


 
City: Miami Florida
Vessel Name: Possum
Vessel Model: Ellis 28
Join Date: Aug 2011
Posts: 3,717
To my thinking there is no point in having an automatic discharge Halon type system without an automatic shutdown. If the engine keeps running during the discharge, it will just pass the agent out through the exhaust and you'll never get enough of a concentration to put out the fire.

This wasn't an issue with CO2 systems as the CO2 would shut the engine down. Of course the draw back was that it would kill you if you happened to be in the engine room when it went off.

The nice thing about the current extinguishing agents is that they will put out fires at lower concentrations than it takes to kill you. That's also why you don't oversize the system just to be sure you have enough.
__________________
Parks Masterson
www.hopkins-carter.com
HopCar is offline   Reply With Quote
Old 08-15-2014, 11:46 PM   #36
Guru
 
ben2go's Avatar
 
City: Upstate,SC
Country: USA
Join Date: May 2012
Posts: 1,161
Quote:
Originally Posted by Capt.Bill11 View Post
While I agree systems like that are great. A complete system like you describe is not that easy to put together nor cheap to assemble and install. And as Scott mentioned, you better be able to override them in a hurry if need be.

Also since they are not required on a private vessel, other than one built to class, I doubt you would save much on your insurance premium. But it would be comforting to have on board.

And of course you can't buy a true Halon system anymore. But you probably know that.
Yep.All the newer systems I have seen were custom designed,and they may have used CO2 or something else.


Quote:
Originally Posted by psneeld View Post
for those interested....general info...not specific to your boat.

USCG: Fixed Fire Extinguishing Systems for T-Boats
Thanks for the info.Bookmarked.



Quote:
Originally Posted by High Wire View Post
$12 discount? YAHOO!

Smoke detectors are great for alarms alerting you of a potential fire but you want the system to dump on an actual fire. For an auto discharge system, use thermal detectors. Where I used to work, we had a computer room protected by smoke detector activated Halon 1301 system. A small instrument power supply overheated one night and dumped $140K worth of Halon based on a little smoke. A 50 cent fuse down powered the power supply before getting anywhere near a fire.
Those would be hard to hear on some boats but I can't leave well enough alone.Modify them suckers with an external alarm.

Ouch! Dumping that much halon had to hurt some feelings and pockets.



Quote:
Originally Posted by eagle419 View Post
This is what I've got courtesy of previous commercial survey requirements.

All manual, simple to operate, and totally over the top.

Unless my ER is on fire of course.
That is a sweet set up.



Quote:
Originally Posted by HopCar View Post
To my thinking there is no point in having an automatic discharge Halon type system without an automatic shutdown. If the engine keeps running during the discharge, it will just pass the agent out through the exhaust and you'll never get enough of a concentration to put out the fire.

This wasn't an issue with CO2 systems as the CO2 would shut the engine down. Of course the draw back was that it would kill you if you happened to be in the engine room when it went off.

The nice thing about the current extinguishing agents is that they will put out fires at lower concentrations than it takes to kill you. That's also why you don't oversize the system just to be sure you have enough.
I thought halon would shut down an engine?I know a large diesel may not be choked out.

CO2 is pretty thick and will choke about anything.

Yeah,I hate being sprayed with CO2.Glad it isn't to rough on person.
__________________


ben2go is offline   Reply With Quote
Old 08-16-2014, 06:38 AM   #37
Guru
 
ulysses's Avatar
 
City: Gulf Shores, Ala.
Country: USA
Vessel Name: Ulysses
Vessel Model: Romsdal 1963
Join Date: May 2013
Posts: 876
Mark: I would ask- if you heard the audio alarm what would you do? If your answer is to go into the engine room, I would warn you not to. Both your older Halon and CO2 displace the oxygen if the audio alarm is used to warn you to get out of the engine room then that is a good thing. Some systems do come with an audio alarm to clear engine room just prior to the release of the agent.
Good luck, I miss the old halon it worked great.
ulysses is offline   Reply With Quote
Old 08-16-2014, 08:15 AM   #38
TF Site Team
 
Bay Pelican's Avatar
 
City: Chicago, IL
Country: USA
Vessel Name: Bay Pelican
Vessel Model: Krogen 42
Join Date: Oct 2007
Posts: 2,885
Quote:
Originally Posted by captrigney View Post
"The old system , where a cable is pulled , the exhaust blower is de-powered and the ER vents are closed ,then massive CO2 is released seems reliable."

I haven't been around trawlers for very long, but I don't recall seeing engine room vent covers installed on any that I looked at before buying. I installed them myself on my previous boat. Anybody have photos of theirs or a place to purchase or designs to build?
I bought a yard of contact paper which I can quickly (I think) stick over the vent drill from outside the boat to stop air from getting into the engine room.
__________________
Marty
Bay Pelican is offline   Reply With Quote
Old 08-16-2014, 08:44 AM   #39
Guru
 
timjet's Avatar
 
Join Date: Apr 2009
Posts: 1,908
Just my thoughts; in trying to get a better understanding of how the fire suppression and auto shutdown works from an electrical stand point I called fire boy with the unit number on my boat and they said they would get back to me with relevant info. They never did.

I would prefer an alarm system with a manual shutdown of the engines and a manual discharge. Things malfunction and like Keith said sometimes the smoke gets out of electrical systems and they break.

So a malfunction could shutdown the engines and deploy the retardant at the wrong time. Aircraft do not auto shutdown engines for obvious reasons, why should boats.

Memory item for engine fire warning:
* Shutdown engines unless doing so would cause a greater emergency
* Turn off blowers
* Deploy supression agent
* Call CG
* Evaluate situation and consider next course of action
__________________
Tim
Tampa Bay
Carver 355 ACMY Twin Cummins Diesels Sold
timjet is offline   Reply With Quote
Old 08-16-2014, 10:08 AM   #40
Guru
 
ulysses's Avatar
 
City: Gulf Shores, Ala.
Country: USA
Vessel Name: Ulysses
Vessel Model: Romsdal 1963
Join Date: May 2013
Posts: 876
Typically, unless you have engine breathers / direct inflow of air to engine's air intake from somewhere other than the engine room the CO2 or Halon is going to shut the engine down for you in about a heartbeat.
One drawback to the manual discharge system is something starting on fire when no one is on board. Everything is a compromise.
dan
__________________

ulysses is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 04:43 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2018, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012