Cruisair 12K BTU split system gives "LO PS" error but only on heat mode

Works fine in cool mode. About 2002 vintage unit, which was icing up the evaporator coils (dual evaporator/fans on this one) early summer so had some R22 added, which cured that problem and it cooled fine all summer...

And still does on warm days like yesterday. But, put it in heat mode and it goes into low pressure shut down within a minute or two.

Could R22 pressure be right at the verge of triggering the LO PS shut down but more prone to that in heat than cool ? Or perhaps the reversing valve is stuck ? Or ??
__________________
Advertisement

Dune is offline   Reply With Quote
Old 11-13-2015, 11:38 AM   #2
Guru
 
djmarchand's Avatar
 
City: East Greenwich, RI
Country: USA
Vessel Name: Bella
Vessel Model: Mainship Pilot 34
Join Date: Aug 2012
Posts: 2,881
First, I wouldn't expect that adding Freon would be the right way to stop evaporator icing. I think all you did was reduce the capacity of the unit due to liquid Freon blocking some of the condenser area so that it no longer iced. The right way to stop icing is to increase air flow.


So, yes I would suspect that your Freon charge is not right. Don't go back to the same guy though ;-).

And BTW I assume that water temps aren't too cold in SC (below 40 F) to cause the LP error.
__________________

djmarchand is offline   Reply With Quote
Old 11-13-2015, 11:48 AM   #3
Senior Member
 
Dune's Avatar
 
City: Coastal SC
Country: USA
Vessel Model: Viking 65 CP MY (run at trawler speeds !)
Join Date: Jul 2015
Posts: 370
Quote:
Originally Posted by djmarchand View Post
The right way to stop icing is to increase air flow.
Actually the condenser tubing was icing as well...a lot...prior to the freon addition. And the air flow in the evaporator was as good as possible....the coil (radiator looking parts) were clean, filters clean, squirrel cage fans working properly. Also the compressor part of the condenser was running too hot to touch prior to additional freon. All of that fixed with more freon.... but now, get immediate LO PS error in heat mode. (SXII control)

FWIW, the boat has 5 Cruisair condensers. One other one is now giving LO PS error as well but that one does so in both cold and heat mode. The other 3 units work fine in both modes.

I have had HI PS errors in the past but they were always due to clogged raw water intake strainer and effected all 5 units. Strainer looks pretty clear now.
Dune is offline   Reply With Quote
Old 11-13-2015, 12:12 PM   #4
Guru
 
Scary's Avatar
 
City: Walnut Grove Ca
Country: USA
Vessel Name: Cary'D Away
Vessel Model: Hatteras 48 LRC
Join Date: Apr 2012
Posts: 884
Water temperature plays a roll in R22 pressure. You probably need refrigeration guy familiar with Cruise air to get correct pressure. Reversing valve works or doesn't.
Scary is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 02:32 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012