Condensation pan draining

My trawler has a 5000 BTU Webasto marine air conditioner. The unit works great and keeps the cabin/V-berth cool and warm.

I crawled under the galley counter/cabinets last night to inspect the unit and noticed that the pan has not been draining as it should because the unit is at a slight angle. The pan is stainless but it appears Webasto used some non-stainless steel nuts/washers to secure that secure the compressor to the pan. Not sure why they would skimp on this but they are rusted and need replacing. I called Wabasto to bring this to their attention--maybe they'll send me some replacement hardware.

I'm going to purchase a "Mermaid Condensator" to empty my condensate pan by pulling the water from the pan into the AC cooling water flow and out the through hull. It is presently draining into the bilge, which is not ideal.

Anyone use this draining system?
__________________
Advertisement

__________________
“Go small, go simple, go now”
― Larry Pardey, Cruising in Seraffyn
Vashon_Trawler is offline   Reply With Quote
Old 11-30-2013, 11:37 AM   #2
Senior Member
 
HeyJude's Avatar
 
City: Boerne, Tx
Country: USA
Vessel Name: HEY JUDE
Vessel Model: Kadey Krogen 36 Manatee #46
Join Date: Jan 2011
Posts: 220
We have something similar to what you describe. A small flexable pickup hose in the pan that leads to a syphon device that is installed in the AC cooling water output hose that utilizes a venturi to suck the pan water out. Works well. You can hear a slight "slurping" sound if you know what to listen for. The small pickup hose has a small cleanable filter inline that I relocated to under the vanity sink to facilitate cleaning.
__________________

__________________
HEY JUDE, a 1986 Kadey Krogen 36 Manatee, #46 of 99. After 13 yrs on Lake Travis she's on Clear Lake TX being prepped for coastal cruising.
HeyJude is offline   Reply With Quote
Old 11-30-2013, 01:25 PM   #3
Guru
 
River Cruiser's Avatar
 
City: UMR MM283
Country: US
Vessel Name: Northern Lights II
Vessel Model: Bayliner 3870
Join Date: Jan 2013
Posts: 1,226
I have 2 marine air units & both drain condensate into the bilge. I've purchased a shower drain box that I intend to plumb the drains into along with the shower drain. This will replace the existing diaphram shower drain pump.
__________________
Ron on Northern Lights II
I don't like making plans for the day because the word "premeditated" gets thrown around in the courtroom.
River Cruiser is offline   Reply With Quote
Old 11-30-2013, 03:08 PM   #4
Guru
 
Moonstruck's Avatar
 
City: Hailing Port: Charleston, SC
Country: USA
Vessel Name: Moonstruck
Vessel Model: Sabre 42 Hardtop Express
Join Date: Nov 2008
Posts: 7,848
On my Blackfin is a 5000 btu unit with heat strips in the bow. It drains in similar fashion, and works well.
__________________
Don on Moonstruck
Sabre 42 Hardtop Express & Blackfin 25 CC
When cruising life is simpler, but on a grander scale (author unknown)
http://moonstruckblog.wordpress.com/
Moonstruck is offline   Reply With Quote
Old 06-22-2014, 08:00 AM   #5
Veteran Member
 
City: Easton, MD
Country: USA
Vessel Name: Happy Thought
Vessel Model: Mariner Seville 37/Helmsman 38
Join Date: May 2012
Posts: 35
I use 2 mermaid condensators. I have had them installed for 2 years and have had no issues, just dry pans.


Sent from my iPhone using Trawler Forum
Happy Thought is offline   Reply With Quote
Old 06-22-2014, 08:30 AM   #6
Guru
 
City: Tuckerton, NJ
Country: USA
Vessel Name: WIRELESS ONE
Vessel Model: 36 Gulstar MarkII
Join Date: Mar 2011
Posts: 937
Having used 2 Condensators from Mermaid Air on (2) Marine Airr 16,000 BTU units I can tell you it's the way to go. It's pretty much install it and almost forget it. There is an in line small strainer that will need bi-annual cleaning. Other than that I haven't had a problem with either unit that uses this to discharge the condensate water out with the AC units raw water source. Shower sumps are prone to needing service enough when they are fed with a shower. I like leaving the shower sump for the shower water's discharge.
As for dumping AC units condensate directly into the bilge your boat will stink and you will get mold in the bilge.
Bill
Billylll is offline   Reply With Quote
Old 06-22-2014, 12:37 PM   #7
Guru
 
Aquabelle's Avatar
 
City: sydney
Country: australia
Vessel Name: Aquabelle
Vessel Model: Ocean Alexander Flushdeck
Join Date: Jun 2012
Posts: 537
Quote:
Originally Posted by HeyJude View Post
We have something similar to what you describe. A small flexable pickup hose in the pan that leads to a syphon device that is installed in the AC cooling water output hose that utilizes a venturi to suck the pan water out. Works well. You can hear a slight "slurping" sound if you know what to listen for. The small pickup hose has a small cleanable filter inline that I relocated to under the vanity sink to facilitate cleaning.
HeyJude: can you tell us what specifically you use please...and with what a/c unit?
thanks
Aquabelle is offline   Reply With Quote
Old 06-22-2014, 12:39 PM   #8
Guru
 
Aquabelle's Avatar
 
City: sydney
Country: australia
Vessel Name: Aquabelle
Vessel Model: Ocean Alexander Flushdeck
Join Date: Jun 2012
Posts: 537
Quote:
Originally Posted by Billylll View Post
Having used 2 Condensators from Mermaid Air on (2) Marine Airr 16,000 BTU units I can tell you it's the way to go. Bill
Bill: no problems/issues in mating the Memaid Condensators to the MarineAirr units?

thanks
Aquabelle is offline   Reply With Quote
Old 06-22-2014, 12:48 PM   #9
Veteran Member
 
City: Easton, MD
Country: USA
Vessel Name: Happy Thought
Vessel Model: Mariner Seville 37/Helmsman 38
Join Date: May 2012
Posts: 35
Should not be a problem mating w/any unit. You cut outgoing seawater hose and insert. Put the pickup to pan drain hole.


Sent from my iPhone using Trawler Forum
Happy Thought is offline   Reply With Quote
Old 06-22-2014, 12:50 PM   #10
Guru
 
Aquabelle's Avatar
 
City: sydney
Country: australia
Vessel Name: Aquabelle
Vessel Model: Ocean Alexander Flushdeck
Join Date: Jun 2012
Posts: 537
Found very mixed reviews of this device here: Mermaid condensator - Cruisers & Sailing Forums
Aquabelle is offline   Reply With Quote
Old 06-22-2014, 01:35 PM   #11
Veteran Member
 
City: Easton, MD
Country: USA
Vessel Name: Happy Thought
Vessel Model: Mariner Seville 37/Helmsman 38
Join Date: May 2012
Posts: 35
I have seen those. My experience has been perfect. It is a high quality brass valve. I think that if it is installed properly and filter looked at regularly, it should work forever. Any maintenance required is user done. It does lower the efficiency of the a/c unit by about 10% due to less water flow. I have not found that to be an issue on my 2 16k BTU units.


Sent from my iPhone using Trawler Forum
Happy Thought is offline   Reply With Quote
Old 06-22-2014, 01:48 PM   #12
Guru
 
mbevins's Avatar
 
City: Windsor
Country: Canada
Vessel Name: Keeper IV
Vessel Model: 44 Viking ACMY
Join Date: Nov 2013
Posts: 1,305
I ran mine into my existing shower sump boxes and forgot about them. Total cost a few of hose and a couple of clamps.

Sent from my Nexus 4 using Trawler
__________________
"The democracy will cease to exist when you take away from those who are willing to work and give to those who would not."

mbevins is offline   Reply With Quote
Old 06-22-2014, 01:55 PM   #13
Veteran Member
 
City: Easton, MD
Country: USA
Vessel Name: Happy Thought
Vessel Model: Mariner Seville 37/Helmsman 38
Join Date: May 2012
Posts: 35
Can't argue with that. When I purchased boat some idiot had run to shower sump, uphill! Naturally gravity won out and I had floor puddles. Not wanting to dump in bilge, led me to the Mermaid product.


Sent from my iPhone using Trawler Forum
Happy Thought is offline   Reply With Quote
Old 06-22-2014, 01:58 PM   #14
Guru
 
Join Date: Aug 2012
Posts: 741
Our Cuisair units have the "slurper" hoses in the pans, which pull the condensate into the discharge water via venture action. The only problem is that some of the hardware in the pan has started to rust and shows up as a rust stain on either the side of the boat where the raw water discharges. I like the idea of simply draining the condensate into one of the shower sumps (which exits at the rear of the boat and out of sight). One of these days I'll attend to the rusting hardware...
Underway is offline   Reply With Quote
Old 06-22-2014, 03:17 PM   #15
TF Site Team
 
dimer2's Avatar
 
City: Houston
Country: USA
Vessel Name: Baobab
Vessel Model: Bayliner 4788
Join Date: Aug 2013
Posts: 2,193
The Kent venturi for fish tanks run about $25 and have worked well the few months I have had them installed. Had to buy a couple barb connectors but all done for about $30 a piece.

Kent Marine Black Turbo Venturi - 3/4 inch
__________________
No one who achieves success does so without acknowledging the help of others.
dimer2 is offline   Reply With Quote
Old 06-22-2014, 03:20 PM   #16
Veteran Member
 
City: Easton, MD
Country: USA
Vessel Name: Happy Thought
Vessel Model: Mariner Seville 37/Helmsman 38
Join Date: May 2012
Posts: 35
The Mermaid costs about 250, it must be better, right? Lol


Sent from my iPhone using Trawler Forum
Happy Thought is offline   Reply With Quote
Old 06-22-2014, 03:29 PM   #17
Member
 
City: Marion, SC
Country: USA
Join Date: Sep 2012
Posts: 11
So what's the deal with having a filter on the outgoing condensate drain? If you're "slurping" the condensate for discharge why would you need to filter it?
Dream Trawl is offline   Reply With Quote
Old 06-22-2014, 03:35 PM   #18
Veteran Member
 
City: Easton, MD
Country: USA
Vessel Name: Happy Thought
Vessel Model: Mariner Seville 37/Helmsman 38
Join Date: May 2012
Posts: 35
Stuff can get in the pan and you don't want a blockage be ause you'd be assuming the water is leaving the pan when it isn't


Sent from my iPhone using Trawler Forum
Happy Thought is offline   Reply With Quote
Old 06-22-2014, 07:15 PM   #19
Guru
 
City: Tuckerton, NJ
Country: USA
Vessel Name: WIRELESS ONE
Vessel Model: 36 Gulstar MarkII
Join Date: Mar 2011
Posts: 937
Quote:
Originally Posted by Dream Trawl View Post
So what's the deal with having a filter on the outgoing condensate drain? If you're "slurping" the condensate for discharge why would you need to filter it?
The filter is to keep dust, lint, rust particals from the older pans, paint chips and mold from clogging the one way check valve to the Venturi device. Thecheck valve is very similar to the red valves used in Raritan PuraSan MSD units.
Bill
Billylll is offline   Reply With Quote
Old 06-22-2014, 07:21 PM   #20
Guru
 
City: Tuckerton, NJ
Country: USA
Vessel Name: WIRELESS ONE
Vessel Model: 36 Gulstar MarkII
Join Date: Mar 2011
Posts: 937
I would think twice before using the shower sump. What happens if the sump fails and you get water backed up and the drain lines you just ran are the path of least resistance?
You could get water all over the floor sure you aren't going to flood the boat but it could be costly to repair moldy carpet or flooring.
Bill
__________________

Billylll is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 01:35 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012