Condensate Drain Issue

Had the salon air handler unit start overflowing two days ago. Blew the lines out but still leaking so yesterday I shop vacuumed them to back flush still leaking.
Today I replaced the complete line from salon to bilge, still leaking.
If I go to the bilge and draw on it ever so slightly water comes pouring out but doesnít continue to run. Itís like I need to vent the line to get it to flow. The line is 1/2Ē id and has 4 Ď of fall. I can run a cable all the way through with no obstruction.
Any thoughts?
__________________
Advertisement

Deano is offline   Reply With Quote
Old 09-01-2018, 05:25 PM   #2
Guru
 
psneeld's Avatar
 
City: AICW
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 19,656
Mine had an ever so slight, barely visible rise out of the pan.

A bubble would form and while I can't say for sure, it seemed like the resistance formed by the bubble was enough to keep it from draining the pan.

I was able to get it flat enough to overcome the bubble...an alternative might have been to put a t in where the tubing formed the bubble...but I don't know if that would work.
__________________

psneeld is offline   Reply With Quote
Old 09-01-2018, 05:37 PM   #3
Senior Member
 
Deano's Avatar
 
City: St. Pete
Country: USA
Vessel Name: Becca
Vessel Model: Gulfstar 44
Join Date: Nov 2013
Posts: 191
Air seems to be the issue. I may try to back fill the entire line with water and add a trap on the end.
Itís odd that this issue come after several years of ownership.
Deano is offline   Reply With Quote
Old 09-01-2018, 10:21 PM   #4
Senior Member
 
Deano's Avatar
 
City: St. Pete
Country: USA
Vessel Name: Becca
Vessel Model: Gulfstar 44
Join Date: Nov 2013
Posts: 191
Turning that unit off for the night Try again tomorrow. Wife not happy.
Deano is offline   Reply With Quote
Old 09-02-2018, 12:00 AM   #5
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 5,105
Maybe a dip and then uphill somewhere in the hose? That might stop it from draining. It sounds like you have done reasonable things so far.
Comodave is offline   Reply With Quote
Old 09-02-2018, 02:20 AM   #6
Guru
 
City: Between Oregon and Alaska
Country: US
Vessel Name: Charlie Harper
Vessel Model: Wheeler Shipyard 83'
Join Date: Jun 2016
Posts: 1,527
It might be an air pressure problem. A slight difference in air pressure between the pan and the end of the tubing.
Lepke is offline   Reply With Quote
Old 09-02-2018, 01:59 PM   #7
Guru
 
motion30's Avatar
 
Join Date: Jan 2010
Posts: 933
Yes hoes need some sort of trap that way the weight of the water will overcome the suction of the blower.
motion30 is online now   Reply With Quote
Old 09-02-2018, 02:37 PM   #8
Guru
 
Maerin's Avatar
 
City: East Coast
Country: USA
Vessel Name: M/V Maerin
Vessel Model: Solo 4303
Join Date: Jun 2013
Posts: 783
1st off, the line is pretty small diameter, it exacerbates any problem you may have with air. A line that small will have trouble draining by gravity unless there's a lot of fall in the line, even then it can become air bound. A larger diameter line allows air and water to cross paths/directions. Run it in 3/4 the problem will probably disappear. Hard pipe is better, it won't sag & create traps. You can clean the line till the cows come home and it won't drain if it's air locking. Of course it flows if you blow through it, you're changing the physics acting on the water column. A tee/vent may or may not help, then you're introducing a point of failure (overflow) if the line backs. Most marine condensate drains are open to the atmosphere, so the blower suction isn't an issue, but if its in a blower compartment you may be getting some negative pressure as others noted. A trap solves that. It may help to drop the line vertically right out of the drain connection then change to horizontal if you have the elevation, so if the line does air lock a bit, it'll build a bit of head in the drop to push the condensate past the air trap.
__________________
Steve Sipe
Selene 4303 Maerin
http://maerin.net
Maerin is offline   Reply With Quote
Old 09-02-2018, 03:14 PM   #9
Senior Member
 
Deano's Avatar
 
City: St. Pete
Country: USA
Vessel Name: Becca
Vessel Model: Gulfstar 44
Join Date: Nov 2013
Posts: 191
Put a small trap on this morning and it’s been fine all day. I’m not sure why this started happening since we’ve made no changes in that compartment in two years.
Deano is offline   Reply With Quote
Old 09-02-2018, 05:44 PM   #10
Guru
 
City: Melbourne, FL
Country: USA
Join Date: Dec 2014
Posts: 1,396
Quote:
Originally Posted by Maerin View Post
1st off, the line is pretty small diameter, it exacerbates any problem you may have with air. A line that small will have trouble draining by gravity unless there's a lot of fall in the line, even then it can become air bound. A larger diameter line allows air and water to cross paths/directions. Run it in 3/4 the problem will probably disappear. Hard pipe is better, it won't sag & create traps. You can clean the line till the cows come home and it won't drain if it's air locking. Of course it flows if you blow through it, you're changing the physics acting on the water column. A tee/vent may or may not help, then you're introducing a point of failure (overflow) if the line backs. Most marine condensate drains are open to the atmosphere, so the blower suction isn't an issue, but if its in a blower compartment you may be getting some negative pressure as others noted. A trap solves that. It may help to drop the line vertically right out of the drain connection then change to horizontal if you have the elevation, so if the line does air lock a bit, it'll build a bit of head in the drop to push the condensate past the air trap.
To test the possibility that you have reverse airflow combatting the drain flow, put the end of the hose in a cup of water. If that stops the problem, the cup will overflow, if not you don't have enough drop to compete with the vacuum of the blower.
stubones99 is offline   Reply With Quote
Old 09-02-2018, 09:38 PM   #11
Guru
 
City: Hampton, va
Country: USA
Vessel Name: Didi Mau
Vessel Model: 2003 Ocean Alexander 456
Join Date: Jul 2015
Posts: 897
How do folks keep their condenser drain line clean? I just had two overflow. After freeing the blockage I pour a half gallon of vinegar into each pan. I am thinking that might not be good enough
Gordon J is offline   Reply With Quote
Old 09-03-2018, 04:04 AM   #12
Senior Member
 
Deano's Avatar
 
City: St. Pete
Country: USA
Vessel Name: Becca
Vessel Model: Gulfstar 44
Join Date: Nov 2013
Posts: 191
Peroxide and bleach
Deano is offline   Reply With Quote
Old 09-03-2018, 06:24 AM   #13
Guru
 
City: Hampton, va
Country: USA
Vessel Name: Didi Mau
Vessel Model: 2003 Ocean Alexander 456
Join Date: Jul 2015
Posts: 897
A friend used bleach in his, and it destroyed the aluminum fins on the condenser.
Gordon J is offline   Reply With Quote
Old 09-03-2018, 08:44 AM   #14
Guru
 
City: Melbourne, FL
Country: USA
Join Date: Dec 2014
Posts: 1,396
The safest natural solution (currently) is white vinegar. Put a cup of it in each drip pan every month. Clorox bleach can corrode aluminum.
stubones99 is offline   Reply With Quote
Old 09-03-2018, 09:33 AM   #15
Guru
 
Maerin's Avatar
 
City: East Coast
Country: USA
Vessel Name: M/V Maerin
Vessel Model: Solo 4303
Join Date: Jun 2013
Posts: 783
Look for Nu-Calgon products. They make condensate pan tabs, pads, that are all easy to apply and won't damage the coils. They also make evap cleaners that are good for cleaning a dirty coil. Don't try to mechanically clean (brush, scraper, etc) a coil, you'll just damage it and make it worse. Use a foaming, self-rinsing spray, the condensate will rinse it off, it will get deep into the coil to give it a thorough cleaning. These products are much better suited than home-grown application of household chemicals. Bleach in particular.
__________________
Steve Sipe
Selene 4303 Maerin
http://maerin.net
Maerin is offline   Reply With Quote
Old 09-17-2018, 02:43 PM   #16
Member
 
City: Annapolis / Ft Myers
Country: United States
Vessel Name: Myrtea / Harbor Quest
Vessel Model: CL Bermuda 30, Egg 40
Join Date: Jul 2018
Posts: 11
I have used bromine tablets to keep both drain and supply lines clear of organic growth. Much less caustic than chlorine or bleach and available from spa supply shops. Drop a few tabs in the strainer and drip try as experience dictates.
CaptRowlands is offline   Reply With Quote
Old 09-17-2018, 10:29 PM   #17
Guru
 
rgano's Avatar
 
City: Southport, Florida
Country: USA
Vessel Name: FROLIC
Vessel Model: Mainship 30 Pilot II since 2015. GB-42 1986-2015. Former Unlimited Tonnage Master
Join Date: Oct 2007
Posts: 702
Send a message via Skype™ to rgano
Living in buzillion percent humidity here, we all learn quickly to use pan tabs both in house and boat. Came home many years ago to a house (on slab) with 1/4 inch of water throughout when the a/c pan over flowed for just a day!
__________________
Rich Gano
FROLIC (2005 MainShip 30 Pilot II)
Panama City area
rgano is offline   Reply With Quote
Old 09-18-2018, 05:38 PM   #18
Senior Member
 
Symphony's Avatar
 
City: New Haven, Ct
Country: USA
Vessel Name: Song Bird
Vessel Model: Vicem 58
Join Date: Sep 2017
Posts: 103
time to move to more northerly climes, Rich!
Symphony is offline   Reply With Quote
Old 09-18-2018, 06:35 PM   #19
Guru
 
rgano's Avatar
 
City: Southport, Florida
Country: USA
Vessel Name: FROLIC
Vessel Model: Mainship 30 Pilot II since 2015. GB-42 1986-2015. Former Unlimited Tonnage Master
Join Date: Oct 2007
Posts: 702
Send a message via Skype™ to rgano
I need to become a reverse snowbird!
__________________
Rich Gano
FROLIC (2005 MainShip 30 Pilot II)
Panama City area
rgano is offline   Reply With Quote
Old 09-18-2018, 08:14 PM   #20
Guru
 
City: Seaford Va on Poquoson River, VA
Country: United States
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 2,182
I use that hard clear plastic 1/2" polyethylene tubing It is a straight drop then makes a gradual turn and runs about 10 foot for both being a split system with 2 evaporators you have 2 drain lines. Not had any clogging yet. Simply joined together with short rubber hose sections. The ends dump direct into the shower drain, a square bucket really, which is wide open on top. Simply, it is an old 5 gallon gas can with top cut off and a 300 gpm Rule pump screwed on the bottom.
I wonder if your dumping into a sealed top container, dose that cause a backup? are those things vented?
Before I had the boat, the AC drain water was just dumping into the bilge.
Whatever I had before, it was nasty dirty, and was also broken, the pump did not pump out the shower water. I tossed it all and started over. what I have now is easy to clean and was cheap to make, basically free, I had all those pieces given to me as dumpster finds at the marina. That marina crushed a lot of old boats, and most of it went to a landfill.
__________________

sdowney717 is online now   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 10:05 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012