A/C keeps flipping the breaker!

Installed my A/C at the end of last month. Worked fine and then while cleaning the strainer basket, it took flight and landed at the bottom of the marina.

I bought another one on Sunday and installed it yesterday. This morning I got back to the boat and found only my blower running. No compressor.

I flipped the breakers off inside the boat and restarted the ac. Compressor was working, water was flowing.

Went back this afternoon and again found only the blower working. After flipping the dock switch and the breakers inside the boat again, compressor kicked on for a few minutes and tripped the breaker again.

Any ideas what could be causing this? My basket had a jellyfish in it and two or three minnows.
toocoys is offline   Reply With Quote
Old 07-24-2018, 09:56 PM   #2
Dauntless Award
 
Wxx3's Avatar
 
City: Wrangell, Alaska
Vessel Name: Dauntless
Vessel Model: Kadey Krogen 42 - 148
Join Date: Jan 2013
Posts: 2,820
How was the outflow of water?
Was water flowing normally?
__________________
Richard on Dauntless,
New York

a Kadey Krogen 42 currently: https://share.garmin.com/dauntless
Blog:
https://dauntlessatsea.com
Wxx3 is offline   Reply With Quote
Old 07-24-2018, 10:08 PM   #3
Scraping Paint
 
City: nowhere
Join Date: Oct 2016
Posts: 934
As normally as it was before.
toocoys is offline   Reply With Quote
Old 07-24-2018, 11:18 PM   #4
Guru
 
Lepke's Avatar
 
City: Between Oregon and Alaska
Vessel Name: Charlie Harper
Vessel Model: Wheeler Shipyard 83'
Join Date: Jun 2016
Posts: 3,023
Breakers can wear out and trip at reduced amperage. Try tightening the screw on the breaker, and other connections between the ac and the breaker. Then try a different breaker.

Make sure you're getting full voltage. You could be getting reduced voltage when everyone is running ac. Lower voltage means the ac draws more amps and could trip the breaker.
Lepke is offline   Reply With Quote
Old 07-25-2018, 04:38 AM   #5
Guru
 
City: Seaford Va on Poquoson River, VA
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 2,264
Start relay could have failed, or a start capacitor.
You can easily tell if you have an amp gauge on the AC power line.
It consumes too many amps which will flip off the breaker.
sdowney717 is offline   Reply With Quote
Old 07-25-2018, 06:31 AM   #6
Veteran Member
 
Cliff Meima's Avatar
 
City: Little River, SC
Vessel Name: Memory Lane (fiberglass)
Vessel Model: 1974 Pacemaker 40 Flush deck Motor Yacht
Join Date: Jan 2016
Posts: 89
Based on the very limited amount of information that you provided I will hazard a guess. The high pressure switch in the AC has opened shutting down the compressor. The high pressure is due to insufficient cooling of the condenser coil due to hot sea water due to restricted flow possibly due to a new basket with smaller holes in the basket. I would examine the water flow after running for a few hours. Measure the water output with a thermometer at start up and then again every 30 minutes.
Cliff Meima is offline   Reply With Quote
Old 07-25-2018, 07:01 AM   #7
Guru
 
LaBomba's Avatar
 
City: Beaverton, Ontario
Vessel Name: Looking Glass
Vessel Model: Carver 370 Voyager
Join Date: Nov 2012
Posts: 1,240
Quote:
Originally Posted by Cliff Meima View Post
Based on the very limited amount of information that you provided I will hazard a guess. The high pressure switch in the AC has opened shutting down the compressor. The high pressure is due to insufficient cooling of the condenser coil due to hot sea water due to restricted flow possibly due to a new basket with smaller holes in the basket. I would examine the water flow after running for a few hours. Measure the water output with a thermometer at start up and then again every 30 minutes.
If the high pressure switch tripped it would not have tripped the breaker it would just have shut down on high pressure. I think an ammeter is needed to see if there is actually an overload or whether it is a weak breaker. Checking all connections as pointed out earlier is certainly a must.
__________________
Allan
LaBomba is offline   Reply With Quote
Old 07-25-2018, 07:10 AM   #8
Enigma
 
RT Firefly's Avatar
 
City: Slicker?
Join Date: Oct 2007
Posts: 16,566
Greetings,
NOT an AC person but have been through a similar scenario. Things to check. As mentioned: restriction in raw water "loop", weak breaker or possibly dirty air filters, low Freon, compressor is on it's way out.
__________________
RTF
RT Firefly is offline   Reply With Quote
Old 07-25-2018, 07:36 AM   #9
Guru
 
City: LI or Fla
Join Date: Jul 2013
Posts: 1,148
I agree with this:
Quote:
Originally Posted by Cliff Meima View Post
Based on the very limited amount of information that you provided I will hazard a guess. The high pressure switch in the AC has opened shutting down the compressor. The high pressure is due to insufficient cooling of the condenser coil due to hot sea water due to restricted flow possibly due to a new basket with smaller holes in the basket. I would examine the water flow after running for a few hours. Measure the water output with a thermometer at start up and then again every 30 minutes.
Marlinmike is offline   Reply With Quote
Old 07-25-2018, 09:16 AM   #10
Guru
 
City: Seaford Va on Poquoson River, VA
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 2,264
Non working water cooling wont flip the panel distribution breaker off, not in my experience.
As it gets too hot, the compressor high side pressure can go over 400 PSI, then the hi pressure cutoff switch turns off the compressor.

When it rests, hi side pressure falls, mine auto restarts.
Newer ones wont auto restart, they need to be manually reset.
sdowney717 is offline   Reply With Quote
Old 07-25-2018, 09:47 AM   #11
Guru
 
kchace's Avatar
 
City: Brookline, NH
Vessel Name: Shalloway
Vessel Model: Defever 44, twin Perkins
Join Date: Sep 2013
Posts: 2,260
Start with the simplest things first. Check the voltage with the AC running. Then check the current that the AC is drawing with a clamp on meter. If those are both good, change the breaker. If that doesn't fix it, then start worrying about the AC itself.

Ken
kchace is offline   Reply With Quote
Old 07-25-2018, 12:27 PM   #12
Scraping Paint
 
City: nowhere
Join Date: Oct 2016
Posts: 934
Quote:
Originally Posted by Cliff Meima View Post
Based on the very limited amount of information that you provided I will hazard a guess. The high pressure switch in the AC has opened shutting down the compressor. The high pressure is due to insufficient cooling of the condenser coil due to hot sea water due to restricted flow possibly due to a new basket with smaller holes in the basket. I would examine the water flow after running for a few hours. Measure the water output with a thermometer at start up and then again every 30 minutes.
Well, water has been low. We’re only floating in about 3’ right now and temps have been around 97 the last two weeks so the water is extremely hot. Even the pool at the marina is like a hot tub.
toocoys is offline   Reply With Quote
Old 07-25-2018, 12:41 PM   #13
Moderator Emeritus
 
Comodave's Avatar
 
City: Au Gres, MI
Vessel Name: Black Dog
Vessel Model: Formula 41PC
Join Date: Jul 2015
Posts: 21,191
It could be that the water is too hot. If you want to test that you can hook a garden hose from the dock to the hose coming from the strainer to the water pump and see if it works then. We had a pump go bad when we lived in Arizona so we hooked up to the dock water so we could run the A/C temporarily. Not sure if it would hurt the pump or not since we hooked it after the pump that had gone bad.
Comodave is offline   Reply With Quote
Old 07-25-2018, 06:35 PM   #14
Veteran Member
 
City: Gold Coast
Join Date: Mar 2014
Posts: 34
Turn the system off for 10 minutes and allow the compressor to equalise. If it starts and runs but then trips when the compressor cycles out (rotor lock) you may well find your problem and need the services of a A/C repair man
I agree with the comments on amp draw, run current against voltage is the simplest way to understand whats going on - you may have a simple power issue - low volts / high amp situation.
Delta Tango is offline   Reply With Quote
Old 07-25-2018, 07:02 PM   #15
Guru
 
City: Seaford Va on Poquoson River, VA
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 2,264
My Cruisair 16k btu heat pump draws 10 to 12 amps depending on temp.
But instantaneous starting amp draw may be 50 to 60 amps.

If my start relay gets stuck on, the amp draw is perhaps 25 to 27 amps, compressor motor gets hot, and it will trip the 20 amp panel breaker after a minute or two.

I upgraded the start cap to a higher voltage model, it used to blow that to pieces if the start relay failed. Now it just gets warm. I just replaced my start relay, it rusted on the inside and could no longer disconnect the start capacitor.

Some compressors may have a built in auto reset thermal breaker inside the compressor for self protection.
sdowney717 is offline   Reply With Quote
Old 07-25-2018, 08:54 PM   #16
Scraping Paint
 
City: nowhere
Join Date: Oct 2016
Posts: 934
Quote:
Originally Posted by Delta Tango View Post
Turn the system off for 10 minutes and allow the compressor to equalise. If it starts and runs but then trips when the compressor cycles out (rotor lock) you may well find your problem and need the services of a A/C repair man
I agree with the comments on amp draw, run current against voltage is the simplest way to understand whats going on - you may have a simple power issue - low volts / high amp situation.

I can get the compressor to start by flipping the breakers on and off. It'll start, and will run for 3 - 4 minutes but then shuts off, just as the air starts to cool. Flip the breaker on and off and it will restart and do the same thing.

I guess I'm going to have to call my HVAC friend and have him come look at it because it seems to be a bit over my head.
toocoys is offline   Reply With Quote
Old 07-25-2018, 09:27 PM   #17
Senior Member
 
HenryD's Avatar
 
City: North Port, FL
Vessel Name: Seven Tenths (sold)
Vessel Model: Mirage / Great Harbour 47
Join Date: Dec 2012
Posts: 477
I would check the wiring from the panel to the AC unit. If it is undersized, could cause the breaker to pop.
If I read the original post correctly, this is a new unit install, but is it a replacement for a older unit? was the AC water pump replaced? new?
HenryD is offline   Reply With Quote
Old 07-28-2018, 10:52 AM   #18
Scraping Paint
 
City: nowhere
Join Date: Oct 2016
Posts: 934
I didn’t check anything, I didn’t change anything, I didn’t do anything except to decide I wasn’t going to worry about it.

And now it’s working. Go figure.
toocoys is offline   Reply With Quote
Old 07-28-2018, 11:27 AM   #19
Senior Member
 
Duvie's Avatar
 
Join Date: Nov 2011
Posts: 340
Doesn't sound like the breaker is tripping

The OP stated that the breaker was tripping but the fan was still running. It sounds to me like the compressor is locking out on a safety and he is resetting the safety by cycling the power OFF then back ON. The fan would not run if the breaker was tripped.

In this case the previous posts concerning warm water or flow seem likely.

Toocoy, you mentioned that the system is now working ok. Has the ambient temperature gone down? High cooling water temp. low water flow or high ambient temperatures all increase the head pressure which can cause the compressor to lock out.
Duvie is offline   Reply With Quote
Old 07-28-2018, 12:18 PM   #20
Scraping Paint
 
City: nowhere
Join Date: Oct 2016
Posts: 934
Quote:
Originally Posted by Duvie View Post
The OP stated that the breaker was tripping but the fan was still running. It sounds to me like the compressor is locking out on a safety and he is resetting the safety by cycling the power OFF then back ON. The fan would not run if the breaker was tripped.

In this case the previous posts concerning warm water or flow seem likely.

Toocoy, you mentioned that the system is now working ok. Has the ambient temperature gone down? High cooling water temp. low water flow or high ambient temperatures all increase the head pressure which can cause the compressor to lock out.

Outdoor temps have been slightly lower and were floating in higher water again. When it was tripping we were only in about 3’ at the dock. We’re back up to 6 or 7 now.

Extreme tides, temps causing the issue?
toocoys is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 05:44 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012