|
06-01-2018, 04:55 PM
|
#1
|
Senior Member
City: Matagorda Bay
Vessel Name: Salty
Vessel Model: 2005 Defever 44
Join Date: May 2013
Posts: 227
|
A/C Charging Specs
I have one of my 3 split system A/C units (R22) that will only obtain ~14 degrees TD....The other 2 units are doing 18-20 degrees TD. Good condenser flow through all units and evaporator coil/filter clean.
I checked the pressures and suction line temp and came up with ~4 degrees of superheat...seems a little low (too much charge) to me as most non-TXV units call for 15-20 degrees of superheat, if memory serves. I called the manufacturer's "tech line" who referred me to several authorized dealers for charging info. I called 3 of them, and got 3 different answers as to target superheat. One of them even used the old shade tree mechanic adage "beer can sweat" on the suction line, so I discounted him right away!
I intend to play with the pressures a little and watch the evaporator TD, but would like to know if there is a spec for target superheat before I start. Any Marine Airrrrr pros out there?
Thanks in advance!
__________________
Fair winds,
Luke
|
|
|
06-01-2018, 07:26 PM
|
#2
|
Valued Technical Contributor
City: Litchfield, Ct
Join Date: Aug 2012
Posts: 6,786
|
My understanding is that it is very difficult to get the charge right in these units by looking at temps and pressures. The right way is to remove all of the refrigerant and put the right amount back in by weight.
David
|
|
|
06-01-2018, 10:22 PM
|
#3
|
Guru
City: East Coast
Vessel Name: M/V Maerin (Sold)
Vessel Model: Solo 4303
Join Date: Jun 2013
Posts: 886
|
For cap tube systems, the most accurate method is to use a https://www.google.com/search?q=supe...s-lzvowB5lDqM:chart based on outdoor dry bulb and indoor wet bulb. Since the condenser is water cooled, you can approximate the temp based on water temps. Granted, it's a fudge, but the wet bulb factor is the key to getting the SH close, and it gives you more accuracy than a SWAG. Make sure your system is cap tube! Some of the CruiseAire systems have a TXV, and if it does, you charge by subcooling, and that can be 10-15F and it will work, the TXV will compensate. If you don't have a sling psychrometer, improvise with a t-couple probe and a wet paper towel and fan. Take the refrigerant temps on the suction line, optimal location is downstream of the evap coil, and best to use a thermocouple probe that's taped to the tube and insulated or with a clamp-on tube thermocouple purpose-built for that function. Shooting with an IR reads too much background, won't be nearly accurate enough.
|
|
|
06-02-2018, 05:49 AM
|
#4
|
Guru
City: Stuart FL
Vessel Name: Lucky Lucky
Vessel Model: Pacific Mariner 65
Join Date: Aug 2013
Posts: 2,760
|
I think I just woke up in a foreign country.
__________________
Howard
Lucky Lucky
Stuart, FL
|
|
|
06-02-2018, 07:35 AM
|
#5
|
Senior Member
City: Matagorda Bay
Vessel Name: Salty
Vessel Model: 2005 Defever 44
Join Date: May 2013
Posts: 227
|
Thanks Maerin.....Yes I'm sure that the unit is not a TXV, and I am using a psychrometer and clamp thermocouple for temps. I'm just trying to find the manufacturer's superheat curves for a Marine Airrrr 10k BTU unit. I'll use the generic R22 curves as a last resort, but wanted to be as precise as I can.
__________________
Fair winds,
Luke
|
|
|
06-02-2018, 07:45 AM
|
#6
|
Guru
City: Groton, CT
Vessel Name: Datenight
Vessel Model: North Pacific 45
Join Date: Jan 2008
Posts: 1,106
|
Quote:
Originally Posted by djmarchand
My understanding is that it is very difficult to get the charge right in these units by looking at temps and pressures. The right way is to remove all of the refrigerant and put the right amount back in by weight.
David
|
+!
Rob
__________________
North Pacific 45
|
|
|
06-02-2018, 07:51 AM
|
#7
|
Senior Member
City: Matagorda Bay
Vessel Name: Salty
Vessel Model: 2005 Defever 44
Join Date: May 2013
Posts: 227
|
Weight may be the optimal methodology for a self-contained unit, but split units can have varying lengths on linesets, which affects the required amount of charge. I have one unit with 7' lines, another with 35'.
__________________
Fair winds,
Luke
|
|
|
06-02-2018, 07:55 AM
|
#8
|
Guru
City: Groton, CT
Vessel Name: Datenight
Vessel Model: North Pacific 45
Join Date: Jan 2008
Posts: 1,106
|
Quote:
Originally Posted by greysailor
Weight may be the optimal methodology for a self-contained unit, but split units can have varying lengths on linesets, which affects the required amount of charge. I have one unit with 7' lines, another with 35'.
|
Manufacturers provide specs for added line lengths.
Rob
__________________
North Pacific 45
|
|
|
06-02-2018, 07:55 AM
|
#9
|
Member
City: PARRISH
Vessel Name: Calypso
Vessel Model: Nimble Nomad
Join Date: Jan 2018
Posts: 12
|
Unless you are a certified refrigeration technician, as a past HVAC technician for the F.A.A., I wouldn't want to get caught with a set of manifold gauges, a can of refrigerant, (especially R-22), and no recovery equipment with you, and "oh, my recovery equipment is in the garage" won't hack it. The EPA is super serious about refrigerants these days and will pay informants who snitch on you. I know most of the refrigerant laws are an overkill, but the risk of serious fines just isn't worth it in my opinion. The days of DIY refrigeration repairs are long over.
Hire a professional........
Don
|
|
|
06-02-2018, 10:38 AM
|
#10
|
Guru
City: East Coast
Vessel Name: M/V Maerin (Sold)
Vessel Model: Solo 4303
Join Date: Jun 2013
Posts: 886
|
Quote:
Originally Posted by CaptDon01
Unless you are a certified refrigeration technician, as a past HVAC technician for the F.A.A., I wouldn't want to get caught with a set of manifold gauges, a can of refrigerant, (especially R-22), and no recovery equipment with you, and "oh, my recovery equipment is in the garage" won't hack it. The EPA is super serious about refrigerants these days and will pay informants who snitch on you. I know most of the refrigerant laws are an overkill, but the risk of serious fines just isn't worth it in my opinion. The days of DIY refrigeration repairs are long over.
Hire a professional........
Don
|
With all respect, the EPA threat is a paper tiger. With all the regulations and red tape created with the Montreal Protocol and the resultant scare tactics that followed, in my 30 yrs in the HVAC business, I've NEVER met in person, nor have I encountered another tech who has met, an EPA cop. The certification is a farcical test of successful indoctrination and has little to do with qualification of a service tech yet EVERYTHING to do with bureaucratic intrusion.
I would not argue that technical service work should remain in the realm of an experienced tech, there is simply too much technical knowledge involved in effecting a repair, to wit: the "foreign country" comment. But EPA regulations would not discourage me from working on a system, nor would it dissuade me from offering technical advice to a knowledgable individual who asks. I DO have a well-worn EPA card; I can legally buy refrigerant. Woo-hoo! That's about the extent of the value of that certification. It does not represent much else.
|
|
|
06-02-2018, 10:48 AM
|
#11
|
Guru
City: East Coast
Vessel Name: M/V Maerin (Sold)
Vessel Model: Solo 4303
Join Date: Jun 2013
Posts: 886
|
Quote:
Originally Posted by greysailor
Thanks Maerin.....Yes I'm sure that the unit is not a TXV, and I am using a psychrometer and clamp thermocouple for temps. I'm just trying to find the manufacturer's superheat curves for a Marine Airrrr 10k BTU unit. I'll use the generic R22 curves as a last resort, but wanted to be as precise as I can.
|
The wet bulb entering is about as accurate as you can get, even with having to judge the variance in condenser air vs water temps. You can also check with frostback on evap, useful for small unitary stuff, but my go-to would be wet bulb.
|
|
|
06-02-2018, 02:01 PM
|
#12
|
Veteran Member
City: Little River, SC
Vessel Name: Memory Lane (fiberglass)
Vessel Model: 1974 Pacemaker 40 Flush deck Motor Yacht
Join Date: Jan 2016
Posts: 89
|
By TD I assume you are talking about the temperature difference of the air entering the remote air handler and the temperature of the air leaving the air handler (evaporator).
I am not an expert on your particular unit. After reading your posting I think you understand the refrigeration cycle reasonably well. I offer this advice. Do not overlook the possibility that the inside of the air handler has rusted apart and is pulling in hot air from behind the bulkhead. Also take a look at the inline filter dryer, if it is restricted it will be very cold. By the way that old guy with his hand on the suction line is not as dumb as you might think he is. Slow down and look at your system in its entirety, I am sure you will find the answer. By the way I am certified Universal.
|
|
|
06-02-2018, 03:51 PM
|
#13
|
Guru
City: Aventura FL
Vessel Name: Kinja
Vessel Model: American Tug 34 #116 2008
Join Date: Oct 2017
Posts: 10,595
|
Unless you have the gauges and correct tools and work on reversible A/C on a regular bases....
My best advice, employ a certified technician with lots of experience. That way, if it is not right, you can bitch at someone other than yourself.
__________________
Two days out the hospital after a week in the hospital because of a significant heart attack.
|
|
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Trawler Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|