Old 12-12-2014, 09:29 PM   #1
Guru
 
O C Diver's Avatar
 
City: Fort Myers, FL... Summers in Crisfield, MD
Country: USA
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 4,813
Bilge Pump wiring options

So I'm working hard on my trawler refit and am in the process or rewiring, plumbing, and upgrading my bilge pumps. The two pumps were originally set up on a seperate fuse panel that is always on (unlike the main breaker panel that can be switched off), and each pump is switched (in the pilothouse) with either "on" or "controlled by a float switch" (no off position). Liked the idea of a seperate panel for the four pumps I now have, but keep going back and forth on the switches not having an off position. Not having an off position clearly eliminates the possibility of them being accidentally turned off, a trip to the engine room to pull a fuse isn't a big deal and most likely will never happen anyway. But on all my other boats, there has always been an off position. What do you think?

Ted
__________________
Advertisement

__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
O C Diver is offline   Reply With Quote
Old 12-12-2014, 09:33 PM   #2
Guru
 
N4712's Avatar
 
City: South FL
Country: U.S.A
Vessel Name: Oliver
Vessel Model: Nordhavn 47 Hull# 12
Join Date: Apr 2013
Posts: 3,613
Quote:
Originally Posted by O C Diver View Post
So I'm working hard on my trawler refit and am in the process or rewiring, plumbing, and upgrading my bilge pumps. The two pumps were originally set up on a seperate fuse panel that is always on (unlike the main breaker panel that can be switched off), and each pump is switched (in the pilothouse) with either "on" or "controlled by a float switch" (no off position). Liked the idea of a seperate panel for the four pumps I now have, but keep going back and forth on the switches not having an off position. Not having an off position clearly eliminates the possibility of them being accidentally turned off, a trip to the engine room to pull a fuse isn't a big deal and most likely will never happen anyway. But on all my other boats, there has always been an off position. What do you think?

Ted
I wouldn't have an off position.
__________________

__________________
Thanks, Oliver
M/V Oliver
Nordhavn 47 Hull #12
N4712 is offline   Reply With Quote
Old 12-12-2014, 09:40 PM   #3
Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 3,884
I fretted over that too when I wired my boat. I ended up including an off position. The thinking at the time was if I had a diesel spill into the bilge I could stop the pumps. I use the push button breakers, four pumps in four compartments, two on house batt, two on starting batt, alternating fwd to aft. Hard wired to batts so batt switch position has no effect. On off auto, with a red led that lights when pump is on.

The pump panel is located away from the AC and DC panels, out of the traffic area, so anyone fiddling with those panels is not going to mess with the pumps. You can rack every breaker on the DC panel to off, pumps still active.
Ski in NC is offline   Reply With Quote
Old 12-12-2014, 09:41 PM   #4
Veteran Member
 
alberto's Avatar
 
City: Valencia
Country: Spain
Vessel Name: Song of Summer
Vessel Model: GB 42 Classic
Join Date: Nov 2012
Posts: 85
I would not have an off position.
You can use the braker instead of an OFF position for testing, etc.

Do you have beepers when the float switch activates? this is important.

I have also a cycle counter, to see if I am not in the boat for days, if something has been wrong in the bilge.
alberto is offline   Reply With Quote
Old 12-12-2014, 10:34 PM   #5
Guru
 
BruceK's Avatar
 
Join Date: Oct 2011
Posts: 7,563
I have one breaker, and individual switches for each of 2 pump/auto-switches, with On/Auto/Off. (Unlike the Lucas Dim/Flicker/Off options).
One day the breaker kept tripping due to a defect in one pump. Pending replacement, I could turn that pump off. The breaker no longer tripped and I still had an operative pump. Probably could have got there another way but with an "Off" position, it was literally "flick of a switch". Go with 3 position switches.
__________________
BruceK
Island Gypsy 36 Europa "Doriana"
Sydney Australia
BruceK is offline   Reply With Quote
Old 12-13-2014, 01:08 AM   #6
Guru
 
LarryM's Avatar
 
City: League City, TX
Country: USA
Vessel Name: Pelago
Vessel Model: Wellcraft 3300 Coastal
Join Date: Aug 2011
Posts: 843
I have one main pump and one larger emergency pump. They are connected to different batteries via inline fuses and Blue Sea 3-way bilge pump switches on a separate panel. I also connected a Sonalert horn to the emergency pump so that if it is engergized, I will know it immediately. So far, so good. Just the way I wanted it.

A couple of weeks ago I discovered that an OFF position can be a trap. While I was cleaning, I inadvertantly turned both switches OFF and didn't discover it for several days. They are Contura rocker switches and it is not that easy to tell the switch position.


Nothing bad happened, but I am now going to add green LEDs directly above each switch so I can determine at a glance when the pumps are armed in the 'AUTO' position. Live and learn.

Now, my advice is to really think about whether or not you want an OFF position on your bilge pump switches. If you do, be sure to include "Check Bilge Pump Switches" on your check lists.

Larry
M/V Boomarang
LarryM is offline   Reply With Quote
Old 12-13-2014, 01:25 PM   #7
Guru
 
Edelweiss's Avatar
 
City: PNW
Country: USA
Vessel Model: 1976 Californian Tricabin LRC
Join Date: May 2011
Posts: 1,834
Quote:
Originally Posted by Ski in NC View Post
I fretted over that too when I wired my boat. I ended up including an off position. The thinking at the time was if I had a diesel spill into the bilge I could stop the pumps. I use the push button breakers, four pumps in four compartments, two on house batt, two on starting batt, alternating fwd to aft. Hard wired to batts so batt switch position has no effect. On off auto, with a red led that lights when pump is on.

The pump panel is located away from the AC and DC panels, out of the traffic area, so anyone fiddling with those panels is not going to mess with the pumps. You can rack every breaker on the DC panel to off, pumps still active.
This is the way to do it. Completely separate from the main DC panel and battery switch with multiple pump redundancy. I went a step further and added an LED to each pump switch to show when the switch is in the "Auto" position, as another poster mentioned. A little paranoid overkill maybe, but better safe than sorry!!
__________________
Larry B
Careful . . .I Have a Generator and I'm not afraid to use it !
Edelweiss is offline   Reply With Quote
Old 12-13-2014, 01:55 PM   #8
Guru
 
tpbrady's Avatar
 
City: Anchorage/Wrangell
Country: USA
Vessel Name: Silver Bay
Vessel Model: Nordic Tug 42-002
Join Date: Sep 2012
Posts: 505
I have a small fuse panel near the helm that is directly connected to the battery. That is for things that always need power like the bilge float switches, memory in fuel flow meter, and bilge alarm. Each bilge float switch is wired through a fuse position on that panel. The manual switch for each bilge pump is on its own breaker at the helm and all have indicator lights. To shut down the float switch, all I do is pull the fuse.

I also have two other fuse panels in the same area, one that is ignition switched and one that is house battery for electronics. I did this to eliminate any in line fuses buried in wiring bundles.

Tom
tpbrady is offline   Reply With Quote
Old 12-13-2014, 04:20 PM   #9
Scraping Paint
 
City: -
Country: -
Join Date: Oct 2007
Posts: 13,748
I would not want an electrical device on a boat that did not have its own on/off switch. Ski brings up an important consideration with his statement about contaminants in a bilge. Particularly today when boat owners are increasingly responsible, aka have to pay for, any damage their boats do to the environment.

But anything that can run away, get stuck on, short out, overheat, catch fire, etc. I want an easy and quick means of cutting the power to.

Our electric bilge pump has the manufacturer's off/auto/manual switch and indicator light. It is mounted on the helm consol but not on or even near the DC breaker panel. To ensure that the switch can't be inadvertently bumped from one position to another, I mounted a small, simple drawer pull over it. This lets us get a finger underneath to operate or test the pump while eliminating the risk of the dog or one of us bumping the switch out of its set position.
Marin is offline   Reply With Quote
Old 12-13-2014, 04:28 PM   #10
Guru
 
HopCar's Avatar


 
City: Miami Florida
Vessel Name: Possum
Vessel Model: Ellis 28
Join Date: Aug 2011
Posts: 3,500
The switch panels that Rule sells for use with their bilge pumps have Momentary On, Off, and Auto positions.


"Controls any pump equipped with an automatic float switch. Toggle has three positions (automatic, off, or manual) and has a "fail safe" spring return to "off" from the "manual" position. Panel is black stainless steel and has red indicator light and fuse holder."

__________________
Parks Masterson
www.hopkins-carter.com
HopCar is online now   Reply With Quote
Old 12-13-2014, 04:36 PM   #11
Scraping Paint
 
City: -
Country: -
Join Date: Oct 2007
Posts: 13,748
The panel in Park's post is what we have.
Marin is offline   Reply With Quote
Old 12-13-2014, 04:52 PM   #12
TF Site Team
 
Larry M's Avatar
 
City: JAX, FL
Country: USA
Vessel Name: Hobo
Vessel Model: Krogen 42-120
Join Date: Nov 2008
Posts: 5,729
When we had the sailboat, 1 bilge and 2 pumps. We had the day to day standard, small pump wired/fused to batteries with a counter, buzzer and no on/off switch (you could turn off the buzzer). The second pump was a Rule 3700 GPH with an on/off switch only for emergencies. The system worked well for the boat.

Hobo has 2 bilges and 2 pumps and these switches (plus a portable 3700 GPH pump). Only once have I screwed up and shut a pump off via the switch(s). I do like the pump "on" light. More than once I have noticed the light on. It has never been critical but something that needed attention. Is one system better than the other?
Attached Thumbnails
Click image for larger version

Name:	008.jpg
Views:	95
Size:	67.9 KB
ID:	35323   Click image for larger version

Name:	009.jpg
Views:	110
Size:	81.1 KB
ID:	35324  
Larry M is offline   Reply With Quote
Old 12-13-2014, 05:43 PM   #13
Guru
 
O C Diver's Avatar
 
City: Fort Myers, FL... Summers in Crisfield, MD
Country: USA
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 4,813
Lots of good points. Have 2 bilges, and each bilge now has a rule 2000 with a float switch as a primary, and a Rule 3700 with float switch mounted 2" higher as a backup / emergency. All pumps have panel indicator lights for pump running. The two 3700s have loud buzzers also. Still vacillating on the off position switch.

Ted
__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
O C Diver is offline   Reply With Quote
Old 12-13-2014, 06:21 PM   #14
Guru
 
High Wire's Avatar
 
City: Cape May, NJ and Englewood, FL
Country: USA
Vessel Name: Irish Lady
Join Date: Dec 2007
Posts: 1,600
I went with one of these
Amazon.com : MARINE BOAT BILGE ALARM PUMP SWITCH ALUMINUM PLATE MANUAL AUTOMATIC : Sports & Outdoors

Actuating the high high level switch triggers the alarm and starts the pump even if the switch is accidently placed in off.
Both normal and high high level switch needs to be able to handle pump current.
__________________
Archie
1984 Monk 36 Hull #46
Englewood, FL and Cape May, NJ
High Wire is offline   Reply With Quote
Old 12-16-2014, 12:29 AM   #15
Senior Member
 
Jay N's Avatar
 
City: Edmonds, WA
Country: USA
Vessel Name: WESTERLY
Vessel Model: 1974 Pacific Trawler 37
Join Date: Oct 2007
Posts: 387
I have two 3700 GPM pumps in the engine room bilge. Each has separate circuit breakers (25A), Auto/Manual control switches, and wiring. Since the bilge is normally dry, an alarm sounds whenever either pump is drawing power (these alarms can be muted while dealing with a flooding situation). An additional high water sensor is connected to an alarm siren guaranteed to wake everyone in the bay or adjacent docks if in a marina.

One of the questions about this wiring scenario is the appropriateness of circuit breakers for these pumps. One magazine writer is on record saying that these pumps are safe enough without wiring protection, and that it is more important to keep them going in an emergency. ABYC E11 wants protection on all circuits.

So, while the circuit breakers can be used as on/off switches, they are always left on, except when removing the pumps from the bilge. Yes, you have to remember to turn them back on.
Jay N is offline   Reply With Quote
Old 12-16-2014, 06:58 AM   #16
Guru
 
O C Diver's Avatar
 
City: Fort Myers, FL... Summers in Crisfield, MD
Country: USA
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 4,813
Quote:
Originally Posted by Jay N View Post
I have two 3700 GPM pumps in the engine room bilge. Each has separate circuit breakers (25A), Auto/Manual control switches, and wiring. Since the bilge is normally dry, an alarm sounds whenever either pump is drawing power (these alarms can be muted while dealing with a flooding situation). An additional high water sensor is connected to an alarm siren guaranteed to wake everyone in the bay or adjacent docks if in a marina.

One of the questions about this wiring scenario is the appropriateness of circuit breakers for these pumps. One magazine writer is on record saying that these pumps are safe enough without wiring protection, and that it is more important to keep them going in an emergency. ABYC E11 wants protection on all circuits.

So, while the circuit breakers can be used as on/off switches, they are always left on, except when removing the pumps from the bilge. Yes, you have to remember to turn them back on.
Had a fire start in my bilge from a faulty bilge pump and too big a fuse in the circuit. The correct size fuse is specified for a good reason. The circuit needs to go open quickly when a device is failing.

Ted
__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
O C Diver is offline   Reply With Quote
Old 12-16-2014, 08:01 AM   #17
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,518
The bilge pumps and bilge alarms will usually be hooked to an >always hot bus< .

Even with the rotary switch off the feed to the pumps will stay live , I prefer a control by a CB sized for the wire , a fuse near the pump..

I also would suggest the House batterys be the bilge pump power source.

Bigger , deep cycle and the start is still reserved for the engine , which if started can be cross fed to power the house.

The engine batt Might be OK hooked to a simple bilge alarm , as they draw little juice , tho if unheard for a couple of days would kill the start batt.
FF is offline   Reply With Quote
Old 12-16-2014, 11:56 AM   #18
Senior Member
 
Skinny's Avatar
 
City: Portsmouth, NH
Country: United States
Vessel Name: Misfit Toy
Vessel Model: 79' Mainship 34 MKI
Join Date: Nov 2014
Posts: 169
I need to rewire my pump in the spring. I would probably use a beaker that has a pull feature in order to disable it or use a switch which requires a manual action in order to position in the OFF mode. A red LED above it may be a good indicator when its in the OFF position.
Skinny is offline   Reply With Quote
Old 12-17-2014, 08:17 AM   #19
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,518
> I would probably use a beaker that has a pull feature in order to disable it or use a switch which requires a manual action in order to position in the OFF mode.<

Fewer guests or children are liable to pull a breaker than mess with a switch.

I vote for the pull .
FF is offline   Reply With Quote
Old 12-19-2014, 05:19 PM   #20
Guru
 
Shoalwaters's Avatar
 
City: Rodney Bay Lagoon
Country: St. Lucia, West Indies
Vessel Name: "Dragon Lady"
Vessel Model: DeFever 41
Join Date: Feb 2008
Posts: 681
Bilge sumps

In all the discussion on bilge pumps and related issues, I don't recall seeing mention of bilge sumps. I am fortunate to have one built into the lowest part of my boat's bilge. It is such a good idea that I am surprised all boats don't have them.

IMHO many bilge pump problems are caused by the pump and its wiring being continuously submerged in water - especially oily water which tends to make the wiring insulation brittle. The sump allows me to use a Jabsco 36600 belt-driven pump mounted well clear of bilge-water level. The only component of the whole system that gets wet is the bottom half of an Ultra Pump switch that controls the pump.

Rule pumps #1 and #2 with their own float switches are located slightly above the top of the sump. These would (I hope) take care of a major inrush of water, but otherwise stay warm and dry. They do of course need to be tested every few months.

The blue pipes are part of the fresh-water flush system - nothing to do with the bilge pumps.
Attached Thumbnails
Click image for larger version

Name:	Pump layout.jpg
Views:	187
Size:	74.8 KB
ID:	35541  
__________________

__________________
Mike
If all else fails, read the instructions
If it ain't broke, don't fix it
Shoalwaters is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 12:45 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012