Another Air Conditioning Queston

My current 'river' water (as opposed to sea) plumbing setup, has a 1000GPM pump supplying a 7K unit and a 16K unit. The pump was a 1/2" T plumbed to it's output then 1/2" hose going to each unit. The 16K unit is about 3' higher than the 7K unit. So the unit that needs the most flow, must have its water lifted 3' higher. That has been OK, mostly I believe, because the pump is a bit bigger than required, but hardly seems ideal. It seems some sort of flow restriction in the line going to the smaller, lower unit, would balance things better. Perhaps a valve closed slightly might work. That said, I hate unnecessary complexity. The current setup has worked for several years.

What Ye Think??
__________________
Advertisement

Capn Craig is offline   Reply With Quote
Old 06-16-2016, 03:59 PM   #2
Guru
 
Carolena's Avatar
 
City: DC
Country: USA
Vessel Name: Carolena II
Vessel Model: Nordic Tug 32/34
Join Date: Aug 2012
Posts: 605
Sounds very similar to our setup, which came that way from the factory. We have a single pump that services a 12k unit for the Saloon, and a 16k unit for the pilothouse and berth. The smaller 12k unit sits a little higher than the 16k, but the 16k has a much longer hose run. We've never had any issue with the single pump servicing both units. We get good flow from both of the above waterline thruhulls for each unit - looks more like a garden hose in terms of volume, unlike the trickle I see on some boats. I'd say that if it is working, then no need to worry. How does the water flow look?
__________________

Carolena is offline   Reply With Quote
Old 06-16-2016, 04:05 PM   #3
Guru
 
caltexflanc's Avatar
 
City: North Carolina for now
Country: USA
Vessel Name: Small Incentive
Vessel Model: Boston Whaler 130 Sport
Join Date: Aug 2011
Posts: 3,801
Quote:
The current setup has worked for several years.
Then that's what I think too!
__________________
George

"There's the Right Way, the Wrong Way, and what some guy says he's gotten away with"
caltexflanc is offline   Reply With Quote
Old 06-16-2016, 05:19 PM   #4
Guru
 
djmarchand's Avatar
 
City: East Greenwich, RI
Country: USA
Vessel Name: Bella
Vessel Model: Mainship Pilot 34
Join Date: Aug 2012
Posts: 2,881
Well, if it ain't broke, don't fix it. But in the spirit of prevention take a look at the thru hull output of both systems- are you getting a good stream of water out of both?


If not, and I would assume that the 16K unit would be getting less flow of course, then this is what I would do: Replace the 1/2" tee with a 3/4 x 1/2" tee with the 1/2" on the branch. Then run new 3/4" tubing all the way to the 16K unit. That will approximately balance the flow.


BTW, it is 1,000 gph not 1000 gpm.


David
djmarchand is offline   Reply With Quote
Old 06-16-2016, 05:23 PM   #5
Senior Member
 
Capn Craig's Avatar
 
Join Date: Oct 2010
Posts: 418
Quote:
Originally Posted by djmarchand View Post
Well, if it ain't broke, don't fix it. But in the spirit of prevention take a look at the thru hull output of both systems- are you getting a good stream of water out of both?


If not, and I would assume that the 16K unit would be getting less flow of course, then this is what I would do: Replace the 1/2" tee with a 3/4 x 1/2" tee with the 1/2" on the branch. Then run new 3/4" tubing all the way to the 16K unit. That will approximately balance the flow.


BTW, it is 1,000 gph not 1000 gpm.


David
Thanks, Yes that should be 1000 gph. I know better.
Capn Craig is offline   Reply With Quote
Old 06-18-2016, 05:44 PM   #6
Guru
 
Pgitug's Avatar
 
City: Punta Gorda, fl
Country: Usa
Vessel Name: Escapade
Vessel Model: Nordic Tug 37 2002
Join Date: Jan 2015
Posts: 989
Quote:
Originally Posted by djmarchand View Post
Well, if it ain't broke, don't fix it. But in the spirit of prevention take a look at the thru hull output of both systems- are you getting a good stream of water out of both?


If not, and I would assume that the 16K unit would be getting less flow of course, then this is what I would do: Replace the 1/2" tee with a 3/4 x 1/2" tee with the 1/2" on the branch. Then run new 3/4" tubing all the way to the 16K unit. That will approximately balance the flow.


BTW, it is 1,000 gph not 1000 gpm.


David

Increasing the hose to the 16k unit will increase the flow even after you adapt back to 1/2" at the unit.
Best idea. 👍
Pgitug is offline   Reply With Quote
Old 06-18-2016, 06:19 PM   #7
Guru
 
O C Diver's Avatar
 
City: Fort Myers, FL... Summers in Crisfield, MD
Country: USA
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 4,817
Have a similar setup supplying 3 12K btu units all at different levels. When replumbing the units I put 3/4" pvc ball valves before each unit. This allows me to match the flows. I use a 5 gallon bucket to measure flow. Simple stick it under the discharge and time how long it takes to fill.

Ted
__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
O C Diver is offline   Reply With Quote
Old 06-19-2016, 08:08 AM   #8
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,530
"plumbing setup, has a 1000GPM pump"

That would be a very large pump, that your main engine probably could not power.
FF is offline   Reply With Quote
Old 06-19-2016, 08:53 AM   #9
Guru
 
HiDHo's Avatar
 
City: Scottsboro, Al.
Country: USA
Vessel Name: Hi-D-Ho
Vessel Model: 1987 Krogen Manatee
Join Date: Feb 2012
Posts: 735
Turn the tee around so the water to the larger unit is a straight flow.
HiDHo is offline   Reply With Quote
Old 06-19-2016, 09:32 AM   #10
Guru
 
City: gulf coast
Country: pinellas
Join Date: Jun 2014
Posts: 2,199
Rather than look at the hose positions look at the outlets. Are they both pushing water well away from the boat in a steady stream?
__________________

bayview is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 01:55 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012