Old 06-02-2011, 06:15 PM   #1
Guru
 
Keith's Avatar
 
Vessel Name: Anastasia III
Vessel Model: Krogen 42
Join Date: Oct 2007
Posts: 2,716
AC temp differential

I seem to recall that a well functioning air conditioning unit cooled the ambient air by 20 degrees, is that right? It's a hot day here, and I'm getting ambient air inside the boat at the return at about 83 and it's coming out at 70. Sounds like it's not cooling like it should.

*
__________________
Advertisement

Keith is offline   Reply With Quote
Old 06-02-2011, 10:18 PM   #2
Senior Member
 
HeyJude's Avatar
 
City: Boerne, Tx
Country: USA
Vessel Name: HEY JUDE
Vessel Model: Kadey Krogen 36 Manatee #46
Join Date: Jan 2011
Posts: 220
RE: AC temp differential

Our '05 Sea Ray 340DA started off with a delta of 18-20 that fell to 12-14 by 2010. The cooling water discharge was noticeably less & upon recommendation of SR forum guru I flushed the AC system with phosphoric acid to dissolve the minerals that had deposited themselves within the AC coils. Post procedure the cooling water flow increased by 30%, the outflow temp rose 10 & the delta returned to 18-20. The acid is a paint prep, available at HD & fairly benign to work with.
__________________

HeyJude is offline   Reply With Quote
Old 06-04-2011, 04:42 AM   #3
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,515
RE: AC temp differential

Most air cond output readings are at the evap , about 40F is the goal.Below that and icing is a possibility .

Measuring at the end of a duct allows too many variables.

THe key to efficient air cond is in having a very efficient ducted return system.
FF is offline   Reply With Quote
Old 06-13-2011, 03:58 PM   #4
Member
 
Join Date: Jan 2011
Posts: 20
RE: AC temp differential

Quote:
FF wrote:
Most air cond output readings are at the evap , about 40F is the goal.Below that and icing is a possibility .

Measuring at the end of a duct allows too many variables.

THe key to efficient air cond is in having a very efficient ducted return system.
*Not really true...34 to 42 degrees is the target with a 15 to 18 degree TD...
<ul>[*]Higher than 18 degree TD usually means restricted air flow and is where you will see coil icing in ambient air temps below 68 degrees or higher depending on how restricted...[*]Less than 15 degree TD usually means a system problem...[/list]These figures are what Cruisair & Marine Air design for...

Yes a long duct run can reduce TD a bit...

I do agree about the duct system needs to be efficient, but many times ducted return is anything but in a boat, and more often too small for the Btu design due to space restraints aboard....

Steve~

Marine-AC.com
spcoolin is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hot Water Temp Control dvd Other Trawler Systems 13 03-16-2012 02:41 AM
Dual station temp. guages geezer Electrical and Electronics & Navigation 13 10-05-2011 03:12 PM
Temp. Gauge (again) Max Simmons Electrical and Electronics & Navigation 3 07-24-2011 04:35 AM
Oil pressure/temp alarm geezer General Discussion 2 08-07-2010 09:09 AM




All times are GMT -5. The time now is 06:10 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012