AC High Pressure shutdown

One of our AC units has started shutting down with a high pressure error code. It'll run for a while, then shut down. Besides backwashing the unit, which we've already tried, is there anything else we can do before we have to pay someone else to fix it?
__________________
Advertisement

No Mast is offline   Reply With Quote
Old 08-06-2015, 10:42 AM   #2
Guru
 
hmason's Avatar
 
City: Westport, CT
Country: USA
Vessel Name: Magic
Vessel Model: Grand Banks 46 Europa
Join Date: Aug 2013
Posts: 1,895
We had a similar problem. The digital display on the MarineAir unit read "CLF."
This means compressor load failure. We did what you did plus cleaning all the return air filters and vacuuming the evaporator coils. Could not fix it. Called in a repair company and they had to replace the circuit board. The one last thing I would investigate is to be sure the unit is getting proper voltage. Good luck, Howard
__________________

__________________
Howard
Magic, 1996 Grand Banks Europa
Westport, CT and Stuart, FL
hmason is offline   Reply With Quote
Old 08-06-2015, 11:22 AM   #3
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,422
High pressure fault is almost always a water flow issue. Start by cleaning your strainer and making sure your pump is functioning property. Then acid flush all your A/C units.
Capt.Bill11 is offline   Reply With Quote
Old 08-06-2015, 12:39 PM   #4
Guru
 
No Mast's Avatar
 
City: Atlantic Highlands, NJ
Country: US
Vessel Name: Moana Huaka'i
Vessel Model: Selene 53
Join Date: Dec 2014
Posts: 816
it doesn't seem to be a flow issue, We cleaned all the lines. The same pump handles another AC unit and its running fine. So it isn't the pump. I'll double check the voltage at the unit.
No Mast is offline   Reply With Quote
Old 08-06-2015, 12:39 PM   #5
Guru
 
healhustler's Avatar
 
City: Longboat Key, FL
Country: USA
Vessel Name: Bucky
Vessel Model: Krogen Manatee 36 North Sea
Join Date: Oct 2009
Posts: 4,178
Have the same issue now with 16K Cruisair unit. Cleaned strainer, blew it out just in case, replaced all cooling lines, acid cleaned coils, flow wonderful but same issue. Bypassed hi pressure switch, same issue. Called A/C guy and he jump wired everything he could, same issue. He says the problem is either in the board or in an internal thermal switch inside the compressor. Taking the unit out now for bench evaluation.
__________________
Larry

"I'd rather be happy than dignified".
healhustler is offline   Reply With Quote
Old 08-06-2015, 12:45 PM   #6
Guru
 
No Mast's Avatar
 
City: Atlantic Highlands, NJ
Country: US
Vessel Name: Moana Huaka'i
Vessel Model: Selene 53
Join Date: Dec 2014
Posts: 816
Quote:
Originally Posted by healhustler View Post
Have the same issue now with 16K Cruisair unit. Cleaned strainer, blew it out just in case, replaced all cooling lines, acid cleaned coils, flow wonderful but same issue. Bypassed hi pressure switch, same issue. Called A/C guy and he jump wired everything he could, same issue. He says the problem is either in the board or in an internal thermal switch inside the compressor. Taking the unit out now for bench evaluation.
ugh. good luck! hope we end up with a somewhat faster solution, but it wouldn't be the first thing to get "fixed" multiple times before its right.

Thanks for the info, ours is also cruisair, good to know.
No Mast is offline   Reply With Quote
Old 08-06-2015, 02:13 PM   #7
Guru
 
siestakey's Avatar
 
City: Sarasota,FL/Thomasville,GA
Country: USA
Vessel Name: Steppin Stone IV
Vessel Model: Marine Trader Kelly Trawler 46
Join Date: Jul 2013
Posts: 1,271
Send a message via Skype™ to siestakey
On my salon I get this has always been the waterflow
siestakey is offline   Reply With Quote
Old 08-06-2015, 04:21 PM   #8
Guru
 
MYTraveler's Avatar
 
City: West Coast
Country: USA
Join Date: Apr 2014
Posts: 850
Quote:
Originally Posted by No Mast View Post
it doesn't seem to be a flow issue, We cleaned all the lines. The same pump handles another AC unit and its running fine. So it isn't the pump. I'll double check the voltage at the unit.
Could it be that all (or most) of the water flow from the pump is being directed to the AC unit that is working fine? I would think that a blockage in the portion of the line supplying the bad AC unit (or in that unit's discharge line) could create that problem.

FWIW, I occasionally had that problem with an ice maker (one that produces 800 pounds of ice per day). I solved the problem by installing a higher capacity pump.
MYTraveler is offline   Reply With Quote
Old 08-06-2015, 05:10 PM   #9
Guru
 
Forkliftt's Avatar
 
City: Biloxi Mississippi
Country: USA
Vessel Name: Patricia Louise II
Vessel Model: 1983 42' Present Sundeck
Join Date: Oct 2007
Posts: 2,433
AC High Pressure shutdown

I have always had low water flow out of my front AC I always felt. One shared pump which I upgraded about 5 weeks ago. All the same maintenance approaches as listed except I didn't replace cooling hoses until two weeks ago. Wow. Front discharge now looks like one that you pass on the pier and think "sure wish mine flowed like that". Lots of obstructions in the hoses. Mucho barnacles.
An idea to ponder if you replace your hoses. I used a 5/8" male barbed grey plastic union- connected new hose and old together. Afterwards screwed a couple of #6 x 1/2" ( I believe) screws into the coupler. Sunk these into the hose to streamline things. This allowed me to pull the new hose through bulkheads/ etc. with the old hose. Click image for larger version

Name:	ImageUploadedByTrawler Forum1438895408.943974.jpg
Views:	130
Size:	27.5 KB
ID:	42924


1983 Present 42 Sundeck
Twin Lehman 135's
✌️
__________________
Steve Point Cadet/ Biloxi, Mississippi USA
*Present 42 twin 135 Lehmans
Forkliftt is offline   Reply With Quote
Old 08-07-2015, 08:14 AM   #10
Guru
 
ranger42c's Avatar
 
City: Maryland
Country: USA
Vessel Model: 42' Sportfish
Join Date: Aug 2013
Posts: 3,157
Products like Rydlyme, Barnacle Buster, or Triton Marine will get a lot of stuff out of the hoses...


-Chris
__________________
South River, Chesapeake Bay
ranger42c is offline   Reply With Quote
Old 08-07-2015, 10:52 AM   #11
Senior Member
 
sum escape's Avatar
 
City: Muskegon, MI
Country: Cruising
Vessel Name: Sum Escape
Vessel Model: Grand Banks 47' Europa
Join Date: Jun 2014
Posts: 133
Air handler

Fighting same issue. Water flow was OK. Replaced defective (very noisy) compressor unit. Same problem HPF code. Apparently when compressor deteriorated, "junk" clogged air handler. So now this is on order.
We'll see....
sum escape is offline   Reply With Quote
Old 08-07-2015, 10:52 AM   #12
Senior Member
 
City: Marathon
Country: Usa
Vessel Name: silver gift
Vessel Model: 45 jefferson
Join Date: Nov 2013
Posts: 202
If you are acid washing the water circuit make sure you are circulating the acid ,not just pumping it overboard. Take a 5 gallon bucket and installed a thru hull fitting at bottom and just take hose off intake put on bucket ,disc change hoses into bucket and run pump for an hour or so. Then put city water to intake and flush to force shells ,growth on hose ,etc out of system. Acid may loosen stuff or dissolve build up put things can get hung up . Also flush with city pressure from discharge to pump connection ,that way you push out caught stuff inline.
Deckape is offline   Reply With Quote
Old 08-07-2015, 01:37 PM   #13
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,422
Quote:
Originally Posted by No Mast View Post
it doesn't seem to be a flow issue, We cleaned all the lines. The same pump handles another AC unit and its running fine. So it isn't the pump. I'll double check the voltage at the unit.
By clean the lines what do you mean? Acid flush? The flow can be good but if the tubes are coated with scale you will not get proper heat exchange. Hence the high pressure fault.
Capt.Bill11 is offline   Reply With Quote
Old 08-09-2015, 07:51 AM   #14
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,518
I would replace the freon filter/dryer.

A drop of moisture in the system will shut it down.
FF is offline   Reply With Quote
Old 08-10-2015, 11:15 AM   #15
Guru
 
No Mast's Avatar
 
City: Atlantic Highlands, NJ
Country: US
Vessel Name: Moana Huaka'i
Vessel Model: Selene 53
Join Date: Dec 2014
Posts: 816
ok I'll go back and check our lines closer. Maybe I didn't do the acid flush long enough. I'll also pull the hoses from the pump and visually check them.
No Mast is offline   Reply With Quote
Old 08-10-2015, 11:30 AM   #16
Senior Member
 
City: MD
Country: USA
Vessel Name: Blue Yonder
Vessel Model: 37
Join Date: Mar 2013
Posts: 346
This is what Barnacle Buster cleaned out of my AC after four seasons of use in mainly brackish water. If you have one pump servicing two units, you might try blocking the flow to the good unit and trying the system with only the problem unit running and getting flow.
Attached Thumbnails
Click image for larger version

Name:	Barnacle Buster AC.jpg
Views:	70
Size:	94.9 KB
ID:	43044  
BlueYonder is offline   Reply With Quote
Old 08-10-2015, 11:46 AM   #17
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,422
Quote:
Originally Posted by FF View Post
I would replace the freon filter/dryer.

A drop of moisture in the system will shut it down.
Yes, best course of action is to just start replacing things willy nilly.
Capt.Bill11 is offline   Reply With Quote
Old 08-10-2015, 12:20 PM   #18
Guru
 
No Mast's Avatar
 
City: Atlantic Highlands, NJ
Country: US
Vessel Name: Moana Huaka'i
Vessel Model: Selene 53
Join Date: Dec 2014
Posts: 816
Quote:
Originally Posted by BlueYonder View Post
If you have one pump servicing two units, you might try blocking the flow to the good unit and trying the system with only the problem unit running and getting flow.
Now thats a good thought! Hmm, I honestly didn't think about that. Of course, will do. thanks!
No Mast is offline   Reply With Quote
Old 08-10-2015, 12:22 PM   #19
Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 3,884
High pressure shutdown is usually high pressure in the condenser, the water cooled loop. Most have a pressure sensor there, which of course could be bad. Usually low water flow or fouled insides of the heat exchanger. When two units share a pump, it easily could be one getting more of the water flow. Hopefully you have a discharge for each so you can visualize flow.

One trick is to check temp of water coming out of the condenser. Also check temp of refrigerant coming out of condenser. If water is cool with good flow and ref is hot, fouled HX. If water and ref are hot, poor flow. If both are cool, then bad p-sensor or goofy expansion valve or clogged filter/dryer.

At some point you may need a tech with a gauge set to read actual pressures.
Ski in NC is offline   Reply With Quote
Old 08-10-2015, 07:01 PM   #20
Guru
 
Forkliftt's Avatar
 
City: Biloxi Mississippi
Country: USA
Vessel Name: Patricia Louise II
Vessel Model: 1983 42' Present Sundeck
Join Date: Oct 2007
Posts: 2,433
I finally found this pic of the inside of the front AC hoses I discussed earlier-
Note: these barnacles were attached inside the dark blue hose. Click image for larger version

Name:	ImageUploadedByTrawler Forum1439247685.150892.jpg
Views:	73
Size:	41.1 KB
ID:	43055


1983 Present 42 Sundeck
Twin Lehman 135's
✌️
__________________

__________________
Steve Point Cadet/ Biloxi, Mississippi USA
*Present 42 twin 135 Lehmans
Forkliftt is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On