Old 12-30-2015, 12:11 PM   #1
Guru
 
JDCAVE's Avatar
 
City: North Vancouver
Vessel Name: Phoenix Hunter
Vessel Model: Kadey Krogen 42 (1985)
Join Date: Apr 2011
Posts: 2,877
Petcocks for sight gauge on fuel tanks

The PO replaced the two back iron tanks with (700 gallons total), with 4 aluminum tanks (760 gallons total). The two forward most tanks are 200 gallons each and the two aft tanks are 180 gallons each. Each tank has a sight gauge with a petcock, top and bottom.

The petcocks are kept in the closed orientation. However, sometimes one forgets to close them. I have found that two of the bottom petcocks "weep" a bit only when they are in the open orientation. Clearly these should be replaced and I am looking for a supplier, if anyone can provide.

On purchase, my surveyor identified these sight gauges as a cause for concern and suggested that I replace them with tank tenders of some sort. He felt they were a fire hazard. I suggested that they could be enclosed in a protective chamber (suggestions please), and he still felt they could fail and be a hazard.

So here are the options as I see it:

1) replace the Petcocks at the very least.

2) 1) above and also put some sort of shield around them.

3) Other low cost alternative? (i.e. put permanent plugs in).

Note: I cannot get a dip stick to the bottom of these tanks.

Thought please.



Jim
Attached Thumbnails
Petcock and Valve port rear fuel tank.jpg   Fuel Lines and tank.jpg  
JDCAVE is offline   Reply With Quote
Old 12-30-2015, 12:47 PM   #2
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 22,553
You might just cycle the valve a hundred times or so to see if the tiny leak is from gunk.

Sit with a brew and hope for the seal to clear as you move it.
FF is offline   Reply With Quote
Old 12-30-2015, 12:58 PM   #3
TF Site Team
 
Larry M's Avatar
 
City: Jacksonville
Join Date: Nov 2008
Posts: 11,682
I'd stay with the sight tubes. Just make sure you close the valves.

Did your surveyor site any specific regulations regarding them? (and please no offense) or was it just his personal opinion? I though sight tubes were an industry accepted practice as long as you had valves similar to what you have so you can shut the flow off from the tank?
Larry M is online now   Reply With Quote
Old 12-30-2015, 01:52 PM   #4
Guru
 
psneeld's Avatar
 
City: Ft Pierce
Vessel Name: Sold
Vessel Model: Was an Albin/PSN 40
Join Date: Oct 2011
Posts: 28,149
Sight gauges are only a fire hazard if left open...I hope he told you that or it is yet another time that we discuss why there is a problem with run of the mill opinions...from anyone.

There are spring loaded valves that auto shut...yes it involves getting right up to them to activate them...but that is one safety factor against what the surveyor was saying.

Even then...unless you have remote shutoffs to bottom takeoff engine supply lines...what's the difference?

Anyone have the spring loaded valves or know of a supplier?

The Azimuts I used to run had them.
psneeld is online now   Reply With Quote
Old 12-30-2015, 01:56 PM   #5
Guru
 
JDCAVE's Avatar
 
City: North Vancouver
Vessel Name: Phoenix Hunter
Vessel Model: Kadey Krogen 42 (1985)
Join Date: Apr 2011
Posts: 2,877
Thanks guys. Of course no offense taken! Harsher words have been said on this forum, for sure.

I distinctly remember the surveyor mentioning his concerns on inspection but he did not identify them on his written survey for insurance. Also, I have another survey from a previous failed purchaser. There was no mention of concern in this regard.

Those petcocks are a bit of a concern. The weeping is slight but over time can be significant and eventually it can get into the bilge. As I mentioned, neither petcock weeps when shut but these can be bumped. We go to the boat at least once a week for inspection and I always check these.

Does anyone know of a better petcock design? I do not know the manufacturer.
JDCAVE is offline   Reply With Quote
Old 12-30-2015, 01:58 PM   #6
Guru
 
City: Hotel, CA
Join Date: Sep 2011
Posts: 8,323
Granger and pretty much all the other normal suspects carry spring loaded ball valves as well. Spendy little things but will keep you out of the running for the Darwin Award.

I still see nothing wrong with the op running things as is. Even the leak in the open position is no big deal in the grand scheme of things IMO.
__________________
Craig

It's easier to fool people than to convince them that they've been fooled - Mark Twain
CPseudonym is offline   Reply With Quote
Old 12-30-2015, 02:29 PM   #7
Guru
 
JDCAVE's Avatar
 
City: North Vancouver
Vessel Name: Phoenix Hunter
Vessel Model: Kadey Krogen 42 (1985)
Join Date: Apr 2011
Posts: 2,877
Hmmm! These fittings might be aluminum. I had thought they were SS. Better if they were aluminum it seems.


Replacing A Fuel Tank Photo Gallery by Compass Marine How To at pbase.com


Jim
JDCAVE is offline   Reply With Quote
Old 12-30-2015, 02:51 PM   #8
Guru
 
obthomas's Avatar
 
City: Seabrook Texas
Vessel Name: TheVenture
Vessel Model: 1985 Bestway Labelle Sundeck 40ft
Join Date: May 2013
Posts: 560
Some excerps

NFPA 302 Fire Protection Standard for Pleasure and Commercial Motor Craft

7.3.12 The use of gauge glasses shall be restricted to day tanks and service tanks of diesel fuel systems.
7.5.1.7.1 Plastic pipe and plastic fittings shall not be used in fuel distribution lines, vent lines, and fill lines unless permitted by 7.5.1.7.2 or 7.5.1.7.3.
7.5.1.7.2 Components of deck fill fittings, vent fillings, carburetor fittings, fuel pump fittings, and fuel filter fittings shall be permitted to be of plastic.
7.5.1.7.3 Engineering-grade plastics, such as glass-reinforced nylons, shall be permitted to be used in fuel distribution lines, vent lines, and fill lines.
obthomas is offline   Reply With Quote
Old 12-30-2015, 03:21 PM   #9
TF Site Team
 
koliver's Avatar
 
City: Saltspring Island
Vessel Name: Retreat
Vessel Model: C&L 44
Join Date: Nov 2007
Posts: 5,663
I use my log book.
I record engine hours when I refuel, and knowing my /hr consumption, I know when to refuel.
This wouldn't work if I lost both my log book and my memory of my last fill, so there is some redundancy.
koliver is offline   Reply With Quote
Old 12-30-2015, 03:35 PM   #10
Dauntless Award
 
Wxx3's Avatar
 
City: Wrangell, Alaska
Vessel Name: Dauntless
Vessel Model: Kadey Krogen 42 - 148
Join Date: Jan 2013
Posts: 2,820
Quote:
Originally Posted by Larry M View Post
I'd stay with the sight tubes. Just make sure you close the valves.

Did your surveyor site any specific regulations regarding them? (and please no offense) or was it just his personal opinion? I though sight tubes were an industry accepted practice as long as you had valves similar to what you have so you can shut the flow off from the tank?
also, you may consider just exercising the petcocks as already mentioned, or leave alone.

Unless they feed from the absolute bottom of the tank, not sure I see the point.

On the other hand, if bottom feed, then they are useful.
__________________
Richard on Dauntless,
New York

a Kadey Krogen 42 currently: https://share.garmin.com/dauntless
Blog:
https://dauntlessatsea.com
Wxx3 is offline   Reply With Quote
Old 12-30-2015, 03:53 PM   #11
Guru
 
rwidman's Avatar
 
City: North Charleston, SC
Join Date: Sep 2010
Posts: 4,870
Quote:
Originally Posted by JDCAVE View Post
The PO replaced the two back iron tanks with (700 gallons total), with 4 aluminum tanks (760 gallons total). The two forward most tanks are 200 gallons each and the two aft tanks are 180 gallons each. Each tank has a sight gauge with a petcock, top and bottom.

The petcocks are kept in the closed orientation. However, sometimes one forgets to close them. I have found that two of the bottom petcocks "weep" a bit only when they are in the open orientation. Clearly these should be replaced and I am looking for a supplier, if anyone can provide.

On purchase, my surveyor identified these sight gauges as a cause for concern and suggested that I replace them with tank tenders of some sort. He felt they were a fire hazard. I suggested that they could be enclosed in a protective chamber (suggestions please), and he still felt they could fail and be a hazard.

So here are the options as I see it:

1) replace the Petcocks at the very least.

2) 1) above and also put some sort of shield around them.

3) Other low cost alternative? (i.e. put permanent plugs in).

Note: I cannot get a dip stick to the bottom of these tanks.

Thought please.

Jim
1) They are not a fire hazard unless you have a fire.

2) Any safety standard that requires humans to remember to do something isn't worth the paper it's written on.

Are the sight tubes plastic or high temperature glass made for the purpose? Plastic would melt in a fire and dump fuel onto the fire. If you forgot to close the petcocks, you would have a steady source of fuel for a very long time. Glass, of course could break and do the same thing.

It's up to you to decide the risk, but in any case, I would replace the petcocks with self closing ones and make sure the tubes were not plastic, but glass designed for the purpose and I would put a metal guard (screen so you could see through it) around them.
rwidman is offline   Reply With Quote
Old 12-30-2015, 03:54 PM   #12
Guru
 
twistedtree's Avatar
 
City: Vermont
Join Date: Jan 2013
Posts: 10,092
Our site gauges are recessed into an aluminum channel for physical protection. On CE certified boats, my understanding is that the spring loaded valves previously mentioned are required. That way if a glass does break, the fuel loss is limited to the contents of the glass. That seems like the best belt and suspenders approach.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 12-30-2015, 04:02 PM   #13
Guru
 
Xsbank's Avatar
 
City: Pender Harbour, BC
Vessel Name: Gwaii Haanas
Vessel Model: Custom Aluminum 52
Join Date: Sep 2013
Posts: 3,791
Mine are always off, I open them to check the level, shut off. If you think you can accidentally open them, rotate the valve so the handle is harder to get to. No worries.
__________________
Don't believe everything that you think.
Xsbank is offline   Reply With Quote
Old 12-30-2015, 04:25 PM   #14
Guru
 
City: Venice Louisiana
Join Date: Dec 2013
Posts: 1,097
Most of the sight tubes used in the oil industry are protected by a housing. Looks like aluminum with oval "holes" the length of it. I dont have a clue where to get them.
kulas44 is offline   Reply With Quote
Old 12-30-2015, 11:11 PM   #15
Guru
 
C lectric's Avatar
 
City: Gibsons, B.C., Canada
Vessel Name: Island Pride
Vessel Model: Palmer 32'
Join Date: Oct 2007
Posts: 4,414
Those valves look like cheapies.

There are good quality miniature ball valves that will not leak. 600psi WOG. You may need to use a SS 316 nipple for isolation from the tank to the valve as many valves are brass. The SS will isolate the alum tank from the brass valve.

Check out:
Fairview Fittings, 1st ave., Burnaby

They may also have spring loaded valves but don't know.

As far as guarding the valve and the tube itself it looks like with some thought you could use an aluminum angle secured to the stringer just below the tank and to the overhead. Stand it off a bit so it does not contact the tank.
C lectric is offline   Reply With Quote
Old 12-31-2015, 12:23 AM   #16
Scraping Paint
 
City: -
Join Date: Oct 2007
Posts: 13,745
Our boat has sight tubes on the four saddle tanks. The tubes are PVC flexible tubing. There are other types of flexible tubing that are more resistant to discoloration from the dye in the fuel. Glass can be a poor choice because it can be broken or shattered accidentally.

Ideally there should be a shutoff valve at the top and bottom of the tube. Our sight gauges have shutoff valves only at the bottoms of the tubes but so far in 17+ years no surveyor has commented on them or written them up. We keep the valves closed at all times and only open them momentarily to get a level reading.
Marin is offline   Reply With Quote
Old 12-31-2015, 06:40 AM   #17
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 22,553
"neither petcock weeps when shut but these can be bumped."

Drill hole 1/16 inch in petcock handle , install safety wire .

DONE
FF is offline   Reply With Quote
Old 12-31-2015, 07:35 AM   #18
Senior Member
 
Join Date: Aug 2008
Posts: 265
Easy solution to bumping the handles open. Remove the handles and keep them tied nearby. You'll only need them to check the levels anyway.
folivier is offline   Reply With Quote
Old 12-31-2015, 09:30 AM   #19
Guru
 
City: Carefree, Arizona
Vessel Name: sunchaser V
Vessel Model: DeFever 48 (sold)
Join Date: Apr 2008
Posts: 10,186
Quote:
Originally Posted by C lectric View Post
Those valves look like cheapies.

There are good quality miniature ball valves that will not leak. .
Marine grade ball valves, I have eight of them on my tanks and ten on the fuel manifold
sunchaser is offline   Reply With Quote
Old 12-31-2015, 09:48 AM   #20
Guru
 
rwidman's Avatar
 
City: North Charleston, SC
Join Date: Sep 2010
Posts: 4,870
[QUOTE=Marin;399967]Our boat has sight tubes on the four saddle tanks. The tubes are PVC flexible tubing. There are other types of flexible tubing that are more resistant to discoloration from the dye in the fuel. Glass can be a poor choice because it can be broken or shattered accidentally.QUOTE]

PVC will melt if there's a fire.
rwidman is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 03:49 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012