Reply
 
Thread Tools Search this Thread Display Modes
 
Old 09-30-2019, 10:10 AM   #1
Veteran Member
 
City: Antalya
Country: Turkey
Vessel Name: Möbius
Vessel Model: Custom Expedition Passagemaker under build
Join Date: Aug 2016
Posts: 32
Xpm-78 -All the amenities/No generator

Wayne's latest post is on the DC Battery-Based electrical system for our new custom 78-foot aluminum extreme expedition passage maker (XPM-78) under build in Turkey.

All electric galley, washer/dryer, and two techie nerds with lots of tools and toys.

Lots of solar and big alternators, but we will have NO generator.

Everything is theoretical since we've never done this before, so we're very interested to learn from your comments.

Check out the electrical diagram here:

https://mobius.world/tech-talk-xpm78...stem-overview/

__________________
Advertisement

ChristineKling is offline   Reply With Quote
Old 09-30-2019, 11:30 AM   #2
Guru
 
cardude01's Avatar
 
City: Victoria TX
Country: USA
Vessel Name: Bijou
Vessel Model: 2008 Island Packet steadysailer
Join Date: Nov 2012
Posts: 4,321
Xpm-78 -All the amenities/No generator

Wow, 14x360W solar panels is a lot of surface area!

From a guy with a boat that got caught in Dorian and had his two big solar panels blown off the mounts, how will you be sure the solar will withstand possible very high wind loads?

Granted, mine were probably not mounted as securely as they should have been, and if I was close to the boat I would probably have removed them and stored them inside the boat, but just wondering how y’all plan to mount your solar.
__________________

cardude01 is offline   Reply With Quote
Old 09-30-2019, 11:42 AM   #3
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 4,940
Great stuff, as always. And what would a reply be without a few questions? ......

I’m curious how you envision operating on 60hz shore power with a 50hz boat? Assuming your inverters are programmed to 50hz, they will only
Lock on to 50hz shore power. Alternately you can open up the acceptable input frequency really wide to accept both 50 and 60hz. But if you do that then the 60hz shore power will pass through yielding 60hz on board rather than your native 50hz. This implies that all the onboard loads are 50/60hz agnostic.
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 09-30-2019, 11:48 AM   #4
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 4,940
Oops, that was only one question.

Personally I wouldn’t be comfortable without a generator, if go no other reason than to provide a backup power source.

And I’m really envious of your 5kw of solar.

I’m also interested that you have separate inverter systems for 120 and 240v. The alternative is to use an auto transformer or just a reduction transformer off a 240v inverter system. Curious what your thinking is on this. I have personally become very sensitive to the standby power draw of the Victron’s, all of which run all the time. Others like outback idle parallel inverters and bring them online progressively as loads demand.
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 09-30-2019, 05:49 PM   #5
TF Site Team
 
Insequent's Avatar
 
City: Brisbane
Country: Australia
Vessel Name: Insequent
Vessel Model: Ocean Alexander 50 Mk I
Join Date: Mar 2012
Posts: 2,358
I have 6 x 345W solar, 2 x 200A engine alternators and a house bank of 1284Ah @ 12v. And no generator. So, a scaled down version of what is planned for the xpm78. I have a propane galley, but refers are 12V. They are the biggest draws.

After a six years of use, a few observations are:
1. weaker winter irradiance and/or angle means noticeably less solar Ah replacement. In higher latitudes this would be accentuated unless the panels can be tilted.
2. If I get panel shading, and that occurs with SE winds at anchor for me, then solar will not match daily use in winter. Down here in Oz the SE trades blow all winter, so it is an issue!
3. Moving after a few nights at anchor allows the house bank to be boosted enough for the solar to cope. But if you want to spend a week somewhere, other than in low latitudes in warmer months, then you need to do serious power management (saving) on board.
4. I have the ubiquitous Honda 2000 for backup, and on average over a year I use it 5-10% of time anchored. All things considered I would install a 5kW genny if doing it again.

For the schematic on the blog, there is a typo. Alternators are "250V @24V" should obviously be "250A @24V".

Using inverter/chargers would not be my choice next time. I would seperate the functions. So, both 230V and 120V inverters (at 50Hz and 60Hz respectively) and Victron's universal input chargers (90-265V, 50/60Hz). Wiring & switching is more simple.

As TT notes, parasitic loads add up and its not just the Victron's. eg Sat dish always on in case I've set the PVR to record something, TV on standby, laptop plugged in, USB chargers plugged in for phone/ipad charging, router and switches running. It ends up being a surprising amount, and too much of a PITA to be running round turning off/on etc. Easier to have a larger house bank and more charging options. Hence the genny.
__________________
Brian
Insequent is online now   Reply With Quote
Old 10-01-2019, 07:12 AM   #6
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 19,736
" I have a propane galley, but refers are 12V. They are the biggest draws."

A switch to propane reefers would cancel the biggest electrical load on most boats.

Second choice would be custom built super insulated (4-6 inches) and eutetic plates.

These could be engine charged or solar tho the engine driven seem to do better with freezer temps 0-F plates with -10F needed to charge . The downside is the plates and thick insulation take up a lot of room.


Air cond only under way?
FF is offline   Reply With Quote
Old 10-01-2019, 09:31 AM   #7
Guru
 
djmarchand's Avatar
 
City: Litchfield, Ct/Punta Gorda, Fl
Country: USA
Vessel Model: Atlas Pompano 23
Join Date: Aug 2012
Posts: 4,835
For comparison my 1,500 SF Florida condo uses 12 kWhr per day on average during the winter months. No air conditioning or room heat and all other loads are comparable to your boat: electric stove, washer dryer and water heater for two, TV, router all on 24/7, etc.

A 5 kW solar panel should put out 20 kW on an average sunny day so you should be in balance with your solar capability in most latitudes even with cloudy days and even if you don't move and supply power with the engine alternators.

Since your hot water is electric (except presumably when you have run the propulsion engine recently), consider installing a heat pump hot water heater. Should cut your hot water energy usage in half, although these don't typically have a coil for engine heat. Depends on your ratio of hanging out on the hook vs underway whether it helps or not.

David
djmarchand is online now   Reply With Quote
Old 10-01-2019, 12:22 PM   #8
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 8,069
As echoed by others, a genset install may prove helpful more often than not. My 12.5 kW unit in its sound shield measures 23"x40"x26" with a 5kw unit for sure smaller. A lot more money can be spent trying to avoid a genset than installing one.
sunchaser is offline   Reply With Quote
Old 10-01-2019, 12:30 PM   #9
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 4,940
I think their plan is to use the main as the genset, when required. That’s a pretty common sail boat approach, and is perfectly viable with an accompanying set of trade offs. But as a infrequently used power source, I don’t think it’s a bad approach. My biggest concern would be having a backup if there is some issue with the main engine charging system. Then you only have solar, and there WILL be times when it’s not enough. But a little portable screamer may be all that’s needed as a backup. Hopefully Wayne will be able to share his thinking soon. He’s probably typing away.
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 10-01-2019, 02:48 PM   #10
Veteran Member
 
darkside's Avatar
 
City: Tauranga
Country: New Zealand
Vessel Name: Mahimahi
Vessel Model: Roger Hill Powercat
Join Date: Apr 2016
Posts: 48
If the boat is set up to live off the batteries the shore power is simple, you just need it to run a battery charger.
Hz problem solved.
We had no generator on the sail cat, just big alternators and solar. I didn't want air conditioning and three small diesel engines seemed one too many. However running a 38hp diesel to charge the batteries is easier to justify than 120hp or 300hp on a trawler.
We also had a propane fridge but having a pilot light going the whole time plays on your mind. When it failed in Thailand we replaced it with another 12v
darkside is offline   Reply With Quote
Old 10-02-2019, 05:36 AM   #11
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 19,736
"We also had a propane fridge but having a pilot light going the whole time plays on your mind."

A proper installation is safe ,a poor one is never safe.

The pilot light is doing refrigeration 24/7 the energy is not lost .

Thats how a 20lb bottle can last a month (with cooking too) with a home sized reefer on board..
FF is offline   Reply With Quote
Old 10-02-2019, 02:52 PM   #12
Veteran Member
 
darkside's Avatar
 
City: Tauranga
Country: New Zealand
Vessel Name: Mahimahi
Vessel Model: Roger Hill Powercat
Join Date: Apr 2016
Posts: 48
The number one safety label you see on boats in New Zealand is "turn the gas off at the bottle"
It is really good advice and saves lives.
With a propane fridge you can't do that, plus you have a pilot light going.
Even though we had one for two years of continuous use I didn't like it.
To me it is RV technology where, when you have a leak, the gas eventually drains outside, not into the bilges.
darkside is offline   Reply With Quote
Old 10-02-2019, 06:09 PM   #13
Member
 
City: Port Stephens, NSW
Country: Australia
Vessel Model: Whittley Monterey 600
Join Date: Jan 2017
Posts: 12
I like it.

I like the redundancy of the separate 120v and 220v inverter banks, although being from Australia where the standard supply is single-phase 240v/50Hz, I would delete the 120v system completely and just use 240v appliances. Nearly all guest 'plug in' chargers etc. are voltage/frequency intolerant these days.

At this point in the design phase, I would definitely explore running the house DC system at 48v rather than 24v. The current draw on the DC bus in a "everything off the inverters all the time" system is massive, and I like the reduction in current at 48v. It also seems to make for an easier transition to lithium-based battery banks later if the system is already 48v nominal.
Another DC-DC converter for the 24v bus is easy.

Awesome looking boat!
nitrolx is offline   Reply With Quote
Old 10-03-2019, 05:40 AM   #14
Veteran Member
 
City: Antalya, Turkey
Country: Canada
Vessel Name: mv Möbius
Vessel Model: XPM78 eXtreme eXploration Passage Maker, Naval Yachts
Join Date: Sep 2016
Posts: 93
Quote:
Originally Posted by cardude01 View Post
Wow, 14x360W solar panels is a lot of surface area!

From a guy with a boat that got caught in Dorian and had his two big solar panels blown off the mounts, how will you be sure the solar will withstand possible very high wind loads?

Granted, mine were probably not mounted as securely as they should have been, and if I was close to the boat I would probably have removed them and stored them inside the boat, but just wondering how y’all plan to mount your solar.
Sorry for taking so long to responds here "Cardude". We can relate all too well to your concern about solar panels and other equipment when your boat is caught in severe weather. When I was singlehanding my steel sailboat around the world I had quite the experience when the tsunami hit Pango Pango in American Samoa almost 10 years ago to this day. (Sept. 29, 2009) and then when Christine and I happened to be hauled out in Fiji, doing a huge refit to that same 52' steel Bruce Roberts cutter, when Winton hit and we experienced winds reportedly over 220kmh and were actually "knocked down" when the big steel support stands underneath gave way.

Those experiences taught us well to take such situations into account as we designed the new boat and we have several ways of protecting the solar panels in a cascading degree of severity of conditions. The first stage is "just" eXtremely strong mounting of the panels to the boat. We have three "banks" of solar cells, one bank of 3 up front on top of the PH roof that are mounted on a dedicated single frame which in turn is mounted very solidly to the aluminium superstructure of the PH. Then there is a bank of 8 solar panels which also act as the roof panels on the roof over the SkyBridge which is a single welded structure of rectangular aluminium extrusions. These 8 panels are held in place with a combination of bolts through the AL extrusions and industrial adhesive. Then the aft 3 panels are mounted to the aluminium roof which is pat of the PH superstructure itself which forms a overhanging roof above the deck to the rear of the PH. All these panels should be able to withstand weather and sea conditions we experience 90+% of the time.

For the exceptional scenarios, our practice is go into what we call "hunkered down" mode where we remove any and all gear that can be removed and additionally secure that which cannot. For example, we have gone to great lengths to design and now build the roof overtop the SkyBridge to be able to fold down such that its whole perimeter is down resting atop the coaming and can be secured there. We designed in this feature as part of a larger system where the whole arch assembly is hinged and we can lower our air draft dramatically to enable us to go cruise canals or other situations where there are low height restrictions. This same capability also serves us well when we want to go into this "hunkered down" mode such as we would do if we were to leave the boat for an extended time in a location within hurricane/cyclone zones.

You will be seeing more of this articulated fold down roof/arch system in the coming weeks here as we start mounting the roof.

-Wayne
Whodgins is offline   Reply With Quote
Old 10-03-2019, 06:00 AM   #15
Veteran Member
 
City: Antalya, Turkey
Country: Canada
Vessel Name: mv Möbius
Vessel Model: XPM78 eXtreme eXploration Passage Maker, Naval Yachts
Join Date: Sep 2016
Posts: 93
Quote:
Originally Posted by twistedtree View Post
Great stuff, as always. And what would a reply be without a few questions? ......

I’m curious how you envision operating on 60hz shore power with a 50hz boat? Assuming your inverters are programmed to 50hz, they will only
Lock on to 50hz shore power. Alternately you can open up the acceptable input frequency really wide to accept both 50 and 60hz. But if you do that then the 60hz shore power will pass through yielding 60hz on board rather than your native 50hz. This implies that all the onboard loads are 50/60hz agnostic.
Hi Peter, thanks for stopping by as I'm sure things are very busy for you as well as your new build progresses.

Great question and I will cover this in more depth in coming Tech Talk posts on the blog but short answer (for me) is as follows. Given that we very rarely ever have shore power and when we do it is usually when we are leaving the boat for some time, the first way we deal with 50/60Hz supply is via the different inverters. The three 220 inverters will be 50Hz and the two 120V will be 60Hz, so this will cover us in probably more than 95% of the time.

On those occasions when we do plug into shore power, all of it comes aboard through the Isolation Transformer which gives us the ability to chose and match any voltage we want for input/output from 120-240V, but of course does not directly address your question about Hz. What we are doing to have both Hz onboard when on shore power is to have the shore power supply ONLY the charge side of the inverters and have ALL AC output coming from the inverters only. This is why in the Electrical Summary article on the blog, I've characterised our electrical system and our boat as being "Battery Based". With no generator and no shore power supplied AC onboard, we have no "inverter only" load switch as everything is "inverter only". In this setup, shore power is only used to run the battery chargers, which can accept 50 and 60Hz and then all the AC (and DC) comes from the batteries.

In the little diagram I made for the Electrical System Overview article, you can see that coming out of the Isolation Transformer, the AC power goes directly to the AC input of the inverter/chargers and is only used for the charger side of the MultiPlus units, not passed directly through.

Your question has pointed out to me that I forgot to label the diagram in the TT post to have the Hz for the AC outputs so I will go and update that. Thanks.

I fully understand that this type of setup would not make sense for many/most boats as they are much more often plugged into shore power or running a genset, but for our use case this is what we think will work best.

Make sense to you? Raise any concerns? I would certainly welcome and appreciate any and all questions and suggestions you would have as you are certainly for more experienced and expert in such matters.

Thanks!
Wayne
Whodgins is offline   Reply With Quote
Old 10-03-2019, 06:04 AM   #16
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 19,736
"To me it is RV technology where, when you have a leak, the gas eventually drains outside, not into the bilges."

When installed in a vessel the fridge is secured above the water line and in a deep lipped pan , with an overboard drain.
We placed ours in the cockpit that is self draining .
PIA in the AM getting breakfast goodies , but great in the PM for a cold beverage.


Never a dead battery .
FF is offline   Reply With Quote
Old 10-03-2019, 06:28 AM   #17
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 4,940
Quote:
Originally Posted by Whodgins View Post

In the little diagram I made for the Electrical System Overview article, you can see that coming out of the Isolation Transformer, the AC power goes directly to the AC input of the inverter/chargers and is only used for the charger side of the MultiPlus units, not passed directly through.

Hi Wayne,


If I'm following you correctly, I don't think the Multiplus devices operate the way you want them to. Or maybe I don't understand them either...


But my understanding is that they are always either inverting OR charging, but never both. They can be set up to only charge, but in that case they will not invert.


I think you want them to invert at 60hz on the output side, while simultaneously accepting 50hz on the input side and using that to charge. But I believe they can only do one of those things at a time.
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 10-03-2019, 06:28 AM   #18
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 8,069
Wayne
When contemplating a new build FPB the discussions around inverters, gensets and get home engines were interesting. When in NZ we talked with the folks in Whangerei about various subtleties of these combinations. Each prospective owner had a slightly different take on the various combinations.

Given Steve's decade plus of many FPBs I'd guess you've got his current thinking based upon field experience? As I recall he removed his genset from his big sailboat. But, his first FPB Windhorse came with a genset I believe.

Your clean sheet build is to be applauded and presents great reading on boat building 101. Along with Peter's posts over the years lots to learn on TF for the inquisitive.
sunchaser is offline   Reply With Quote
Old 10-03-2019, 06:35 AM   #19
Member
 
City: Port Stephens, NSW
Country: Australia
Vessel Model: Whittley Monterey 600
Join Date: Jan 2017
Posts: 12
Quote:
Originally Posted by Whodgins View Post

In the little diagram I made for the Electrical System Overview article, you can see that coming out of the Isolation Transformer, the AC power goes directly to the AC input of the inverter/chargers and is only used for the charger side of the MultiPlus units, not passed directly through.
That's not how they work.

A Multiplus will actually pass directly through the AC source when connected.
It can boost this using the inverter as well, but in general operation, when AC is present at the input, that AC is switched through to the output.
The charger will also operate and charge the batteries when AC is present.

The better way to become shore-power intolerant as far as frequency and voltage, is to replace the Multiplus units with straight inverters, and add a bank of multi-voltage/multi-frequency chargers. This way it will work as you have stated; shore power will only charge the batteries, and your ship loads will only ever see inverter output AC.
nitrolx is offline   Reply With Quote
Old 10-03-2019, 06:41 AM   #20
Veteran Member
 
City: Antalya, Turkey
Country: Canada
Vessel Name: mv Möbius
Vessel Model: XPM78 eXtreme eXploration Passage Maker, Naval Yachts
Join Date: Sep 2016
Posts: 93
Quote:
Originally Posted by twistedtree View Post
Oops, that was only one question.

Personally I wouldn’t be comfortable without a generator, if go no other reason than to provide a backup power source.

And I’m really envious of your 5kw of solar.

I’m also interested that you have separate inverter systems for 120 and 240v. The alternative is to use an auto transformer or just a reduction transformer off a 240v inverter system. Curious what your thinking is on this. I have personally become very sensitive to the standby power draw of the Victron’s, all of which run all the time. Others like outback idle parallel inverters and bring them online progressively as loads demand.
Quite right Peter that having a generator adds another layer of redundancy or backup for onboard AC power and we thought long and hard about it as we designed Möbius. Our thinking is that we have two independent "generators" onboard in the form of our two ~6kW alternators on the Gardner. Granted, this makes Mr. Gee our Gardner, a single point of failure, but we think the probability of loosing the engine or both alternators is acceptably low.

I'm glad you brought up the question about inverters vs autotransformers and I would REALLY appreciate knowing your thoughts on the pros/cons of each and which way you are going on your new build? I'm a bit undecided as to the best route to go for the 120V via inverter vs Autotransformer and we have not placed the Victron order quite yet but need to soon.

I've worked through the parasitic “No loads” which the Victron inverters have and have convinced myself at least that these are manageable with a combination of running only as many inverters as needed for a given situation, just one at night on anchor for example, and then using some of Victron’s “Search Mode” to reduce the “no load” drains. I don’t have any personal experience with these settings yet so if you or others have direct experience with these MultiPlus inverter/chargers I would sure appreciate you sharing it On our previous boat I just ran our MultiPlus units with AES (Automatic Economy Switch) turned on which as per Victron: “If this setting is turned ‘on’, the power consumption in no-load operation and with low loads is decreased by approx. 20%, by slightly
'narrowing' the sinusoidal voltage. Applicable in stand-alone configuration only.”. However on the new boat I will experiment with the additional “Search Mode” option which again as per Victron manuals is “If search mode is ‘on’, the power consumption in no-load operation is decreased by approx. 70%. In this mode the MultiPlus, when
operating in inverter mode, is switched off in case of no load or very low load, and switches on every two seconds for a short period. If
the output current exceeds a set level, the inverter will continue to operate. If not, the inverter will shut down again.
The Search Mode “shut down” and “remain on” load levels can be set with VEConfigure.
The standard settings are:
Shut down: 40 Watt (linear load)
Turn on: 100 Watt (linear load)”

Again, I look forward to your much more informed opinion and what you are doing regarding things like these parasitic loads. You mentioned that “Others like outback idle parallel inverters and bring them online progressively as loads demand.” And I’m not sure how this is different than the MultiPlus “Search Mode” and would appreciate any help with understanding the differences.

I should also mention that being a “Battery Based” boat, DC is our primary voltage, both 24 and 12 and so where given the choice we have 24V DC equipment rather than 220v AC so in many situations we can simply turn the inverters off. For example all our navigation equipment is running off 24DC, we are all PC based with Furuno and TimeZero so no MFD. All our many monitors are all 24V DC as are all our personal techie devices running on 24V DC. Hot water primarily comes from our Kabola diesel boiler and/or the heat exchanger from the Gardner when he is running so no AC needs there for domestic hot water or our in floor heating. We do have a 240V heating coil in our calorifier so that’s always an option if we are on shore power or need such a load. However we definitely have our share of equipment that requires AC such as all electric cooking (induction hob, smart oven and BBQ) and washing machine. We do have the cabinets and infrastructure for a dishwasher and dryer but we prefer to not have these onboard, a very personal decision I appreciate, but then what decision in building a boat isn’t?

Thank for the great questions Peter, that’s one of the biggest values and reasons for blogging and posting right?

- Wayne
__________________

Whodgins is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 10:24 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012
×