Two Generators

Why do some boats in the 40' to 60' range have two gensets? Just redundancy?
Example-One 48' Hatteras I've seen on line has a 15kw and a 9kw and others are similarly equipped.

That seems like a lot for a boat that size. You could remove one and free up a lot of engine room space.

Ken
__________________
Advertisement

ktdtx is offline   Reply With Quote
Old 06-14-2015, 02:19 PM   #2
Guru
 
N4712's Avatar
 
City: South FL
Country: U.S.A
Vessel Name: Oliver
Vessel Model: Nordhavn 47 Hull# 12
Join Date: Apr 2013
Posts: 3,613
Quote:
Originally Posted by ktdtx View Post
Why do some boats in the 40' to 60' range have two gensets? Just redundancy?
Example-One 48' Hatteras I've seen on line has a 15kw and a 9kw and others are similarly equipped.

That seems like a lot for a boat that size. You could remove one and free up a lot of engine room space.

Ken

Yes. I wouldn't remove them. Also might be a "night" or "cruise" genny to run a couple Ac's at night.
__________________

__________________
Thanks, Oliver
M/V Oliver
Nordhavn 47 Hull #12
N4712 is offline   Reply With Quote
Old 06-14-2015, 02:34 PM   #3
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,903
Quote:
Originally Posted by ktdtx View Post
Why do some boats in the 40' to 60' range have two gensets? Just redundancy?
Example-One 48' Hatteras I've seen on line has a 15kw and a 9kw and others are similarly equipped.

That seems like a lot for a boat that size. You could remove one and free up a lot of engine room space.

Ken
Not necessarily just redundancy....depending...some have drastically different load needs.

Some travel from cold to hot with temperate inbetween...so full loading where big AC and Heat systems may require the 15kW and other times the 9Kw is better loaded.

My friend had a 55 Viking that had 2 -20kWs...way overkill but the PO wanted FULL redundancy.

My redundancy on my 40 footer is a 1kW Honda for my 8kW Westerbeke.

That is too small now that I upgraded my battery charger but I can still rig my 25 amp charger and charge batteries and run DC equipment for 8 hours on less than a gallon of gas.

I doubt to many 40 footers have 2 big diesel gensets in them...not till you get tup o 50 foot or more flushdecks with walk in engine rooms.
psneeld is offline   Reply With Quote
Old 06-14-2015, 03:08 PM   #4
THD
Guru
 
City: Seattle
Country: US
Join Date: Apr 2012
Posts: 1,142
We have an 8kw and a 20kw on a 58' boat. While on the move, or anchored, the 8kw handles the loads for all 120VAC items. Our AC, W/D and water heater are 240 VAC and if the AC and or W/D is in use, we need to use the 20kw. Our 20kw has about 35% of the hours that the 8kw does. The 8kw burns less than half the fuel of the 20kw.
THD is offline   Reply With Quote
Old 06-14-2015, 03:37 PM   #5
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 3,955
You gotta remember allot of these boats were built "back in the day"

Back in the day we did not have inverter technology like we have today.

That is one of the reasons many boats in that size range had smaller cruise generators.

Today much of that need has gone away. We have inverters up to several kilowatts that will run the smaller AC loads, making the generators job recharging the batteries and taking care of larger loads like Air Conditioning.

Thats not to say that two generators is not a good thing. Redundancy is great. Its saying that the need for two generators on boats in the 50' range has diminished with inverter technology.
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
www.mvlisasway.com
ksanders is offline   Reply With Quote
Old 06-14-2015, 03:56 PM   #6
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,903
Gonna say...this coming from a generator guy?
psneeld is offline   Reply With Quote
Old 06-14-2015, 04:38 PM   #7
Senior Member
 
City: Bohemia
Country: USA
Join Date: Sep 2014
Posts: 140
On the 58' Kady Krogen, they have a 12 KW and a 20KW genny. The 12 is for when you are only running to charge the batteries, maybe the A/C and the lights. If you want to run everything, dishwasher, trash compactor, micro wave, washer/dryer and all the other stuff, you use the 20 KW. You shouldn't run the genny under a small load. So, you have a "small load" 12KW and a "big load" 20 KW. I know, it sounds crazy. Doesn't it? I have a 2.7 KW on my 27 foot tug. That Kady Krogen was 2.9 mill!
chester613 is offline   Reply With Quote
Old 06-14-2015, 04:50 PM   #8
Guru
 
N4712's Avatar
 
City: South FL
Country: U.S.A
Vessel Name: Oliver
Vessel Model: Nordhavn 47 Hull# 12
Join Date: Apr 2013
Posts: 3,613
Quote:
Originally Posted by chester613 View Post
On the 58' Kady Krogen, they have a 12 KW and a 20KW genny. The 12 is for when you are only running to charge the batteries, maybe the A/C and the lights. If you want to run everything, dishwasher, trash compactor, micro wave, washer/dryer and all the other stuff, you use the 20 KW. You shouldn't run the genny under a small load. So, you have a "small load" 12KW and a "big load" 20 KW. I know, it sounds crazy. Doesn't it? I have a 2.7 KW on my 27 foot tug. That Kady Krogen was 2.9 mill!

That's about right for the boat. We have a 12kw but really need a 16kw to suffice our needs. I know some people with a N60 they have a 9kw in the lazz and a 20kw main genny in the ER. Nothing crazy.
__________________
Thanks, Oliver
M/V Oliver
Nordhavn 47 Hull #12
N4712 is offline   Reply With Quote
Old 06-14-2015, 05:02 PM   #9
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 3,955
Quote:
Originally Posted by psneeld View Post
Gonna say...this coming from a generator guy?

__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
www.mvlisasway.com
ksanders is offline   Reply With Quote
Old 06-14-2015, 05:05 PM   #10
TF Site Team
 
Larry M's Avatar
 
City: JAX, FL
Country: USA
Vessel Name: Hobo
Vessel Model: Krogen 42-120
Join Date: Nov 2008
Posts: 5,737
Oh, no. This a single vs twins debate. And to the OP, you could remove one and free up a lot of engine room space.
Larry M is offline   Reply With Quote
Old 06-14-2015, 05:13 PM   #11
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,903
Quote:
Originally Posted by Larry M View Post
Oh, no. This a single vs twins debate. And to the OP, you could remove one and free up a lot of engine room space.
Or leave it and get rid of the engine for an electric main propulsion conversion.....new thread
psneeld is offline   Reply With Quote
Old 06-14-2015, 05:21 PM   #12
Enigma
 
RT Firefly's Avatar
 
City: Slicker?
Country: Bumpkin?
Join Date: Oct 2007
Posts: 9,996
Greetings,
"...and free up a lot of engine room space." So you can stow all your anchors in there. BONUS!

__________________
RTF
RT Firefly is offline   Reply With Quote
Old 06-14-2015, 05:21 PM   #13
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 3,955
There is also another thing to consider...

If you have say 1500 watts of Air Conditioning that runs at for discussion sake a 33% duty cycle on a typical evening you might be actually better off running that on an inverter.

Lets do some math regarding that. 1500 watts is 125 amps at 12v. 125/3=41 amp hours average on your battery bank.

With no other loads applied you could run all night long and not have to run your generator if you had around 800 amp hours of battery.

If you had a higher load or higher duty cycle you could use a State Of Charge meter and tie that to an auto start on your generator. Then when the batteries got low the generator would automatically start up, charge your batteries, then turn itself off.

You could even use a system like that to keep your batteries charged while you were anchor'd off and playing on shore all day, or stuck on a mooring bouy and off the boat for a few days exploring.
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
www.mvlisasway.com
ksanders is offline   Reply With Quote
Old 06-14-2015, 07:21 PM   #14
Senior Member
 
catalinajack's Avatar
 
City: Edgewater, MD
Country: USA
Vessel Name: Catalina Jack
Vessel Model: Defever 44
Join Date: Nov 2011
Posts: 354
Defever 44 owner here. Boat came with a 12.5 kw Kohler and a 7.7 kw Westerbeke.
catalinajack is offline   Reply With Quote
Old 06-14-2015, 09:11 PM   #15
Senior Member
 
ktdtx's Avatar
 
City: Galveston, Texas
Country: U.S.A.
Vessel Name: Howdy
Vessel Model: 52' North Pacific
Join Date: Nov 2014
Posts: 417
I thought if I freed up that space I could store a lot more anchor chain
ktdtx is offline   Reply With Quote
Old 06-15-2015, 12:25 AM   #16
Guru
 
BandB's Avatar
 
City: Fort Lauderdale
Country: USA
Join Date: Jan 2014
Posts: 13,153
As others have said, two reasons. Backup and to balance to load.
BandB is offline   Reply With Quote
Old 06-15-2015, 12:33 AM   #17
Wannabe
 
Britannia's Avatar
 
City: SF Bay Area
Country: USA
Vessel Name: Stillwater
Vessel Model: Kadey-Krogen 54
Join Date: Dec 2014
Posts: 766
Single main but two gensets on my KK54 - go figure!

I have an 8kW and a 20kW NL. The 8 is in the lazarette and the 20 in the ER. With 4 cruisairs, WD, etc it's possible to load up the 20kW. Most of the time the 8kW has enough to satisfy my needs.

I may add a hydraulic get home motor to the 20kW. Others have done the same and it seems like good use of all that extra power.

Richard
Stillwater
KK54 #5
Britannia is offline   Reply With Quote
Old 06-15-2015, 12:57 AM   #18
Guru
 
MYTraveler's Avatar
 
City: West Coast
Country: USA
Join Date: Apr 2014
Posts: 852
Two 17 kw's. Only for redundancy.
MYTraveler is offline   Reply With Quote
Old 06-15-2015, 08:45 AM   #19
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,525
"1500 watts is 125 amps at 12v. 125/3=41 amp hours average on your battery bank.

PER HOUR!

41 amps per hour from a battery for 8 hours is 168 amps from a single battery

125Amps for 8 hours is 1000AH which would require about 2200AH from the batt set as this discharge would be at an 8 hour rate , not the std 20 hour rate.

A guess would be a ton (2000lbs+) of LA batteries that would require 10-12 hours of a 125A charge to be refilled.

Double the battery price and they might be refilled faster , with a hefty 200A+ charge source.
********
Two sized noisemakers are to assure the minimum load will be enough not to underload the diesel, and shorten its service life.
FF is offline   Reply With Quote
Old 06-15-2015, 09:39 AM   #20
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 3,955
Quote:
Originally Posted by ksanders View Post
There is also another thing to consider...

If you have say 1500 watts of Air Conditioning that runs at for discussion sake a 33% duty cycle on a typical evening you might be actually better off running that on an inverter.

Lets do some math regarding that. 1500 watts is 125 amps at 12v. 125/3=41 amp hours average on your battery bank.

With no other loads applied you could run all night long and not have to run your generator if you had around 800 amp hours of battery.

If you had a higher load or higher duty cycle you could use a State Of Charge meter and tie that to an auto start on your generator. Then when the batteries got low the generator would automatically start up, charge your batteries, then turn itself off.

You could even use a system like that to keep your batteries charged while you were anchor'd off and playing on shore all day, or stuck on a mooring bouy and off the boat for a few days exploring.
Quote:
Originally Posted by FF View Post
"1500 watts is 125 amps at 12v. 125/3=41 amp hours average on your battery bank.

PER HOUR!

41 amps per hour from a battery for 8 hours is 168 amps from a single battery

125Amps for 8 hours is 1000AH which would require about 2200AH from the batt set as this discharge would be at an 8 hour rate , not the std 20 hour rate.

A guess would be a ton (2000lbs+) of LA batteries that would require 10-12 hours of a 125A charge to be refilled.

Double the battery price and they might be refilled faster , with a hefty 200A+ charge source.
********
Two sized noisemakers are to assure the minimum load will be enough not to underload the diesel, and shorten its service life.

Now Now FF, I for discussion sake indicated a 1/3 duty cycle... See it in red in my original post above... Read carefully and I think you'll find my math is probably correct.
__________________

__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
www.mvlisasway.com
ksanders is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 05:25 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012