Stray current and indicator lights

Two questions that may or may not be related.

I have a steel boat so galvanic corrosion and Electrolytic corrosion are a concern. I have been reading "Motorboat Electrical and Electronics manual" by John Payne trying to learn as much as I can. In the Electrolytic corrosion section under Ground Faults on page 212 it says; "In any area where a cable can contact grounded metal, leakage or fault currents can flow. Install a leakage test lamp unit such as a Mastervolt that handles both AC and DC. This allows the hull to be monitored continuously and any problems can be rectified promptly". Maybe you can Google better than I but I can't find a "leakage test lamp" anywhere on the internet.

Thinking through this issue brought me to my second question. My DC panel is large and wired such that just about everything has it's own circuit breaker on the panel and it has indicator lights next to each circuit breaker so when the CB is on there is a little red light next to it... I have noticed for some items when I turn off the CB the little light immediately goes out but for other things the light slowly dims then goes out taking 3-4 seconds. The indicator lights are wired directly to the output side of the CB and to a ground bus bar on the backside of the panel.

Are the lights next to the CB the "Leakage test lamp"? I always assumed they were just indicators saying the CB was on. Is how fast the light goes out linked to some type of ground fault or leak in the wiring?
__________________
Advertisement

Talonewo is offline   Reply With Quote
Old 12-12-2017, 06:31 PM   #2
TF Site Team
 
Larry M's Avatar
 
City: JAX, FL
Country: USA
Vessel Name: Hobo
Vessel Model: Krogen 42-120
Join Date: Nov 2008
Posts: 7,890
Cool boat by the way. I’d get some professional help from an ABCY Corrosion/Electrical Tech. Worth the money to make sure your boat is wired correctly and help answer some questions.
__________________

Larry M is online now   Reply With Quote
Old 12-12-2017, 07:19 PM   #3
Guru
 
City: Fairport
Country: United States
Join Date: Jan 2017
Posts: 1,681
So, by design, all of your current carrying circuit conductors should not contact the steel hull.
Now, imagine two 12v light bulbs connected in series, connected to your 12 v system. Take the middle connection and attach that to the hull. If no other conductor in the 12v system contacts the hull, you will see two dim lamps. Now, a short develops between the hull and + 12 volts. One lamp goes off and the other goes to full brightness.
That is a ground fault detector in its simple form. Iíve done some design work on electronic ones but hopefully you get the principle.

Your question on the action of the panel lights is unrelated. That is simply some stored energy discharging thru the lamp. Capacitive charge or sometimes a running dc motor will do that. A bilge pump will do that if its running and you kill the breaker.
diver dave is offline   Reply With Quote
Old 12-12-2017, 07:38 PM   #4
Senior Member
 
Ex Sailor's Avatar
 
City: Toronto
Country: Canada
Join Date: Nov 2015
Posts: 271
Quote:
Originally Posted by diver dave View Post
So, by design, all of your current carrying circuit conductors should not contact the steel hull.
Now, imagine two 12v light bulbs connected in series, connected to your 12 v system. Take the middle connection and attach that to the hull. If no other conductor in the 12v system contacts the hull, you will see two dim lamps. Now, a short develops between the hull and + 12 volts. One lamp goes off and the other goes to full brightness.
That is a ground fault detector in its simple form. Iíve done some design work on electronic ones but hopefully you get the principle.

Your question on the action of the panel lights is unrelated. That is simply some stored energy discharging thru the lamp. Capacitive charge or sometimes a running dc motor will do that. A bilge pump will do that if its running and you kill the breaker.

Very well put ( written ) ........ FB
Ex Sailor is offline   Reply With Quote
Old 12-12-2017, 08:13 PM   #5
Guru
 
boathealer's Avatar
 
City: North Carolina
Country: US
Vessel Name: SCOUT
Vessel Model: Great Harbour N37
Join Date: Aug 2017
Posts: 582
A few youtube videos:



boathealer is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 06:24 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012
×