I've insulated my dry stack to the metal pipe that goes through the roof, should I allow some air space or seal it up
Click image for larger version

Name:	IMG_0152.jpg
Views:	91
Size:	86.5 KB
ID:	63344Click image for larger version

Name:	IMG_0154.jpg
Views:	101
Size:	87.0 KB
ID:	63345Click image for larger version

Name:	IMG_0153.jpg
Views:	86
Size:	98.4 KB
ID:	63346
__________________
Advertisement

swampu is offline   Reply With Quote
Old 04-03-2017, 02:27 AM   #2
Guru
 
Xsbank's Avatar
 
City: Pender Harbour, BC
Country: Canada
Vessel Name: Gwaii Haanas
Vessel Model: Vancouver Shipyards Custom Aluminum 52
Join Date: Sep 2013
Posts: 3,154
My stack is tightly insulated but the area around it is open, it is also the main vent for my engine room as my "funnel" has vents too. I have large air intakes in the side of the engine room so it clears the heat out a lot faster. My space where the stack goes is also lined with sheet metal.

Sooner or later you will need to service or replace the muffler and resonator (if there is one - my boat didn't have one when I bought it) so I would spend some effort making access panels to get in there. Also, don't forget expansion - you need joints and supports that will allow this. Don't forget that when you are running there is a LOT of heat.
__________________

__________________
Don't believe everything that you think.
What are we offended about today?
Xsbank is offline   Reply With Quote
Old 04-03-2017, 08:22 AM   #3
Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 5,079
The air space in the stack chase needs to be vented at bottom and at top. The insulation around the pipe reduces heat transfer, but does not eliminate it. Some heat makes it though the insulation and will heat up the air in the void space. That heat needs a path for convection to carry it out. If the chase was sealed up, temps inside will gradually rise to dangerous levels.
Ski in NC is online now   Reply With Quote
Old 04-03-2017, 10:48 AM   #4
Senior Member
 
The Other Gary's Avatar
 
City: Toronto
Country: Canada
Vessel Name: Adios Dinero
Vessel Model: Bayliner 3988 2 x 330 Cummins
Join Date: Sep 2016
Posts: 331
That is a scary looking installation, especially with paper backed fiberglass insulation.
I suggest that you remove it, screw sheet metal to the inside of your framing, add a louvered vent to the exterior wall at the top and bottom of the pipe compartment to vent heat. You can then insulate between the studs with 2 inch foam siding board on the outside of the metal. You may want to modify your framing to make a removable panel as well for future maintenance access.
The Other Gary is offline   Reply With Quote
Old 04-03-2017, 12:07 PM   #5
Guru
 
psneeld's Avatar
 
City: ACIW
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 18,912
From my professional marine engineer friend....

"... that boat has already had one fire, it looks like he is setting it up for another!

All that dry wood so close to the stack, "insulated" or not, presents a serious fire hazard. That guy needs to go look at some dry stack workboat exhaust systems."
psneeld is online now   Reply With Quote
Old 04-03-2017, 12:35 PM   #6
Enigma
 
RT Firefly's Avatar
 
City: Slicker?
Country: Bumpkin?
Join Date: Oct 2007
Posts: 12,366
Greetings,
I wonder if something like this would work. Maybe in a 4" size or so...
DuraTech 5-inch Chimney
__________________
RTF
RT Firefly is online now   Reply With Quote
Old 04-03-2017, 12:55 PM   #7
Senior Member
 
Roamer Blue's Avatar
 
City: Toronto ON
Country: Canada
Join Date: Aug 2016
Posts: 126
Quote:
Originally Posted by RT Firefly View Post
Greetings,
I wonder if something like this would work. Maybe in a 4" size or so...
DuraTech 5-inch Chimney
1000 degree F continuous going to be ok for the engine involved?

RB
Roamer Blue is offline   Reply With Quote
Old 04-03-2017, 03:23 PM   #8
Guru
 
Keysdisease's Avatar
 
City: South Florida
Country: USA
Join Date: Sep 2014
Posts: 671
Quote:
Originally Posted by The Other Gary View Post
That is a scary looking installation, especially with paper backed fiberglass insulation.
I suggest that you remove it, screw sheet metal to the inside of your framing, add a louvered vent to the exterior wall at the top and bottom of the pipe compartment to vent heat. You can then insulate between the studs with 2 inch foam siding board on the outside of the metal. You may want to modify your framing to make a removable panel as well for future maintenance access.
What he said

Keysdisease is offline   Reply With Quote
Old 04-03-2017, 03:26 PM   #9
Enigma
 
RT Firefly's Avatar
 
City: Slicker?
Country: Bumpkin?
Join Date: Oct 2007
Posts: 12,366
Greetings,
Mr. RB. VERY valid point. I would defer to Mr. ps's "professional marine engineer" friend. Thank you.
__________________
RTF
RT Firefly is online now   Reply With Quote
Old 04-03-2017, 03:53 PM   #10
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 7,785
Examples and detailed designs for properly constructed dry stack setups are not difficult to find. Swampu, have you looked at ABYC guidelines for their recommendations?

A trip onboard a dry stack Nordhavn would be instructive. Psneelds friend would be a great contact for getting advice and benchmark designs as well as recommended materials of construction.

Good luck.
sunchaser is offline   Reply With Quote
Old 04-03-2017, 07:56 PM   #11
Guru
 
Maerin's Avatar
 
City: East Coast
Country: USA
Vessel Name: M/V Maerin
Vessel Model: Solo 4303
Join Date: Jun 2013
Posts: 690
I'd treat that chase like a chimney, e.g. would it withstand open flame? There is available a variety of silicate type board that is virtually fireproof. Even so, I think it'd be prudent to have a sheet metal backing of a minimum of 26ga. galvanized steel (not aluminum). Presume that the exhaust pipe will come apart, and have the chase designed to withstand that sort of scenario.

As ski correctly pointed out, the insulation slows down the rate of transfer, it does not stop it or eliminate it. Provide a means to remove the heat, and create a fireproof chase in the event something goes wrong.

There's a safe way to accomplish what you need, I don't think the picture is it!
__________________
Steve Sipe
Selene 4303 Maerin
http://maerin.net
Maerin is offline   Reply With Quote
Old 04-03-2017, 08:12 PM   #12
Guru
 
City: ??
Country: ??
Vessel Name: ??
Vessel Model: ??
Join Date: Oct 2007
Posts: 2,370
Should I leave air space in my dry stacks?



Yes, actual ventilation is needed.
C lectric is offline   Reply With Quote
Old 04-03-2017, 08:30 PM   #13
Senior Member
 
Spottsville's Avatar
 
City: Newburgh, Indiana
Country: US
Vessel Name: Quiet Company
Vessel Model: Great Harbour GH-47
Join Date: May 2012
Posts: 263
A commercial industrial insulator is a professional trade and should be consulted! Looks like trouble......
Spottsville is offline   Reply With Quote
Old 04-03-2017, 08:38 PM   #14
Guru
 
Steve's Avatar
 
City: Thibodaux, Louisiana
Country: USA
Vessel Name: Gumbo
Vessel Model: 2003 Monk 36
Join Date: Oct 2007
Posts: 3,843
I'd go take a look at a bunch of the commercial luggers and shrimpers near you and see what they have done.
Good luck
__________________
Steve W.
http://mvgumbo.blogspot.com/
Steve is offline   Reply With Quote
Old 04-03-2017, 09:25 PM   #15
Guru
 
swampu's Avatar


 
City: Biloxi, MS
Country: USA
Vessel Name: Cajun Rose
Vessel Model: Biloxi Lugger
Join Date: Jul 2011
Posts: 1,320
Thank you all, I'll be rethinking this whole set up. Great advice and I will use all of it
swampu is offline   Reply With Quote
Old 04-04-2017, 06:20 AM   #16
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 19,008
Extra space in the stack chase can be useful as a wet locker .
FF is offline   Reply With Quote
Old 05-16-2017, 06:28 PM   #17
Guru
 
swampu's Avatar


 
City: Biloxi, MS
Country: USA
Vessel Name: Cajun Rose
Vessel Model: Biloxi Lugger
Join Date: Jul 2011
Posts: 1,320
Update on this topic, I reconfigured the stacks and had phenomenal success, ran the boat 5 hours and temps on the stacks never got above 90 or so by touch,
Click image for larger version

Name:	IMG_0032.jpg
Views:	34
Size:	94.0 KB
ID:	64809Click image for larger version

Name:	IMG_0034.jpg
Views:	34
Size:	129.6 KB
ID:	64810Click image for larger version

Name:	IMG_0036.jpg
Views:	36
Size:	84.1 KB
ID:	64811Click image for larger version

Name:	IMG_0035.jpg
Views:	41
Size:	58.9 KB
ID:	64812
__________________

swampu is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 06:35 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012