Old 09-07-2016, 04:09 PM   #201
Senior Member
 
Join Date: Dec 2007
Posts: 372
tadhana,as to marinas,they do fall under the scope of the Nec.Article 555-1,and 2.To be brief,and I quote-this article covers the installation of wiring and equipment in the areas comprised of fixed or floating piers,wharfs,docks and other areas in marinas,etc. Part two reads wiring and equipment in marinas shall comply with this article,and also with the applicable provisions of other articles of this code.Basically,everything at the marina,including fuel,except the boats,which is then becomes abyc compliant . The only reason I stated prior about the fixed wiring issue is that abyc doesn't write the original text to there standards,they use the nec codes as there starting point.They tweak some of them to be more applicable to the marine,and boating needs,thats why they are called standards,not codes(so I was told)Do they have a different interpretation,maybe,but I put that disclaimer in there,about myself,and for others to seek further clarification.The abyc standards that I know(not many)were taken verbatim form the nec,no changes.
__________________
Advertisement

tinped is offline   Reply With Quote
Old 09-07-2016, 05:02 PM   #202
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 13,883
Thankfully boats don't strictly follow land based regs....apples and oranges.

Hardwiring your glendenning at boat side makes perfect sense....and I have never heard of a fire started from Hardwiring vesus crappy plugs.

Any rule against it shows total lack of common sense as well as no knowledge of what boating is...when and if those rules ever apply, I hope I am long gone as a boater, because beauracrats, not boaters with brains will be running the show.
__________________

psneeld is offline   Reply With Quote
Old 09-07-2016, 05:15 PM   #203
Guru
 
Codger2's Avatar
 
City: San Diego
Country: US
Vessel Name: "Sandpiper"
Vessel Model: 2006 42' Ocean Alexander Sedan
Join Date: Oct 2007
Posts: 5,271
Quote:
Originally Posted by Bruce B View Post
I'm not worried about finding a replacement as I will simply have a spare aboard!
That wasn't even complicated was it?
__________________
Codger2

My passion for improving my boat(s) exceeds my desire to constantly cruise them.
Codger2 is offline   Reply With Quote
Old 09-07-2016, 05:17 PM   #204
Guru
 
City: Seaford Va on Poquoson River, VA
Country: United States
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 995
Quote:
Originally Posted by Bacchus View Post
Bruce...
I thought your ref to the Compass article was worth repeating given the # of posts.

If you have 2 -30A cords/inlets consider having a panel w a transfer sw to connect both sides to one cord. Our Mainship is set up this way and I can run anything I choose w only one cord attached... I just have to manage load to keep it at 20-25 A when using one cord.
Some lications especially when traveling I may only have access to one 30A outlet.

I can provide more info if necessary and you are interested.
I did the same when designing my electrical system.
I bought a Leviton 30 amp two pole switch.
It joins both hots and both neutrals from each cord together.
The switch is actually a locking key switch. I keep the key on a wire right next to the switch, prevents it from being accidentally switched.

It is never a problem. even if I plugged into a split phase 240/120vac plug, the breaker would trip on a direct short. Our marina has free 30 amp power, single plug only. So this way I can power the entire boat.

Other thing, turn off your boat main breaker on the unused 30 amp side, so the unused 30 amp connector socket is not energized, otherwise it will be live. I use a GE breakered weatherproof box, I put in 2 30 amp dual pole breakers, and I can lock the door shut.
The box never gets wet. It is about 6 feet from the shore power sockets.

I got it off Amazon years ago for $6, good price.

https://store.leviton.com/collection...nt=18216233219
sdowney717 is online now   Reply With Quote
Old 09-07-2016, 05:55 PM   #205
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,146
Quote:
Originally Posted by tinped View Post
Seen this happen at a home,when the power system was restored,the transformer was being backfed,blew it right off the pole,when they bucked.Not popular with the neighbors as they were in a power outage situation again,and I believe the municipality,in conjunjunction with the power authority imposed a ten thousand dollar fine,for damages,and unlicensed work.Ouch!! I was contracted to do the correct job.Just about everything was fried.
Seems like all you'd have to do to prevent that is to turn off the main breaker feeding the house. Then the generator couldn't back feed to the transformer.
Capt.Bill11 is offline   Reply With Quote
Old 09-07-2016, 06:02 PM   #206
Senior Member
 
Join Date: Dec 2007
Posts: 372
absolutely,just missed that one step,and a costly one.
tinped is offline   Reply With Quote
Old 09-07-2016, 06:20 PM   #207
Guru
 
Steve's Avatar
 
City: Thibodaux, Louisiana
Country: USA
Vessel Name: Gumbo
Vessel Model: 2003 Monk 36
Join Date: Oct 2007
Posts: 3,329
Most Monk 36 have two 30A inlets, one for the air conditioning/heating system, the other for everything else, each has it's separate panel. I have seen at least one owner who used a cord like this FURRION Y-Adapter 2X30A Connector To 30A Male | West Marine worked fine as long as he limited the total consumption to less than 30 Amps. One Aircon unit drew 15 amps.
__________________
Steve W.
http://mvgumbo.blogspot.com/
Steve is offline   Reply With Quote
Old 09-07-2016, 08:08 PM   #208
Guru
 
Bacchus's Avatar
 
City: Seneca Lake NY
Country: US
Vessel Name: Bacchus
Vessel Model: MS 34 HT Trawler
Join Date: Nov 2014
Posts: 1,169
Quote:
Originally Posted by tinped View Post
Corrosion is not the big enemy of copper inhibiting its ability to conduct electricity,oxidation is,which boeshield makes no claim on.T

[COLOR=#252525][FONT=sans-serif]

Unoxidized copper wire (left) and oxidized copper wire (right).

...copper will suffer from oxidation,regardless of the environment,as it attempts to return to its natural state.The marine environment just complicates it. Thanks
Where exactly is the copper you refer to in the boat AC system???
__________________
Don
MS 34 HT Trawler
"Bacchus"
Bacchus is offline   Reply With Quote
Old 09-07-2016, 08:16 PM   #209
Senior Member
 
Join Date: Dec 2007
Posts: 372
Quote:
Originally Posted by Bacchus View Post
Where exactly is the copper you refer to in the boat AC system???
not sure what you mean I referred to. went back thru my posts,no mention of ac anywhere - alternating current,air conditioning?
tinped is offline   Reply With Quote
Old 09-07-2016, 08:19 PM   #210
Guru
 
Bacchus's Avatar
 
City: Seneca Lake NY
Country: US
Vessel Name: Bacchus
Vessel Model: MS 34 HT Trawler
Join Date: Nov 2014
Posts: 1,169
Quote:
Originally Posted by sdowney717 View Post
I did the same when designing my electrical system...

Other thing, turn off your boat main breaker on the unused 30 amp side, so the unused 30 amp connector socket is not energized, otherwise it will be live. I use a GE breakered weatherproof box, I put in 2 30 amp dual pole breakers, and I can lock the door shut.
The box never gets wet. It is about 6 feet from the shore power sockets.
The proper AC distribution panel will have a transfer Sw to combine the load side and diconnect the #2 inlet.

Same w/ an AC panel w/ a generator - it will allow feeding the panel from Gen or Cord / inlet(s) but not both and it prevents the backfeed to the unused source.

Diagram of my panel that includes both features mentioned above attached - using separate Switches and manually switching is asking for trouble
Attached Files
File Type: pdf 1003154 REV2 120V Panel.pdf (176.0 KB, 13 views)
__________________
Don
MS 34 HT Trawler
"Bacchus"
Bacchus is offline   Reply With Quote
Old 09-07-2016, 08:23 PM   #211
Senior Member
 
Join Date: Dec 2007
Posts: 372
Quote:
Originally Posted by Bacchus View Post
Where exactly is the copper you refer to in the boat AC system???
ok,I found it-air conditioning.On the west coast,most buyers chose diesel heat,not air conditioning.For example,north pacific yachts offers an east coast package(with ac,no heat)or a west coast package(the reverse)there is no need for a second 30 amp shore power with the heat option.So in the factory,all the other 110v needs are prewired thru one shore power,making them identical for east coast/west coast,then a second is added for an east coast order.Saves the builder money.
tinped is offline   Reply With Quote
Old 09-07-2016, 08:23 PM   #212
Senior Member
 
City: Northport
Country: USA
Join Date: Aug 2015
Posts: 439
"I did the same when designing my electrical system.
I bought a Leviton 30 amp two pole switch.
It joins both hots and both neutrals from each cord together.
The switch is actually a locking key switch. I keep the key on a wire right next to the switch, prevents it from being accidentally switched."

"Other thing, turn off your boat main breaker on the unused 30 amp side, so the unused 30 amp connector socket is not energized, otherwise it will be live."


Our boats came with a parallel switch that allowed the use of two or more lines of loads (breakers) off of one or more lines of feeds (power cords) by just a turn of the switch. These switches did not allow any unused prongs to be energized nor was it a 'problem' if someone happened to turn the switch unexpectedly.
Why would anyone accept a situation that offered anything less safe or easy?
smitty477 is offline   Reply With Quote
Old 09-07-2016, 08:36 PM   #213
Guru
 
Bacchus's Avatar
 
City: Seneca Lake NY
Country: US
Vessel Name: Bacchus
Vessel Model: MS 34 HT Trawler
Join Date: Nov 2014
Posts: 1,169
Quote:
Originally Posted by tinped View Post
not sure what you mean I referred to. went back thru my posts,no mention of ac anywhere - alternating current,air conditioning?
I thought this whole thread was about Shore Power? That is AC current.

Where in the shore power system is the copper several have talked about protecting w/ various sprays etc?
__________________
Don
MS 34 HT Trawler
"Bacchus"
Bacchus is offline   Reply With Quote
Old 09-07-2016, 08:50 PM   #214
Senior Member
 
Join Date: Dec 2007
Posts: 372
I was responding to a question about why there are two separate 30 amp shore power,instead of a single 50 amp. As regards to the spray,both the plug ends,and the wire terminals,if accessible,of the shore power would benefit,that would also include the disconnect breaker connections on the boat side,or any place you can get at copper connections that are not sealed for that matter.Additional means of anti-corrosive,oxidation,or whatever terms everyone feels appropriate,certainly would be a big benefit in the marine environment,even if they were already treated,like tinning.
tinped is offline   Reply With Quote
Old 09-07-2016, 08:56 PM   #215
Senior Member
 
Join Date: Dec 2007
Posts: 372
I thought this whole thread was about Shore Power? That is AC current.





air conditioning uses ac,not dc,supplied under this discussion by shore power.Or thru your inverter from the genny.not gettingyour question,sorry it is late.
tinped is offline   Reply With Quote
Old 09-07-2016, 10:37 PM   #216
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,146
Quote:
Originally Posted by Bacchus View Post
I thought this whole thread was about Shore Power? That is AC current.

Where in the shore power system is the copper several have talked about protecting w/ various sprays etc?
The wires in most shore cords are not tinned.
Capt.Bill11 is offline   Reply With Quote
Old 09-08-2016, 02:28 AM   #217
Moderator Emeritus
 
BruceK's Avatar
 
Join Date: Oct 2011
Posts: 6,596
What`s the best color for a shorepower cord?
__________________
BruceK
Island Gypsy 36 Europa "Doriana"
Sydney Australia
BruceK is offline   Reply With Quote
Old 09-08-2016, 06:48 AM   #218
Guru
 
Steve's Avatar
 
City: Thibodaux, Louisiana
Country: USA
Vessel Name: Gumbo
Vessel Model: 2003 Monk 36
Join Date: Oct 2007
Posts: 3,329
Black, even the yellow ones wind up that way.
__________________
Steve W.
http://mvgumbo.blogspot.com/
Steve is offline   Reply With Quote
Old 09-08-2016, 07:12 AM   #219
Guru
 
City: Seaford Va on Poquoson River, VA
Country: United States
Vessel Name: Old Glory
Vessel Model: 1970 Egg Harbor 37 extended salon model
Join Date: Jan 2016
Posts: 995
Quote:
Originally Posted by smitty477 View Post
"I did the same when designing my electrical system.
I bought a Leviton 30 amp two pole switch.
It joins both hots and both neutrals from each cord together.
The switch is actually a locking key switch. I keep the key on a wire right next to the switch, prevents it from being accidentally switched."

"Other thing, turn off your boat main breaker on the unused 30 amp side, so the unused 30 amp connector socket is not energized, otherwise it will be live."


Our boats came with a parallel switch that allowed the use of two or more lines of loads (breakers) off of one or more lines of feeds (power cords) by just a turn of the switch. These switches did not allow any unused prongs to be energized nor was it a 'problem' if someone happened to turn the switch unexpectedly.
Why would anyone accept a situation that offered anything less safe or easy?
The way I do that join is safe and easy, I have the main breakers under cover and locked down with a key. It would take a deliberate action to decide to electrocute yourself by unlocking the cover, turning on the breaker and then touching the prongs, a self destructive behavior.

I assume most dual 30 amp systems don't have a parallel combiner switch.

Got a schematic that shows the circuit lockouts?

Other than a switch. make a 30 amp Y splitter to energize both 30 amp inlets at once.
sdowney717 is online now   Reply With Quote
Old 09-08-2016, 07:21 AM   #220
Guru
 
City: East Coast
Country: USA
Join Date: Dec 2013
Posts: 2,471
Quote:
Originally Posted by Capt.Bill11 View Post
Seems like all you'd have to do to prevent that is to turn off the main breaker feeding the house. Then the generator couldn't back feed to the transformer.
Of course and that was his argument. The problem is, that depends on a human remembering to do this and humans sometimes forget. He also argued that the "hot" 220 volt dryer plug hanging from the ceiling waiting to be plugged in wasn't a hazard because he knew to plug it in before starting the generator.

Remember, he didn't just do this one time in an emergency, this was his standard, permanent setup for power outages. He had plenty of time to have it installed correctly.

He got tired of having to lift the mower over the wires from the shed to the house (three wires, not a cable and no ground) so he buried them six inches deep.


The NEC and on boats, ABYC frowns on any system that requires human action to provide safety and for good reason.
__________________

WesK is online now   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 11:56 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012