Sequence for Switching from Shore to Ship (Genny)

What is the proper sequence for switching from shore power to Genny? I have a selector switch with three positions: Shore - Both - Ship This on a 1974 vintage boat with diesel genny.
__________________
Advertisement

SeaBreeze is offline   Reply With Quote
Old 06-04-2019, 01:44 PM   #2
Veteran Member
 
NWSeadog's Avatar
 
City: La Conner, WA
Country: USA
Vessel Name: Full Circle
Vessel Model: CHB 34
Join Date: Jun 2018
Posts: 98
I would never combine (both) AC sources, unless they had a synchronization system, which is unlikely. With the two sources out of phase something is likely to be unhappy and possibly burn out / blow fuses. My procedure would be to disconnect from shore power then switch to the generator / ship.
__________________

NWSeadog is online now   Reply With Quote
Old 06-04-2019, 01:53 PM   #3
Senior Member
 
SeaBreeze's Avatar
 
City: Va Beach
Country: USA
Vessel Name: SeaShell
Vessel Model: 1974 Marine Trader 34 Sedan
Join Date: Aug 2018
Posts: 168
Seadog are you switching to generator (Ship) before or after you have started the Genny?
SeaBreeze is offline   Reply With Quote
Old 06-04-2019, 02:15 PM   #4
Veteran Member
 
NWSeadog's Avatar
 
City: La Conner, WA
Country: USA
Vessel Name: Full Circle
Vessel Model: CHB 34
Join Date: Jun 2018
Posts: 98
I usually have the generator running before switching the ship to it. That way if the generator is putting out low voltage and or frequency during start up it will not affect any of the ship's electronics.
NWSeadog is online now   Reply With Quote
Old 06-04-2019, 02:32 PM   #5
Guru
 
HiDHo's Avatar
 
City: Scottsboro, Al.
Country: USA
Vessel Name: Hi-D-Ho
Vessel Model: 1987 Krogen Manatee
Join Date: Feb 2012
Posts: 1,000
Warm the generator up for several minutes. Turn off any high load items like air conditioners, etc. Move selector switch from shore to generator, load up the generator by turning back on air conditioners, etc Turn the shore power pedestal switches off, remove power cords and cap off the power inlet plugs on the boat.
When removing the electric load from the generator let it run unloaded for at least five minutes or more to cool down the electrical end of the generator before stopping it.
HiDHo is offline   Reply With Quote
Old 06-04-2019, 02:37 PM   #6
Guru
 
psneeld's Avatar
 
City: AICW
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 20,019
Very unlikely you have a Shore, Both, Gen switch unless it is for battery banks (12V) on small vessels such as yours.


As mentioned, the chances you have the electrical system that could synchronize both is not likely.


There may be a shore, off, gen switch but not a both.
psneeld is offline   Reply With Quote
Old 06-04-2019, 02:55 PM   #7
Guru
 
Tom.B's Avatar
 
City: Cary, NC
Country: USA
Vessel Name: Skinny Dippin'
Vessel Model: Navigator 4200 Classic
Join Date: Jul 2009
Posts: 5,703
Start generator (to warm up and look for water in exhaust)... boatside main AC breaker to OFF... ship/shore switch to off... turn off power at pedestal breaker... ship/shore switch to ship... turn on main boatside breaker
__________________
2000 Navigator 4200 Classic
(NOT a trawler)
Tom.B is offline   Reply With Quote
Old 06-04-2019, 02:57 PM   #8
Senior Member
 
SeaBreeze's Avatar
 
City: Va Beach
Country: USA
Vessel Name: SeaShell
Vessel Model: 1974 Marine Trader 34 Sedan
Join Date: Aug 2018
Posts: 168
psneeld - it definitely is Shore Both Ship and it looks original. Since the boat is 45 years old it may be that the boat originally didn't have a generator. There is a separate Ac/Dc switch.
SeaBreeze is offline   Reply With Quote
Old 06-04-2019, 03:09 PM   #9
Senior Member
 
Flybull's Avatar
 
City: USA
Country: USA
Vessel Model: 1983 Trojan F44 FBMY
Join Date: Dec 2018
Posts: 154
Is there two shore inlets? This may be the "both" it is referencing.

My boat has 2-50 amp shore cables labeled shore 1 and shore 2. Switch is shore 1, shore 2, both (1 and 2), OFF, and Gen.

Same sequence as HiDHo above...^^^^
Flybull is offline   Reply With Quote
Old 06-04-2019, 03:19 PM   #10
Guru
 
High Wire's Avatar
 
City: Cape May, NJ and Englewood, FL
Country: USA
Vessel Name: Irish Lady
Join Date: Dec 2007
Posts: 2,813
BOTH??? Wow is that wrong! Can you say KA-BLAM!!!
Hopefully everything goes dead in the Both position and it is just mis-labeled instead of OFF. Just to be safe, make sure the generator output BREAKER is OFF before switching.
__________________
Archie
1984 Monk 36 Hull #46
Currently southbound in Georgia.
High Wire is online now   Reply With Quote
Old 06-04-2019, 03:20 PM   #11
Guru
 
Aquabelle's Avatar
 
City: sydney
Country: australia
Vessel Name: Aquabelle
Vessel Model: Ocean Alexander Flushdeck
Join Date: Jun 2012
Posts: 907
Quote:
Originally Posted by psneeld View Post
Very unlikely you have a Shore, Both, Gen switch unless it is for battery banks (12V) on small vessels such as yours.


As mentioned, the chances you have the electrical system that could synchronize both is not likely.


There may be a shore, off, gen switch but not a both.
Agree that it is very unlikely the OP has a BOTH position. Mine is ShorePower Aft/S'power Fwd (two inlets, only 1 can be selected at a time), Off and Ship. When wanting to use the genset, I switch to Off (usually already selected if we've left the dock); check that all AC breakers including charger are off, start genset and let it warm up briefly, then select Ship, then progressively turn on each relevant AC breaker starting with the charger.
Aquabelle is offline   Reply With Quote
Old 06-04-2019, 03:29 PM   #12
Veteran Member
 
NWSeadog's Avatar
 
City: La Conner, WA
Country: USA
Vessel Name: Full Circle
Vessel Model: CHB 34
Join Date: Jun 2018
Posts: 98
It is always possible that a previous owner mis-used a standard battery joining switch for the AC connection.
NWSeadog is online now   Reply With Quote
Old 06-04-2019, 03:35 PM   #13
Guru
 
psneeld's Avatar
 
City: AICW
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 20,019
That would be a real wiring trick.


If that's the case and it works when it is switched..... that's a huge problem.


It could only switch one out of 3 wires and that would mean the others would have to be directly connected with no interlock.
psneeld is offline   Reply With Quote
Old 06-04-2019, 03:45 PM   #14
Guru
 
djmarchand's Avatar
 
City: Litchfield, Ct/Punta Gorda, Fl
Country: USA
Vessel Model: Atlas Pompano 23
Join Date: Aug 2012
Posts: 4,851
Quote:
Originally Posted by HiDHo View Post
Warm the generator up for several minutes. Turn off any high load items like air conditioners, etc. Move selector switch from shore to generator, load up the generator by turning back on air conditioners, etc Turn the shore power pedestal switches off, remove power cords and cap off the power inlet plugs on the boat.
When removing the electric load from the generator let it run unloaded for at least five minutes or more to cool down the electrical end of the generator before stopping it.

HiDHo has it exactly right.


If you have the shore/genset breakers lockout slide then turn the shore breaker off, push the slide over then turn the genset breaker on, always after warming it up and cooling it down after using it.



David
djmarchand is online now   Reply With Quote
Old 06-04-2019, 03:58 PM   #15
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 4,948
I’ve never heard of a “both” switch like this, but my guess would be that “both” has shore powering some loads, and the gen powering others (probably air con). It’s probably to allow air con use when the shore power can’t otherwise handle it.
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 06-04-2019, 04:19 PM   #16
Guru
 
psneeld's Avatar
 
City: AICW
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 20,019
Quote:
Originally Posted by twistedtree View Post
I’ve never heard of a “both” switch like this, but my guess would be that “both” has shore powering some loads, and the gen powering others (probably air con). It’s probably to allow air con use when the shore power can’t otherwise handle it.
Having a hard time thinking why someone would use a switch if the panel isn't split or separate somehow...and then a "both" position still boggles the mind.
psneeld is offline   Reply With Quote
Old 06-04-2019, 04:26 PM   #17
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 5,786
If indeed you do have a both switch for the generator and shore power get rid of it. In both position you can backfeed into the shore which can be dangerous. You could potentially electrocute someone if they think the electricity is turned off on the shore and are working on the wiring and you start your generator in both position and feed electricity into the shore wiring. There should be no way for your generator to hook to the shore wiring, either your boat should be on shore power or on the generator, never both.
Comodave is offline   Reply With Quote
Old 06-04-2019, 04:47 PM   #18
Guru
 
Conrad's Avatar
 
City: Calgary
Country: Canada
Vessel Name: Blue Sky
Vessel Model: Nordic Tugs 42 Hull #001
Join Date: Oct 2007
Posts: 1,743
I would highly recommend that you get a qualified marine electrician to look at your system.
__________________
Conrad
Berthed in
Campbell River BC
Conrad is offline   Reply With Quote
Old 06-04-2019, 04:53 PM   #19
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 5,786
Quote:
Originally Posted by Conrad View Post
I would highly recommend that you get a qualified marine electrician to look at your system.
+1
Comodave is offline   Reply With Quote
Old 06-04-2019, 04:58 PM   #20
Guru
 
High Wire's Avatar
 
City: Cape May, NJ and Englewood, FL
Country: USA
Vessel Name: Irish Lady
Join Date: Dec 2007
Posts: 2,813
Somehow this boat has survived for 45 years with the current configuration so I seriously doubt the BOTH position is true.
Turn off all large loads like the air conditioners first.
As others said, let the genny warm up before applying full load. My manual says wait until coolant temp above 150F. I try to always switch the transfer switches unloaded. The contacts will last longer that way. Once over on the genny then load it up one load at a time.
OTOH, I've watched people start their gen then throw the transfer switches immediately to GEN with no thought whatsoever of slowly loading it. Not my style!
__________________

__________________
Archie
1984 Monk 36 Hull #46
Currently southbound in Georgia.
High Wire is online now   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 03:20 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012
×