Reversed Polarity Help

When using AC shore power via a Honda 2000 the reversed polarity light blinks ONLY when I turn on the battery charger, no other AC appliances cause the polarity light to come on. Would a defective charger cause this? What/where should I be looking for cause and remedy.
__________________
Advertisement

David Kimmel is offline   Reply With Quote
Old 08-19-2019, 07:41 AM   #2
Guru
 
City: Fairport
Country: United States
Join Date: Jan 2017
Posts: 1,583
The Honda likely has no neutral to ground bond in place. So, you have a "floating" ac system off ground, confusing a primitive reverse polarity detect system.
Besides the light blinking, any other issue? I don't see this as a problem, so far.
__________________

diver dave is offline   Reply With Quote
Old 08-19-2019, 07:53 AM   #3
Senior Member
 
David Kimmel's Avatar
 
City: Chesapeake Bay,Middle River,Md.
Country: USA
Vessel Name: Patty Ann
Vessel Model: Mainship 34 MK1 1980
Join Date: Jan 2014
Posts: 144
No other issues with operation of AC powered items ie,water heater, oven, refrigerator, and coffee pot. I often used the Honda and never seen this polarity light come on ,that's what is confusing
David Kimmel is offline   Reply With Quote
Old 08-19-2019, 09:04 AM   #4
Guru
 
djmarchand's Avatar
 
City: Litchfield, Ct/Punta Gorda, Fl
Country: USA
Vessel Model: Atlas Pompano 23
Join Date: Aug 2012
Posts: 4,694
I agree with diver dave's diagnosis above. Honda and most portable generators do not connect the grounding wire at the generator end. But if you disassemble the outlet you can get to the green wire coming from the load and connect it to generator's metal block. This will form a properly grounded circuit and should correct the reverse polarity light you are getting.


But I also agree with d d that it isn't causing any problem.


Davi
djmarchand is online now   Reply With Quote
Old 08-19-2019, 09:28 AM   #5
Guru
 
City: Fairport
Country: United States
Join Date: Jan 2017
Posts: 1,583
As far as why the charger causes the light to blink. That is because many/most electronic items have some capacitors from L and Neutral to earth, usually as a RFI mitigation strategy. These caps will now allow small ground currents to flow. I suspect your polarity lamp is a low current LED type?
If you wanted to get further into this, take an AC voltmeter, and measure L to GND, and then N to GND, with/without the charger connected to see yourself how the line is "floating". Floating, means not tied to any reference, so is "non-deterministic".

btw, Navy ships have historically been floating, with an array of light bulbs in a panel for viewing by the electrician. The status of 3 lights (for three phase), indicates if any phase has a fault to earth/hull. Three dim is good. One out and two bright indicates a ground fault. This system is a very primitive ground fault indicator; not for human safety, but for ships fault tolerance.
diver dave is offline   Reply With Quote
Old 08-19-2019, 11:52 AM   #6
Senior Member
 
David Kimmel's Avatar
 
City: Chesapeake Bay,Middle River,Md.
Country: USA
Vessel Name: Patty Ann
Vessel Model: Mainship 34 MK1 1980
Join Date: Jan 2014
Posts: 144
Thanks for the responses. We were anchored last evening and decided to get a slip today due to the excessive temps and humidity. When I plugged into marinas 30 amp service all was good, no reversed polarity light when charger was operating, I'm assuming its "floating" ac system off ground, confusing a primitive reverse polarity detect system.as Diver D stated and djmarchand concured. Thanks for the help.
David Kimmel is offline   Reply With Quote
Old 08-19-2019, 07:14 PM   #7
Guru
 
tiltrider1's Avatar
 
City: Seattle
Country: USA
Vessel Name: AZZURRA
Vessel Model: Ocean Alexander 54
Join Date: Aug 2017
Posts: 1,379
You should not use a portable generator on a boat unless you know for certain that the neutral and ground are bonded at the generator.

Many portable generators have isolated neutral and grounds. Yes, everything seems to be working fine until one day some one swims up to your boat and dies from Elextro-shock drowning.
tiltrider1 is offline   Reply With Quote
Old 08-19-2019, 07:43 PM   #8
Guru
 
City: Fairport
Country: United States
Join Date: Jan 2017
Posts: 1,583
I think u will find that the live water shock scenario will require two wiring faults in either bonded or non-bonded cases.
diver dave is offline   Reply With Quote
Old 08-19-2019, 07:45 PM   #9
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 5,016
Quote:
Originally Posted by tiltrider1 View Post
You should not use a portable generator on a boat unless you know for certain that the neutral and ground are bonded at the generator.

Many portable generators have isolated neutral and grounds. Yes, everything seems to be working fine until one day some one swims up to your boat and dies from Elextro-shock drowning.
+1.
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you aren’t one, there is no explanation possible.
Comodave is offline   Reply With Quote
Old 08-19-2019, 07:57 PM   #10
Senior Member
 
City: Clearwater, FL
Country: United States
Vessel Name: Seas the Bay
Vessel Model: Hardin Europa
Join Date: Aug 2016
Posts: 490
Quote:
Originally Posted by tiltrider1 View Post
You should not use a portable generator on a boat unless you know for certain that the neutral and ground are bonded at the generator.

Many portable generators have isolated neutral and grounds. Yes, everything seems to be working fine until one day some one swims up to your boat and dies from Elextro-shock drowning.
I'm not seeing how a voltage differential can exist across the water with neither the generator's hot nor neutral interacting with the water.

With a single fault, we might connect the generator's neutral to the water. Or, we might get a hot wire in the water. But, we don't have a complete circuit.

But, I think we'd need two faults to get the hot in the water in one place, and the neutral in the water in another place, and the resulting voltage differential in between. This, for example, would require neutral and ground bonded on the boat and to metal thru-hulls and a hot wire in the water, or maybe an outlet getting swamped or a wet swimmer or something ending up with a human connected to both the hot and the neutral.

I'm not arguing that the safety ground shouldn't be bonded to neutral when on generator power. I'm just not sure on this particular scenario.
gkesden is offline   Reply With Quote
Old 08-19-2019, 08:04 PM   #11
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 5,016
It may not be a problem but I would hate to find out by someone dying from ESD.
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you aren’t one, there is no explanation possible.
Comodave is offline   Reply With Quote
Old 08-19-2019, 08:05 PM   #12
Senior Member
 
City: Clearwater, FL
Country: United States
Vessel Name: Seas the Bay
Vessel Model: Hardin Europa
Join Date: Aug 2016
Posts: 490
Comodave,

True that!
gkesden is offline   Reply With Quote
Old 08-20-2019, 12:13 AM   #13
Guru
 
tiltrider1's Avatar
 
City: Seattle
Country: USA
Vessel Name: AZZURRA
Vessel Model: Ocean Alexander 54
Join Date: Aug 2017
Posts: 1,379
It’s the age old problem, everybody does it and everybody gets away with it until that one day were two wrongs just happen to make a right and some one is dead.

ESD is real, it’s been killing people for years, we only just figured it out a few years ago. That’s why ECLI’s are now required on docks.
tiltrider1 is offline   Reply With Quote
Old 08-20-2019, 12:29 AM   #14
Senior Member
 
City: Clearwater, FL
Country: United States
Vessel Name: Seas the Bay
Vessel Model: Hardin Europa
Join Date: Aug 2016
Posts: 490
I wish, in practice, ELCI were required on docks :-(

I worry as much about my shore power cord and it falling in as anything. (And, yes, I replace it every couple or few years). I have ELCI on my boat.
__________________

gkesden is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 09:31 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012