Old 04-14-2012, 04:51 PM   #101
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 3,956
Quote:
Originally Posted by psneeld View Post
What you are describing is what I envisioned...a blue seas blade 12 or 6 position fuse panel in the fwd stateroom/head/galley, one in the main salon, one in the engine room for auto bilge pumps and other non-switched items, one aft for the master strm/head, one for lower helm/electronics and one on the flying bridge. One main running fwd to supply 4 subs, one aft to supply 2. Each fused at a main Positve post/block.

But you do give me the idea to think each sub feed from the main via a CB.
One of the advantages of the main panel-sub panel design is overlapping levels of overcurrent protection, and limiting the areas of an outage due to an equipment failure.

Here's an example...

Lets say that you have a main-sub panel topology in your electrical system. Lets say that you have a 50 amp breaker, feeding 6 awg wire going to a sub panel. At the sub panel you have distribution breakers feeding loads. wire sizes ranging from 10-12 awg and breakers of 15-30 amps.

You have a fault that results in a fail to operate of a distribution breaker (yes, this happens). The breaker feeding the sub panel will operate, protecting the system from a complete outage and possibly from a fire.

In a ring system, assuming the same fault, best case scenario is that you generate enough fault current to take down the entire ring, (but remember that your ring system is powering everything so its probably using something like 2/0 cable and a 200 amp breaker), this takes down everything. Worst case and in all probability you do not have enough fault current to take down the ring. In this case the ring powers the fault current and a fire results.

We haven't even started into the ease of maintaining, ease of fault isolation issues yet.

There are reasons why electrical systems are designed in a star topology, and where they are designed in a ring, they employ very sophisticated protective relay equipment to protect them.
__________________
Advertisement

ksanders is offline   Reply With Quote
Old 04-14-2012, 04:59 PM   #102
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,928
Quote:
Originally Posted by ksanders View Post
One of the advantages of the main panel-sub panel design is overlapping levels of overcurrent protection, and limiting the areas of an outage due to an equipment failure.

Here's an example...

Lets say that you have a main-sub panel topology in your electrical system. Lets say that you have a 50 amp breaker, feeding 6 awg wire going to a sub panel. At the sub panel you have distribution breakers feeding loads

You have a fault that results in a fail to operate of a distribution breaker (Yes, this happens). The breaker feeding the sub panel will operate. protecting the system from a complete outage and possibly from a fire.

In a ring system, best case scenario is that you generate enough fault current to take down the entire ring. this takes down everything. worsst case you do not have enough fault current to take down the ring. In this case the ring powers the fault current and a fire results.

We haven't even started into the ease of maintaining, ease of fault isolation issues yet.

There are reasons why electrical systems are designed in a star topology, and where they are designed in a ring, they employ very sophisticated protective relay equipment to protect them.
Good points....I may do just that... but I will say that I'm leary of CBs...they work for a dead short...most of the time.. but their failure rate in high amperage situations that aren't dead shorts resulting in hot wires/fires is just to high for my liking. So I'm not sure what I'll do.

Plus, I'm not sure of your example where a fault between a fixture and the sub-panel wouldn't trip a breaker/fuse and who care about the ring circuit unless it dead shorts?
__________________

psneeld is offline   Reply With Quote
Old 04-14-2012, 06:12 PM   #103
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 3,956
Quote:
Originally Posted by psneeld View Post
Good points....I may do just that... but I will say that I'm leary of CBs...they work for a dead short...most of the time.. but their failure rate in high amperage situations that aren't dead shorts resulting in hot wires/fires is just to high for my liking. So I'm not sure what I'll do.

Plus, I'm not sure of your example where a fault between a fixture and the sub-panel wouldn't trip a breaker/fuse and who care about the ring circuit unless it dead shorts?
OK, lets take your post and take an example from it.


Assume a 12 volt DC system, 12 awg wire, 20 amp breaker feeding a load.

Create a short at the equipment. For calculations assume that the short including the resistance of the 12 awg wire is .1 ohm. Assume for calculations that the panel feeding the wire has zero resistance (we call this an infinite buss in fault current studies).

Your calculated fault current will be 120 amps.

The 20 amp breaker has approx 6 times its overcurrent rating flowing through it. I do not have the time overcurrent curves for the breaker right here but a typical operate time would be in the range of say 10 miliseconds or so.

But in this case the 20 amp breaker fails to operate. It malfunctions.

Now assume that your panel with the 20 amp breaker is a sub panel off of a main panel, fed by a 50 amp breaker.

assuming no other load on the sub panel, the current through 50 amp breaker is still 120 amps. This is 2.4X the capacity of the 50 amp breaker. a typical time overcurrent curve would cause the 50 amp breaker operate in around 3 seconds.

Now take the ring system 2/0 cable, 200 amp breaker feeding the ring. its easy to see that the 200 amp breaker would never operate. I promise you thast 120 amps flowing through a 12 awg wire will quickly get hot enough to start a fire.

This concept of overlapping overcurrent protection is a industry standard in electrical equipment design for good reason.

The only way a ring system makes any electrical sense is if every tap off of the ring is to a sub panel, with the very first thing being an intermediate overcurrent protection device. Anything other than that is risking an uncontrolled overcurrent and all the hazards that come with it.

If you think about it, you have the same hazards by having a gigantic main panel on a boat, and having every load tied directly to it. A better design would be to logically divide the load on the main panel into mini sub panels for example.
ksanders is offline   Reply With Quote
Old 04-14-2012, 06:21 PM   #104
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,928
Quote:
Originally Posted by ksanders View Post
OK, lets take your post and take an example from it.


Assume a 12 volt DC system, 12 awg wire, 20 amp breaker feeding a load.

Create a short at the equipment. For calculations assume that the short including the resistance of the 12 awg wire is .1 ohm. Assume for calculations that the panel feeding the wire has zero resistance (we call this an infinite buss in fault current studies).

Your calculated fault current will be 120 amps.

The 20 amp breaker has approx 6 times its overcurrent rating flowing through it. I do not have the time overcurrent curves for the breaker right here but a typical operate time would be in the range of say 10 miliseconds or so.

But in this case the 20 amp breaker fails to operate. It malfunctions.

Now assume that your panel with the 20 amp breaker is a sub panel off of a main panel, fed by a 50 amp breaker.

assuming no other load on the sub panel, the current through 50 amp breaker is still 120 amps. This is 2.4X the capacity of the 50 amp breaker. a typical time overcurrent curve would cause the 50 amp breaker operate in around 3 seconds.

Now take the ring system 2/0 cable, 200 amp breaker feeding the ring. its easy to see that the 200 amp breaker would never operate. I promise you thast 120 amps flowing through a 12 awg wire will quickly get hot enough to start a fire.

This concept of overlapping overcurrent protection is a industry standard in electrical equipment design for good reason.

The only way a ring system makes any electrical sense is if every tap off of the ring is to a sub panel, with the very first thing being an intermediate overcurrent protection device. Anything other than that is risking an uncontrolled overcurrent and all the hazards that come with it.
OK...I'm not sure a lot of boats are really set up to your standard...especially when it comes to high amp loads like windlasses, bow thrusters...but I see and like your pointing out the redundancy of a 50 amp panel feeding much more than it is usually tasked for.
psneeld is offline   Reply With Quote
Old 04-15-2012, 06:54 AM   #105
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,534
"but I will say that I'm leary of CBs...they work for a dead short...most of the time.. but their failure rate in high amperage situations that aren't dead shorts resulting in hot wires/fires is just to high for my liking."


That's why they sell fuses. Cheap , easy to trouble shoot or replace.

Fast as you want , just pick the correct ones.

FF
FF is offline   Reply With Quote
Old 04-15-2012, 07:57 AM   #106
Guru
 
Anode's Avatar


 
City: Missourah
Country: USA
Vessel Name: M/V Scout
Vessel Model: Sundowner Tug 30'
Join Date: Jul 2010
Posts: 645
It's completed now but here's a 'work in progress' pic of the BlueSea breaker panel I added. I needed some additional breakers for our add ons and did not want to replace the original AC/DC panel.
Fed off the main lugs in the original panel and located in the helm station.
Attached Thumbnails
Click image for larger version

Name:	SDC10480.jpg
Views:	49
Size:	69.5 KB
ID:	10927  
__________________
Chip

Deliveries & Yacht Services
www.captainchip.com
Anode is offline   Reply With Quote
Old 04-17-2012, 01:54 PM   #107
Guru
 
Phil Fill's Avatar
 
City: Everett Wa
Country: US
Vessel Name: Eagle
Vessel Model: Roughwater 58 pilot house
Join Date: Oct 2007
Posts: 2,919
Quote:
Originally Posted by RT Firefly View Post
Greetings,
I fully agree with Mr. psneed and to add, ABYC "codes" are nothing of the sort. They are GUIDELINES or SUGGESTIONS so as to provide a comparison with voluntarily accepted practices. If they had ANY basis in law, the vast majority on board here would have to re-wire!
A good surveyor should apply a certain amount of discretion when passing judgement.
Definition for code - Oxford Dictionaries Online (US English)
I agree they are guidelines that insurance and surveyors do follow. Its up to the owner if the boat meets the guidelines, its up the insurance company if they want to insure and/or a buyer if they want to buy. Since bring the Eagle up to ABYC guidelines the Eagle is saver and I sleep better.
Phil Fill is offline   Reply With Quote
Old 04-17-2012, 05:38 PM   #108
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,928
Quote:
Originally Posted by Phil Fill View Post
I agree they are guidelines that insurance and surveyors do follow. Its up to the owner if the boat meets the guidelines, its up the insurance company if they want to insure and/or a buyer if they want to buy. Since bring the Eagle up to ABYC guidelines the Eagle is saver and I sleep better.
If you think just meeting ABYC or USCG standards makes a safe boat....yeowwwwww!!!!

And meeting those standards is really no big deal for someone in or around the boating business if you open a book/web page or two...
psneeld is offline   Reply With Quote
Old 04-17-2012, 08:04 PM   #109
Enigma
 
RT Firefly's Avatar
 
City: Slicker?
Country: Bumpkin?
Join Date: Oct 2007
Posts: 9,997
Greetings,
Yup, they (ABYC USCG) are a minimum level BUT there has to be SOME benchmark somewhere. During a recent insurance survey I had to bite my tongue several times when the surveyor gentleman mentioned that such and such were not according to ABYC "code". Hey, I can more appreciate the fellow saying "This is not the safest" and giving his reason as opposed to "the code is...".
As it turns out, prior to the survey, I checked out every nook and cranny myself and found items that needed addressing which I will attend to that the surveyor never saw so some good DID come out of it all. But CODE....really!
Apologies to hfoster for the morph of the thread but hopefully you're absorbing some of this.
__________________
RTF
RT Firefly is offline   Reply With Quote
Old 04-18-2012, 06:20 AM   #110
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,534
If your boat is for work, you meet the USCG (usually Subchapter T ) requirements in full, or you dont get your inspection sticker.

Then you dont work.
FF is offline   Reply With Quote
Old 04-18-2012, 08:14 AM   #111
Guru
 
hfoster's Avatar
 
City: Cleveland
Country: USA
Join Date: Mar 2012
Posts: 515
RTF. No apologies is needed My Friend. This is what the froum is about, kicking ideas around and everyone having a input. Some good always comes out in the end. Yes I am absorbing all the info that is being brought forth. All of it is great stuff.

Thanks!

H.Foster
hfoster is offline   Reply With Quote
Old 04-18-2012, 10:35 AM   #112
Guru
 
Phil Fill's Avatar
 
City: Everett Wa
Country: US
Vessel Name: Eagle
Vessel Model: Roughwater 58 pilot house
Join Date: Oct 2007
Posts: 2,919
Quote:
Originally Posted by psneeld View Post
If you think just meeting ABYC or USCG standards makes a safe boat....yeowwwwww!!!!

And meeting those standards is really no big deal for someone in or around the boating business if you open a book/web page or two...




I did not say it made the Eagle a SAFE boat. What I said it made the Eagle a safer boat. Well if I did not spell SAFER as saver. The audit had 19 recomendations which quoted the ABYC guideline not met. It took about 20 hours and 3 grand in 60 days to meet the guidlines, if I wanted insurance. So it can be a big deal.
Phil Fill is offline   Reply With Quote
Old 04-18-2012, 11:16 AM   #113
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,928
20 hours in 60 days? Sounds like my winter work schedule...
psneeld is offline   Reply With Quote
Old 04-18-2012, 12:29 PM   #114
Guru
 
Phil Fill's Avatar
 
City: Everett Wa
Country: US
Vessel Name: Eagle
Vessel Model: Roughwater 58 pilot house
Join Date: Oct 2007
Posts: 2,919
Quote:
Originally Posted by psneeld View Post
20 hours in 60 days? Sounds like my winter work schedule...

Have you ever tried to schedule a marine electrician and a diesel mechanic the middle of July? It was not my 20 hours but the 3 grand for the electrician and mechanic.
Phil Fill is offline   Reply With Quote
Old 04-22-2012, 12:29 PM   #115
Guru
 
hfoster's Avatar
 
City: Cleveland
Country: USA
Join Date: Mar 2012
Posts: 515
Just want to say Thanks to everyone for all your input. I was very helpful

THANKS!

H Foster
hfoster is offline   Reply With Quote
Old 04-22-2012, 12:47 PM   #116
Art
Guru
 
Art's Avatar
 
City: SF Bay Area
Country: USA
Vessel Model: Tollycraft 34' Tri Cabin
Join Date: Feb 2011
Posts: 7,986
H - Keep us apprised on your decissions as they come to fruition! - Cheers, Art
Art is offline   Reply With Quote
Old 04-22-2012, 12:49 PM   #117
Member
 
City: Anacortes Washington
Country: U.S.A.
Vessel Name: Jupiter
Vessel Model: 42-ft. Camano Offshore
Join Date: Feb 2011
Posts: 10
Quote:
Originally Posted by psneeld View Post
Sure it will...why not? As long as every wire is fuse protected and correct size and the connections meet ABYC...what's the diff?

At least my system will be visable(traceable) for a surveyor...as opposed to a bunch of hidden wire bundles that he has no idea of what's going on when he looks at them.
Master Volt has all of the remote switching systems. ABYC cert's and EU ISO certs. New Technology is cool ,BUT the money is it worth it? KISS is cool.

Don
Don Souza is offline   Reply With Quote
Old 04-22-2012, 02:16 PM   #118
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,928
Quote:
Originally Posted by Don Souza View Post
Master Volt has all of the remote switching systems. ABYC cert's and EU ISO certs. New Technology is cool ,BUT the money is it worth it? KISS is cool.

Don
My imagined system is way simpler than whats there now...and I never imagined remote switching systems...just sub-panels instead of long wire runs and wire bundles that you can't find do-do in.
psneeld is offline   Reply With Quote
Old 04-22-2012, 06:32 PM   #119
JAT
Guru
 
JAT's Avatar
 
Country: US
Vessel Name: Just a Tinch
Vessel Model: Gulfstar 44 MC
Join Date: Jan 2010
Posts: 595
Quote:
Originally Posted by FF View Post
Dockage at $5.00 a ft in many areas is a big money pit. FF
Oh, please tell me where I can find dockage at $5.00 a foot!! I last paid over $9.00 a foot and $12.00 a foot.....
JAT is offline   Reply With Quote
Old 04-22-2012, 07:28 PM   #120
JAT
Guru
 
JAT's Avatar
 
Country: US
Vessel Name: Just a Tinch
Vessel Model: Gulfstar 44 MC
Join Date: Jan 2010
Posts: 595
I think the Flemings are really great looking boats, well built, and hold their value pretty well...if the owner decides to sell.

My only issue with these boats, as with many other makes...is that they are not American made... I know for some people this may be a non-issue, but for me it is a touchy one.... I prefer American made products, and yes I will pay more for them. Why? Quality control, warranty, service, and all the rest.

We liveaboard our Guflstar 44 MC...built in St Petersburg, Fl...and she is well built. I guess if I was going to buy a new boat, as in really NEW...I would be looking to Hatteras or Mainship...

I guess I'm just tired of the "Made in China" label.......
__________________

JAT is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 06:05 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012