Old 02-19-2015, 11:30 AM   #21
Member
 
City: Comox b c
Country: canada
Join Date: Jan 2015
Posts: 13
Sight tubes in the engine room are a weak spot for fires IMHO . They may get brittle of crack and voila you could have a problem . I just have a good dip stick handy , doesn't hurt to put some water paste on it once and a while too for an added bonus . Of course some tanks you can't dip .
__________________
Advertisement

west coast troller is offline   Reply With Quote
Old 02-19-2015, 01:57 PM   #22
Scraping Paint
 
City: -
Country: -
Join Date: Oct 2007
Posts: 13,748
I think the only way a sight tube on a diesel tank could be a fire hazard is if you already have a fire going. If a sight tube cracks or breaks under normal circumstances all that will happen is a few cups of fuel will end up in the bilge. This is assuming, of course, that the operator is smart enough to keep the valves on the sight tube closed at all times other than when checking the amount of fuel in the tank.
__________________

Marin is offline   Reply With Quote
Old 02-19-2015, 03:01 PM   #23
Guru
 
LarryM's Avatar
 
City: League City, TX
Country: USA
Vessel Name: Pelago
Vessel Model: Wellcraft 3300 Coastal
Join Date: Aug 2011
Posts: 843
Quote:
Originally Posted by Marin View Post
I think the only way a sight tube on a diesel tank could be a fire hazard is if you already have a fire going. If a sight tube cracks or breaks under normal circumstances all that will happen is a few cups of fuel will end up in the bilge. This is assuming, of course, that the operator is smart enough to keep the valves on the sight tube closed at all times other than when checking the amount of fuel in the tank.
Actually, if true 'gauge cocks' are used in the sight tube installation, the lower valve contains a ball-check valve to prevent fluid from escaping if the tube is broken. It also provides a drain for servicing. Penberthy is one of the popular suppliers. The valves are sold in upper/lower sets. An added benefit is that they have 4 ears that allow ss guard rods to be installed to protect the tubes. A little expensive, but in the grand scheme of things, fly stuff.



As Marin stated though, best practice is to run with the valves closed, at least the lower valves.

I gotta try to remember that one . . . . . . . like seacocks
__________________
Larry
M/V Pelago
LarryM is offline   Reply With Quote
Old 02-19-2015, 03:11 PM   #24
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,887
For those leery of sight gauges, but have fuel fills not straight enough for a hard dip stick can possibly use a sounding tape.

It's nothing more than a very flexible tape measure with a weight on it.
psneeld is offline   Reply With Quote
Old 02-21-2015, 07:23 AM   #25
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,524
IF a stick or tape can be used to read a tank, remember there are shmeer on compounds that will tell you how deep the water in the bottom of the tank is.

Many fuel pickups are raised a couple of inches , so one never knows till the water gets rough.
FF is offline   Reply With Quote
Old 02-21-2015, 09:25 AM   #26
Guru
 
Steve's Avatar
 
City: Thibodaux, Louisiana
Country: USA
Vessel Name: Gumbo
Vessel Model: 2003 Monk 36
Join Date: Oct 2007
Posts: 3,607
Check the position of the valves, off, as they should be except when checking the fuel level. Then open, check the level and close. I guess spring loaded, turn to open, close automatically valves may available.
In a fire this tube will surely melt but probably so will the engine supply and return hoses and their valves will usually be open, not to mention the jugs of engine oil.
Attached Thumbnails
Click image for larger version

Name:	Port fuel sight tube.JPG
Views:	74
Size:	68.0 KB
ID:	37594  
__________________
Steve W.
http://mvgumbo.blogspot.com/
Steve is offline   Reply With Quote
Old 02-21-2015, 10:11 AM   #27
Guru
 
Codger2's Avatar
 
City: San Diego
Country: US
Vessel Name: "Sandpiper"
Vessel Model: 2006 42' Ocean Alexander Sedan
Join Date: Oct 2007
Posts: 5,420
Quote:
Originally Posted by Steve View Post
I guess spring loaded, turn to open, close automatically valves may available.
"Push" to open valves have been around for a long time. The photo below is 7 years old.
Attached Thumbnails
Click image for larger version

Name:	Auto set valve on sight gauge.jpg
Views:	72
Size:	98.1 KB
ID:	37596  
__________________
Codger2

My passion for improving my boat(s) exceeds my desire to constantly cruise them.
Codger2 is offline   Reply With Quote
Old 02-21-2015, 11:04 AM   #28
Guru
 
City: gulf coast
Country: pinellas
Join Date: Jun 2014
Posts: 2,199
Those simple arm type gauges are actually fairly accurate if you know how to use them. What they are really is repeatable. that is every time the fuel is the same level in the tank they will give the same readout.
Mine were marked in 1/8 tank intervals but it was easy to interpolate to 1/16 tank. Knowing the tank capacity I could figure how much fuel was used. The key was to calibrate the gauges as I filled the tanks. e.g. If they read half full I would measure how much fuel it took to fill them form that point on it always took the same amount from half full.


You can easily do the same from any level . Then I could easily predict how much fuel I needed or how much fuel I had used on a trip. Lots simpler and cheaper than flow scans and good enough for me.
bayview is offline   Reply With Quote
Old 02-21-2015, 11:34 AM   #29
Senior Member
 
Old deckhand's Avatar
 
City: Sitka
Country: Same
Vessel Model: Transpacific Marine Eagle 32
Join Date: Dec 2014
Posts: 497
Another vote for tank tenders and sight tubes.
Old deckhand is offline   Reply With Quote
Old 02-21-2015, 12:26 PM   #30
Guru
 
Codger2's Avatar
 
City: San Diego
Country: US
Vessel Name: "Sandpiper"
Vessel Model: 2006 42' Ocean Alexander Sedan
Join Date: Oct 2007
Posts: 5,420
Quote:
Originally Posted by markpierce View Post
I use a flow scan to monitor fuel use/rate and the tank tender to measure the levels in the six fuel and water tanks.
__________________
Codger2

My passion for improving my boat(s) exceeds my desire to constantly cruise them.
Codger2 is offline   Reply With Quote
Old 02-21-2015, 12:35 PM   #31
Guru
 
Codger2's Avatar
 
City: San Diego
Country: US
Vessel Name: "Sandpiper"
Vessel Model: 2006 42' Ocean Alexander Sedan
Join Date: Oct 2007
Posts: 5,420
Quote:
Originally Posted by N4712 View Post
They're are way more accurate solutions out such as Maretrons. No need for those big pulse dampeners either.
Although my 32' Halvorsen has a FloScan, it's not the easiest thing to calibrate...no matter what anyone says. In my (new to me) boat, the addition of the multi tank "Tank Tender" is most welcome! Other than a sight tube, the "Tank Tender" is the most accurate devise out there. (Dip sticks not withstanding.) MY OA 42 has both.
__________________
Codger2

My passion for improving my boat(s) exceeds my desire to constantly cruise them.
Codger2 is offline   Reply With Quote
Old 02-21-2015, 12:37 PM   #32
Guru
 
Heron's Avatar
 
City: Cypress Landing Marina (NC)
Country: USA
Vessel Name: Heron (2)
Vessel Model: '88 Cape Dory 28 Flybridge #115
Join Date: Nov 2014
Posts: 1,078
Question on the Flosan.....Since there is a return line, is there a way of calibrating these to somewhat accurately measure Accurate fuel usage since some is being returned to the tank?? Or is installation in the final feed line accurate?

I have mechanical float gauges on both tanks...One easy to read through a glass port in the settee foor, the other I have to pull some panels to see. Not a big deal, and they appear pretty accurate, but i am curious on the Floscan.
__________________
Steve
Heron is offline   Reply With Quote
Old 02-21-2015, 12:54 PM   #33
Guru
 
Codger2's Avatar
 
City: San Diego
Country: US
Vessel Name: "Sandpiper"
Vessel Model: 2006 42' Ocean Alexander Sedan
Join Date: Oct 2007
Posts: 5,420
Quote:
Originally Posted by Heron View Post
Question on the Flosan.....Since there is a return line, is there a way of calibrating these to somewhat accurately measure Accurate fuel usage since some is being returned to the tank??
This is done automatically in the FloScan's algorithm. The hardest thing to accomplish is an accurate calibration of the "fuel used." Instructions came with the unit for the calibration procedure but do to my limited ability to comprehend instructions, I never achieved the 1% accuracy that FF speaks of. Although it sounds neat, I would never buy another one.
Attached Thumbnails
Click image for larger version

Name:	DSCN1156.JPG
Views:	66
Size:	52.3 KB
ID:	37603  
__________________
Codger2

My passion for improving my boat(s) exceeds my desire to constantly cruise them.
Codger2 is offline   Reply With Quote
Old 02-21-2015, 01:53 PM   #34
Guru
 
N4712's Avatar
 
City: South FL
Country: U.S.A
Vessel Name: Oliver
Vessel Model: Nordhavn 47 Hull# 12
Join Date: Apr 2013
Posts: 3,613
Quote:
Originally Posted by Codger2 View Post
Although my 32' Halvorsen has a FloScan, it's not the easiest thing to calibrate...no matter what anyone says. In my (new to me) boat, the addition of the multi tank "Tank Tender" is most welcome! Other than a sight tube, the "Tank Tender" is the most accurate devise out there. (Dip sticks not withstanding.) MY OA 42 has both.

Yes that's what's nice about the maretron's. They make them super simple to calibrate. Google Maretron FFM-100 Manual to get and idea
__________________
Thanks, Oliver
M/V Oliver
Nordhavn 47 Hull #12
N4712 is offline   Reply With Quote
Old 02-21-2015, 01:56 PM   #35
Guru
 
N4712's Avatar
 
City: South FL
Country: U.S.A
Vessel Name: Oliver
Vessel Model: Nordhavn 47 Hull# 12
Join Date: Apr 2013
Posts: 3,613
Quote:
Originally Posted by Heron View Post
Question on the Flosan.....Since there is a return line, is there a way of calibrating these to somewhat accurately measure Accurate fuel usage since some is being returned to the tank?? Or is installation in the final feed line accurate?



I have mechanical float gauges on both tanks...One easy to read through a glass port in the settee foor, the other I have to pull some panels to see. Not a big deal, and they appear pretty accurate, but i am curious on the Floscan.

Yep, the Maretrons measure both sides. Cool thing is you can set the display up to display any combination of numbers you want like return amount NMPG, etc. The Maretron flow sensors even have temp sensors in them.
__________________
Thanks, Oliver
M/V Oliver
Nordhavn 47 Hull #12
N4712 is offline   Reply With Quote
Old 02-21-2015, 02:07 PM   #36
Guru
 
Heron's Avatar
 
City: Cypress Landing Marina (NC)
Country: USA
Vessel Name: Heron (2)
Vessel Model: '88 Cape Dory 28 Flybridge #115
Join Date: Nov 2014
Posts: 1,078
Quote:
Originally Posted by N4712 View Post
Yep, the Maretrons measure both sides.
Ah...I see. They have a flowmeter on the return leg as well...

__________________
Steve
Heron is offline   Reply With Quote
Old 02-21-2015, 03:32 PM   #37
Master and Commander
 
markpierce's Avatar
 
City: Vallejo CA
Country: USA
Vessel Name: Carquinez Coot
Vessel Model: 2011 Seahorse Marine Coot hull #6
Join Date: Sep 2010
Posts: 10,262
Quote:
Originally Posted by Codger2 View Post
This is done automatically in the FloScan's algorithm. The hardest thing to accomplish is an accurate calibration of the "fuel used." Instructions came with the unit for the calibration procedure but do to my limited ability to comprehend instructions, I never achieved the 1% accuracy that FF speaks of. Although it sounds neat, I would never buy another one.
I didn't even attempt to calibrate the FloScan. Actual fuel consumption is about 70% of that displayed, so I just use mental arithmetic.






FloScan factors both fuel to engine and well as the return to tank, so there are two measuring devices for the engine.


__________________
Kar-KEEN-ez Koot
markpierce is offline   Reply With Quote
Old 04-21-2015, 07:24 PM   #38
Veteran Member
 
City: Camano island wa
Country: usa
Vessel Name: Pert'Near
Vessel Model: hershine 37
Join Date: Nov 2013
Posts: 29
sight tubes

We bought a trawler about 9 months ago. Though she is work in progress she is functional and we have taken numerous short day and weekend trips locally learning our new boat. Her twin tanks approx. 400 gallons were filled upon us receiving the boat. I have been watching the sight glasses pretty regularly and became concerned when they didn't show the fuel usage I figure we were using knowing how many hours I had run the engine. I had checked the valves at the top and bottom more than once to ensure they were open. This weekend while in the engine room checking things over I reached over and thumped the fuel tanks. To my horror they sounded really empty still showing about 3/4 full in the sight tubes in both tanks. I shut the valves drained the sight tubes and reconnected them. turned the valves on and low and behold they show about 1/8 full each tank. I am confused how can sight gauges be that far off. Do I have a venting issue. Ideas anyone? Considering a alternate fuel monitoring system that doesn't require going to the engine room to look. But I figured the sight glasses were probably the most accurate way to go and it never hurts to take a peek in the bilge.
jetmech59 is offline   Reply With Quote
Old 04-21-2015, 08:34 PM   #39
Guru
 
hmason's Avatar
 
City: Westport, CT
Country: USA
Vessel Name: Magic
Vessel Model: Grand Banks 46 Europa
Join Date: Aug 2013
Posts: 1,901
Sight glasses are accurate. They require that both the top valve and bottom valve be open at the same time to get a reading. At times valves are installed incorrectly and it may appear to be in the open position when in fact it's closed. So, "open" the bottom valve and then open and close the top valve to see if you get a reading in one of the positions. If not, change the position of the bottom valve and repeat the top valve routine. You should get a reading. If not, you probably have a clog in one of the valves. The sight glasses do not depend on a vent to operate. Good luck.
__________________
Howard
Magic, 1996 Grand Banks Europa
Westport, CT and Stuart, FL
hmason is offline   Reply With Quote
Old 04-21-2015, 08:48 PM   #40
Scraping Paint
 
City: -
Country: -
Join Date: Oct 2007
Posts: 13,748
Quote:
Originally Posted by jetmech59 View Post
I figured the sight glasses were probably the most accurate way to go and it never hurts to take a peek in the bilge.
They are. So as Hmason suggests, you have some sort of problem with the valves on the sight tubes or you are positioning them incorrectly.

They should be closed at all times unless you are actually taking a reading. This is to prevent a fuel spill into the bilge of your boat if a tube cracks, splits, or breaks and having that fuel pumped overboard by the bilge pump(s) and netting you a big fine if the spill is traced back to you.

When you want to know how much fuel is in a tank, open the valves at each end of the tube. get your reading, and then close the valves again. The fuel level in the sight tubes will not change again until you open the valves again for another reading.
__________________

Marin is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 05:12 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012