Old 05-24-2016, 01:04 PM   #41
Guru
 
City: Satsuma FL
Country: United States
Vessel Name: No Mo Trawla
Vessel Model: Hurricane SS188
Join Date: Jul 2014
Posts: 1,382
Quote:
Originally Posted by ranger42c View Post
And then there's the idea of 6V Fireflies, perhaps sometime in the future:
- 440 Ah @ 80% SOC = 352 routinely usable Ah
If I had to guess, I would rationalize the price hike for the Fireflies was due to the inability to meet demand. If they can't meet the demand for 12V batteries, why would they want to venture into the 6V arena any time soon?
__________________
Advertisement

Donsan is online now   Reply With Quote
Old 05-24-2016, 01:09 PM   #42
CMS
Veteran Member
 
City: Casco Bay
Country: USA
Join Date: Feb 2016
Posts: 69
Quote:
Originally Posted by ranger42c View Post

And then there's the idea of 6V Fireflies, perhaps sometime in the future:
- 440 Ah @ 80% SOC = 352 routinely usable Ah

-Chris
Chris,

Keep in mind that with many premium AGM batteries, such as Lifeline, Northstar or Odyssey there will usually be no difference in projected cycle life between 6V & 12V. There certainly is when you compare between a cheap garden variety flooded G-24, 27, 31, 4D or 8D batter to a 6V but not so much with AGM..

None of the 12V batteries in the mentioned sizes in flooded are really *"deep cycle" regardless of what the sticker says. (*exception Rolls & Dyno 4D/8D) when compared to the cycle life of a flooded golf cart or L-16 battery. There are also 12V golf cart batteries too, such as a the Trojan T1275, which have equal lab cycle life ratings to their 6V counterparts or double the G24, 27 & 31 cycling ratings..

The cycle life ratings of a premium 12V AGM is usually right in line with the 6V batteries from the same line up.

In other words I don't find that a Lifeline 4CT or 6CT lasts any longer than a Lifeline GPL-31 but I do find that a flooded Group 31 gets easily bested on cycle life when compared to a deep cycle GC battery.
__________________

CMS is offline   Reply With Quote
Old 05-24-2016, 01:46 PM   #43
Guru
 
ranger42c's Avatar
 
City: Maryland
Country: USA
Vessel Model: 42' Sportfish
Join Date: Aug 2013
Posts: 2,288
Quote:
Originally Posted by Donsan View Post
If I had to guess, I would rationalize the price hike for the Fireflies was due to the inability to meet demand. If they can't meet the demand for 12V batteries, why would they want to venture into the 6V arena any time soon?
Yep, Bruce said as much (not soon), so I'm not holding my breath...



Quote:
Originally Posted by CMS View Post
Keep in mind that with many premium AGM batteries, such as Lifeline, Northstar or Odyssey there will usually be no difference in projected cycle life between 6V & 12V.

The cycle life ratings of a premium 12V AGM is usually right in line with the 6V batteries from the same line up.

In other words I don't find that a Lifeline 4CT or 6CT lasts any longer than a Lifeline GPL-31 but I do find that a flooded Group 31 gets easily bested on cycle life when compared to a deep cycle GC battery.

Yep, got that. Wasn't thinking about comparing flooded to Firefly, just AGMs like the ones we have now (Odyssey).

Wasn't thinking so much abut long-term cycle life (although important) as I was about immediate Ah gain when I started my whole (almost-) plan about replacing 3XG31s with 4xGCs (probably Lifeline). Not critically necessary, but when we troll on the port engine for 6-8 hours or so, our electronics can bring the starboard bank to its knees.

And then if I do it, I might also add an inverter to that bank... for minor cooking chores (nuke, coffeemaker) and interior stereo and so forth... and I reckon extra available Ah won't hurt for that.

-Chris
__________________
South River, Chesapeake Bay
ranger42c is offline   Reply With Quote
Old 05-24-2016, 02:08 PM   #44
Art
Guru
 
Art's Avatar
 
City: SF Bay Area
Country: USA
Vessel Model: Tollycraft 34' Tri Cabin
Join Date: Feb 2011
Posts: 6,760
Quote:
Originally Posted by CMS View Post
When you consider that the other batteries should only be cycled to 50% DOD, in order to maximize cycle life, and they don't handle PSOC use nearly as well, it certainly makes a strong case for these batteries not costing as much as they may appear to, when judged only on the per unit price.

For example: (current street price from my distributors)

Three Firefly G-31's = 330Ah - At 80% DOD = 264 Usable Ah's - $486.00 X 3 = $1458.00

Four Lifeline G-31's = 420Ah - At 50% DOD = 210 Usable Ah's - $370.00 X 4 = $1480.00

Four Odyssey G-31's - 400Ah - At 50% DOD = 200 Usable Ah's - $377.00 X 4 = $1508.00

Four Northstar G-31's - 404Ah - At 50% DOD = 202 Usable Ah's - $390.00 X 4 = $1560.00
CMS I appreciate you sharing qualified expertise in this extremely interesting battery thread.

In addition to the four comparisons above that you listed do you have a fifth comparison for LA deep cycle batteries. My four in parallel house bank (used to start twin engines too) are East Penn 31's and have provided exemplary performance since 2008. I maintain them well; they are still going strong.

Thanks for input you provide! - Art
Art is offline   Reply With Quote
Old 05-24-2016, 03:12 PM   #45
Guru
 
BandB's Avatar
 
City: Fort Lauderdale
Country: USA
Join Date: Jan 2014
Posts: 9,112
CMS

Tossing one back your way. The above assumptions were all based on people drawing their batteries down and especially the advantage of Firefly as it is more conducive to a deeper draw down.

Now, what about the person who doesn't draw the batteries down. Is on either the generator or shore power at all times. What is the advantage, if any, of Firefly to this person?
BandB is online now   Reply With Quote
Old 05-24-2016, 03:29 PM   #46
Art
Guru
 
Art's Avatar
 
City: SF Bay Area
Country: USA
Vessel Model: Tollycraft 34' Tri Cabin
Join Date: Feb 2011
Posts: 6,760
Quote:
Originally Posted by BandB View Post
CMS

Tossing one back your way. The above assumptions were all based on people drawing their batteries down and especially the advantage of Firefly as it is more conducive to a deeper draw down.

Now, what about the person who doesn't draw the batteries down. Is on either the generator or shore power at all times. What is the advantage, if any, of Firefly to this person?
If I may be so bold as to answer: Nearly Nutten!

Cause... if all you use your boat for is stayen in slip for access to shore power then virtually there taint no big-bad batt-bank necessary! On other hand... if you run gen set 24/7 then little need for a big batt-bank too.

Art is offline   Reply With Quote
Old 05-24-2016, 04:07 PM   #47
Guru
 
ranger42c's Avatar
 
City: Maryland
Country: USA
Vessel Model: 42' Sportfish
Join Date: Aug 2013
Posts: 2,288
Quote:
Originally Posted by BandB View Post
CMS

Tossing one back your way. The above assumptions were all based on people drawing their batteries down and especially the advantage of Firefly as it is more conducive to a deeper draw down.

Now, what about the person who doesn't draw the batteries down. Is on either the generator or shore power at all times. What is the advantage, if any, of Firefly to this person?
Quote:
Originally Posted by Art View Post
If I may be so bold as to answer: Nearly Nutten!

Cause... if all you use your boat for is stayen in slip for access to shore power then virtually there taint no big-bad batt-bank necessary! On other hand... if you run gen set 24/7 then little need for a big batt-bank too.


Yep, the only advantage I'd see in that situation is the no-maintenance thing... and that's easily acquired with much less expensive AGMs, or Gels, or a watering system on flooded batteries...

MaineSail even has a name for this kind of usage; he calls it UPS-like. (Not the delivery company, not the University...)

-Chris


-Chris
__________________
South River, Chesapeake Bay
ranger42c is offline   Reply With Quote
Old 05-24-2016, 04:19 PM   #48
CMS
Veteran Member
 
City: Casco Bay
Country: USA
Join Date: Feb 2016
Posts: 69
Quote:
Originally Posted by BandB View Post
CMS

Tossing one back your way. The above assumptions were all based on people drawing their batteries down and especially the advantage of Firefly as it is more conducive to a deeper draw down.

Now, what about the person who doesn't draw the batteries down. Is on either the generator or shore power at all times. What is the advantage, if any, of Firefly to this person?
I think you answered your own question..

When batteries are used and hauled around as dead-lead or standby/buffer banks essentially the least expensive battery that will give you the satisfaction, the few times that you actually need them, will suffice.

The Firefly was not designed nor built to be used as a standby/buffer bank battery. It was designed to handle deep cycle PSOC use such as is often seen on cruising boats, especially sailboats, boondocking RV's and off-grid solar. I would not spend the money on any AGM for your described use unless you had a dire fitment issue that excluded flooded batteries.
CMS is offline   Reply With Quote
Old 05-24-2016, 04:50 PM   #49
CMS
Veteran Member
 
City: Casco Bay
Country: USA
Join Date: Feb 2016
Posts: 69
Quote:
Originally Posted by Art View Post
CMS I appreciate you sharing qualified expertise in this extremely interesting battery thread.

In addition to the four comparisons above that you listed do you have a fifth comparison for LA deep cycle batteries. My four in parallel house bank (used to start twin engines too) are East Penn 31's and have provided exemplary performance since 2008. I maintain them well; they are still going strong.

Thanks for input you provide! - Art
I did not include that because we are not comparing apples to apples.

When a flooded G-31 battery can handle the fast charge rates that AGM batteries do, has the charge efficiencies AGM's do and has the self discharge characteristics etc. then it would be a more apples to apples comparison.

You'll notice that I also did not compare the Firefly to the Deka G-31 AGM either because that is not a true deep cycle AGM product and has rather low lab cycle life (especially compared to the East Penn GEL). It also performs rather poorly in a PSOC application, much, much worse than Lifeline, Northstar, Firefly and Odyssey.

Also the Firefly, Lifeline, Odyssey etc. will all out cycle an EP G-31 flooded battery so if you were to run a cycles to $$ comparison you might be surprised at how expensive an EP G-31 really is when put into a cycling application.. Even East Penn rates that battery at just 350 lab cycles to 50% DOD but in the real world where we tend to abuse batteries those often turn into 65-130 cycle batteries.. The Odyssey & Northstar are rated at 400 cycles to 80% DOD and the Firefly in excess of 1000 cycles to 80% DOD. My beater Firefly has been to 10.5V/0% capacity now approx 36 times and has cycled to 80% DOD no less than 140 times and still delivers 100% of its capacity. Most probably don't find that remarkable, because they have no idea of their batteries actual Ah capacity, but until you test battery capacity as part of your career/job then you'd be shocked to see how batteries compare.

A fairer comparison would be a true deep cycle battery like a GC2, T1275, L-16 etc. etc. but they still don't have the charge efficiency nor the fast charging capability that an AGM has, so of one is looking for that, then a flooded battery is simply out of the mix.

Actual deep-cycle flooded batteries such as golf cart batteries (T105's etc.), T1275's GC12 batteries, J-305's, J-185's, J-150's, L-16's etc. (G24, 27, 31, 4D & 8D are not actually deep cycling batteries other than on the sticker) are much less money and can cycle really well but they don't do what an AGM can in terms of fast charging. Some boaters are looking for this.

If you are not looking for AGM characteristics nothing really beats a true deep cycle flooded battery in value.

Unfortunately your EP G-31's are not really a "deep cycle" battery so the 8 year life is most likely from not PSOC cycling them and keeping them charged most of the time (standby/buffer batteries). Put those batteries into a cycling/PSOC application and they are a 1-4 year, 65-130 +/- cycle battery pretty consistently.

If you are not interested in the premium features of an AGM, then there is nothing wrong with quality deep cycle flooded batteries and they are, and have always been, a tremendous value..
CMS is offline   Reply With Quote
Old 05-24-2016, 05:31 PM   #50
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 2,304
Does the number of expected cycles from a Firefly vary inversely to the DOD like it does with AGMs? Or is the number of cycles regardless of the DOD?

I guess I'm trying to get clear on the advantages. I totally get the advantage of running to a greater DOD, and I get the resulting advantage of spending more of your charging time in bulk rather than absorb. That part is all good. Beyond that, is it

1) More lifetime cycles than an AGM at any given DOD?

2) Lifetime cycle expectancy that is independent of DOD?

3) Complete or just better immunity to sulfation at PSOC?

4) Higher bulk acceptance current than AGMs?

5) Shorter absorb time because it can accept higher currents to a greater SOC than AGMs?

Thanks. This is all very interesting.
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 05-24-2016, 05:43 PM   #51
Guru
 
ranger42c's Avatar
 
City: Maryland
Country: USA
Vessel Model: 42' Sportfish
Join Date: Aug 2013
Posts: 2,288
Quote:
Originally Posted by twistedtree View Post
Does the number of expected cycles from a Firefly vary inversely to the DOD like it does with AGMs?


Not sure I understand this question to CMS, TT. Far as I know, cycle life of ALL batteries -- any chemistry, like lead acid; any format, like flooded or AGM) -- goes down as cycles at greater DoD goes up.

I think. (And I'm not sure if/how/whether that applies to LiFePO4...)

FWIW, I also think I understand Firefly batteries ARE AGMs, just the "carbon foam" part makes them different from other AGMs.

-Chris
__________________
South River, Chesapeake Bay
ranger42c is offline   Reply With Quote
Old 05-24-2016, 08:01 PM   #52
Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 2,940
I get about 5yr out of a grp 31 flooded batt in a sub-optimal duty cycle. 100-150bucks. Not worth it to spend much more unless I can be convinced they will last 10-15yrs.
Ski in NC is offline   Reply With Quote
Old 05-24-2016, 09:58 PM   #53
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 2,304
Quote:
Originally Posted by ranger42c View Post
Not sure I understand this question to CMS, TT. Far as I know, cycle life of ALL batteries -- any chemistry, like lead acid; any format, like flooded or AGM) -- goes down as cycles at greater DoD goes up.

I think. (And I'm not sure if/how/whether that applies to LiFePO4...)

FWIW, I also think I understand Firefly batteries ARE AGMs, just the "carbon foam" part makes them different from other AGMs.

-Chris
Yes, that's what I mean. Greater DOD yields fewer cycles. Smaller DOD yields more cycles. If one goes up, the other goes down - that's the inverse relationship I was referring to.

I'm guessing carbon foam behaves the same way, but don't know. What I really am trying to understand in this one regard is whether the relationship between DOD and life cycles is really different for carbon foam. There is no reason you can't take your AGMs down to 80% DOD on a regular basis, but it will yield fewer lifetime cycles. The shallower DOD you cycle to, the more cycles you get. There seems to be a heavy focus on 80% DOD with carbon foam, and I'm trying to understand what's really different, or if they are just shining a light on a well-known (well, apparently not so well known) characteristic of all LA batteries.
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 05-24-2016, 10:09 PM   #54
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 2,304
Quote:
Originally Posted by Ski in NC View Post
I get about 5yr out of a grp 31 flooded batt in a sub-optimal duty cycle. 100-150bucks. Not worth it to spend much more unless I can be convinced they will last 10-15yrs.
I have not yet tried this myself, but think there is a very strong argument in favor of Ski's approach. Basically run the batteries hard, then replace them. It all comes back to the fact that they can delivery a relatively fixed number of AH over their life. You can consume them in a large number of shallow cycles, or a small number of deep cycles, or anything in between. It's your choice.

The alternate approach is to cut the battery bank in half and double your planned DOD from 40% to 80%. You will get half the number of cycles before needing to replace the batteries, but you will have spent half the money on the batteries in the first place. And in the shorter time you own the batteries, you have 1/2 as much opportunity to trash them in other ways. And by running to 80% DOD, your charger runs more of it's time in bulk mode rather than absorb, so you get that advantage too.

One variable is how hard it is to change batteries on your boat. If it's really hard, this may be less attractive than if it's pretty straight forward. But remember, you will have half the number so it will already be half as hard.
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 05-24-2016, 10:39 PM   #55
Art
Guru
 
Art's Avatar
 
City: SF Bay Area
Country: USA
Vessel Model: Tollycraft 34' Tri Cabin
Join Date: Feb 2011
Posts: 6,760
Quote:
Originally Posted by CMS View Post

If you are not looking for AGM characteristics nothing really beats a true deep cycle flooded battery in value.

Unfortunately your EP G-31's are not really a "deep cycle" battery so the 8 year life is most likely from not PSOC cycling them and keeping them charged most of the time (standby/buffer batteries). Put those batteries into a cycling/PSOC application and they are a 1-4 year, 65-130 +/- cycle battery pretty consistently.

If you are not interested in the premium features of an AGM, then there is nothing wrong with quality deep cycle flooded batteries and they are, and have always been, a tremendous value..
Due to our extremely conservative 12 volt batt usage (120v stove/oven, fridge... etc) while anchored aboard boat it is not often that our 4 batt house bank is let to go below 60% charge and then fully recharged by gen set or engine running. We do not use a converter. And, yes... the 8 yr old EP 31 G's are a tremendous dollar value. At $100 a piece when purchased ($400 + tax eight years ago) they are currently costing me an approx. deferred cost of only $50 per year ... which is lessening in annual cost with each passing year of their use.
Art is offline   Reply With Quote
Old 05-25-2016, 06:05 AM   #56
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 14,915
It is my belief that our house batt problems will eventually be solved by recycling.

The number of coal fired cars that use a huge battery pack is increasing , and those batts all have a limited service life.

The off grid house and car folks are purchasing these old packs , disassembling 3 or 4 of them , selecting the good batts and re assembling.

I do not think it will be long before this is done as a commercial venture and 1000AH sets will be sold or rented.

As these sets are small and powerful we might own a modest house set and rent a big set for a long cruise.
FF is offline   Reply With Quote
Old 05-25-2016, 06:43 AM   #57
Guru
 
angus99's Avatar
 
City: Signal Mtn., TN
Country: US
Vessel Name: Stella Maris
Vessel Model: Defever 44
Join Date: Feb 2012
Posts: 1,049
Quote:
Originally Posted by FF View Post
The number of coal fired cars that use a huge battery pack is increasing , and those batts all have a limited service life.
You mean natural gas-fired cars, don't you? Not sure who's service area you're in, but coal only produced 4% of Florida Power and Light's total generation in 2014.
angus99 is offline   Reply With Quote
Old 05-25-2016, 07:29 AM   #58
Senior Member
 
City: Hampton, va
Country: USA
Vessel Name: Didi Mau
Vessel Model: 2003 Ocean Alexander 456
Join Date: Jul 2015
Posts: 314
CMS,

How sensitive are firefly batteries to charge voltage? It is easy to cook an AGM should something go bad in the charging system. Wet cell batteries are more resilient. What about fireflies?

Gordon
Gordon J is offline   Reply With Quote
Old 05-25-2016, 08:06 AM   #59
CMS
Veteran Member
 
City: Casco Bay
Country: USA
Join Date: Feb 2016
Posts: 69
Quote:
Originally Posted by twistedtree View Post
Does the number of expected cycles from a Firefly vary inversely to the DOD like it does with AGMs? Or is the number of cycles regardless of the DOD?
Number of cycles and how deep always drives a batteries decline. The Firefly has a design cycle life of 1000 cycles to 80% DOD and 3600 cycles to 50%. The carbon foam makes this possible. The carbon foam limits and minimizes the sulfate from hardening and clustering something that murders other batteries when PSOC cycled.



Quote:
Originally Posted by twistedtree View Post
1) More lifetime cycles than an AGM at any given DOD?
Yes because it is sulfation that is almost always the death of marine batteries.

Quote:
Originally Posted by twistedtree View Post
2) Lifetime cycle expectancy that is independent of DOD?
No.

Quote:
Originally Posted by twistedtree View Post
3) Complete or just better immunity to sulfation at PSOC?
Not immune but significantly better. All batteries create lead sulfate upon discharge, the Firefly form sulfation on the plates but unlike other batteries the sulfate left behind in PSOC cycling use is recoverable even after as much as 30+ days of PSOC cycling.

Cycle #1 - This graph is showing at cycle #1 the as new tested Ah capacity using BCI standard testing procedures for 20 hour capacity testing.

Cycle #2 - Takes the battery to 11.7V at the 20 hour discharge rate or about 25% SOC on the Firefly.

Cycle #3 - From cycle #3 through #32 the test used an 11.7V cut off voltage at the 20 hour discharge rate at 77F. The battery was then recharged with a timed 1 hour 50.6A current or .46C charge rate. You can see the PSOC cycling capacity "walk down" as sulfate forming on the plates shortens how much energy can be put back into the battery in the 1 hour duration at 50.6A.

Essentially as the PSOC cycling goes on the battery attains absorption voltage earlier in the hour, and less energy can be stored in the plates as can be seen by the walking down of "usable PSOC capacity".. You may also notice some "ping pong" effect where one cycle is a lower capacity and the next slightly higher. This is due to the slightly longer times spent at absorption voltage in the previous cycle and recovering some more of that sulfation. At cycle #3 the charger never exited bulk and 49.7Ah's out of a 50.6A charge rate was fully usable back down to 11.7V. This means a very high bulk charge efficiency.

Cycle #33 - This cycle followed a 1 hour .46C recharge but the battery was taken to 0% SOC or 10.5V (BCI bottom voltage for 20 hour test)..

Line #34 - Initial capacity test after 30 PSOC cycles to 80% DOD. This is where I thought I had the Firefly beat, but I spoke with the Firefly inventor and he told me to discharge to 10.5V once more and do another full recharge. I doubted it seeing as the battery was only at 94Ah's a loss of 16Ah's of capacity.

Line #35 - On the second capacity test the battery recovered all of it capacity with no capacity loss at all. To this day after much more of a beating that battery still has all its capacity. No other AGM battery survived this testing with all its capacity and one AGM lost 30% of its capacity or 1% per day when PSOC cycled.



Quote:
Originally Posted by twistedtree View Post
4) Higher bulk acceptance current than AGMs?
Comparable to other AGM's but the thin plate batteries (TPPL's) sometimes hold bulk an SOC percent or two longer.

Quote:
Originally Posted by twistedtree View Post
5) Shorter absorb time because it can accept higher currents to a greater SOC than AGMs?
Again comparelbe to other AGM's. The secret to the Firefly is in sulfation resistance and net cycle life.. It would have shorter absorption times than flooded because an AGM battery requires less over charging to attain 100% SOC than flooded batteries do. At .4C I can take a Lifeline to 95% SOC, from 50% SOC in just two hours even though it hit absorption at 19 minutes. The last 4%, which is critical for longevity, takes 3.5 hours. With the Firefly you can stay out of this slow charging range for longer in-between times.. AGM's in general attain and hold higher currents for longer than flooded batteries will.

Simple math with the Firefly shows that it hits absorption at approx 70-71% SOC when charged at .46C. A .46C charge rate is a massive charge rate. A 440Ah bank would need to be charged at 202A to mimic this on a boat.

The bulk to absorption point at SOC% is driven by the charge rate applied to the battery. A higher charge rate means longer times spent in absorption, if pushing above the absorption point. Early absorption is still fairly efficient but the longer you stay in absorb the less efficient it becomes. A lower charge rate means longer times in bulk. Most boats will not even have .25C to .3C in charge capability so the Firefly, or any AGM, would will stay in bulk to a higher SOC..

The benefit to the Firefly is its ability to deal with abusive PSOC use and come back to live another day. If you don't PSOC cycle your batteries then the benefit and greatest feature of the Firefly would not be taken advantage of. Batteries need to be chosen to match use and all AGM's, & GEL too, should be installed using a "system-approach" not just as a drop-in for flooded batteries, if you want to maximize your dollar spent..
CMS is offline   Reply With Quote
Old 05-25-2016, 08:08 AM   #60
CMS
Veteran Member
 
City: Casco Bay
Country: USA
Join Date: Feb 2016
Posts: 69
Quote:
Originally Posted by Gordon J View Post
CMS,

How sensitive are firefly batteries to charge voltage? It is easy to cook an AGM should something go bad in the charging system. Wet cell batteries are more resilient. What about fireflies?

Gordon
If you don't have temp compensation for all charge sources, can set absorption to 14.4V and float to 13.2V (float at 13.2V is very important) then I would not suggest buying Firefly batteries.
__________________

CMS is offline   Reply With Quote
Reply

Tags
12v, batteries, carbon foam, video

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 11:08 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012