I have two Marine Air Systems units. The forward unit is 7K and functions perfectly. The stern unit is 16K also functions perfectly, except when I start it up. After a few seconds the digital control gives an HHH code. I shut it wait 2-3 minutes, start again and it will run all day. It will cycle on and off as the temperature settings require and function perfectly. It runs cold,and cycles. If I turn the unit off and then back on it is fine. Both units run off the same raw water pump and the filter basket is clean. The mystery unit is a split unit model CSP-16K..
I have spoken to their tech service dept. They think it is a wire issue but I don't see how a wire would fix it self when you turn it on a second time.
I thought it might be the high pressure switch, but if it cycles and runs continuously after the initial try I would think that the high pressure switch is functioning.
I would appreciate some help
Thanks
__________________
Advertisement

oak is offline   Reply With Quote
Old 09-05-2014, 11:48 AM   #2
Guru
 
SCOTTEDAVIS's Avatar
 
City: Vero Beach, FL.
Country: US
Vessel Name: FIREFLY
Vessel Model: Pilgrim 40
Join Date: Nov 2012
Posts: 913
High head pressure on first start-up, check voltage (low voltage not uncommon in marinas). Check wire connections including at the breaker for good clean connections.

If the unit is getting old the initial start requirements may be more then the compressor can do until it's run some to "loosen" things up a bit. Installing a start capacitor (hard start kit) may help.


Regards,
__________________

SCOTTEDAVIS is offline   Reply With Quote
Old 09-05-2014, 11:53 AM   #3
Guru
 
City: Fort Myers
Country: USA
Join Date: Jul 2013
Posts: 956
Might want to start looking at the relay box next, possibly by cycling it the contacts make a better connection, I'd measure (volt) the line going to the compressor, before start 0 vac, then when thermostat is called in should read 120vac. Do you have a manual with the wiring schematic, if not maybe manufacture could email you that page?
Just a thought off the top of my head, I'm not an A/C expert by no means.
Marlinmike is offline   Reply With Quote
Old 09-05-2014, 11:58 AM   #4
oak
Member
 
oak's Avatar
 
Join Date: Feb 2014
Posts: 19
Thanks for the quick reply
Boat at my home dock and voltage is ok
I will check the breaker for any corrosion
However I have never heard of a hard start kit capacitor
Would this be a Marine Air Systems product?
oak is offline   Reply With Quote
Old 09-05-2014, 01:47 PM   #5
oak
Member
 
oak's Avatar
 
Join Date: Feb 2014
Posts: 19
Did some research on hard start kit
Seems very logical
I will try and let you know
oak is offline   Reply With Quote
Old 09-05-2014, 08:30 PM   #6
Guru
 
City: North Charleston, SC
Country: USA
Join Date: Sep 2010
Posts: 4,390
Quote:
Originally Posted by oak View Post
Boat at my home dock and voltage is ok
You need to check the voltage under load and specifically under the load of the AC when starting. Connect your meter (an analog meter will work best for this) and have someone start the unit. Look for a short term voltage drop. Do this at the power pedestal first and if you don't see a voltage drop, connect the meter to the power leads at the AC unit and repeat the test. If you now see a voltage drop, the problem is with the shorepower cord or connectors or the boat's wiring.

Since wire won't get smaller on it's own, the problem would be with one or more connections in the circuit.
rwidman is offline   Reply With Quote
Old 09-06-2014, 01:58 AM   #7
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,422
The air flow over the condenser isn't blocked or restricted in any way is it?

Have you tried switching control panels?
Capt.Bill11 is offline   Reply With Quote
Old 09-06-2014, 11:19 AM   #8
oak
Member
 
oak's Avatar
 
Join Date: Feb 2014
Posts: 19
The air flow over condenser is clear. The bow unit starts with no problem.
When I get a second hand I will check the voltages, if not an issue
I will look into switching the bow control to the stern
oak is offline   Reply With Quote
Old 09-08-2014, 10:06 PM   #9
Senior Member
 
City: Marathon
Country: Usa
Vessel Name: silver gift
Vessel Model: 45 jefferson
Join Date: Nov 2013
Posts: 202
Get a hard start relay. Two wire hookup to start cap. Will give start cap and comp a good starting voltage if low and is better when the unit short cycles. Check any a/c ,appliance repair shop,or granger. Also see if wires are cooked at relay ,comp ,or cap.
__________________

Deckape is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 07:45 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012