Go Back   Trawler Forum > Trawler Forum > General Discussion
Click Here to Login


Reply
 
Thread Tools Search this Thread Display Modes
 
Old 06-13-2019, 05:50 PM   #1
Senior Member
 
Turner's Avatar
 
City: Biloxi
Join Date: Mar 2017
Posts: 160
50 amps coming OUT of pedistal end of power cord when power cord is plugged into boat

We have a Trace inverter with battery charger model #U2512SB. It is feeding back power to the slip pedistal. When battery charger is turned off, all is good. The inverter had a relay switch that when power cord is unplugged the inverter comes on. When the feedback reading from the power cord pedistal end was done it was plugged into the boat! Could this be caused by the battery charger? Or possibly a bad relay switch.? I do know one thing, this is a dangerous situation. Not sure how long this has been going on, it was found by accident by maintenance crew who noticed our pedistal box was hot.
Turner is offline   Reply With Quote
Old 06-13-2019, 05:58 PM   #2
Senior Member
 
Turner's Avatar
 
City: Biloxi
Join Date: Mar 2017
Posts: 160
I need to edit this post. 50 amps is a typo, power is feeding back to pedistal.
Turner is offline   Reply With Quote
Old 06-13-2019, 06:37 PM   #3
Technical Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 6,194
Definitely an unsafe situation. Suspect something is not wired correctly vs a faulty component.
Ski in NC is offline   Reply With Quote
Old 06-13-2019, 07:19 PM   #4
Guru
 
tiltrider1's Avatar
 
City: Seattle
Vessel Name: AZZURRA
Vessel Model: Ocean Alexander 54
Join Date: Aug 2017
Posts: 4,281
I believe you have a Trace SW2512. This is one of the best units ever made. In fact I wouldn’t mind buying it off of you even though it’s probably close to 20 years old. There is nothing wrong with the unit. It is programmed wrong for your use. Some how it has gotten programmed to feed power back to the grid. There is a hidden menu. You push both the red and the green button at the same time while in the menus mode. This will put you in the advanced menu were you can turn off this feature. You might be better off to pay a tec to come out and train you on this unit rather than attempting it your self. You should go on line and down load the manual if you don’t already have a copy. You will see that it is a very complex unit that does more things than you ever imagined.
tiltrider1 is offline   Reply With Quote
Old 06-13-2019, 07:37 PM   #5
Senior Member
 
Turner's Avatar
 
City: Biloxi
Join Date: Mar 2017
Posts: 160
Quote:
Originally Posted by tiltrider1 View Post
I believe you have a Trace SW2512. This is one of the best units ever made. In fact I wouldn’t mind buying it off of you even though it’s probably close to 20 years old. There is nothing wrong with the unit. It is programmed wrong for your use. Some how it has gotten programmed to feed power back to the grid. There is a hidden menu. You push both the red and the green button at the same time while in the menus mode. This will put you in the advanced menu were you can turn off this feature. You might be better off to pay a tec to come out and train you on this unit rather than attempting it your self. You should go on line and down load the manual if you don’t already have a copy. You will see that it is a very complex unit that does more things than you ever imagined.
Thank you, you made a lot of sense. We are definitely getting an electrician to come adjust it. Glad to hear nothing wrong with the unit.
Turner is offline   Reply With Quote
Old 06-13-2019, 08:13 PM   #6
Guru
 
High Wire's Avatar
 
City: Cape May, NJ
Vessel Name: Irish Lady
Vessel Model: Monk 36
Join Date: Dec 2007
Posts: 4,947
How are you determining current direction?
High Wire is offline   Reply With Quote
Old 06-13-2019, 08:52 PM   #7
Senior Member
 
Turner's Avatar
 
City: Biloxi
Join Date: Mar 2017
Posts: 160
Quote:
Originally Posted by High Wire View Post
How are you determining current direction?
We put a meter on the incoming shore power recepticle on the side of the boat while the inverter was on.
Turner is offline   Reply With Quote
Old 06-13-2019, 09:03 PM   #8
Guru
 
Lou_tribal's Avatar
 
City: Quebec
Vessel Name: Bleuvet
Vessel Model: Custom Built
Join Date: Jan 2016
Posts: 4,374
Quote:
Originally Posted by Turner View Post
We put a meter on the incoming shore power recepticle on the side of the boat while the inverter was on.
I am more wondering how you metered that 50 AMPS are going out?

L
Lou_tribal is offline   Reply With Quote
Old 06-13-2019, 09:16 PM   #9
Senior Member
 
Turner's Avatar
 
City: Biloxi
Join Date: Mar 2017
Posts: 160
Quote:
Originally Posted by Lou_tribal View Post
I am more wondering how you metered that 50 AMPS are going out?

L
That was a typo, 49 volts was reading on the boat incoming shore power recepticle, in other words it was back feeding when not plugged into the pedistal. Plug into pedistal, inverter automatically cuts off.
Turner is offline   Reply With Quote
Old 06-13-2019, 09:24 PM   #10
Guru
 
syjos's Avatar


 
City: Gig Harbor
Vessel Name: Sandpiper
Vessel Model: Bluewater 40 Pilothouse Trawler
Join Date: Nov 2012
Posts: 2,315
Quote:
Originally Posted by tiltrider1 View Post
I believe you have a Trace SW2512. This is one of the best units ever made. In fact I wouldn’t mind buying it off of you even though it’s probably close to 20 years old. There is nothing wrong with the unit. It is programmed wrong for your use. Some how it has gotten programmed to feed power back to the grid. There is a hidden menu. You push both the red and the green button at the same time while in the menus mode. This will put you in the advanced menu were you can turn off this feature. You might be better off to pay a tec to come out and train you on this unit rather than attempting it your self. You should go on line and down load the manual if you don’t already have a copy. You will see that it is a very complex unit that does more things than you ever imagined.
I agree 100%

Those older Trace inverters are rugged. They have a huge surge capacity to start motors and compressors. I had one for over 20 years without any problems. Would still have it if it was pure sine wave.

Follow tiltriders direction and you will be back in business.
syjos is offline   Reply With Quote
Old 06-13-2019, 09:58 PM   #11
Senior Member
 
Turner's Avatar
 
City: Biloxi
Join Date: Mar 2017
Posts: 160
Quote:
Originally Posted by syjos View Post
I agree 100%

Those older Trace inverters are rugged. They have a huge surge capacity to start motors and compressors. I had one for over 20 years without any problems. Would still have it if it was pure sine wave.

Follow tiltriders direction and you will be back in business.
[emoji106]
Turner is offline   Reply With Quote
Old 06-14-2019, 05:48 AM   #12
Guru
 
twistedtree's Avatar
 
City: Vermont
Join Date: Jan 2013
Posts: 10,076
You said the model is a U2512SB, which is a valid model number, so no reason to assume it's actually an SW model. They are quite different, with the U being a modified sine wave inverter, not a full sine wave like the SW. Still a good inverter nonetheless.


If you read voltage on the boat's inlet with the power cord not connected to anything, AND the inverter shuts down when you do connect shore power, then I agree there is a fault in the inverter. Perhaps a fused relay.


But diagnose it carefully since it's not uncommon to measure small voltages on devices that are actually turned off, especially older gear. If the voltage persists with a load on it, then there is a problem.


But heck, if you ran that inverter until now, it owes you nothing. Celebrate, and replace it.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 06-14-2019, 07:41 AM   #13
Technical Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 6,194
49v is not 110v, so there may be no amps behind it. If no amps (really mA) it might not be a safety problem. Just a residual from capacitance, whatever. Put a resistor across it and see what happens to the voltage. Might go to zero.
Ski in NC is offline   Reply With Quote
Old 06-14-2019, 08:05 AM   #14
Guru
 
High Wire's Avatar
 
City: Cape May, NJ
Vessel Name: Irish Lady
Vessel Model: Monk 36
Join Date: Dec 2007
Posts: 4,947
Quote:
Originally Posted by Turner View Post
That was a typo, 49 volts was reading on the boat incoming shore power recepticle, in other words it was back feeding when not plugged into the pedistal. Plug into pedistal, inverter automatically cuts off.
ok. That is a whole different situation. There should be 0 volts. Im with Ski and try putting a pig-tailed 40 watt 120v old school light bulb across the shore power cord terminals. If there is enough to make the bulb glow, then more than enough to kill.
__________________
Archie
Irish Lady
1984 Monk 36 Hull #46
Currently in Cape May, NJ
High Wire is offline   Reply With Quote
Old 06-14-2019, 10:18 AM   #15
Senior Member
 
gsholz's Avatar
 
City: Out and About
Vessel Model: Sold-GB 52 Europa, Queenship 59, Tolly 45
Join Date: Nov 2016
Posts: 484
What you are seeing is "induced" voltage, aka "ghost" voltage. A wire carrying current will induce (magnetically couple) a voltage in nearby wires. There will be very little energy behind it but you can "measure" it with a high-impedance voltmeter. What you need is a low impedance mode (low-Z) on your multimeter. Multimeters targeted at electricians typically have that mode as this is a common problem for them. There is nothing wrong with your shore power setup.
gsholz is offline   Reply With Quote
Old 06-14-2019, 02:24 PM   #16
Senior Member
 
Turner's Avatar
 
City: Biloxi
Join Date: Mar 2017
Posts: 160
Quote:
Originally Posted by twistedtree View Post
You said the model is a U2512SB, which is a valid model number, so no reason to assume it's actually an SW model. They are quite different, with the U being a modified sine wave inverter, not a full sine wave like the SW. Still a good inverter nonetheless.


If you read voltage on the boat's inlet with the power cord not connected to anything, AND the inverter shuts down when you do connect shore power, then I agree there is a fault in the inverter. Perhaps a fused relay.


But diagnose it carefully since it's not uncommon to measure small voltages on devices that are actually turned off, especially older gear. If the voltage persists with a load on it, then there is a problem.


But heck, if you ran that inverter until now, it owes you nothing. Celebrate, and replace it.
This inverter has been on this boat from the beginning, 1984. It works perfectly and so does the battery charger, after looking at the diagram, I believe it has a built in relay,. And the way it works , I think, when you plug or power the shore power in the relay shuts the inverter off. So, there is no feed back to pedistal, but if you unplug or shut power off the relay turns inverter on. Now that when voltage is at shore plug receptacle at boat. I turly believe it's been this way from the time of installation. This is to dangerous . I'm not going to play technician, I'm going to hire a professional. Thank you
Turner is offline   Reply With Quote
Old 06-14-2019, 04:08 PM   #17
Guru
 
twistedtree's Avatar
 
City: Vermont
Join Date: Jan 2013
Posts: 10,076
Quote:
Originally Posted by Turner View Post
This inverter has been on this boat from the beginning, 1984. It works perfectly and so does the battery charger, after looking at the diagram, I believe it has a built in relay,. And the way it works , I think, when you plug or power the shore power in the relay shuts the inverter off. So, there is no feed back to pedistal, but if you unplug or shut power off the relay turns inverter on. Now that when voltage is at shore plug receptacle at boat. I turly believe it's been this way from the time of installation. This is to dangerous . I'm not going to play technician, I'm going to hire a professional. Thank you

Getting help is the right thing to do if you are at all uncomfortable working on it yourself.


The U2512SB is an Inverter/Charger. Your understanding of the relay operation is pretty good. With no shore power (or gen, if so equipped), it inverts and powers loads, and the incoming AC feed is disconnected. When shore power is present, the U2512SB detects that and operates the relay, connecting all the loads directly to shore power. It also puts the inverter into charger mode, and starts to charge your batteries. When incoming AC goes away, it again disconnects, the charger stops, and the inverter resumes powering the loads. This operation is typical of most all inverter/chargers.


Unless the unit is generating a fault when you apply shore power, I suspect there is absolutely nothing wrong, and the tech who thought the pedestal was warm because of your inverter didn't really know what they were talking about. The measured voltage on the shore power inlet to the boat is just a zero current, induced voltage as described by someone earlier, and is probably harmless. But absolutely worth verifying.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 06-14-2019, 04:31 PM   #18
Senior Member
 
Turner's Avatar
 
City: Biloxi
Join Date: Mar 2017
Posts: 160
Quote:
Originally Posted by twistedtree View Post
Getting help is the right thing to do if you are at all uncomfortable working on it yourself.


The U2512SB is an Inverter/Charger. Your understanding of the relay operation is pretty good. With no shore power (or gen, if so equipped), it inverts and powers loads, and the incoming AC feed is disconnected. When shore power is present, the U2512SB detects that and operates the relay, connecting all the loads directly to shore power. It also puts the inverter into charger mode, and starts to charge your batteries. When incoming AC goes away, it again disconnects, the charger stops, and the inverter resumes powering the loads. This operation is typical of most all inverter/chargers.


Unless the unit is generating a fault when you apply shore power, I suspect there is absolutely nothing wrong, and the tech who thought the pedestal was warm because of your inverter didn't really know what they were talking about. The measured voltage on the shore power inlet to the boat is just a zero current, induced voltage as described by someone earlier, and is probably harmless. But absolutely worth verifying.
I agree with you a 100%. I m on the boat now and traveled 4hr using the inverter as usual,. But to be safe I made sure the shore power recepticle on boat was caped,. I truly believe it is working as should,. Thank you
Turner is offline   Reply With Quote
Old 06-22-2019, 04:31 AM   #19
Guru
 
Steve DAntonio's Avatar


 
City: Deltaville
Join Date: Dec 2015
Posts: 1,061
Quote:
Originally Posted by Turner View Post
I'm not going to play technician, I'm going to hire a professional. Thank you
I'm curious, how did you discover this, what made you check?

If you are calling in a tech, make sure he or she is ABYC Electrical Certified, that way you'll know they know what they are doing and not waste their time and your money, especially for something like this.

You can search for techs here https://abycinc.org/mpage/findatech

(In China, bound for Malaysia yard)
__________________
Steve D'Antonio Marine Consulting, Inc.
https://www.stevedmarineconsulting.com
Steve DAntonio is offline   Reply With Quote
Old 06-22-2019, 07:28 AM   #20
Senior Member
 
Turner's Avatar
 
City: Biloxi
Join Date: Mar 2017
Posts: 160
Quote:
Originally Posted by Steve DAntonio View Post
I'm curious, how did you discover this, what made you check?

If you are calling in a tech, make sure he or she is ABYC Electrical Certified, that way you'll know they know what they are doing and not waste their time and your money, especially for something like this.

You can search for techs here https://abycinc.org/mpage/findatech

(In China, bound for Malaysia yard)
The marina tech found it by chance. He was checking each pedistal and noticed ours was hot to touch and unplugged us. Since that time we have found a list if things that need correcting such as no switch between shore power and inverter, inverter is not grounded ( this is suspected to be where the main problem is that is causing the feed back to shore power pedistal). I'm adding a galvanic isolator on ground wire shore power plug, also replacing the shore power cord. After hours of reading these are what we have found. On the Mississippi Gulf Coast there is ONE certified marine electrician! We are on his waiting list about 3 months away. I will be correcting the issues we have found and when we come up on his list he will do a complete inspection of all the electrical. Until these changes are made inverter will not be used and will be turned off.
Turner is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 01:02 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012