Shore power issue

Every time I go to a marina that has redone there shore power using the new 30 amp outlets with GFI breaker , they keep popping when I plug in my boat , Iím fine using a non GFI shore power. Any ideas
__________________
Advertisement

Rhodewaves is offline   Reply With Quote
Old 11-03-2019, 09:11 AM   #2
Veteran Member
 
MT Nest's Avatar
 
City: PNW
Country: USA
Vessel Name: M/T Nest
Vessel Model: 1984 Monk 36 #31
Join Date: Apr 2011
Posts: 47
Check your inverter. I had the same issues and found out my inverter was wired wrong.
__________________

MT Nest is offline   Reply With Quote
Old 11-03-2019, 09:23 AM   #3
Member
 
City: Punta gorda
Country: us
Vessel Name: Rhode waves
Vessel Model: Mainship pilot 34
Join Date: Feb 2017
Posts: 24
I don’t have one, wish it was that simple

Thank you
Rhodewaves is offline   Reply With Quote
Old 11-03-2019, 09:43 AM   #4
Veteran Member
 
AKFish's Avatar
 
City: Seward, AK
Country: USA
Vessel Model: Custom 45' Steel Trawler
Join Date: Sep 2013
Posts: 74
You might find a neutral connected to the ground onboard (on the AC side). Start taking it apart where it enters the boat and work you way along the AC wiring, looking for continuity between neutral and ground (white and green). That connection between these two needs to be carried separately from load circuit all the way to the shore power pedestal, otherwise it will trip a GFCI due to ground fault. It will not trip a non-GFCI breaker.



Inverters often have a relay that makes this connection for you when they are used; opening the connection when shore power is selected so line protection works properly.
AKFish is offline   Reply With Quote
Old 11-03-2019, 09:50 AM   #5
TF Site Team
 
Bacchus's Avatar
 
City: Seneca Lake NY
Country: US
Vessel Name: Bacchus
Vessel Model: MS 34 HT Trawler
Join Date: Nov 2014
Posts: 2,922
Here is a link to a decent article about the problem.
Your best bet is to solve the issue on the boat as more and more marinas will be moving in this direction.
As the article states inverters and neutral to ground connections aboard are common sources of the problem.

http://magazine.boatus.com/publication/?m=53247&l=1#{%22issue_id%22:%22587116%22,%22view% 22:%22articleBrowser%22,%22article_id%22:%22337857 9%22}
__________________
Don
2008 MS 34 HT Trawler
"Bacchus"
Bacchus is offline   Reply With Quote
Old 11-03-2019, 09:52 AM   #6
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 8,073
RW
Short of adding an isolation transformer, there is not an easy amateur (most of us) answer as to dealing with the newer GFIC dock power setups. On our vessel we lucked out and found the correct marine electrician who really knows the ins and outs of vessel grounding as it pertains to the new dock codes.

We re-did each and every 110/240V grounding wire by taking them off the common copper strip, or wherever, and tying all to a central grounding buss bar. Then at one and only one point a ship's ground was established from this common buss. Voila, problems with "new" GFIC trips solved with no IT needed.

So in a nutshell, your entire ship's grounding system needs a careful and experienced eye applied.
sunchaser is offline   Reply With Quote
Old 11-03-2019, 10:00 AM   #7
Guru
 
CaptTom's Avatar
 
City: Southern Maine
Country: USA
Vessel Model: Prairie 36 Coastal Cruiser
Join Date: Dec 2012
Posts: 1,834
This is pretty common. Lots of information out there on boats and GFCIs. Not only the inverter, but something as simple as the little "polarity" light on the power console can cause this.

You can search and find all kinds of troubleshooting suggestions. Here's one I hadn't seen:

My boat will trip a GFCI outlet if I plug it in with the breakers on. I even went so far as to use one of those two-prong to three-prong outlet adapters, plugged into a 15A outlet, to make sure there was no current on the ground prong. One marina I was at had some high-tech system which was able to test each outlet, and it showed my boat was fine; no neutral-to-ground problems.

I've narrowed it down to leaving charger "wall warts" plugged in. I can only guess that maybe these inductive loads cause a surge, and maybe the long run along the power cord and back to the outlet somehow exaggerates it to the point that the GFCI "sees" a voltage difference between ground and neutral.

If I unplug everything, and turn the breakers on one at a time, then plug the chargers back in one at a time, I never get a GFCI trip.
CaptTom is offline   Reply With Quote
Old 11-03-2019, 10:15 AM   #8
Member
 
City: Punta gorda
Country: us
Vessel Name: Rhode waves
Vessel Model: Mainship pilot 34
Join Date: Feb 2017
Posts: 24
Thank you, I will do that tomorrow. I’m assuming I remove the shore power plug and trace the wires to where they terminate at the breaker panel inside the boat
Rhodewaves is offline   Reply With Quote
Old 11-03-2019, 10:35 AM   #9
Member
 
City: Punta gorda
Country: us
Vessel Name: Rhode waves
Vessel Model: Mainship pilot 34
Join Date: Feb 2017
Posts: 24
I have a galvanic isolator , could that be the issues
Rhodewaves is offline   Reply With Quote
Old 11-03-2019, 10:49 AM   #10
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 5,770
Do you have 1 or 2 30 amp inlets?
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you arenít one, there is no explanation possible.
Comodave is offline   Reply With Quote
Old 11-03-2019, 10:58 AM   #11
Guru
 
City: gulf coast
Country: pinellas
Join Date: Jun 2014
Posts: 2,798
Check your power cords and inlets for neutral to ground faults.
bayview is offline   Reply With Quote
Old 11-03-2019, 11:44 AM   #12
Member
 
City: Punta gorda
Country: us
Vessel Name: Rhode waves
Vessel Model: Mainship pilot 34
Join Date: Feb 2017
Posts: 24
One 30 amp outlet
Rhodewaves is offline   Reply With Quote
Old 11-03-2019, 11:44 AM   #13
Guru
 
tiltrider1's Avatar
 
City: Seattle
Country: USA
Vessel Name: AZZURRA
Vessel Model: Ocean Alexander 54
Join Date: Aug 2017
Posts: 1,516
It’s highly unlikely to be the galvanic isolator. You should contact a yard or marine electrician and have an ELCI master breaker installed. This breaker preforms the same function as the docks GFI. Once the ELCI breaker is installed you will know that your boat is not the issue.

In your case it might be as simple as a ground neutral bond but I have also see appliances that have internal failures cause this issue.
tiltrider1 is offline   Reply With Quote
Old 11-03-2019, 01:36 PM   #14
Senior Member
 
porman's Avatar
 
City: Duvall, Wa
Country: USA
Vessel Name: Beach Music II
Vessel Model: 2003 Mainship 430 Trawler
Join Date: Aug 2014
Posts: 499
Does your galvanic isolator have a test panel with green and red lights that shows ground and neutral problems? Our Mainship has one and that is our problem when plugging into GFCI shore power. Everything is fine for several seconds as the panel goes through it's tests, then the GFCI trips. The suggestion from the isolator manufacturer was to buy a new one without the test panel. They said they knew about problems with that particular isolator, which was made long before the GFCI outlets came into use. I hesitate to get rid of it because it has found shore power problems three times that could have damaged our boat. Note that even if you have this type of isolator your boat could have other problems.
porman is offline   Reply With Quote
Old 11-03-2019, 01:45 PM   #15
Guru
 
Alaskan Sea-Duction's Avatar
 
City: Inside Passage Summer/Columbia River Winter
Country: USA
Vessel Name: Alaskan Sea-Duction
Vessel Model: 1988 M/Y Camargue YachtFisher
Join Date: Jul 2012
Posts: 4,811
Turn everything in the boat OFF. Hook up shore power, then start switching systems on one at a time. If a breaker pops, then that system could be your issue.
Alaskan Sea-Duction is offline   Reply With Quote
Old 11-03-2019, 02:00 PM   #16
Senior Member
 
localboy's Avatar
 
City: Lake Stevens, WA via Honolulu
Country: USA
Vessel Name: 'Au Kai (Ocean Traveler)
Vessel Model: C-Dory 25
Join Date: Sep 2019
Posts: 108
Same issue here. Plugged into the (new) dock pedestals at H dock, Friday Harbor, turn on the main breaker in the boat and snap...dock GFCI flipped instantly.


There is a new NEC code standard (Article 555.3 issued in 2011) that came into effect in2014 that requires the use of GFCI breakers at all marinas. Basically, the electricity is disconnected with 30 milliamps of ground fault leakage. This is the new standard. If a marina updated or rebuilt for whatever reason, they are now mandated to comply.

I was told it has to do with the negative ground on our boat but that's all I've gleaned. From another boater I know:
Quote:
What I found was the onboard breaker panel had the ground bus and the neutral bus connected. Separating them solved the problem.

https://www.powerandmotoryacht.com/m...to-shore-power
__________________
Aloha...Mark
localboy is offline   Reply With Quote
Old 11-03-2019, 03:26 PM   #17
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 5,770
If you only have one 30 amp inlet then I would unhook it from shorepower and turn everything off. Then ohm between neutral and ground. It should be open or no connection. If it is open then turn on circuits one at a time and see if there is a connection on any of the circuits. If there is any connection then some current can flow back on the ground wire. No current should be on the ground. If there is any then the GFCI will trip because it is looking for the exact amount of current returning on the neutral that is going out on the hot wire. If the imbalance is more than 30 mAmps for docks with individual GFCIs or 100 mAmps for docks that have one GFCI for the whole dock then the GFCI will trip. There should be no connection between the neutral and ground except at the source of power, in this case the shore power. If you have a genset then the connection between neutral and ground will be inside the genset. If you find a circuit that has a connection between neutral and ground then you know where to start looking for the problem.
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you arenít one, there is no explanation possible.
Comodave is offline   Reply With Quote
Old 11-03-2019, 03:52 PM   #18
Senior Member
 
Soo-Valley's Avatar
 
City: Gulf Islands
Country: canada
Vessel Name: Soo Valley
Vessel Model: Grand Banks 36
Join Date: Jul 2019
Posts: 179
Neutral and ground bonded onboard will cause the issue.

What I am not certain about is if reversed neutral and hot anywhere will cause a GFCI to trip. i.e a plug receptacle hot/neutral reverse will still work an appliance but may send a feed to ground too.
Soo-Valley is online now   Reply With Quote
Old 11-03-2019, 05:07 PM   #19
Guru
 
CaptTom's Avatar
 
City: Southern Maine
Country: USA
Vessel Model: Prairie 36 Coastal Cruiser
Join Date: Dec 2012
Posts: 1,834
Quote:
Originally Posted by Comodave View Post
If you only have one 30 amp inlet then I would unhook it from shorepower and turn everything off. Then ohm between neutral and ground. It should be open or no connection. If it is open then turn on circuits one at a time and see if there is a connection on any of the circuits.
I hadn't heard of this test. It seems like it would be the most thorough way to be sure. Thank you for posting it!

Even though I don't have this problem, I'm going to try it next chance I get. It's possible there is a connection between ground and neutral somewhere, but not enough current flows back through the ground to trip the breaker.
CaptTom is offline   Reply With Quote
Old 11-03-2019, 06:30 PM   #20
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 5,770
If the current flows back through the ground wire, it wonít trip a regular breaker unless you overload it. However, it will cause ESD, electro shock drowning, which is the main reason for GFCI on the docks. You could have half of your current flowing back on the ground wire and a regular breaker wouldnít care but a GFCI will trip. A common reason for this is boats with 2 shore power inlets may have the neutrals tied together so current from SP1 could flow back on SP2 neutral which will trip the GFCI. The OP only has 1 30 amp inlet so that isnít the issue here. The next most likely thing would be a ground to neutral connection somewhere on the boat. It could be a connection on the neutral bus bar or the ground bus bar or it could be a connection on an appliance. Some household appliances have internal connection from neutral to ground. That is why you start with everything off and check for a neutral to ground connection. If that is ok, then proceed one circuit at a time to find the neutral to ground connection. I use a portable extension cord with a GFCI breaker to simulate the dock. I plug the boat into the extension cord and see when it trips. Most of the docks still donít have the GFCI breakers to test the boat after you find what you think is the problem. I was working on a friends boat for this issue. He has 2 30 amp inlets. We found 4 problems that would trip the GFCI. His neutrals were all on one bus bar. His 2 voltmeters were daisy chained with the neutrals from one shore power. One of his outlets had been replaced by a PO and they swapped the neutral and ground on the outlet. And his water heater had a ground to neutral short. So just because you find one problem it may not fix the issue at a GFCI equipped dock.
__________________

__________________
Boat Nut:
If you are one there is no explanation necessary.
If you arenít one, there is no explanation possible.
Comodave is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 06:01 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012
×