Generator battery - no charger???
I have a Mainship 34T
I was under the assumption that Mainship would have wired the separate battery for the generator to the main AC battery charger. To keep the generator battery charged at all times.
My friend says no. He put in a separate trickle charger for that battery. He found this out only when his generator would not start because of the battery not charged.
Has anyone else experienced this problem. Please advise.
|
|
|
04-27-2014, 08:39 AM
|
#2
|
TF Site Team
City: Jacksonville
Join Date: Nov 2008
Posts: 11,683
|
We have no external charger for the engine and generator start batteries. They only get charged when the they are running by their own alternators. A battery in good condition should only loose about ~3 or 4%/month of it's charge at rest. In 7 years on Hobo and 10 years on the last boat, we never needed to jump start.
|
|
|
04-27-2014, 09:41 AM
|
#3
|
Guru
City: Carefree, Arizona
Vessel Name: sunchaser V
Vessel Model: DeFever 48 (sold)
Join Date: Apr 2008
Posts: 10,186
|
Our vessel has a separate Newmar charger for the engine and generator starting batteries. It is on a switch/breaker and part of the main E panel. If for some reason the inverter charger isn't operable the Newmar will charge the house banks too through the parallel switch, albeit slowly as compared to the inverter.
Lots of ways to skin a cat in the charger arena.
|
|
|
04-27-2014, 10:25 AM
|
#4
|
Guru
City: Solomons Island Md
Vessel Name: Fryedaze
Vessel Model: MC 42 (Overseas Co) Monk 42
Join Date: Sep 2011
Posts: 1,721
|
Our genset battery was not tied to the charger either. I needed space for additional house batteries so I eliminated the genset battery and tied the genset to the port engine battery that doesnt have the ability to tie to boat loads.
|
|
|
04-27-2014, 10:48 AM
|
#5
|
Technical Guru
City: Wilmington, NC
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 6,194
|
I too set up mine with gennie sharing engine batt. I find no downside to that arrangement. I also disabled the gennie charging circuit, as its regulator is very crude and tended to overcharge. With gennie running, batt gets charge from boat charger or the more precise main engine alt.
In the OP's case, I don't see any big need to add a charge link to gennie batt. Many boats run same configuration with no issue. As others have posted, without any drain the batt will maintain charge for a long time. Maybe a trickle charger (maintainer) for winter layup.
|
|
|
04-27-2014, 12:37 PM
|
#6
|
Guru
City: East Coast, Australia
Join Date: Jun 2012
Posts: 935
|
Is your genset battery the same technology as your engine start battery? If so, no problem combining the two as one 'start bank' and charging both as you do now for engine start. If your genset start battery is just a small-ish/basic thin-plate flooded auto battery, then check if your genset has a small alternator already fitted: they often/usually do for charging such a battery.
|
|
|
04-27-2014, 03:45 PM
|
#7
|
Guru
City: Ft Pierce
Vessel Name: Sold
Vessel Model: Was an Albin/PSN 40
Join Date: Oct 2011
Posts: 28,154
|
My philosophy...if your genset isn't keeping it's own battery charged.....you aren't running your genset enough and it's dying a slow death like most.
If for any reason you can't or won't run your genset...and you pickle it for 6 or more months....then I just throw a good electronic portable charger (25 amp max) on it till it says fully charged which is between 1/2 to an hour tops.
More wiring and charging circuits is just "extra stuff" in my mind for a genset...I prefer to run mine every month to make sure it's there when I need it.
|
|
|
04-27-2014, 08:20 PM
|
#8
|
Guru
City: Sarasota/Ft. Lauderdale
Join Date: Apr 2014
Posts: 5,438
|
Quote:
Originally Posted by psneeld
My philosophy...if your genset isn't keeping it's own battery charged.....you aren't running your genset enough and it's dying a slow death like most.
|
Running often it is good. But to keep a genset alive the longest, running it under the proper load is the best thing you can do for it. Most gensets die an early death not so much from non-use as from running hours and hours on end under a light load.
As to the genset battery charging issue, as others have pointed out it's not mandatory to have one but as you found out it can be nice to have. And these days a low amp output smart charger is not to expensive to get and install. And a lot of boat come with one. So if you feel more comfortable having one as a back up, go for it.
|
|
|
04-27-2014, 09:28 PM
|
#9
|
Guru
City: South FL
Vessel Name: Oliver
Vessel Model: Nordhavn 47 Hull# 12
Join Date: Apr 2013
Posts: 3,607
|
Our genny battery is a 4D and is also shared with the wing and the engine has a dedicated 8D, the engine and gen/wing batteries are charged by a separate charles charger although if it broke I could parallel them with the house and charge them like that or if they went dead.
__________________
Thanks, Oliver
M/V Oliver
Nordhavn 47 Hull #12
|
|
|
04-27-2014, 09:34 PM
|
#10
|
Senior Member
City: Everett, Wa
Vessel Name: The 6-Pack
Vessel Model: 1974 Custom Aluminum Pilothouse
Join Date: Jan 2012
Posts: 205
|
I have had the same problem. I picked up a trickle charger for the genset battery only. No problems since. It is plugged into an AC outlet. It was about $25 bucks at Wally's back by the tires and batteries: )
__________________
Jeff & Michelle
The 6-Pack
1974 Custom Aluminum Pilothouse
|
|
|
04-27-2014, 11:57 PM
|
#11
|
Guru
City: Sydney
Vessel Name: Sojourn
Vessel Model: Integrity 386
Join Date: Oct 2011
Posts: 13,333
|
I have a dedicated 25w solar panel via a basic regulator to maintain the 150ah genset battery. Full batteries are happy batteries and live longer. My Onan genset has a 35A alternator.
__________________
BruceK
2005 Integrity 386 "Sojourn"
Sydney Australia
|
|
|
04-28-2014, 05:55 AM
|
#12
|
Guru
City: Ft Pierce
Vessel Name: Sold
Vessel Model: Was an Albin/PSN 40
Join Date: Oct 2011
Posts: 28,154
|
Quote:
Originally Posted by Capt.Bill11
Running often it is good. But to keep a genset alive the longest, running it under the proper load is the best thing you can do for it. Most gensets die an early death not so much from non-use as from running hours and hours on end under a light load.
As to the genset battery charging issue, as others have pointed out it's not mandatory to have one but as you found out it can be nice to have. And these days a low amp output smart charger is not to expensive to get and install. And a lot of boat come with one. So if you feel more comfortable having one as a back up, go for it.
|
This is a highly debated topic and I doubt there's definitive proof either way.
Yes ....too light of a load isn't good...never said run it unloaded.
Also..a large chunk of the cost of gensets isn't just the engine the electrical side loves to work rather than sit and rust too.
|
|
|
04-28-2014, 12:57 PM
|
#13
|
Moderator Emeritus
City: SEWARD ALASKA
Vessel Name: DOS PECES
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 6,267
|
Quote:
Originally Posted by sunchaser
Our vessel has a separate Newmar charger for the engine and generator starting batteries. It is on a switch/breaker and part of the main E panel. If for some reason the inverter charger isn't operable the Newmar will charge the house banks too through the parallel switch, albeit slowly as compared to the inverter.
Lots of ways to skin a cat in the charger arena.
|
We have the same kind of setup.
The inverter/charger charges the house bank
We have a Charles industries 40 amp charger that charges the two start batteries, and the genset battery. With the closing of a breaker we can use it to charge the house batteries as well, but as you indicated much slower.
Redundancy is a good thing.
|
|
|
04-28-2014, 02:55 PM
|
#14
|
Guru
City: Sarasota/Ft. Lauderdale
Join Date: Apr 2014
Posts: 5,438
|
Quote:
Originally Posted by psneeld
This is a highly debated topic and I doubt there's definitive proof either way.
Yes ....too light of a load isn't good...never said run it unloaded.
Also..a large chunk of the cost of gensets isn't just the engine the electrical side loves to work rather than sit and rust too.
|
I don't think there is much debate about it. At least not among all the diesel techs, engineers and service shops I've spoken with over the years. Wet stacking, carbon build up, etc. are common results of under loading a genset. Hence the use of "night" gensets and load banks in some cases.
The kw capacity of gensets in most boats has been picked based on the potential max amp load for that vessel. And since those gensets may rarely see even 50% of that for long stretches, they end up wearing out prematurely not from lack of use, but from continual light load use.
But of course the reality is they can still run for thousands even under light load use. Just smoke a bit more while doing so. :-)
|
|
|
04-28-2014, 05:04 PM
|
#15
|
TF Site Team
City: California Delta
Vessel Name: FlyWright
Vessel Model: 1977 Marshall Californian 34 LRC
Join Date: Apr 2008
Posts: 13,728
|
Quote:
Originally Posted by Capt.Bill11
I don't think there is much debate about it. At least not among all the diesel techs, engineers and service shops I've spoken with over the years. Wet stacking, carbon build up, etc. are common results of under loading a genset. Hence the use of "night" gensets and load banks in some cases.
The kw capacity of gensets in most boats has been picked based on the potential max amp load for that vessel. And since those gensets may rarely see even 50% of that for long stretches, they end up wearing out prematurely not from lack of use, but from continual light load use.
But of course the reality is they can still run for thousands even under light load use. Just smoke a bit more while doing so. :-)
|
I think what he means is that it's highly debated by him...as are many things. You'll get used to it.
|
|
|
04-28-2014, 06:20 PM
|
#16
|
Guru
City: Sarasota/Ft. Lauderdale
Join Date: Apr 2014
Posts: 5,438
|
Thanks for the clarification.
|
|
|
04-28-2014, 06:55 PM
|
#17
|
Senior Member
City: marco island
Join Date: Apr 2012
Posts: 111
|
Psneeld
I like your Idea best
When I don't use my genset I will exercise once a month, under load ( with both AC's on), for 30 min.
Prior to turning on the generator, I will charge the battery until full with my garage charger.
Don't need any more "stuff" on board
Thanks again
|
|
|
|